[Equest-users] Query regarding PDEC ( Passive cooling ) simulation in eQuest

Jason Glazer jglazer at gard.com
Fri Mar 16 11:21:50 PDT 2012


Please don't send EXE files to the mailing list. If you want 
to announce that an EXE is available that is fine. Let 
people download it or email it directly to them. When EXE's 
are sent to the mailing list, I get dozens (maybe hundreds) 
of bounce messages as servers reject them.

Thanks,

Jason

On 3/16/2012 1:16 PM, CleanTech Analytics wrote:
> What is the attached file?
> Could you send it as .exe, because it did not translate..
>
>
> /Jeremiah D. Crossett/
> /CleanTech Analytics/
> /503-688-8951/
> /www.cleantechanalytics.com/ <http://www.cleantechanalytics.com>
>
>
> *
>
> This document may contain valuable information proprietary
> to CleanTech Analytics which is private and confidential. It
> may not be shared, copied, stored or transmitted in any form
> without the prior written consent of CleanTech Analytics
>
> *
>
>
>
> On Fri, Mar 16, 2012 at 10:19 AM, Chalfoun, Nader V -
> (chalfoun) <chalfoun at email.arizona.edu
> <mailto:chalfoun at email.arizona.edu>> wrote:
>
>     Since outlook and the university usually blocks any .exe
>     files I have renamed the program CT.txt and you should
>     rename back to CT.exe once you receive it
>     Nader
>     Check my new online energy courses
>     http://www.hed-online.com <http://www.hed-online.com/>
>     --------------------------------------------
>     *Nader V. Chalfoun*, Ph.D., LEED© AP, CEA
>     Professor of Architecture and Environmental Sciences
>     Director: The House Energy Doctor Program
>     http://houseenergydoctor.arizona.edu
>     <http://houseenergydoctor.arizona.edu/>
>     Chair: Master of Science in Architecture Program
>     Coordinator: Environmental Education Ph.D. Minor
>     Faculty: Global Change Ph.D. Minor
>     Address:  University of Arizona
>                     College of Architecture and Landscape
>     Architecture
>                     1040 N. Olive St., Tucson, AZ 85721, U.S.A.
>                     Phone: (520)621-6751
>     <tel:%28520%29621-6751>    Fax: (520)621-8700
>     <tel:%28520%29621-8700>
>     ------------------------------------------------------------
>     *From:* equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>] On
>     Behalf Of Chalfoun, Nader V - (chalfoun)
>     [chalfoun at email.arizona.edu
>     <mailto:chalfoun at email.arizona.edu>]
>     *Sent:* Friday, March 16, 2012 10:16 AM
>     *To:* Joe Huang; Mansi Jayswal
>     *Cc:* equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>; Design
>     Builder USA
>
>     *Subject:* Re: [Equest-users] Query regarding PDEC (
>     Passive cooling ) simulation in eQuest
>
>     Dear Mansi,
>     I am attaching the CoolTprogram for sizing Passive
>     Downdraft Evaporative Cooling devices.  As Vikramsaid,
>     the program is a dos based and can be run from windows
>     XP.  The program calculates temperature drop, water
>     consumption and other important thermodynamic values
>     based on many variables including Pads evaporative
>     cooling efficiency, thicknessand area, tower effective
>     height (z), discharge mode (bottom or side) indoor (with
>     screens or outdoor).
>     The only issue is that it has 8 built-in climate zones.
>     If your climate zone is not included, I have to added
>     and re-compile the program.  If your climate zone has
>     somehow close moisture and temperature data than the
>     once included, you can approximate the results.
>     Good luck with that and let me know if I could be of
>     additional assistance to you.
>     Cheers,
>     Nader
>     Check my new online energy courses
>     http://www.hed-online.com <http://www.hed-online.com/>
>     --------------------------------------------
>     *Nader V. Chalfoun*, Ph.D., LEED© AP, CEA
>     Professor of Architecture and Environmental Sciences
>     Director: The House Energy Doctor Program
>     http://houseenergydoctor.arizona.edu
>     <http://houseenergydoctor.arizona.edu/>
>     Chair: Master of Science in Architecture Program
>     Coordinator: Environmental Education Ph.D. Minor
>     Faculty: Global Change Ph.D. Minor
>     Address:  University of Arizona
>                     College of Architecture and Landscape
>     Architecture
>                     1040 N. Olive St., Tucson, AZ 85721, U.S.A.
