[Equest-users] outside air flow during unoccupied/setback hours
R B
slv3sat at gmail.com
Tue Apr 24 09:54:25 PDT 2012
I normally have a min sch specified at the zone level - 0 for unoccupied
hours and -999 for other hours that takes care of this comment.
There is an hourly report for fan coming on during night cycle flag (or
something similar). If you do not have the fan coming on or do not have the
night cycle control, you should be ok. You can also look at the hourly
report for OA ratio and whether fan is on/off during the unoccupied time.
-Rohini
On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti <ramana.koti at gmail.com> wrote:
> Dear All,
>
> One of the LEED review comments on a university building project I'm
> working on suggests to verify that all systems in baseline and proposed
> models contain zero outside air flow when fans are cycled on to meet
> setback temperatures during unoccupied hours.
>
> What is the best way to go about verifying this? In the 'Hourly Report
> Block' options under a system, I find 'Hourly summed zone OA CFM for DCV
> calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation
> (cfm/cf/). Is one or both of these options under an hourly report, the way
> to go or is there a better way of doing it?
>
> Thanks,
> Ramana.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120424/16dba0cf/attachment.htm>
More information about the Equest-users
mailing list