[Equest-users] 90.1 App G Fan Power and EER Calculations
Steve Burley
steve.burley at csa-eng.biz
Tue May 29 07:23:59 PDT 2012
Uday,
My understanding is the EER in the table, in this case 11.2 for packaged AC between 65,000 and 135,000 Btu/h, is the overall efficiency of the equipment, i.e. including the fan power. It seems from what you have written below you say it does not; is that correct?
Regards,
Steven Burley
From: Uday Gorre [mailto:u_k_gorre at ateindia.com]
Sent: 29 May 2012 16:41
To: Steve Burley
Subject: RE: [Equest-users] 90.1 App G Fan Power and EER Calculations
Dear Steven Burely
How you calculated the EIR (0.1779).
As per my calculations
COP= EER/3.412 = 11.2/3.412 = 3.28 ( Generally EER = (Cooling Load/ Work input)* 3.412 here cooling load is in btu/hr and work input is compressor and condenser power in W )
Work input = Cooling load/ COP = 23445.7 (in W)/3.28 =7148 W (Not included fan power)
Fan Power mentioned below is 2972 W
Gross input power = 2942 + 7148 =10090 W
EIR=1/COP= 1/3.28 = 0.3048 (Cooling equipment)
Regards
Uday...
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Burley
Sent: 29 May 2012 5:07 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] 90.1 App G Fan Power and EER Calculations
I'm sure this must have been asked before but I cannot find an answer in the archives - if there is one please point me to it.
I have interpreted the requirements of 90.1, App. G to split the EER of cooling equipment with a supply fan into its components to model the fan energy separately as follows:
1. Say a space has a cooling load of 80,000Btu/h and the system is packaged single zone, EER - 11.2.
2. Calculate airflow for 20°F temperature difference - 3708cfm
3. Calculate fan bhp from Table G3.1.2.9 - 3.49bhp
4. Calculate fan power as per G3.1.2.9 - 2972W
5. Calculate gross input power from load and EER - 7143W
6. Subtract 4 from 5 for compressor/condenser input power - 4171W
7. Convert to EIR - 0.1779
This appears to make sense from reading App. G but ends up with high fan power consumption and low space cooling loads. Am I wrong here?
Thanks,
Steven Burley
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120529/a593ce1b/attachment.htm>
More information about the Equest-users
mailing list