From jason.e.quinn at gmail.com Sun Apr 1 20:28:29 2012 From: jason.e.quinn at gmail.com (Jason Quinn) Date: Mon, 2 Apr 2012 15:28:29 +1200 Subject: [Equest-users] Warning Daylighting unit normal greater than 1 - how to fix this? Message-ID: I've a atrium with glass roof and walls - I've set this up with really large separate windows. This error about unit normal has popped up in the .sim file (although my results have not shifted that I can tell. **WARNING********************************************************************** Daylighting coefficient calculation for SPACE LV8SE Perim Spc (G.SE10) for reference point 1 encountered an ERROR. The unit normal for the contribution from WINDOW LV8Skylt (G.SE10.E19.S1) had a length greater than 1.0. WNORM was: 0.0000000 0.0000000 1.0000001 One or more WNORM components have been reset to 1.0 to correct the problem. Any ideas on how to fix this? I moved the daylight sensor location and changed the azimuth but the error has not changed. -- Jason From aloysiusdecruz2004 at yahoo.com Mon Apr 2 04:16:37 2012 From: aloysiusdecruz2004 at yahoo.com (Aloysius Decruz) Date: Mon, 2 Apr 2012 04:16:37 -0700 (PDT) Subject: [Equest-users] (no subject) Message-ID: <1333365397.57401.YahooMailMobile@web161403.mail.bf1.yahoo.com> http://900li.com/blog.old/wp-content/plugins/extended-comment-options/02efpk.html -------------- next part -------------- An HTML attachment was scrubbed... URL: From fbetz at aeieng.com Mon Apr 2 09:03:06 2012 From: fbetz at aeieng.com (Fred Betz) Date: Mon, 2 Apr 2012 16:03:06 +0000 Subject: [Equest-users] Modeling chilled beams (IU) with zone level cooling as secondary loop Message-ID: Has any tried modeling the IU system with a chilled water loop with ~42F at the AHU, and attached the zone level to a secondary loop with 58F? Does this behave more like a traditional chilled beam setup where dehumidification takes place at the AHU and sensible only cooling at the zone level? Thanks, Fred Fred Betz PhD., LEED AP Sustainable Systems Analyst AEI | AFFILIATED ENGINEERS, INC. 5802 Research Park Blvd. | Madison, WI 53719 P: 608.236.1175 | F: 608.238.2614 fbetz at aeieng.com | www.aeieng.com -------------- next part -------------- An HTML attachment was scrubbed... URL: From ssavich at systemswestengineers.com Mon Apr 2 09:13:26 2012 From: ssavich at systemswestengineers.com (Steven Savich) Date: Mon, 2 Apr 2012 09:13:26 -0700 Subject: [Equest-users] Modeling chilled beams (IU) with zone level cooling as secondary loop In-Reply-To: References: Message-ID: <002701cd10eb$8b352f90$a19f8eb0$@com> Yes, it works. Also modeled this for a project with a ground-coupled loop with separate chillers supplying one temp to the AHU coils and a higher temp (56?F) to the chilled beams. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fred Betz Sent: Monday, April 02, 2012 9:03 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Modeling chilled beams (IU) with zone level cooling as secondary loop Has any tried modeling the IU system with a chilled water loop with ~42F at the AHU, and attached the zone level to a secondary loop with 58F? Does this behave more like a traditional chilled beam setup where dehumidification takes place at the AHU and sensible only cooling at the zone level? Thanks, Fred Fred Betz PhD., LEED AP Sustainable Systems Analyst AEI | AFFILIATED ENGINEERS, INC. 5802 Research Park Blvd. | Madison, WI 53719 P: 608.236.1175 | F: 608.238.2614 fbetz at aeieng.com | www.aeieng.com -------------- next part -------------- An HTML attachment was scrubbed... URL: From jason.e.quinn at gmail.com Mon Apr 2 10:28:32 2012 From: jason.e.quinn at gmail.com (Jason Quinn) Date: Tue, 3 Apr 2012 05:28:32 +1200 Subject: [Equest-users] Advice on modelling nine story atrium across shells Message-ID: I've modeled a nine story office building which requires different shells for several of the levels in the building. It also has a nine story (full height) atrium that will be used to extract all of the exhaust air (i.e. supply OA to the floors and condition via FC units and pull exhaust air out of the top of the atrium). I'm aware that eQuest doesn't track air flows but I'd like to best approximate the atrium effects on the overall energy use of the building. Current approach: I've modeled each floor as a separate zone and I'm going to delete the floors and turn the ceilings into air-walls and link them to the zone above. Currently I'm conditioning all of the zones that make up the atrium but at some point I'd like to explore not conditioning these zones to more accurately approximate how we'd