[Equest-users] eQUEST Detailed Reports: Heating Equipment Efficiency Included in Space Heating & Maximum Heating Load Values?

John Aulbach jra_sac at yahoo.com
Mon Nov 18 14:32:23 PST 2013


hi sandy please forgive my phone texting challenges.

bothe the beps and the bepu are absolute end use site energy, that which would appear on an energy bill. contains allefficiency and ancillary lolads.

max space heating lolad is exactlt that,,,load.

hope that helps.

john r. aulbach, pe

----------
Sent from AT&T's Wireless network using Yahoo! Mail

------Original Message------
From: Sandy LaFlamme <slaflamme at veic.org>
To: "'equest-users at lists.onebuilding.org'" <equest-users at lists.onebuilding.org>
Date: Monday, November 18, 2013 9:37:39 AM GMT-0500
Subject: [Equest-users] eQUEST Detailed Reports: Heating Equipment Efficiency Included in Space Heating & Maximum Heating Load Values?

Does anyone know if the "Space Heating" value in MBtu/y found on the "Building Energy Performance Summary" includes the heating equipment efficiency?  Or is it calculated without including the heating system equipment efficiency?

Also, does the "Maximum Heating Load" in kBtu/y found on the "Building HVAC Load Summary" include the heating equipment efficiency?

Thank you.

Sandy

Sandra LaFlamme, PE, CEM |  Engineering  |  EFFICIENCY VERMONT
128 Lakeside Ave, Suite 401, Burlington, VT 05401
slaflamme at veic.org<mailto:slaflamme at veic.org>  |  Office: (802) 540-7797 |  Cell: (802) 233-8997



_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list