>                     Phone: (520)621-6751
>     <tel:%28520%29621-6751>    Fax: (520)621-8700
>     <tel:%28520%29621-8700>
>     ------------------------------------------------------------
>     *From:* equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>] On
>     Behalf Of Joe Huang [yjhuang at whiteboxtechnologies.com
>     <mailto:yjhuang at whiteboxtechnologies.com>]
>     *Sent:* Thursday, March 08, 2012 12:05 PM
>     *To:* Mansi Jayswal
>     *Cc:* equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>; Design
>     Builder USA
>
>     *Subject:* Re: [Equest-users] Query regarding PDEC (
>     Passive cooling ) simulation in eQuest
>
>     Mansi,
>
>     If CoolT is as Vikram describes, this might be the
>     solution to your problem.  The main issue for you is to
>     know the air flow output of the PDEC  in actual
>     operations, not under design conditions, so that other
>     program you mentioned for sizing the PDEC is of little
>     help.  If CoolT is not able to give you air flow rates
>     based on the ambient conditions and the indoor air
>     temperature, you could try building a simple two-zone
>     model (PDEC, Building) using CONTAM and then run that
>     stand-alone to get the air flows between the two zones.
>
>     In reference to Vikram's comment, I've said all along
>     that the difference between the PDEC and a  standard DEC
>     is the mechanism used to drive the air across the media
>     - using natural bouyancy forces in the first case and a
>     mechanical fan in the second case.  Once you have the
>     air flow rate, the PDEC is actually simpler to model
>     because there's no need to model fan efficiency and heat
>     gain, etc.  In fact, it just takes a single
>     effectiveness curve, or even just a constant
>     effectiveness number.
>
>     Joe
>
>     Joe Huang
>     White Box Technologies, Inc.
>     346 Rheem Blvd., Suite 108D
>     Moraga CA 94556
>     yjhuang at whiteboxtechnologies.com  <mailto:yjhuang at whiteboxtechnologies.com>
>     www.whiteboxtechnologies.com  <http://www.whiteboxtechnologies.com>
>     (o)(925)388-0265  <tel:%28925%29388-0265>
>     (c)(510)928-2683  <tel:%28510%29928-2683>
>     "building energy simulations at your fingertips"
>
>
>     On 3/8/2012 6:49 AM, Mansi Jayswal wrote:
>>
>>     Thanks Vikram,
>>
>>     Could you tell me from where i can download this
>>     Software " CoolT" ? i have tried to Google but did not
>>     find it anyware. I have even found one of your
>>     research paper. it seems you have already worked on
>>     it. it will be great if you could guide me.
>>
>>
>>
>>     On Thu, Mar 8, 2012 at 7:37 PM, Sami, Vikram
>>     <Vikram.Sami at perkinswill.com
>>     <mailto:Vikram.Sami at perkinswill.com>> wrote:
>>
>>         Another option to look into is CoolT developed by
>>         Nader Chalfoun at University of Arizona in Tucson.
>>         It’s a Dos program that is based on empirical data
>>         that they collected from the extensive testing
>>         they did on Cool Towers (Passive Downdraught
>>         Chimneys).
>>
>>         Again – I would throw in words of caution. Passive
>>         downdraught chimneys rely on buoyancy driven
>>         forces – something that you cannot approximate
>>         with a fan driven evaporative cooler or wind
>>         driven. eQUEST might be able to model this, but
>>         its beyond my knowledge. Also – The folks at UA
>>         (Nader Chalfoun & Martin Yoklic) did some testing
>>         with cool towers in enclosed spaces. I would try
>>         writing to them to get some feedback on issues to
>>         consider.
>>
>>         I think Nader is on this list – not sure if he’s
>>         still active.