run the building. Comments? One alternate approach I've seen proposed is to replace all nine zones in the atrium with one full height zone - the advantage is the glass on the roof and upper walls can "see" the floor and walls in all of the zones of the atrium. However this won't let me later go back in and explore any variation of temperature with height. I think this might be important as I would expect the air at the top of the atrium to be warmer and cause more load on the top floor zones next to the atrium. -- Jason Quinn From jeremiah at cleantechanalytics.com Mon Apr 2 14:05:52 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Mon, 2 Apr 2012 14:05:52 -0700 Subject: [Equest-users] Advice on modelling nine story atrium across shells In-Reply-To: References: Message-ID: Sounds like a task that would be better done with single zone and analysed using CFD to me.. Possibly use a CFD program then use insight to work around your Equest model.. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Mon, Apr 2, 2012 at 10:28 AM, Jason Quinn wrote: > I've modeled a nine story office building which requires different > shells for several of the levels in the building. It also has a nine > story (full height) atrium that will be used to extract all of the > exhaust air (i.e. supply OA to the floors and condition via FC units > and pull exhaust air out of the top of the atrium). I'm aware that > eQuest doesn't track air flows but I'd like to best approximate the > atrium effects on the overall energy use of the building. > > Current approach: I've modeled each floor as a separate zone and I'm > going to delete the floors and turn the ceilings into air-walls and > link them to the zone above. Currently I'm conditioning all of the > zones that make up the atrium but at some point I'd like to explore > not conditioning these zones to more accurately approximate how we'd > run the building. > > Comments? > > One alternate approach I've seen proposed is to replace all nine zones > in the atrium with one full height zone - the advantage is the glass > on the roof and upper walls can "see" the floor and walls in all of > the zones of the atrium. However this won't let me later go back in > and explore any variation of temperature with height. I think this > might be important as I would expect the air at the top of the atrium > to be warmer and cause more load on the top floor zones next to the > atrium. > > -- > Jason Quinn > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -------------- next part -------------- An HTML attachment was scrubbed... URL: From jmcclanathan at CDiengineers.com Mon Apr 2 14:26:27 2012 From: jmcclanathan at CDiengineers.com (Jeremy McClanathan) Date: Mon, 2 Apr 2012 14:26:27 -0700 Subject: [Equest-users] Advice on modelling nine story atrium acrossshells In-Reply-To: References: Message-ID: If CFD isn't an option, one other eQuest option would be to break the atrium up into one conditioned, and one or more plenums (TYPE = PLENUM, not UNCONDITIONED). Make an assumption about how much load is displaced or only present in the plenum portion of the atrium. Then, put a portion of the glazing and loads in the plenum(s). You might for example assume that the bottom two floors are one conditioned zone, and the top seven floors are a large plenum. I believe the air in the plenum should pick up the heat from the glazing and loads placed in it. I would be cautious about using eQuest to predict what will actually happen in an atrium though. Jeremy ___________________________________________ Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C [cid:image001.jpg at 01CD10DB.37C9D9B0] 4200 194th St SW, Ste 200, Lynnwood, WA 98036 P 425-672-1071 | F 425-778-8769 P Please consider the environment before printing this email. From: CleanTech Analytics [mailto:jeremiah at cleantechanalytics.com] Sent: Monday, April 02, 2012 2:06 PM To: Jason Quinn Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Advice on modelling nine story atrium across shells Sounds like a task that would be better done with single zone and analysed using CFD to me.. Possibly use a CFD program then use insight to work around your Equest model.. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Mon, Apr 2, 2012 at 10:28 AM, Jason Quinn > wrote: I've modeled a nine story office building which requires different shells for several of the levels in the building. It also has a nine story (full height) atrium that will be used to extract all of the exhaust air (i.e. supply OA to the floors and condition via FC units and pull exhaust air out of the top of the atrium). I'm aware that eQuest doesn't track air flows but I'd like to best approximate the atrium effects on the overall energy use of the building. Current approach: I've modeled each floor as a separate zone and I'm going to delete the floors and turn the ceilings into air-walls and link them to the zone above. Currently I'm conditioning all of the zones that make up the atrium but at some point I'd like to explore not conditioning these zones to more accurately approximate how we'd run the building. Comments? One alternate approach I've seen proposed is to replace all nine zones in the atrium with one full height zone - the advantage is the glass on the roof and upper walls can "see" the floor and walls in all of the zones of the atrium. However this won't let me later go back in and explore any variation of temperature with height. I think this might be important as I would expect the air at the top of the atrium to be warmer and cause more load on the top floor zones next to the atrium. -- Jason Quinn _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies. -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1232 bytes Desc: image001.jpg URL: From smartin at shaunmartinconsulting.com Mon Apr 2 14:51:29 2012 From: smartin at shaunmartinconsulting.com (Shaun Martin) Date: Mon, 2 Apr 2012 14:51:29 -0700 Subject: [Equest-users] Advice on modelling nine story atrium across shells In-Reply-To: References: Message-ID: Hi Jason, Another alternative is to model the lowest floor level of the atrium as a conditioned space, and the upper 8 storey part of the atrium as a return plenum. Shaun Martin LEED AP Principal Shaun Martin Consulting 2060 Pine Street, Vancouver BC V6J 4P8 604-789-1095 smartin at shaunmartinconsulting.com member CAGBC, ASHRAE -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Monday, April 02, 2012 10:29 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Advice on modelling nine story atrium across shells I've modeled a nine story office building which requires different shells for several of the levels in the building. It also has a nine story (full height) atrium that will be used to extract all of the exhaust air (i.e. supply OA to the floors and condition via FC units and pull exhaust air out of the top of the atrium). I'm aware that eQuest doesn't track air flows but I'd like to best approximate the atrium effects on the overall energy use of the building. Current approach: I've modeled each floor as a separate zone and I'm going to delete the floors and turn the ceilings into air-walls and link them to the zone above. Currently I'm conditioning all of the zones that make up the atrium but at some point I'd like to explore not conditioning these zones to more accurately approximate how we'd run the building. Comments? One alternate approach I've seen proposed is to replace all nine zones in the atrium with one full height zone - the advantage is the glass on the roof and upper walls can "see" the floor and walls in all of the zones of the atrium. However this won't let me later go back in and explore any variation of temperature with height. I think this might be important as I would expect the air at the top of the atrium to be warmer and cause more load on the top floor zones next to the atrium. -- Jason Quinn _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From xs2144 at gmail.com Mon Apr 2 16:11:37 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Mon, 2 Apr 2012 19:11:37 -0400 Subject: [Equest-users] eQUEST weather format convertor Message-ID: Hi guys, When I am trying to convert the csv file to bin file for weather data in software eQUEST Weather Format Convertor, after setting everything done, clicking "Convert" button. The software always say "invalid file name". Why? The file name I used is "NYTMY.BIN". Anybody knows about this question? Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Mon Apr 2 16:46:21 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 2 Apr 2012 23:46:21 +0000 Subject: [Equest-users] Warning Daylighting unit normal greater than 1 - how to fix this? In-Reply-To: References: Message-ID: Hi Jason - that's pretty wacky! Short of toying with the azimuth/orientation inputs, which it sounds like you've done, my next guess would be to compare the contents of your daylight sensor's inputs in the .inp against a known working model's - perhaps something will stick out as obvious. Also on re-reading, I wonder if it has to do with the orientation of your contributing window? Try toying with that as well... If messing with either alters the 0,0,1.0000001 