[Equest-users] Electric Block Rate based on monthly demand

Jeremy Poling Jeremy.Poling at transwestern.net
Tue Jan 31 07:18:36 PST 2012


You have my sympathy - that seems like a needlessly confusing rate structure!

I think the block charges will allow you to do this, though.  There is a BLOCK#-TYPE keyword value of "KWH/KW-LIMITSUM" that is defined as "Used when the sum of the kWh in a series of ENERGY blocks is limited by a kWh/kW value. The maximum value is specified in the BLOCK-DATA." This is from the DOE-2 help, Volume 2: Dictionary.  I have never used it so my value may cease there, but that would be my first attempt at getting this rate structure into eQuest.

Jeremy R. Poling, PE, LEED AP+BDC


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Mantai
Sent: Tuesday, January 31, 2012 8:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Electric Block Rate based on monthly demand

I have a utility rate that has blocks based on the kWh/kW for each month rather than strictly kWh usage (see below).  I did not see a way in eQuest to input this type of rate in the detailed edit mode.  Has anyone ever dealt with a rate like this in eQuest or have any suggestions?  I have a spreadsheet set up to calculate the costs but I hate having to figure out the monthly peak kW and input to the spreadsheet for every model iteration.

[cid:image001.png at 01CCDFF8.D99229A0]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120131/927102d9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 65056 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120131/927102d9/attachment.png>


More information about the Equest-users mailing list