[Equest-users] Regarding multiple floors in a building
bfountain at greensim.com
bfountain at greensim.com
Thu May 24 05:25:18 PDT 2012
On the footprint shape screen of the wizard (screen 2 of the DD shell wiz), if your floor-to-ceiling height is more than a foot lower than your floor-to-floor height, eQUEST will create a plenum space. Whether it creates a single plenum for the floorplate or a plenum per zone depends on whether you HVAC system is ducted or plenum return.
I suspect you may be looking at the 3d view where ceiling partitions are turned off by default but they will still be shown on the component tree.
Brian Fountain
bfountain at greensim.com