coordinates in that message that'll be a strong clue as to where the problem lies. Though I've never run into this, I have a strong hunch re-defining/re-entering your windows and/or daylighting inputs will ultimately be part of the solution. ~Nick NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Sunday, April 01, 2012 10:28 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Warning Daylighting unit normal greater than 1 - how to fix this? I've a atrium with glass roof and walls - I've set this up with really large separate windows. This error about unit normal has popped up in the .sim file (although my results have not shifted that I can tell. **WARNING********************************************************************** Daylighting coefficient calculation for SPACE LV8SE Perim Spc (G.SE10) for reference point 1 encountered an ERROR. The unit normal for the contribution from WINDOW LV8Skylt (G.SE10.E19.S1) had a length greater than 1.0. WNORM was: 0.0000000 0.0000000 1.0000001 One or more WNORM components have been reset to 1.0 to correct the problem. Any ideas on how to fix this? I moved the daylight sensor location and changed the azimuth but the error has not changed. -- Jason _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From ncaton at smithboucher.com Mon Apr 2 16:54:49 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 2 Apr 2012 23:54:49 +0000 Subject: [Equest-users] eQUEST weather format convertor In-Reply-To: References: Message-ID: Hi Yang, Have you addressed the .ini file issue after installing the conversion program? If that question makes no sense initially, I'm 99.9% sure it is the root of your problem - the solution is explained briefly on the doe2 website where you downloaded eQ_WthProc ( http://doe2.com/index_Wth.html ), and in further detail with instructions by myself and others in the mailing list archives ;). Best of luck! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of xiaoyang shi Sent: Monday, April 02, 2012 6:12 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] eQUEST weather format convertor Hi guys, When I am trying to convert the csv file to bin file for weather data in software eQUEST Weather Format Convertor, after setting everything done, clicking "Convert" button. The software always say "invalid file name". Why? The file name I used is "NYTMY.BIN". Anybody knows about this question? Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From xs2144 at gmail.com Mon Apr 2 20:35:39 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Mon, 2 Apr 2012 23:35:39 -0400 Subject: [Equest-users] eQUEST weather format convertor In-Reply-To: References: Message-ID: Hi, Thank you very much. I changed the .ini file path to "C:\Users\xiaoyang shi\Documents", then "convert" the file. The software says, " Weather data cleaned successfully. Weather data loaded successfully from CSV file." However, I cannot find the produced "bin" file in folder. The software also says:* "is not a vallid floating point value.* * * Thank you again for your help. Best, Yang On Mon, Apr 2, 2012 at 7:11 PM, xiaoyang shi wrote: > Hi guys, > > When I am trying to convert the csv file to bin file for weather data in > software eQUEST Weather Format Convertor, after setting everything done, > clicking "Convert" button. > > The software always say "invalid file name". Why? > > The file name I used is "NYTMY.BIN". > > Anybody knows about this question? > > Thank you very much. > > Yang > > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From xs2144 at gmail.com Mon Apr 2 20:36:08 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Mon, 2 Apr 2012 23:36:08 -0400 Subject: [Equest-users] eQUEST weather format convertor In-Reply-To: References: Message-ID: On Mon, Apr 2, 2012 at 11:35 PM, xiaoyang shi wrote: > Hi, > Thank you very much. > > I changed the .ini file path to "C:\Users\xiaoyang shi\Documents", then > "convert" the file. > > The software says, " Weather data cleaned successfully. Weather data > loaded successfully from CSV file." However, I cannot find the produced > "bin" file in folder. The software also says:* "is not a vallid floating > point value.