I run into this often as I move projects around and work on them from different locations. The .dwg file itself is never an "integral/imported" part of the project's files - only a path is defined, so eQuest will prompt you on starting up for the CAD file's location any time the project's files or the CAD file is moved around (to be expected if you're working with others on a thumb drive or similar).
To re-emphasis John's point: This isn't something to lose sleep over =). The "CAD file not found" message is something you can safely ignore entirely once you are past zone/perimeter geometry definitions in the wizards. The CAD file is not actually used anywhere in eQuest beyond serving as a "reference" for the duration of those screens.
Once you are finished defining zone/perimeter geometries in wizards, you can feel safe choosing "remove all" from the following dialog:
[cid:image001.png at 01CD165C.FB457D50]
For the duration where your group may wish to go back and revise those geometries using the CAD file, I'd advise keeping a copy of the .dwg file alongside other "reference" files to "browse" to as needed.
As an organizational practice/suggestion, I commonly have a small "reference" directory that I'll save and move around alongside the actual model files containing items like this and other notes, PDF's, messages, and other electronic information I used while assembling the model. Keeping this stuff in one place can make many things easier down the road, even well after finishing the project-at-hand!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr.
Sent: Monday, April 09, 2012 12:02 PM
To: John Aulbach
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] (no subject)
the path to the .dwg file is hard-coded into the equest file so if you move the .dwg the next time you open the simulation file you'll get a prompt that equest can't find it & would you like to locate it.
alternatively you could just edit the .pd2 file and/or .inp file (using notepad) & change the hard-coded path to a moved .dwg file prior to opening the simulation file again.
On 4/9/12 9:55 AM, John Aulbach wrote:
Hi Laura:
You essentially have the .DWG file on your computer, fire up eQuest, and when you get to the drawing mode in the Wizard, call up the .DWG file and trace around it. I am unsure as to whether the image of the .DWG file follows the eQuest model around, or whether the program has to find it each time. Once you trace the building, you will actually not need the .DWG file again.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
2154 Torrance Blvd, Ste. 100, Torrance, CA 90501
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com<http://www.ptrenergy.com> | jaulbach at ptrenergy.com<mailto:%7C%20jaulbach at ptrenergy.com>
From: Laura Falk <laurafalk at hotmail.com><mailto:laurafalk at hotmail.com>
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Sent: Monday, April 9, 2012 9:48 AM
Subject: [Equest-users] (no subject)
I am studying Equest in school, we are working on a group project. Is there a way to "bind" an Autocad drawing to an Equest file? Or does the .dwg file need to be loaded on whatever computer we are working on?
Thank you
Laura Falk-Helgemoe
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120409/03326d68/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8866 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120409/03326d68/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120409/03326d68/attachment.jpg>
More information about the Equest-users
mailing list