[Equest-users] building level energy use metering by zone?
David Eldridge
dse at grummanbutkus.com
Tue Feb 7 08:43:38 PST 2012
If you extend this to the constructed building, you'd still have to make an allocation for energy use at an air-handling unit & central plant amongst the zones (assuming you have a central system here prompting the question).
At least in model space you can create an hourly output report with zonal airflow/heat/cool that you can take back to the hourly plant/AHU reported usage as a basis for your percentage, rather than just by floor area.
It will need to be done in a spreadsheet though, outside of eQuest.
DSE Mobile
On Feb 7, 2012, at 8:12 AM, "Zabaneh, Christopher" <czabaneh at halsall.com> wrote:
> Does anyone know of an ‘easy’ way to track all the building-level energy used by a particular zone in eQuest (including the proportion of fan, pump, heating, cooling, etc energy from common a system and/or plant). Right now attaching a sub-meter to a zone is only giving me the usage of that zone’s loads (lighting, occupant load, gas appliances in the zone), but what I really want is to divvy up all end-uses amongst all the zones.
>
> I’m trying to determine the utility cost of a specific zone and didn’t want to default to an area-weighted approach of dividing each energy end-use among all the zones.
>
> Thanks kindly,
>
> Christopher Zabaneh, P.E., LEED AP BD+C, CEPE
> Project Associate
>
> Halsall Associates
> Tel: 416.644.0416 • Toll Free: 1.888.425.7255 ext. 258• www.halsall.com
> Vancouver • Calgary • Sudbury • Burlington • Toronto • Ottawa • Dubai
> Best Workplaces in Canada, Five Consecutive Years: 2007 - 2011
> __________________________
> A Parsons Brinckerhoff Company
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120207/1d8c6f34/attachment.htm>
More information about the Equest-users
mailing list