We had a recent project with exterior fish ponds looking at their effect on microclimate. Any experience w/ this condition?


Arpan

On May 3, 2012, at 11:46 AM, "Mike Hupel" <mhupel at aegiseng.ca> wrote:

> Bill beat me to it.  Your ventilation load would be calculated as if it were a natatorium using total surface area, temperature and evaporative rates. Then once you get that information you can model the ventilation rates and make-up. 
> 
>  
> 
>  
> 
>  
> 
>  
> 
> <image002.jpg>
> 
> Mike Hupel, B.Tech, CEM, LEED-AP
> 
> Senior Mechanical Designer
> 
> 56 Pennsylvania Ave. Suite 18
> 
> Concord, ON L4K 3V9
> 
> (905) 761-1264 ext. 24
> 
> (647) 702-3316 cell
> 
>  
> 
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
> Sent: May-03-12 11:33 AM
> To: Cristian Salvador Jara Toro; equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] fishpond
> 
>  
> 
> Cristian,
> 
>  
> 
> You can model it but you will need to calculate the latent and sensible loads yourself, at least if you are using eQUEST. Without having experience with fishponds, I would approach it like a natatorium (indoor swimming pool) and use the ASHRAE Handbook – HVAC Applications Chapter 5 for design guidance and loads calculations. Also, see this article: http://hpac.com/humidification-dehumidification/simplified-calculating-evaporation-1011/ for alternate method of calculating evaporation loads. Based on your drawings, I would also research state-of-the-art for aquaculture facilities, as that looks to be what you are designing.
> 
>  
> 
> Regards,
> 
> Bill
> 
>  
> 
> <image003.png>
> 
>  
> 
>  
> 
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cristian Salvador Jara Toro
> Sent: Thursday, May 03, 2012 11:15 AM
> To: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] fishpond
> 
>  
> 
> Sorry, but I meant "design" instead of "model"... because I don´t think to model a room with water in it be possible...
> 
> On Thu, May 3, 2012 at 10:53 AM, Cristian Salvador Jara Toro <cristian.jara.toro at gmail.com> wrote:
> 
> Greetings!
> 
> I have to model a room with a fishpond (more like close to a several fountains where fishes will be inside). WxLxH=9x13x2.5 in meters.
> Has anybody modeled something like that? 
> 
> So, what I need to know is about ventilation rates for a room like that, wich contains water and fishes swimming in it, but my worry is about condensations, so if anybody has some paper or standard, please let me know.
> 
> Thanks in advance...
> 
> -- 
> Cristian Jara Toro
> Cel: 6 207 8566
> 
> 
> 
> 
> -- 
> Cristian Jara Toro
> Cel: 6 207 8566
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120503/03783744/attachment.htm>


More information about the Equest-users mailing list