[Equest-users] Slab extending through wall
    David Reddy 
    david at 360-analytics.com
       
    Tue Nov  5 14:47:54 PST 2013
    
    
  
My guess is that the 3-D thermal model uses a pretty simple surface 
convection/radiation assumption, like an air film.  To properly model 
the fin effects, the thermal model would need to be coupled with CFD and 
a radiation model to account for the more complex heat transfer effects 
associated with "fins".
On 11/5/2013 2:25 PM, Robby Oylear wrote:
> It surprises me that the report indicates a better R-value for the fin 
> effect of a concrete balcony vs. the simplified exposed slab edge 
> approach.  Seems to violate the basic teachings heat transfer 101.  I 
> can't think of a logical explanation of how that could be the case and 
> would chalk it up to intricacies of the modeling tool.  However I 
> agree with Nathan that since the report doesn't show nearly any 
> difference between the fin effect vs. the exposed slab edge that it's 
> not necessarily worth the complication in modeling unless the balcony 
> slabs are the focus of the study.
>
>
> On Tue, Nov 5, 2013 at 2:00 PM, Nathan Miller <nathanm at rushingco.com 
> <mailto:nathanm at rushingco.com>> wrote:
>
>     Kapil,
>
>     No, I am only accounting for the "face" of the balcony, as if you
>     sheared it off at the plane of the wall.
>
>     That is my point, the fancy thermal modeling in the report, which
>     is supposed to account multi-dimensional fin-effects doesn't come
>     out with much different result than if you just take a simplified
>     approach like a typical UA-trade-off calculation (one directional
>     heat transfer, no fin effects accounted for). So by that line of
>     reasoning, you would likely be OVER ESTIMATING heat loss if you
>     throw in all three heat-exchanger surfaces that you mention in
>     your methodology. I'd be interested if you compared your
>     calculation results to the thermal modeling in the report if you
>     feel like a little intellectual exercise.
>
>     *Nathan Miller **-****PE, LEED^® AP BD+C, CEM*
>
>     /Mechanical Engineer/Senior Energy Analyst /
>
>     *RUSHING*| *D*206-788-4577 <tel:206-788-4577> |*O*206-285-7100
>     <tel:206-285-7100>
>
>     *www.rushingco.com <http://www.rushingco.com/>***
>
>     *From:* Kapil Upadhyaya [mailto:KapilU at kirksey.com
>     <mailto:KapilU at kirksey.com>]
>     *Sent:* Tuesday, November 05, 2013 1:53 PM
>     *To:* Nathan Miller; Bishop, Bill; David Griffin; 'Coleman,
>     Kevin'; equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* RE: [Equest-users] Slab extending through wall
>
>     Nathan,
>
>     In the Balcony calculation, are you accounting for both the
>     'edges' and 'exposed area' of the balcony ?
>
>     In my opinion, a concrete balcony should be accounted for as a
>     heat exchanger with 3 surfaces (perimeter edges, upper surface,
>     lower surface); it looks like you are only accounting for the edges.
>
>     I had a 'heated' discussion about this with a vendor recently and
>     the above is more or less a conclusion of that. Some of the
>     structural thermal break products can be too expensive to justify
>     based on energy savings, if area of balconies is not accounted
>     for; the bigger your balcony, the better your payback from thermal
>     breaks.
>
>     Best,
>
>     *Kapil Upadhyaya, LEED AP*
>     Associate
>
>     *Kirksey* | Architecture
>     6909 Portwest Drive | Houston Texas 77024 |www.kirksey.com
>     <http://www.kirksey.com>
>     o 713 426 7508 <tel:713%C2%A0426%C2%A07508> | f 713 850 7308
>     <tel:713%C2%A0850%C2%A07308> |kapilu at kirksey.com
>     <mailto:kapilu at kirksey.com>
>
>     *2012-2013 Firm of the Year *
>     Texas Society of Architects
>
>     *From:*Nathan Miller [mailto:nathanm at rushingco.com]
>     *Sent:* Monday, November 04, 2013 5:27 PM
>     *To:* Bishop, Bill; David Griffin; 'Coleman, Kevin';
>     equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* Re: [Equest-users] Slab extending through wall
>
>     To me the most interesting part of the report isn't the conclusion
>     that thermally broken balconies and slab edges give significantly
>     better thermal performance (we all know that intuitively). Instead
>     it gives a way of back checking what I would consider to be
>     "standard practice" for calculating area-weighted U-factor for
>     these same assemblies using default ASHRAE U-values to
>     sophisticated thermal model results. Here are my thoughts,
>     checking my calcs and comments appreciated.
