[Equest-users] 90.1 App G Fan Power and EER Calculations
Nick Caton
ncaton at smithboucher.com
Thu May 31 06:55:46 PDT 2012
Hi Paul!
I maintained the exact same position for a long while, though I thought I was the vocal minority =)! Ultimately, you can argue for/against either approach as having different advantages of 'correctness.' I've heard future addenda or versions of 90.1 may address the conundrum by stipulating something more simplistic than either approach, like a uniform "factor" to come up with compressor/condenser energies from the total consumption.
My final position is both approaches make sense, and for different reasons - modelers should use whichever they feel most comfortable defending should their methodology come into question. My LEED reviewers have to this point taken zero interest in which approach I've used in my calculations, after using both, so I take it this degree of nuance is probably not on their usual checklists. I've switched over to the ARI approach for a few reasons, but not because I feel a Pfan-based approach is 'wrong.'
Best wishes,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com]
Sent: Thursday, May 31, 2012 7:29 AM
To: Nick Caton; Steve Burley; equest-users at lists.onebuilding.org
Subject: RE: 90.1 App G Fan Power and EER Calculations
Nick, Steve, and list,
I think I concur more with Steve. If you use Nick's approach to calculate the cooling EIR by subtracting out ARI rated fan power from the 90.1 EER AND then model the 90.1 fan power limits directly, you will be modeling a packaged unit that does not comply with the package EER.
I could see using other splits of fan and cooling, but a baseline model should comply with both limits.
Paul Riemer, PE, LEED AP BD+C
DUNHAM
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, May 29, 2012 10:51 AM
To: Steve Burley; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] 90.1 App G Fan Power and EER Calculations
Steve,
There are two schools of thought for dealing with fan power in cooling efficiency calcs. The first pulls away the baseline fan power Pfan, as you're describing, and the other instead pulls out a fan energy draw based on ARI testing procedures... 400 CFM/ton à 365W/1000CFM. I follow the latter these days, but see both as viable.
The two approaches result in similar results when your Pfan calculation doesn't involve a lot of static pressure adders. When it does, the approaches diverge in a fashion that may be either problematic or helpful in a LEED rating sense. Attached discussion sums up things further, includes an outline of an ARI-based approach. You can find more discussions and read into advantages/disadvantages to both approaches in the mailing list archives.
That said, I haven't checked your math or references but the procedure you've roughly outlined sounds alright for a Pfan approach. There are steps in between what you've written for correctly coming up with Pfan, but I take it that's implicit.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Burley
Sent: Tuesday, May 29, 2012 6:37 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] 90.1 App G Fan Power and EER Calculations
I'm sure this must have been asked before but I cannot find an answer in the archives - if there is one please point me to it.
I have interpreted the requirements of 90.1, App. G to split the EER of cooling equipment with a supply fan into its components to model the fan energy separately as follows:
1. Say a space has a cooling load of 80,000Btu/h and the system is packaged single zone, EER - 11.2.
2. Calculate airflow for 20°F temperature difference - 3708cfm
3. Calculate fan bhp from Table G3.1.2.9 - 3.49bhp
4. Calculate fan power as per G3.1.2.9 - 2972W
5. Calculate gross input power from load and EER - 7143W
6. Subtract 4 from 5 for compressor/condenser input power - 4171W
7. Convert to EIR - 0.1779
This appears to make sense from reading App. G but ends up with high fan power consumption and low space cooling loads. Am I wrong here?
Thanks,
Steven Burley
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120531/ccd2020f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120531/ccd2020f/attachment.jpg>
More information about the Equest-users
mailing list