Use Powered induction for the system type, and in the cooling source under
the cooling->coil capacity/control tab cool source as electric DX. If
eQuest is not allowing that, maybe you don't have the latest version
(actually this has been possible for quite some time).
-Rohini
On Wed, Apr 25, 2012 at 10:00 AM, Caleb Freeman <calebsfreeman at gmail.com>wrote:

> I am modeling an ASHRAE system type 6 and cannot seem to get equest to
> model this system type.  I have tried to user override the VAV to parallel
> but that does not work.  The default expression is set up to only allow
> parallel piu boxes for a piu system, but the only available piu system type
> is chilled water.  Any suggestions to override the VAV box type or the
> system type to DX from CHW would be helpful.
>
> Thanks in advance,
>
> Caleb
>