how are you controlling the erv/energy recovery? the default is for it
to run when the supply fan runs. this will cost you more in energy than
it saves. set the control method based on a delta T between the exhaust
air and the outside air you'll see the savings in cooling mode. in my
climate zone (2b/southern arizona) the best delta t i found is 27 d f.
once you set up the erv to run based on a delta t you can set up some
parametric runs (set up one & then copy & rename it in the .inp file to
save time) to try different delta t values without having to change each
hvac unit every time you want to try a different delta t.
On 11/14/13 12:30 PM, Simge Andolsun wrote:
> Dear eQuest users,
> In my models, I realized that using energy recovery in the cooling
> season always gives higher cooling energy consumption results than
> turning off the energy recovery and using economizer only instead. I
> tried using OA Heat/Cool with Bypass OA or Bypass Exhaust thinking
> that such configuration would capture the best benefit of energy
> recovery and let the outside/exhaust air bypass when economizer is
> more beneficial. Then, I read in the eQuest manuals that this
> configuration still lets the energy recovery run when it is not
> beneficial in warm months and just opens up the economizer dampers to
> compensate for the unnecessary heating of the outside air. So, the
> loss caused by the energy recovery eats up the benefit that is
> provided with the economizer.
> Thus, I thought, may be, I should use two separate files to maximize
> the benefit from both the economizer and the energy recovery. The
> first file would be for heating (with OA Heating) where the energy
> recovery would be on whenever it can heat the outside air. Then the
> second file would be for cooling where there would be no energy
> recovery but the economizer would be available whenever the outside
> air is favorable for cooling. Finally, I would get heating energy
> consumption from the heating file and the cooling energy consumption
> from the cooling file.
> The only thing that stops me from following this approach is that I am
> wondering whether there was a logical reason why bypass configurations
> of eQuest give higher cooling energy consumption than the economizer
> only case. Shouldn't they be giving exactly the same cooling energy
> consumption? Is it because part of the outside/exhaust air is being
> bypassed in the bypass configurations instead of fully? or may it be
> because it is known that setting the energy recovery and
> economizer for the best benefit is pretty hard in reality and that's
> why it was assumed that it would not function ideally? Or, is there a
> completely different reason that I do not know?
> Would you please help me with this question?
> I'd appreciate it very much.
> Thanks,
> Best Regards,
> S. Andolsun, PhD
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131114/b3a303a8/attachment.htm>
More information about the Equest-users
mailing list