[Equest-users] how to simulate PTAC reasonably

Nick Caton ncaton at smithboucher.com
Wed Apr 25 14:38:12 PDT 2012


Hi there,

Sounds like you are getting yourself turned around... There are a few schools of thought out there regarding exactly how cooling EIR should be derived from a fan-inclusive energy rating (it's my understanding future versions/addenda to 90.1 may address/clarify this with a sort of generic set of "non-fan cooling/heating efficiency factors"), but you should not be entering 0.0 energy for your fan in any case.

Presently, one can choose to figure a baseline system cooling EIR using either the baseline Pfan or ARI procedure fan power figures...  I have used both without consequence, and the two methods (usually) produce similar results, but I have gathered over time approaches based on ARI fan energies are easier to pick up and may be more widely practiced, so I'll describe that approach here.  The archives contain a few discussions (look for my name) describing Pfan-based methods as well:


-          Use the modeled capacity (SV-A) and prescribed EER to determine the Total system energy at full capacity.

-          Determine the fan power as specified by the ARI rating procedures (365W/CFM) using the modeled baseline system airflow (SV-A).  This is distinct from Pfan.

-          Subtract the ARI fan energy from the total system energy.  The result is the non-fan energy.

-          Divide this remainder (non-fan energy) by the capacity (SV-A) and adjust/convert as necessary to make the ratio unitless - now you've found cooling EIR.

Interesting to note:  I've learned HAP's baseline automation tools use an ARI-based procedure much like the above, but further tweaks the numbers to account for local design conditions differing from ARI test conditions.  In practice this makes the same baseline system in very hot design conditions like Arizona cool less efficiently than in more temperate design conditions... It took me awhile but I've come to wrap my head around the logic.  Does anybody using eQuest or otherwise doing these baseline calcs "by hand" perform a similar efficiency 'de-rating' in their spreadsheet calcs?

~Nick

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Aaron
Sent: Tuesday, April 24, 2012 11:26 PM
To: equest-users
Subject: [Equest-users] how to simulate PTAC reasonably

Dear all
     If baseline is system 1 (PTAC), the equipment is decided according to table 6.8.1D which is for the whole equipment, while 90.1 Manual says the supply fan energy (0.3W/cfm for system 1&2) should be separate from cooling system energy, shown as the picture below
      [cid:image002.png at 01CD22F8.8BB28A20]
     About how to calculate the COP except supply fan energy, the manual also gives the equation as shown below:
   [cid:image003.png at 01CD22F8.8BB28A20]
I try to find the Cooling Capacity for every PTAC system in SV-A report and calculate the COP for the cooling section(Compressor and condenser), while when I input the cooling EIP (1/COP) in cooling uni and 0.3W/cfm for supply fan, the energy consumption is much higher than inputting the whole EER for the cooling EIR and 0 W/cfm for the supply fan before. From the energy breakdown contrast, what surprises me is that the energy for cooling is more than before.
When I try to change the fan delta t from 0.93 to 0 and find the cooling energy is decreasing than inputting the whole EER, but the sum of cooling and fan is still more than inputting the whole EER , have anyone met the same confusion before and tell me the reason and how to simulate PTAC reasonably.
Thanks a lot
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/f94c7d2e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/f94c7d2e/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 72037 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/f94c7d2e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 28229 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/f94c7d2e/attachment-0001.png>


More information about the Equest-users mailing list