[Equest-users] Unmet Load Hours - VAV with no re-heat
R B
slv3sat at gmail.com
Fri May 4 08:00:18 PDT 2012
I am assuming this is an existing building. I have always had this issue. I
do all the stuff that you have and use the reheat also, if the unmet hours
are too many. I also look at the SS-F report to see how low the temps are
and when (hourly report) - if they are acceptable, then I leave the reheat
out. You could also widen the throttling range - there might be unmet hours
in the actual building - people just don't complain if it is a few degrees
less/more than the thermostat. You should look at the hourly report to see
if the heating coil is coming on (these reports are not very clean - since
it is not clear for what point in the air stream eQuest is reporting the
temps). Do you have VAV boxes - sometimes I have seen that a constant
volume system has a VFD added to the fan, without VAV boxes in the space.
You could reduce the min flows to zero and see if that helps. I haven't dug
deeper into it, but I think the VAV system is going to set the supply temps
low when even one zone needs cooling/less heating and so others will need
reheat. If things are working smoothly in the existing building, then the
zones must be similar and may not need too much variation in supply temps
for different zones. I haven't used MZ - but that would probably work -
what is the difference in energy consumption between the two options? I
have not been comfortable with the economizer and MZ together.
I will be curious to know what you find.
-Rohini
On Fri, May 4, 2012 at 8:48 AM, Dana Etherington <
Dana.Etherington at crbusa.com> wrote:
> Hi folks,****
>
> ** **
>
> We are modeling a large facility operating with multiple VAV AHUs with
> central heating and cooling coils, but no re-heat at the zones. There are
> high heat loads in the spaces and therefore higher return air temperatures
> than the norm. ****
>
> ** **
>
> When I remove the re-heat from the systems I have excessive unmet load
> hours (heating). I have specified “HEAT-SET-T” to activate the central
> heating coil. I also have cooling control set to “warmest” and heat control
> set to “coldest”. If I do not set the coil capacity it is still not meeting
> the loads. The only way I have been able to eliminate these unmet hours is
> by adding the re-heat back in or changing it to a multi-zone (MZS) system
> with all the same parameters. ****
>
> ** **
>
> If I model this scenario using the multi-zone system in eQuest to get
> around this would that be vastly different than VAV with no re-heat? Has
> anyone had this issue before? Any insight is appreciated. Thanks!****
>
> ** **
>
> -Dana****
>
> ** **
>
> *Mr. Dana Etherington, E.I.T., LEED AP BD+C *| *CRB *| One Kendall Square
> Ste B2202 | Cambridge, MA 02139****
>
> *Main:* 617-475-3050 *| Direct:* 617-475-3061 | *Mobile:* 617-583-3009 | *
> Fax:* 617-475-3052 | *Ext: 6061*****
>
> *Email:* dana.etherington at crbusa.com | www.crbusa.com****
>
>
> ________________________________________________________________________________________
> ****
>
> ** **
>
> *This document may contain confidential information and is intended for
> use by the addressee only. If you are not *
>
> *the intended recipient, please do not transmit, copy, disclose, or
> utilize this communication in any manner. If you *
>
> *received this message in error, please notify the sender immediately and
> delete this message.*
>
> * *
>
> ü Please consider the environment before printing this email.****
>
> ** **
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120504/bd6bf415/attachment.htm>
More information about the Equest-users
mailing list