[Equest-users] Cooling Sizing Ratio & Unmet Load hours

GK Pandian kgkpandian at gmail.com
Thu Feb 16 01:32:41 PST 2012


Riad,


Q1- You can specify the selected fan capacity (cfm,static
pressure,...etc) in proposed model.

Q2- I do consider whole building unmethours should be <300 hrs. To see
the unmet hours,go to Air-Side HVAC / Summary. The last column "Hours
outside throttling range" represents the unmet hours.(attached screen
shot)

Hope this is helps.

Thanks
GK


On 2/16/12, GK Pandian <kgkpandian at gmail.com> wrote:
> Riad,
>
>
> Q1- You can specify the selected fan capacity (cfm,static
> pressure,...etc) in proposed model.
>
> Q2- I do consider whole building unmethours should be <300 hrs. To see
> the unmet hours,go to Air-Side HVAC / Summary. The last column "Hours
> outside throttling range" represents the unmet hours.(attached screen
> shot)
>
> Hope this is helps.
>
> Thanks
> GK
>
>
>
>
>
>
> On 2/16/12, RIAD ABED <riad_abed at hotmail.com> wrote:
>>
>> Dear All e-Quest Users
>>
>> Please If someone can help :
>>
>> 1- for Sizing Ratio : 1.15 (for Cooling – Equipment Efficiencies) , it
>> should applied be for Baseline Model only ? or also it should be in
>> Proposed
>> Model ?
>> 2- for Umnet Load Hours it should be under 300 Hours for Each Room/Zone ?
>> or
>> For the Total Building ? & where I can find the Umet Load Hours in
>> e-Quest
>> simulation Report
>>
>> Thanks by Advance for all of u …….
>>
>> My Regards,
>> Riad el Abed
>> Chief MEP , LEED GA,PQP
>> ASHRAE MEMBER
>> Tel  +96170 643977
>> www.riadabed.com
>>
>> DEC Consultants
>> Po Box 26330
>> Abu Dhabi
>> Tel +9712 4457505
>> Fax +9712 4457506
>> www.dec.ae
>> _____________________________________________________________________
>> DISCLAIMER
>> This email and any files transmitted with it are confidential and
>> intended
>> solely for the use of the individual or entity to whom they are
>> addressed.
>> If you have received this email in error please notify the sender. Please
>> note that any views or opinions presented in this email are solely those
>> of
>> the author and do not necessarily represent those of DEC Consultants.
>> Finally, although efforts were made to prevent virus transmission, the
>> recipient should check this email and any attachments for the presence of
>> viruses. DEC Consultants accepts no liability for any damage caused by
>> any
>> virus transmitted by this email.
>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Unmet hours.pdf
Type: application/pdf
Size: 105295 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/ec6471a8/attachment.pdf>


More information about the Equest-users mailing list