>
>     *Executive summary: It looks like our standard assembly
>     performance tables and area-weighted U-factor calculations get us
>     "close enough" to the results from this report that it doesn't
>     seem to suggest we should switch methodologies. *
>
>     **
>
>     *Comparison calculation for steel-framed walls (stud insulation +
>     exterior rigid):*
>
>     For a 16" OC metal stud wall, R-12 Batt cavity insulation and R-5
>     continuous rigid insulation, the report states that the Effective
>     R-value for the wall + slab will be R-7.4.This is based on 8'8"
>     floor-to-floor, and 8" slab.
>
>     Using ASHRAE 90.1-2007 Table A3.3 for steel framed walls, we would
>     get an effective U-factor for the wall portion of U = 0.0785
>     (interpolating between the R-13 + R-11 batt values). If we use
>     Table A3.1A for the exposed slab edge (assuming 8" normal weight
>     solid concrete walls), we get a U-factor of U = 0.740 for the slab
>     edge.
>
>     Doing an area weighted U-factor calc: U_eff = U_1 *A_1 +U_2 *A_2
>     /(A_1 +A_2 ) or in this case, factoring out the Length of the wall
>     section we use: U_1 *H_1 +U_2 *H_2 /(H_1 +H_2 ) = (0.0785*8 +
>     0.740*8/12)/(8+8/12) = 0.1294 or an effective R-value of 7.73,
>     which is pretty close to the R-7.4 claimed, a difference of about
>     4% in U-value. Maybe I'm cynical, but to me that seems close enough.
>
>     I only spot checked this assembly, so maybe there is more impact
>     with different construction types.
>
>     Another interesting tid-bit: Apparently the much vaunted
>     fin-effect is actually pretty minimal. If you look at the results
>     of the exposed slab-edge condition vs the full balcony fin-effect,
>     the balcony scenario actually shows slightly BETTER thermal
>     performance. Odd.
>
>     *Nathan Miller **-****PE, LEED^® AP BD+C, CEM*
>
>     /Mechanical Engineer/Senior Energy Analyst /
>
>     *RUSHING*| *D*206-788-4577 <tel:206-788-4577> |*O*206-285-7100
>     <tel:206-285-7100>
>
>     *www.rushingco.com <http://www.rushingco.com/>***
>
>     *From:* equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
>     *Bishop, Bill
>     *Sent:* Monday, November 04, 2013 1:42 PM
>     *To:* David Griffin; 'Coleman, Kevin';
>     equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* Re: [Equest-users] Slab extending through wall
>
>     Here's a timely report on effective R-values of assemblies with
>     slab/balcony thermal bridges:
>
>     The Importance of Slab Edge and Balcony Thermal Bridges
>     <http://www.rdhbe.com/database/files/library/Balcony_and_Slab_Edge_Thermal_Bridges___1___R_values_and_Energy_Code_Canada__Sept_24_13.pdf>
>
>     Regards,
>
>     Bill
>
>     *William Bishop, PE, BEMP, BEAP, LEED AP **|**Pathfinder Engineers
>     & Architects LLP*
>
>     *Senior Energy Engineer*
>
>     	
>
>     webCertified_logo_colorRGB72DPI.jpg
>
>     134 South Fitzhugh StreetRochester, NY 14608
>
>     T: (585) 325-6004 <tel:%28585%29%20325-6004> Ext. 114F: (585)
>     325-6005 <tel:%28585%29%20325-6005>
>
>     bbishop at pathfinder-ea.com
>     <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com
>     <http://www.pathfinder-ea.com/>
>
>     PSustainability -- the forest AND the trees.P
>
>     *From:*equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
>     *David Griffin
>     *Sent:* Monday, November 04, 2013 4:20 PM
>     *To:* 'Coleman, Kevin'; equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* Re: [Equest-users] Slab extending through wall
>
>     Kevin,
>
>     I'm fairly sure eQUEST is not even going to closely approximate
>     the heat loss/gain accurately unless you dial the loads in
>     manually which means you have to calculate them by hand first. I
>     suggest referring to ASHRAE-D-RP-1365 for guidance on estimating
>     the loads. The section you are interested in starts on page 35.
