[Equest-users] Advice on modelling nine story atrium acrossshells

Jeremy McClanathan jmcclanathan at CDiengineers.com
Mon Apr 2 14:26:27 PDT 2012


If CFD isn't an option, one other eQuest option would be to break the atrium up into one conditioned, and one or more plenums (TYPE = PLENUM, not UNCONDITIONED).  Make an assumption about how much load is displaced or only present in the plenum portion of the atrium.  Then, put a portion of the glazing and loads in the plenum(s).  You might for example assume that the bottom two floors are one conditioned zone, and the top seven floors are a large plenum.  I believe the air in the plenum should pick up the heat from the glazing and loads placed in it.   I would be cautious about using eQuest to predict what will actually happen in an atrium though.
Jeremy

___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C
[cid:image001.jpg at 01CD10DB.37C9D9B0]
4200 194th St SW, Ste 200, Lynnwood, WA 98036
P 425-672-1071 | F 425-778-8769
P Please consider the environment before printing this email.

From: CleanTech Analytics [mailto:jeremiah at cleantechanalytics.com]
Sent: Monday, April 02, 2012 2:06 PM
To: Jason Quinn
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Advice on modelling nine story atrium across shells

Sounds like a task that would be better done with single zone and analysed using CFD to me..
Possibly use a CFD program then use insight to work around your Equest model..


Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
www.cleantechanalytics.com<http://www.cleantechanalytics.com>

[http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG]

This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics


On Mon, Apr 2, 2012 at 10:28 AM, Jason Quinn <jason.e.quinn at gmail.com<mailto:jason.e.quinn at gmail.com>> wrote:
I've modeled a nine story office building which requires different
shells for several of the levels in the building. It also has a nine
story (full height) atrium that will be used to extract all of the
exhaust air (i.e. supply OA to the floors and condition via FC units
and pull exhaust air out of the top of the atrium). I'm aware that
eQuest doesn't track air flows but I'd like to best approximate the
atrium effects on the overall energy use of the building.

Current approach: I've modeled each floor as a separate zone and I'm
going to delete the floors and turn the ceilings into air-walls and
link them to the zone above. Currently I'm conditioning all of the
zones that make up the atrium but at some point I'd like to explore
not conditioning these zones to more accurately approximate how we'd
run the building.

Comments?

One alternate approach I've seen proposed is to replace all nine zones
in the atrium with one full height zone - the advantage is the glass
on the roof and upper walls can "see" the floor and walls in all of
the zones of the atrium. However this won't let me later go back in
and explore any variation of temperature with height. I think this
might be important as I would expect the air at the top of the atrium
to be warmer and cause more load on the top floor zones next to the
atrium.

--
Jason Quinn
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws.  If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments.  If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120402/4f5c801b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1232 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120402/4f5c801b/attachment.jpg>


More information about the Equest-users mailing list