  Hello Jing,

Table 23 in the BARB report includes the estimated annual energy use for 
each appliance.  I suggest developing an average sensible and latent 
fraction by multiplying the annual energy for each appliance by the its 
sensible and latent fractions.  Sum these for all appliances and then 
divide the sensible sum and the latent sum by by total annual energy 
use.  This should give you representative sensible and latent fractions.

Regards,
Vern

_______________________
Vernon A. Smith, P.E.
Smith Energy Engineers, LLC
720-320-9154


On 12:59 PM, Jing Hong wrote:
> Hi all,
> When i was trying to put the sensible Ht (frac) in cooking loads 
> section, i met a problem. I followed the Building America Research 
> Benchmark (BARB) to define my model. In that case, I should put the 
> Sensible load fraction of Refringerator, Dishwasher, range showed on 
> BARB into my equest model. However, those appliances has different 
> fraction, but i have only one blank for the sensible fraction of 
> kitchen in eQuest. How could I decide what number I should choose to 
> put in? Did some one use Benchmark to build eQuest model before can 
> help me? I am appreciated.
> Jing