Hi Ben,

 

In this case, it looks like the usual suspect: reheat. If you shut off your dehumidification limit of 50%, it eliminates the summer heating issue. 

 

Also, I don’t know how much control you have over your economizer settings, but if you haven’t read this article <http://www.taylor-engineering.com/downloads/articles/ASHRAE%20Journal%20-%20Economizer%20High%20Limit%20Devices%20and%20Why%20Enthalpy%20Economizers%20Don't%20Work%20-%20Taylor%20&%20Cheng.pdf> , I’d strongly suggest it. As an interesting aside – that author’s comments on RH sensor reliability matches well with what I’ve found on a recent project. Here’s a little data I’ve gathered from a college campus. I harvested 24hr trend data from all the buildings that were measuring OA humidity (y-axis in %). The fat blue line is what I got from the National Weather Service for the area and each other line represents a building’s OA humidity sensor. I think in total these sensors control at least 25 AHU’s enthalpy economizers. From what I can tell, they don’t have a regular PM routine for calibrating/replacing these sensors. Just something to consider…

 

 

 

Eric O'Neill 

608.785.3328 | MICHAELS ENERGY

 

-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of modeling at jeisenhart.com
Sent: Friday, April 13, 2012 8:44 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heating in Summer

 

Hello Everyone!

 

Here's a puzzle for the email group.  (I hope you're having a better

weekend than me!)

I've searched the archived emails to find a solution, but most seem to ask

for the PD2 and INP file so that makes me think that the solutions will

mostly be unique.

I'm attaching a zip file of my model.

 

I have packaged single zone units with electric resistence heat.  I'm

seeing a significant load in the summer on all units.  I've dropped the

thermostat in the summer months on the heating and am still getting a

load. Any ideas on why there would be a load?

 

Thanks,

Ben

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120416/1233dff2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 99922 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120416/1233dff2/attachment.png>


More information about the Equest-users mailing list