>>
>>         **
>>
>>         *Vikram Sami*, LEED AP BD+C
>>
>>         Sustainable Design Analyst
>>
>>         1315 Peachtree St. NE, Atlanta, GA 30309
>>
>>         t: 404-443-7462 <tel:404-443-7462>    f:
>>         404.892.5823 <tel:404.892.5823>     e:
>>         vikram.sami at perkinswill.com
>>         <mailto:vikram.sami at perkinswill.com>
>>         www.perkinswill.com <http://www.perkinswill.com/>
>>
>>         *Perkins+Will.*Ideas + buildings that honor the
>>         broader goals of society
>>
>>         *From:*Mansi Jayswal
>>         [mailto:ar.mansi.jayswal at gmail.com
>>         <mailto:ar.mansi.jayswal at gmail.com>]
>>         *Sent:* Thursday, March 08, 2012 2:40 AM
>>         *To:* Design Builder USA
>>         *Cc:* Dahlstrom, Aaron; Sami, Vikram;
>>         equest-users at lists.onebuilding.org
>>         <mailto:equest-users at lists.onebuilding.org>
>>
>>
>>         *Subject:* Re: [Equest-users] Query regarding PDEC
>>         ( Passive cooling ) simulation in eQuest
>>
>>         Thank you all for your quick response and
>>         Information.
>>
>>         Is it possible that if i use PHDC software to
>>         design the PDEC system and simulate the same
>>         building in eQuest ??  PHDC software can give me
>>         the required size of the passive down
>>         draught evaporating cooling towers for the building.
>>
>>         On Wed, Mar 7, 2012 at 9:37 PM, Design Builder USA
>>         <jcrossett at designbuilderusa.com
>>         <mailto:jcrossett at designbuilderusa.com>> wrote:
>>
>>         You may wish to explore the free trial of Design
>>         Builder, as it has CFD, natural ventilation and
>>         evaporate cooling.
>>
>>         Tho I am not sure if it can be used for your
>>         passive cooling requirement or not..
>>
>>         Best of luck
>>
>>         On Wed, Mar 7, 2012 at 6:53 AM, Dahlstrom, Aaron
>>         <ADahlstrom at in-posse.com
>>         <mailto:ADahlstrom at in-posse.com>> wrote:
>>
>>             Mansi –
>>
>>             We have done some schematic modeling of wind
>>             towers with Fluent, a CFD package as noted.
>>
>>             Our climate didn’t justify evaporative
>>             pre-cooling.
>>
>>             eQUEST has a natural ventilation module, which
>>             I have not fully dived into.
>>
>>             I believe it requires inputs that would likely
>>             be validated by a CFD model – for example, I
>>             don’t think eQUEST’s natural ventilation model
>>             allows for evaporative pre-cooling as a
>>             temperature driver for natural air exchange in
>>             a space.
>>
>>             As eQUEST models each zone as a fully mixed
>>             space, and has limited air transfer between
>>             zones, you may also have trouble getting the
>>             thermal stratification from eQUEST that would
>>             typically be needed to drive natural
>>             ventilation in a PDEC.
>>
>>             *Aaron Dahlstrom , PE, LEED® AP*
>>
>>             *In P**o**sse*– A subsidiary of*AKF*| 1500
>>             Walnut Street, Suite 1414, Philadelphia, PA 19102
>>
>>             d: 215-282-6753 <tel:215-282-6753>| m:
>>             267-507-5470 <tel:267-507-5470>| In Posse:
>>             215-282-6800 <tel:215-282-6800>| AKF:
>>             215-735-7290 <tel:215-735-7290>
>>
>>             e: ADahlstrom at in-posse.com
>>             <mailto:ADahlstrom at in-posse.com> | in posse
>>             web: www.in-posse.com
>>             <http://www.in-posse.com/> | akf web:
>>             www.akfgroup.com <http://www.akfgroup.com/>
>>
>>             *From:*equest-users-bounces at lists.onebuilding.org
>>             <mailto:equest-users-bounces at lists.onebuilding.org>
>>             [mailto:equest-users-bounces at lists.onebuilding.org
>>             <mailto:equest-users-bounces at lists.onebuilding.org>]
>>             *On Behalf Of *Sami, Vikram
>>             *Sent:* Wednesday, March 07, 2012 8:53 AM
>>             *To:* Mansi Jayswal;
>>             equest-users at lists.onebuilding.org
>>             <mailto:equest-users at lists.onebuilding.org>
>>             *Subject:* Re: [Equest-users] Query regarding
>>             PDEC ( Passive cooling ) simulation in eQuest
>>
>>             Mansi,
>>
>>             I doubt you can do this credibly in eQUEST.
>>             You really need a CFD type package to be able
>>             to simulate this. . A word of caution – the
>>             effort to develop the simulation for this is a
>>             master’s thesis in itself.
