[Equest-users] NEW (?) eQUEST DOAS workaround using plenum spaces

Bishop, Bill bbishop at pathfinder-ea.com
Thu Nov 7 09:51:35 PST 2013


Nick,



Thanks for your valuable feedback! I agree that the plenum workaround I described is not ideal for all DOAS systems. In the past, I have used the option you describe below, where you don't model a separate DOAS - you just add heat recovery, additional fan power etc. to the other systems as appropriate. I came up with this workaround for a system configuration that I am starting to see frequently - a packaged DOAS (w/CHW or DX cooling and/or heat pump) supplying OA either directly to zones or to zonal systems (usually water-to-air heat pumps). Regarding your specific concerns:

  *   Overstating ventilation loads - Not sure I understand. The method I described takes the design OA cfm and preconditions it at the DOAS as designed before sending the ventilation "somewhere" (in this case, above the occupied zones), so the load is what it is. Maybe you are just restating your second concern, which is...
  *   Moving the ventilation loads - I agree. You could potentially shift a gas load to an electric heating load, or alter the diversity of heating/cooling modes in your terminal systems. I would think this would be more of a problem if the air-side has a high OA%, and/or if the DOAS supplies air at a non-zone-neutral temperature. For the first model I am trying this on, the DOAS SAT is close to room temperature, largely due to heat recovery, and the terminal units are water-to-air heat pumps which use electricity for both heating and cooling and reject/absorb heat from the same heat pump loop.
  *   Unit sizing and unmet hours - Adjusting the DESIGN-COOL-T and DESIGN-HEAT-T should help with baseline autosizing. If using eQUEST for design you would certainly use design-case space loads. Since the selection is usually larger than the peak load (manufacturers only offer incremental sizes except for custom equipment) unmet hours shouldn't be much of a problem. Again, high OA% or non-zone-neutral OA is a caveat.
  *   I wouldn't consider this another "dummy zone" workaround. Indeed, a big advantage is that you don't create any virtual (not physically part of the building) zones or virtual/estimated loads.



Thanks again,

Bill

________________________________
From: Nick Caton [ncaton at smithboucher.com]
Sent: Wednesday, November 06, 2013 5:06 PM
To: Bishop, Bill; Hall, Brendan; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] NEW (?) eQUEST DOAS workaround using plenum spaces

My past efforts at approximating DOAS and MAU (makeup air unit) setups in eQuest have sometimes paralleled the approach Bill is describing.

Some extra thoughts/cautions from my experience:

-          Common scenario:  A DOAS pre-conditions or does not condition ventilation air beyond heat recovery before supplying to the main conditioning units, which mix that OA with the return airstream and heats/cools as needed to arrive at the intended supply air conditions.

-          An important point is this approach “circumvents” typical supply air conditioning means by dumping the associated ventilation loads (after any DOAS-borne recovery & pre-conditioning) “directly” into the spaces.  This may have effects of:

o   Overstating the actual ventilation loads to be dealt with(where return/relief air would otherwise mitigate/eliminate)

o   “Moving” where ventilation loads are dealt with from a central system to terminal (zonal) units,

o   Causing the conditioned zones to call for heating/cooling where they might otherwise call for the opposite, which may throw off expected behaviors, terminal unit sizing, and in some cases may have effects on how well the main conditioning units handle the situation (i.e. unmet hours)

o   Example for illustration: Typical office building with a DOAS, furnace heated air handler which delivers 55 degree SAT, and electric reheat VAV boxes.  A core office zone might call for cooling from the main system in the winter (internal loads dominant), but the DOAS-supplied (and air wall transferred) ventilation air loads may instead turn the space into a refrigerator for the hour, so the zone thermostat would calling for heating instead… suddenly your whole building is dealing with all your wintertime ventilation heating with electricity instead of gas as anticipated.

You can try to compensate for some of these effects by moving or mirroring your main air handling conditioning sources/capacities into the DOAS system, but at some point you’re facing a potential documentation nightmare for LEED or similar…

I don’t mean to be a negative Nancy – this is the clearest procedural write-up I’ve run into for a “dummy zone” approach to DOAS behavior (more on this in the archives).

The other major alternatives to a “dummy zone” workaround are, in brief:

•         Opt to not model the DOAS system as a separate system for the simulation, and instead define its components within the served systems.  Put another way: Add heat recovery recovery/pre-conditioning/fan power/etc in proportion to the systems the DOAS serves.

•         Look to software other than eQuest if none of these approximations are acceptable.

Best regards,

~Nick


[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com<https://mail.pathfinderengineers.com/owa/UrlBlockedError.aspx>

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, November 06, 2013 2:29 PM
To: Bishop, Bill; Hall, Brendan; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] NEW (?) eQUEST DOAS workaround using plenum spaces

Correction – ceiling surfaces are created for the conditioned spaces below the plenum spaces, so the change to “air wall” is made for the space below, not in the plenum space. You do, however, need to change the plenum zones to “conditioned” in order to assign OA to them. I’m also thinking it might make sense to assign thermostat schedules to one or more DOAS plenum zones, to control whether the DOAS is in heating or cooling mode. You could use schedules with lower heating, higher cooling temps and/or larger throttling range and/or different t-stat type, in order to avoid increasing the reported unmet load hours.

