[Equest-users] Factory Building with Refrigeration
Michael Wilson
mwilson at enerficiency.ca
Mon Jan 30 15:45:13 PST 2012
Hi Nick. Im working on a processing plant with some cold storage rooms
right now, and Ive found you can get 35 degree supply air temps and
maintain room temps down to 37. If youre using PSZ, it doesnt use
COOL-SET-T but uses MIN-SUPPLY-T instead. I had to fudge the supply air
volumes with such a small dT, and change the curves as they didnt make
sense at such low temps. But it seems to work.
I was very interested to hear there was a refrigeration version. That would
have been very handy for this project (too late now), as there are some
rooms below 35. Ill try that next time.
Mike
Michael Wilson, P.Eng.
PO Box 1911 - 458 Abbs Rd.
Gibsons, BC V0N 1V0
604-886-9864
www.enerficiency.ca
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeremy
Poling
Sent: January-30-12 1:00 PM
To: Nick Caton; Ömer Moltay; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Factory Building with Refrigeration
Nick,
Such a coincidence :) Im pretty sure Scott helped out my coworker Ken with
a few items when he was working on the model I described below. Jeff and
Scott are more than welcome to correct me if my memory is incorrect on any
of this.
Heres the research I did over lunch trying to keep myself sane on where the
low-limit on zone temps came from. If you look at the keywords, the
DESIGN-COOL-T keyword has a range of 0-90 and will error on either side of
that number, but the MIN_SUPPLY_T keyword has a range of 35-70 and the
COOL-SET-T keyword has a range of 45-70. So effectively, the system will
not be allowed to go below a cold deck leaving temperature of 45F. This
will probably make it difficult to use for modeling the cold zones of the
penguin exhibit but likely okay for the cool zones (Key part for Scott and
Jeff to confirm).
The refrigeration model can handle packaged refrigeration equipment that can
deal with the colder temperatures. The range you noted of 46-48 is pretty
similar to the temperatures used in food processing and storage for cooler
spaces as opposed to freezer spaces. That said, you would not be able to
model a ground-source system in the refrigeration model, unless you find
some really creative work-around that escaped us or wasnt available when we
were doing our complicated model.
What we did to help mesh the models was to fake the portion of each model
that wouldnt work 100%, created a common back-of-house portion of the
model that was the same in both, then used the strengths of each version of
eQuest to model the respective spaces. So in this case, you would end up
with two separate models (and their respective baselines if youre
ultimately using it for LEED or need to compare it to something):
1. eQuest-Standard Model: back-of-house as designed, cool spaces as
designed, cold spaces faked as close as possible to represent the cold
temperatures
2. eQuest-Refrigeration Model: back-of-house as designed, cool
spaces faked to maintain temperatures without regard for system/energy,
cold spaces as designed
As long as you meter everything out separately, your final energy use is the
sum of the cold space meters from the eQuestR model, the cool spaces
from the eQuest model, then we used the highest of the two back-of-house
results to be conservative (there were minor differences that we didnt have
enough time to ferret out the entire cause).
You can see why, with a huge amount of respect and thanks to Scott, Jeff,
et.al
Id almost rather put the time into learning the extra tool for my
tool belt than try to do this again the same way :) Id be curious to know
if there have been any major changes to the Refrigeration model since then
that might streamline the process we used?
Jeremy R. Poling, PE, LEED AP+BDC
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Monday, January 30, 2012 2:30 PM
To: Jeremy Poling; Ömer Moltay; equest-users at lists.onebuilding.org
Cc: Jeff.Hirsch at DOE2.com; Scott Criswell
Subject: RE: [Equest-users] Factory Building with Refrigeration
Hey Jeremy!
Saw this post today and what weird timing
I have another unique/interesting
scenario for a project on the horizon your advice/experience seems perfect
for: A penguin exhibit for the local zoo!
Will have multiple zones targeting 46-48F. This model is primarily to
explore different options with regard to just what equipment really makes
sense from the outset and over the long term a ground source wellfield is
on the table as a definite option, and I gather our design team is very open
to using entirely separate systems for the cool (68-70) vs. cold (46-48)
zones.
Do you think design temps in the mid-high 40s might still crunch out
alright with the regular eQuest version? Im really not sure what to expect
in the way of system options to be tossed at me, but it would help to have a
solid understanding of the limitations moving forward
I think Id prefer
to stick with the tools Im most familiar with if they remain feasible for
the task at hand.
Jeff/Scott: Copying you gurus per Jeremys advice any thoughts?
Thanks fellas!
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeremy
Poling
Sent: Monday, January 30, 2012 9:01 AM
To: Ömer Moltay; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Factory Building with Refrigeration
The refrigeration version would allow the space temperatures typical of an
ice cream factory. I cant remember the exact temperature, but you cannot
model a space in the regular version of eQuest too much below 50-degrees-F.
Also, I havent seen many industrial ammonia absorbers but ammonia is a
common low-temperature refrigerant. The refrigeration version has the
components typical to a refrigeration plant (separate compressors,
evaporators, and condensers) while the standard version would have to be
forced into modeling it and certain components might not even be able to do
that.
The refrigeration version is very powerful and Ive used it on projects
before, but it is a little bit more raw than the standard version. We had a
complex project that required both ground-source heat pumps and
refrigeration and unfortunately couldnt use just one version of eQuest to
model the building, which made for an interesting process.
I have nothing against eQuest and we ended up with a solid model due partly
to the software, but if I had to do such a complex model over again I would
probably pick TRNSYS instead just due to the flexibility to build in
multiple unique components. If your model is more of a standard
refrigeration system, though, the refrigeration version of eQuest should be
fine. Id recommend getting in touch with the James Hirsch team for
assistance if needed since the experience on the lists tends to be thinner
on this topic. They were very helpful to us when we used the software.
Jeremy R. Poling, PE, LEED AP+BDC
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ömer Moltay
Sent: Monday, January 30, 2012 8:27 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Factory Building with Refrigeration
Dear All,
We are faced with an ice cream factory where all the production spaces and
finished product warehouse spaces are cooled with ammonia absorption
chillers. We are trying to understand if there is any need to use the eQuest
Refrigeration version? What are the advantages of this over the standard
eQuest releases? As far as I know, the standard version can also model
absorption chillers. In which cases does it make sense to use the
Refrigeration version? What are your recommendations on how to approach
modeling this building?
Thank you,
Omer Moltay, LEED AP BD+C, BREEAM Assessor
Mimta Ltd.
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.mimtarch.com
www.eko-yapi.net
www.mimtasolar.com
www.servogas.com
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1901 / Virus Database: 2109/4776 - Release Date: 01/30/12
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120130/a244654e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120130/a244654e/attachment.jpeg>
More information about the Equest-users
mailing list