[Equest-users] Modeling a non-existing cooling system

Daniel Knapp danielk at arborus.ca
Fri Mar 9 13:23:47 PST 2012


Hi Jeff,

Look at ASHRAE 90.1-2010 systems 9 and 10 which are heating only.  They also show up in addenda dn, do, dp, dq, dr to 90.1-2007.  

Best wishes,
Dan


—
Daniel Knapp, PhD, LEED® AP O+M
danielk at arborus.ca

Arborus Consulting
Energy Strategies for the Built Environment
www.arborus.ca
76 Chamberlain Avenue 
Ottawa, ON, K1S 1V9 
Phone: (613) 234-7178 ext. 113
Fax: (613) 234-0740



On 2012-03-09, at 2:59 PM, Jeff Ross-Bain wrote:

> Hi All,
>  
> From my understanding of ASHRAE 90.1 Appendix G Table G3.1 (10) and the User’s Manual, if a space has no cooling system, and it is a conditioned space (i.e. NOT semiheated), then that space must have a cooling system modeled and it would be identical for the proposed and baseline cases. I completely understand the logic of this requirement – in most cases.
>  
> However, I am working on a fire station where the apparatus bay (the fire trucks) are in a 4,000+ sq ft space that is heated only, but is a conditioned space and not a semiheated space. This space is almost half of the building area, will not be cooled, has large overhead doors that are mostly open, and is a place where diesel engines run.
>  
> Does anyone out there know of any exception, or interpretation, to this modeling rule for specific cases such as a fire station where a space can be modeled as heated only for the baseline and proposed cases? The model will be submitted for LEED review. I can certainly model a cooling system but it does not seem to make sense in this case.
>  
> Thanks for your input and I really appreciate this forum.
>  
> Cheers!
>  
> Jeff Ross-Bain, PE, LEED AP BD+C
> Principal
> 404-220-8940 Office
> 404-220-8955 Direct
> www.rbgb.com
> 
> Build Green. Save Time
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120309/2fdd2b13/attachment.htm>


More information about the Equest-users mailing list