[Equest-users] Query regarding PDEC ( Passive cooling ) simulation in eQuest

Joe Huang yjhuang at whiteboxtechnologies.com
Wed Mar 7 11:10:08 PST 2012


I beg to differ on this.  eQUEST has an evaporative cooling module.  The system that Mansi 
describes is essentially a direct evaporative cooler that uses natural forces instead of a 
fan to provide the air flow.  What I would do using eQUEST would be to model the building 
with a direct evaporative cooler at 100% outside air, and play around with the air flow 
rates to get a sense of how much cooling loads can be replaced.  To go further, you can 
also develop a functional equation relating the amount of air flow to the outdoor wind 
speed and temperature difference between the evap cooler outlet and the room air 
temperature.  If you were working with DOE-2.1E, an earlier version of the DOE-2.2 engine 
in eQUEST, you could put that in as a FUNCTION, but unfortunately DOE-2.2 doesn't accept 
FUNCTIONs.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"


On 3/7/2012 5:53 AM, Sami, Vikram wrote:
>
> Mansi,
>
> I doubt you can do this credibly in eQUEST. You really need a CFD type package to be 
> able to simulate this. . A word of caution -- the effort to develop the simulation for 
> this is a master's thesis in itself.
>
> **
>
> *Vikram Sami*, LEED AP BD+C
>
> Sustainable Design Analyst
>
> 1315 Peachtree St. NE, Atlanta, GA 30309
>
> t: 404-443-7462    f: 404.892.5823     e: vikram.sami at perkinswill.com 
> www.perkinswill.com <http://www.perkinswill.com/>
>
> *Perkins+Will.*Ideas + buildings that honor the broader goals of society
>
> *From:*equest-users-bounces at lists.onebuilding.org 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Mansi Jayswal
> *Sent:* Tuesday, March 06, 2012 11:25 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Query regarding PDEC ( Passive cooling ) simulation in eQuest
>
> Hello friends,
>
> My name is Mansi Jayswal. I am a final year student of Masters Programme at CEPT 
> University, India. By profession I am an architect. Currently I am doing thesis on 
> passive cooling technique (Passive down draught evaporative cooling system- PDEC ). And 
> try to identified that how much cooling load of HVAC system can be replaced through this 
> system.
>
> Now my query is that is it eQuest is capable to simulate such building with wind tower 
> or PHDC (PDEC ) system? If anybody knows please kindly reply. I have very days left for 
> final submission and I am stuck here.
>
> Thanks
>
> -- 
>
>
> Regards,
>
> Mansi Jayswal,
>
> B.Arch I IGBC AP I M.Tech in Climate Change & Sustainable Development
>
> Faculty of Sustainable Environment & Climate Change,
>
> Centre for Environmental Planning & Technology (CEPT) University
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120307/aac66633/attachment.htm>


More information about the Equest-users mailing list