[Equest-users] weather processor trouble
Joe Huang
yjhuang at whiteboxtechnologies.com
Fri May 11 16:49:14 PDT 2012
Xavier,
It looks like the eQUEST converter is finding a numerical problem in the EPW version of
the SWEC Barcelona weather file.
According to the documentation, the SWEC weather files were originally developed in DOE-2
*.BIN format, so perhaps
you could contact the developer listed and see if you can get a copy of the *.BIN weather
file.
I all read from the documentation that the SWEC weather files were generated from monthly
statistics, and has constant
wind speeds for all hours. Therefore, you should evaluate whether the use of these data
is appropriate for your needs.
For example, you should not use the SWEC weather files to study natural ventilation !
There are both IWEC and IWEC2 weather files for Barcelonia, developed by ASHRAE. The
IWEC version is available on
the EnergyPlus Weather web site, so you could also try converting that file instead to
*.BIN. The IWEC2 weather files
are currently available only on a DVD from ASHRAE and contains weather files for 3,012
stations. See www.techstreet.com/cgi-bin/detail?product_id=1823067 for details.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 5/11/2012 3:42 AM, Xavier Rigol wrote:
>
> Hello,
>
> I'm Xavi from Barcelona and I'm a recently eQuest user. I'm trying to convert the SWEC
> Barcelona weather file (*.epw) to a .BIN file and I get an error, yo can see it below.
>
> I don't know what can I do. Does anybody can help me. Is there any webpage to get a
> Barcelona.BIN file, as I do with .epw files?
>
> Thank you!!
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120511/d8d711eb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 29942 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120511/d8d711eb/attachment.jpeg>
More information about the Equest-users
mailing list