[Equest-users] Slab extending through wall
    Byron Burns 
    B.Burns at ha-inc.com
       
    Mon Nov  4 11:03:07 PST 2013
    
    
  
Hello Kevin,
 
I would recommend looking at this report prepared for ASHRAE TC4.4 by Morrison Hershfield.  They have some pretty good data which may help you out. 
 
http://www.morrisonhershfield.com/ashrae1365research/Documents/MH_1365RP_Final_%20small.pdf
 
Byron D. Burns, EIT, BEMP 
Energy Analyst/ Modeler 
H&A Architects & Engineers | www.ha-inc.com <http://www.ha-inc.com>  
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Coleman, Kevin
Sent: Monday, November 04, 2013 1:56 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Slab extending through wall
 
I am evaluating a new 10-story hotel design that is proposing glass curtain walls and pre-tensioned concrete floors that project beyond the walls. On 3 sides the projections are minimal (6 inches). However, on one side, the projections extend about 3 ft. 
 
For the small projections, I intent to use the following method recommended in the thread below. "In screen 4 of 25 of the DD shell wizard you can specify "Slab Penetrates Wall Plane" (check box)."
 
I am interested in any tips for modeling the thermal impacts of the larger projections. Thoughts? (I plan to use window shading for the light/shading impacts.)
 
I am hopeful that the analysis will help convince the design team to incorporate some insulation and thermal breaks!
 
Thanks in advance!
Kevin
 
 
Brian Fountain bfountain at greensim.com 
Mon Dec 6 11:45:18 PST 2010
Previous message: [Equest-users] balcony
Next message: [Equest-users] Shading
Messages sorted by: [ date ] [ thread ] [ subject ] [ author ]
 
In screen 4 of 25 of the DD shell wizard you can specify "Slab 
Penetrates Wall Plane" (check box).  If you do, eQUEST created a new 
wall type of height equal to your slab thickness and composed of 1' of 
concrete plus any slab edge insulation you specify on the same wiz 
screen.   That provides a parallel path for the heat transfer from the 
balcony or slab edge.  Not exactly 2D heat transfer modelling -- but at 
least you aren't ignoring the effect of the slab edge or balcony.
 
Kevin Coleman, CEM, LEED AP  ■  Project Manager ■   Nexant, Inc.  ■ Demand Management 
1232 Fourier Drive, Suite 125 ■ Madison, WI 53717 ■  608.824.1230 ■  kcoleman at nexant.com
 
P Please consider the environment before printing this email 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131104/18a0ab0a/attachment.htm>
    
    
More information about the Equest-users
mailing list