~Bill

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, November 06, 2013 2:47 PM
To: Hall, Brendan; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] NEW (?) eQUEST DOAS workaround using plenum spaces

You make no changes to the plenum space geometry as it is normally created via the eQUEST wizard, except to make sure there is a ceiling, and change the ceiling surface TYPE to “Air”. I used the “Default Air Wall Construction” which has a U-value of 2.7 Btu/ft2-hr. I’m not sure about DESIGN-COOL-T and DESIGN-HEAT-T. I think you would want them to represent the DOAS SAT, so that the system(s) serving the occupied zones below can be autosized accordingly (as described in the DOE-2 help menu). I just noticed that you have to use “Adjust Loads” for the zone SIZING-OPTION for this effect to be included.

~Bill

From: Hall, Brendan [mailto:BHall at karpinskieng.com]
Sent: Wednesday, November 06, 2013 2:34 PM
To: Bishop, Bill; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: NEW (?) eQUEST DOAS workaround using plenum spaces

I’d say that is a pretty clever approach. Would you just add the geometry as a normal plenum zone with exterior/interior walls and such or would you just have them exist as plenum zones with only one heat transfer surface in common with each the zone(s) its serving? Wouldn’t you want DESIGN-COOL-T AND DESIGN-HEAT-T to be the same as the zone it is serving? Then you could set the u value of the air wall high so that any cooling or heat that the DOAS provides would then be effectively transferred into the occupied spaces. I think in that scenario it might act as a quasi supply plenum? Not sure without actually trying it. Just my first thoughts, maybe you have already considered all that and the way you described works better.


Brendan Hall,  PE, LEED AP BD+C
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH  44115
P  216.391.3700<tel:216.391.3700> Ext 3111
E  bhall at karpinskieng.com<mailto:bhall at karpinskieng.com>
W www.karpinskieng.com<http://www.karpinskieng.com/>



From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, November 06, 2013 1:17 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] NEW (?) eQUEST DOAS workaround using plenum spaces

I doubt I’m the first to think of this but I don’t recall it being discussed on the List. Simply put, you can model a DOAS system by assigning it to the plenum spaces above occupied spaces, and putting all OA loads in the plenum zones.
I propose the following workaround for modeling dedicated outdoor air systems (DOAS) in eQUEST/DOE-2.2:

-          Model all shells/floors with plenum spaces if they are served by a DOAS

-          Change the plenum zones ZONE: TYPE to “Conditioned”

-          Leave the plenum zone COOL-TEMP-SCH and HEAT-TEMP-SCH as “undefined” (no zone control over the DOAS operation)

-          Pick DESIGN-COOL-T and DESIGN-HEAT-T values for the plenum zones that match the likely DOAS supply air temperature range

-          Create the DOAS as a new SYSTEM (TYPE = [whatever is appropriate])

-          Assign the DOAS to the plenum zones above the conditioned zones that it actually serves

-          Assign outdoor air only to the plenum zones, representing the outdoor air requirement of the conditioned zones below

-          Create/modify internal walls between plenum zones and zones below, making them “Air walls”

This method has the following advantages:

-          No exceptional calcs or separate models needed (but see “Conditioned area” comment below)

-          All DOAS systems can be modeled as designed, within normal eQUEST constraints

-          A single DOAS system can supply ventilation air to multiple zones/systems

-          DOAS system operation and ventilation supply can be independent of the other systems serving the zones

-          Return air temperature to the DOAS closely follows that of the occupied zone, for accurate heat recovery simulation

-          Zonal systems “see” the space load from ventilation air that is not supplied at a “zone-neutral” temperature

-          DCV can be modeled, but people need to be assigned to the plenum spaces instead of the occupied spaces below (which might also be a disadvantage of this method)

-          No ventilation load changes need to be made to create the LEED Baseline from the Proposed design model, but the plenum zones need to be assigned to the baseline systems that serve the zones below.

…but has these disadvantages or does not solve these problems:

-          Conditioned floor area reported (such as in LS-C) is incorrect. Subtract the area served by the DOAS (as reported on SV-A).

-          Latent heat transfer is not simulated across interior walls. Ideally, latent loads should be assigned to the plenum spaces to represent the portion of non-ventilation latent loads handled by the DOAS.

-          Plenum space FLOOR-WEIGHT may need to be adjusted for realistic lag time and peak load damping (I haven’t thought this out yet)

Please discuss!

~Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[webCertified_logo_colorRGB72DPI.jpg]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 325-6004 Ext. 114            F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

P   Sustainability – the forest AND the trees. P



-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131107/a98c2f90/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131107/a98c2f90/attachment-0001.jpg>


More information about the Equest-users mailing list