>
>     Thanks,
>
>     **
>
>     *David W. Griffin II*
>
>     Energy Analyst
>
>     ETC Group, LLC
>
>     801-278-1927 x 128 <tel:801-278-1927%20x%20128>
>
>     Cell 480-736-2945 <tel:480-736-2945>
>
>     dgriffin at etcgrp.com <mailto:dgriffin at etcgrp.com>
>
>     www.etcgrp.com <http://www.etcgrp.com>
>
>     Copy of ETC_LogoOnly2_rgb_sm.png
>
>     *Energy Engineering for a Sustainable Future*
>
>     1997 South 1100 East, Salt Lake City, UT 84106-4471
>
>     -------------------------------------------------------------------------------------------------------------------
>
>     CONFIDENTIALITY NOTICE This e-mail transmission, and any
>     documents, files or previous e-mail messages attached to it may
>     contain confidential information that is legally privileged.  If
>     you are not the intended recipient or the person responsible for
>     delivering it to the intended recipient, you are hereby notified
>     that any disclosure, copying, distribution or use of any of the
>     information contained in or attached to this transmission is
>     strictly prohibited.  If you have received this transmission in
>     error, please immediately notify us by telephone at (801) 278-1927
>     <tel:%28801%29%20278-1927> and destroy the original transmission
>     and its attachments without reading them. Thank you.
>
>     *From:*Coleman, Kevin [mailto:kcoleman at nexant.com]
>     *Sent:* Monday, November 04, 2013 11:56 AM
>     *To:* equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* [Equest-users] Slab extending through wall
>
>     I am evaluating a new 10-story hotel design that is proposing
>     glass curtain walls and pre-tensioned concrete floors that project
>     beyond the walls. On 3 sides the projections are minimal (6
>     inches). However, on one side, the projections extend about 3 ft.
>
>     For the small projections, I intent to use the following method
>     recommended in the thread below. "In screen 4 of 25 of the DD
>     shell wizard you can specify "Slab Penetrates Wall Plane" (check
>     box)."
>
>     I am interested in any tips for modeling the thermal impacts of
>     the larger projections. Thoughts? (I plan to use window shading
>     for the light/shading impacts.)
>
>     I am hopeful that the analysis will help convince the design team
>     to incorporate some insulation and thermal breaks!
>
>     Thanks in advance!
>
>     Kevin
>
>     Brian Fountain bfountain at greensim.com <http://greensim.com>
>
>     Mon Dec 6 11:45:18 PST 2010
>
>     Previous message: [Equest-users] balcony
>
>     Next message: [Equest-users] Shading
>
>     Messages sorted by: [ date ] [ thread ] [ subject ] [ author ]
>
>     In screen 4 of 25 of the DD shell wizard you can specify "Slab
>
>     Penetrates Wall Plane" (check box).  If you do, eQUEST created a new
>
>     wall type of height equal to your slab thickness and composed of
>     1' of
>
>     concrete plus any slab edge insulation you specify on the same wiz
>
>     screen.   That provides a parallel path for the heat transfer from
>     the
>
>     balcony or slab edge.  Not exactly 2D heat transfer modelling --
>     but at
>
>     least you aren't ignoring the effect of the slab edge or balcony.
>
>     *Kevin Coleman, CEM, LEED AP*?*Project Manager **?****Nexant,
>     Inc.****?** Demand Management *
>
>     1232 Fourier Drive, Suite 125?Madison, WI 53717 ?608.824.1230
>     <tel:608.824.1230> ?_kcoleman at nexant.com <mailto:kcoleman at nexant.com>_
>
>     P Please consider the environment before printing this email**
>
>
>     _______________________________________________
>     Equest-users mailing list
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>     To unsubscribe from this mailing list send  a blank message to
>     EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/9cd14724/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 161932 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/9cd14724/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 130868 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/9cd14724/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3124 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/9cd14724/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1559 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/9cd14724/attachment-0001.jpeg>
    
    
More information about the Equest-users
mailing list