First I'd like to thank you for making me feel that im not alone in this
situation.
You've mentioned whole building simulation method, is that the same
as Performance Rating Method (90.1 Appendix-G)?
With performance rating method, Section G.1.1 says all mandatories should
still be met.
Bob
On Wed, Feb 8, 2012 at 6:39 PM, Yusuf Turab <yusuf at ytenterprises.com> wrote:
> [image: Boxbe] <https://www.boxbe.com/overview> Yusuf Turab (
> yusuf at ytenterprises.com) is not on your Guest List<https://www.boxbe.com/approved-list>| Approve
> sender <https://www.boxbe.com/anno?tc=10629537763_582448682> | Approve
> domain <https://www.boxbe.com/anno?tc=10629537763_582448682&dom>
>
> Bob
>
> I understand where you are coming from. Indian developers have the
> same dilemma. Unfortunately, for the prescriptive approach you do not have
> a choice. You have to design as per the standard even though the ROI is
> very poor. I suggest you follow the whole building simulation method. You
> will be able to demonstrate significant savings using simple strategies
> like shading, high performance glass, optimised orientation etc. This might
> help you do away with insulating the walls.
>
> Hope this helps
> Yusuf Turab
>
>
> Turning that around:****
>>>
>>> ** **
>>>
>>> “Where you are not required to have insulation, 5.8.1.1-9 does not come
>>> into play.”****
>>>
>>> ** **
>>>
>>> I don’t believe this is a “follow either A or B” statement – more like
>>> “if A, then B.”****
>>>
>>> ** **
>>>
>>> ~Nick**
>>>
>>> * *
>>>
>>> [image: cid:489575314 at 22072009-0ABB]**
>>>
>>> *NICK CATON, P.E.***
>>>
>>> SENIOR ENGINEER****
>>>
>>> ** **
>>>
>>> Smith & Boucher Engineers****
>>>
>>> 25501 west valley parkway, suite 200****
>>>
>>> olathe, ks 66061****
>>>
>>> direct 913.344.0036****
>>>
>>> fax 913.345.0617****
>>>
>>> www.smithboucher.com* *****
>>>
>>> ** **
>>>
>>> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
>>> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Ty Law
>>> *Sent:* Tuesday, February 07, 2012 2:28 AM
>>> *To:* equest-users at lists.onebuilding.org
>>> *Subject:* [Equest-users] Fwd: Fw: Mandatory Provisions 5.4****
>>>
>>> ** **
>>>
>>> Hi Everyone,****
>>>
>>> ****
>>>
>>> I am quite confused between what the ASHRAE 90.1 and the user’s manual
>>> tell us about Building Envelope Mandatory Provisions:****
>>>
>>> ****
>>>
>>> *5.4 Mandatory Provisions*****
>>>
>>> *“5.4.1 Insulation.** Where insulation is required in Section*****
>>>
>>> *5.5 or 5.6, it shall comply with the requirements found in Sections****
>>> *
>>>
>>> *5.8.1.1 through 5.8.1.9.” - ASHRAE 90.1-2007*****
>>>
>>> * *****
>>>
>>> ****
>>>
>>> *Insulation (§ 5.8.1)*****
>>>
>>> *“**The first set of mandatory requirements*****
>>>
>>> *addresses the proper installation and*****
>>>
>>> *protection of insulation materials. Issues*****
>>>
>>> *that are covered include compression of*****
>>>
>>> *insulation, installing insulation on sloping*****
>>>
>>> *ceilings and around recessed equipment,*****
>>>
>>> *and protecting insulation from physical or*****
>>>
>>> *moisture damage.”- ASHRAE 90.1-2007-User’s Manual*****
>>>
>>> * *****
>>>
>>> ****
>>>
>>> Does this mean that we could use insulation that is not as efficient as
>>> indicated in Table 5.5-1 through 5.5-8 as long as it complies with Section
>>> 5.8.1.1 through 5.8.1.9?****
>>>
>>> ****
>>>
>>> Your thoughts are highly appreciated.****
>>>
>>> ** **
>>>
>>> ** **
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120209/526d812c/attachment.htm>
More information about the Equest-users
mailing list