[Equest-users] Question on LS-C report
    Bishop, Bill 
    bbishop at pathfinder-ea.com
       
    Tue Nov 12 08:39:33 PST 2013
    
    
  
Morteza,
The occupant and infiltration loads reported on LS-C do not have to match between baseline and proposed. Just make sure your number of occupants, infiltration rate, and schedules are the same. Total occupants is easy to compare using the LV-B report. The numbers on LS-C may not match between baseline and proposed, especially when the date/time of the peak cooling and heating loads are different.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P   Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza Kasmai
Sent: Monday, November 11, 2013 7:26 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Question on LS-C report
Hello all,
I have a question regarding figures reported for "OCCUPANTS TO SPACE" and "INFILTRATION" in LS-C Building Peak Load Components report. When we compare LS-C reports of a given project, should occupants load and infiltration load of the baseline model be equal to the same loads of the proposed model?
I would appreciate your comments,
Morteza
[https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131112/d1dde664/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131112/d1dde664/attachment.jpg>
    
    
More information about the Equest-users
mailing list