[Equest-users] Modeling a non-existing cooling system
Jeff Ross-Bain
jeff at rbgb.com
Thu Mar 15 05:47:35 PDT 2012
Thank you very much for your thoughts. This is very helpful.
Regards -
Jeff Ross-Bain, PE, LEED AP BD+C
Principal
404-220-8940 Office
404-220-8955 Direct
www.rbgb.com <http://www.rbgb.com/>
Build Green. Save Time
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Thursday, March 15, 2012 7:26 AM
To: James Hess
Cc: Jeff Ross-Bain; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modeling a non-existing cooling system
As long as the cooling thermostat setpoints are identical in both models,
USGBC should approve of it. We have done this on numerous projects for
small storage spaces and stairwells.
Rob
On Wed, Mar 14, 2012 at 6:14 PM, James Hess <JHess at tmecorp.com> wrote:
I believe you have to include the cooling system in the model (per ASHRAE),
but with the cooling thermostat set-point set high (i.e. up to 90 degrees),
per USGBC, which effectively makes this a moot point. Is the cooling system
in the model? Yes, we met the modeling requirement. Does it have any
impact on the savings? The answer would be no.
That is how I would handle this situation.
I have seen this written down somewhere, maybe a USGBC interpretation, just
cannot remember where I saw this.
Regards,
JAH
James A. Hess, PE, CEM, BEMP
Energy Engineer
TME, Inc.
Little Rock, AR
Mobile: (501) 351-4667 <tel:%28501%29%20351-4667>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Ross-Bain
Sent: Friday, March 09, 2012 1:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling a non-existing cooling system
Hi All,
>From my understanding of ASHRAE 90.1 Appendix G Table G3.1 (10) and the
User's Manual, if a space has no cooling system, and it is a conditioned
space (i.e. NOT semiheated), then that space must have a cooling system
modeled and it would be identical for the proposed and baseline cases. I
completely understand the logic of this requirement - in most cases.
However, I am working on a fire station where the apparatus bay (the fire
trucks) are in a 4,000+ sq ft space that is heated only, but is a
conditioned space and not a semiheated space. This space is almost half of
the building area, will not be cooled, has large overhead doors that are
mostly open, and is a place where diesel engines run.
Does anyone out there know of any exception, or interpretation, to this
modeling rule for specific cases such as a fire station where a space can be
modeled as heated only for the baseline and proposed cases? The model will
be submitted for LEED review. I can certainly model a cooling system but it
does not seem to make sense in this case.
Thanks for your input and I really appreciate this forum.
Cheers!
Jeff Ross-Bain, PE, LEED AP BD+C
Principal
404-220-8940 Office
404-220-8955 Direct
www.rbgb.com <http://www.rbgb.com/>
Build Green. Save Time
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to