[Equest-users] Evaporative Cooling - Heating usage goes UP ??
Joe Huang
yjhuang at whiteboxtechnologies.com
Thu Mar 8 11:18:06 PST 2012
John,
This does not surprise me at all. How are you controlling the evaporative coolers? Many
things change when
you use an evaporative cooler (100% OA, more pre-cooling, etc.) , so you may be leaving
the building at the lower temperature at the beginning of the next day that then
necessitates more heating. I'd suggest you take a look at the indoor temperatures and
compare them to those with a RTU. As to what to do about it, it depends on what's your
objective - to minimize energy cost or electricity, no increase in heating fuel, etc.
Achieving that would
require some tweaking of the operations.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 3/7/2012 4:24 PM, John Aulbach wrote:
> I took several RTU units and replaced them with Evaporative Cooling in the Los Angeles
> area. In some zones, my heating consumption went UP. Any suggestions?
> John Aulbach
> Partner Energy
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120308/1ee77240/attachment.htm>
More information about the Equest-users
mailing list