[Equest-users] ASHRAE 90.1 Baseline HVAC System

Jeremy Poling Jeremy.Poling at transwestern.net
Fri Jan 13 15:37:15 PST 2012


I could be wrong, but I had always understood that you typically did not consider the parking structure when making this determination, so residential would be the predominant condition for this specific case.  Also note exception "a" to G3.1.1 - you would use different system types for the non-residential and residential in this case since both are over the 20,000SF (~2,000 SM rough conversion) size limit under that exception.  Parking would be considered unconditioned or semi-conditioned depending on the BTU/h for heating and climate zone (see the definitions in Section 3 of ASHRAE 90.1) unless you exceed the heating for a semi-conditioned space, which would then make the garage part of your conditioned floor area (not very common but I did see it happen once) and your predominant space type would be non-residential.

Jeremy R. Poling, PE, LEED AP+BDC


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fisnik Rushiti
Sent: Friday, January 13, 2012 5:00 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE 90.1 Baseline HVAC System

Omar,
 you have to use predominant condition to determine the system type for entire building, refer to ASHRAE (as highlighted) provided:

[cid:image001.png at 01CCD219.FCC50F10]
Fisnik Rushiti, Dipl.Eng.Arch.
Energy Analyst
608-232-4323
Flad Architects
644 Science Drive
PO Box 44977
Madison, WI  53711
P 608-238-2661
F 608-238-6727
E frushiti at flad.com<mailto:frushiti at flad.com>
www.flad.com<http://www.flad.com>

Dear All,

In a project to be LEED certified, we have the following areas:

10400 m2 retail and restaurant
11000 m2 residential (multifamily)
12000 m2 underground car parking

In selecting the baseline HVAC system, would this be considered a RESIDENTIAL or NONRESIDENTIAL building type? What is the criteria for selection?

Thank you,

Omer Moltay
Mimta
On 1/13/2012 3:34 PM, equest-users-request at lists.onebuilding.org<mailto:equest-users-request at lists.onebuilding.org> wrote:

Send Equest-users mailing list submissions to

        equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>



To subscribe or unsubscribe via the World Wide Web, visit

        http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org



or, via email, send a message with subject or body 'help' to

        equest-users-request at lists.onebuilding.org<mailto:equest-users-request at lists.onebuilding.org>



You can reach the person managing the list at

        equest-users-owner at lists.onebuilding.org<mailto:equest-users-owner at lists.onebuilding.org>



When replying, please edit your Subject line so it is more specific

than "Re: Contents of Equest-users digest..."




Today's Topics:



   1. Re: Help - Modeling VRV-VRF System with eQuest (Paul Diglio)

   2. How to Claim Credits for Natural Ventilation in Multifamily

      High Rise Residential? (?mer Moltay)

   3. corrupt .sim file (Sangeetha Divakar)

   4. Fwd: corrupt .sim file (Sangeetha Divakar)

   5. Re: Help - Modeling VRV-VRF System with eQuest (Bruce Easterbrook)

   6. Re: Help - Modeling VRV-VRF System with eQuest (Dahlstrom, Aaron)

   7. Re: Fwd: corrupt .sim file (Dahlstrom, Aaron)

   8. Re: How to Claim Credits for Natural Ventilation in

      Multifamily High Rise Residential? (Dahlstrom, Aaron)

   9. DX vs. Chilled Water: Unrealistic cooling loads (Walson, Kristy)

  10. Re: DX vs. Chilled Water: Unrealistic cooling loads

      (Walson, Kristy)

  11. ASHRAE 90.1 Baseline HVAC System (?mer Moltay)

  12. Energy Model for Rowhome (McGrath, Brendan)

  13. Re: Energy Model for Rowhome (Daniel Knapp)

  14. Re: ASHRAE 90.1 Baseline HVAC System (Nathan Miller)

  15. Refrigeration condenser fans (Ron Pecarina)

  16. EnergyPlus versus eQUEST Fan Energy Usage (Campion Mark)




_______________________________________________

Equest-users mailing list

Equest-users at lists.onebuilding.org<mailto:Equest-users at lists.onebuilding.org>

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120113/45f7def8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 16986 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120113/45f7def8/attachment.png>


More information about the Equest-users mailing list