>>
>>             **
>>
>>             *Vikram Sami*, LEED AP BD+C
>>
>>             Sustainable Design Analyst
>>
>>             1315 Peachtree St. NE, Atlanta, GA 30309
>>
>>             t: 404-443-7462 <tel:404-443-7462>    f:
>>             404.892.5823 <tel:404.892.5823>     e:
>>             vikram.sami at perkinswill.com
>>             <mailto:vikram.sami at perkinswill.com>
>>             www.perkinswill.com <http://www.perkinswill.com/>
>>
>>             *Perkins+Will.*Ideas + buildings that honor
>>             the broader goals of society
>>
>>             *From:*equest-users-bounces at lists.onebuilding.org
>>             <mailto:equest-users-bounces at lists.onebuilding.org>
>>             [mailto:equest-users-bounces at lists.onebuilding.org]
>>             <mailto:[mailto:equest-users-bounces at lists.onebuilding.org]>
>>             *On Behalf Of *Mansi Jayswal
>>             *Sent:* Tuesday, March 06, 2012 11:25 PM
>>             *To:* equest-users at lists.onebuilding.org
>>             <mailto:equest-users at lists.onebuilding.org>
>>             *Subject:* [Equest-users] Query regarding PDEC
>>             ( Passive cooling ) simulation in eQuest
>>
>>             Hello friends,
>>
>>             My name is Mansi Jayswal. I am a final year
>>             student of Masters Programme at CEPT
>>             University, India. By profession I am an
>>             architect. Currently I am doing thesis on
>>             passive cooling technique (Passive down
>>             draught evaporative cooling system- PDEC ).
>>             And try to identified that how much cooling
>>             load of HVAC system can be replaced through
>>             this system.
>>
>>             Now my query is that is it eQuest is capable
>>             to simulate such building with wind tower or
>>             PHDC (PDEC ) system? If anybody knows please
>>             kindly reply. I have very days left for final
>>             submission and I am stuck here.
>>
>>             Thanks
>>
>>             --
>>
>>
>>             Regards,
>>
>>             Mansi Jayswal,
>>
>>             B.Arch I IGBC AP I M.Tech in Climate Change &
>>             Sustainable Development
>>
>>             Faculty of Sustainable Environment & Climate
>>             Change,
>>
>>             Centre for Environmental Planning & Technology
>>             (CEPT) University
>>
>>
>>             This e-mail may contain information that is
>>             confidential, privileged or otherwise
>>             protected from disclosure. If you are not an
>>             intended recipient of this e-mail, do not
>>             duplicate or redistribute it by any means.
>>             Please delete it and any attachments and
>>             notify the sender that you have received it in
>>             error. Unintended recipients are prohibited
>>             from taking action on the basis of information
>>             in this e-mail. E-mail messages may contain
>>             computer viruses or other defects, may not be
>>             accurately replicated on other systems, or may
>>             be intercepted, deleted or interfered without
>>             the knowledge of the sender or the intended
>>             recipient. If you are not comfortable with the
>>             risks associated with e-mail messages, you may
>>             decide not to use e-mail to communicate with
>>             In Posse.
>>
>>             _______________________________________________
>>             Equest-users mailing list
>>             http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>             To unsubscribe from this mailing list send  a
>>             blank message to
>>             EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>             <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>
>>
>>
>>         --
>>
>>         Jeremiah D. Crossett
>>
>>         Energy Modeling Consultant
>>
>>         503-688-8951 <tel:503-688-8951>
>>
>>         www.DesignBuilderUSA.com
>>         <http://www.DesignBuilder.com>
>>
>>
>>
>>         --
>>
>>
>>         Regards,
>>
>>         Mansi Jayswal,
>>
>>         B.Arch I IGBC AP I M.Tech in Climate Change &
>>         Sustainable Development
>>
>>         Faculty of Sustainable Environment & Climate Change,
>>
>>         Centre for Environmental Planning & Technology
>>         (CEPT) University
>>
>>
>>
>>
>>     --
>>
>>     Regards,
>>     Mansi Jayswal,
>>     B.Arch I IGBC AP I M.Tech in Climate Change &
>>     Sustainable Development
>>     Faculty of Sustainable Environment & Climate Change,
>>     Centre for Environmental Planning & Technology (CEPT)
>>     University
>>
>>
>>     _______________________________________________
>>     Equest-users mailing list
>>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>     To unsubscribe from this mailing list send  a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG  <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>     _______________________________________________
>     Equest-users mailing list
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>     To unsubscribe from this mailing list send  a blank
>     message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-- 
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists


More information about the Equest-users mailing list