* > * > * > Thank you again for your help. > > Best, > Yang > > On Mon, Apr 2, 2012 at 7:11 PM, xiaoyang shi wrote: > >> Hi guys, >> >> When I am trying to convert the csv file to bin file for weather data in >> software eQUEST Weather Format Convertor, after setting everything done, >> clicking "Convert" button. >> >> The software always say "invalid file name". Why? >> >> The file name I used is "NYTMY.BIN". >> >> Anybody knows about this question? >> >> Thank you very much. >> >> Yang >> >> >> > -------------- next part -------------- An HTML attachment was scrubbed... URL: From mak.jonathan at pbworld.com Tue Apr 3 03:00:44 2012 From: mak.jonathan at pbworld.com (Mak, Jonathan Wai-Ho) Date: Tue, 3 Apr 2012 18:00:44 +0800 Subject: [Equest-users] Campus cooling / heating system Message-ID: Dear all, I am simulating a building (LEED NC v2.2) in a campus with centralized cooling / heating system. As according to "Treatment of district or campus thermal energy in LEED v2 & LEED 2009", a virtual plant with default efficiency can be used. There are few questions regarding the COP as well as the thermal loss: a) The COP of cooling plant shall be 4.4 including cooling towers and primary pumps. Does it mean that chillers, cooling towers as well as primary pumps shall be sized with COP 4.4? how can we enter the pump and cooling tower efficiency with COP4.4? Or we just only need to input COP 4.4 for chillers while the others can use the rated efficiency in our design? b) How can we input the thermal distribution losses? What I suppose is that, Q=mcdT, so if there are 5% thermal loss, the dT loss shall also be 5%. Does it mean to enter 5% of design dT in the "supply loss dT" column? Or make it simple, just multiplying 5% to the energy consumption by space cooling is already sufficient? Thanks all. Best Regards, Jonathan Mak ______________________________________________________________________ NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Tue Apr 3 06:42:50 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 3 Apr 2012 13:42:50 +0000 Subject: [Equest-users] eQUEST weather format convertor References: Message-ID: I haven't run into this 'floating point' error before... if it helps, I used the procedure that just deletes the .ini file to create a new one, try that using the default directories first. If that doesn't work, I would try to convert another file (try the example files that come with the program)... this might answer whether something in the weather file isn't quite formatted correctly. If the program doesn't work with the provided sample files, you might need to solicit the input of Paul Reeves or others on the DOE2 team - you may have stumbled into something new. As a last resort you might just try removing and reinstalling the program to see if that helps. ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: xiaoyang shi [mailto:xs2144 at gmail.com] Sent: Monday, April 02, 2012 8:57 PM To: Nick Caton Subject: Re: [Equest-users] eQUEST weather format convertor Hi Nick, Thank you very much. I changed the .ini file path to "C:\Users\xiaoyang shi\Documents", then "convert" the file. The software says, " Weather data cleaned successfully. Weather data loaded successfully from CSV file." However, I cannot find the produced "bin" file in folder. The software also says: "is not a vallid floating point value. Thank you again for your help. Best, Yang On Mon, Apr 2, 2012 at 7:54 PM, Nick Caton > wrote: Hi Yang, Have you addressed the .ini file issue after installing the conversion program? If that question makes no sense initially, I'm 99.9% sure it is the root of your problem - the solution is explained briefly on the doe2 website where you downloaded eQ_WthProc ( http://doe2.com/index_Wth.html ), and in further detail with instructions by myself and others in the mailing list archives ;). Best of luck! ~Nick NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of xiaoyang shi Sent: Monday, April 02, 2012 6:12 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] eQUEST weather format convertor Hi guys, When I am trying to convert the csv file to bin file for weather data in software eQUEST Weather Format Convertor, after setting everything done, clicking "Convert" button. The software always say "invalid file name". Why? The file name I used is "NYTMY.BIN". Anybody knows about this question? Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From jesse at viridianusa.com Tue Apr 3 09:07:19 2012 From: jesse at viridianusa.com (Jesse Eisenhart) Date: Tue, 3 Apr 2012 16:07:19 +0000 Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units Message-ID: Hello All! I am having an issue regarding a dedicated outside air unit that takes advantage of a condensing water loop. When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an error saying this system type is not eligible for "OA-FROM-SYSTEM". One of my thoughts is to * model all the units served by the outside air unit with no fresh air * model the dummy zone with a summation of the fresh air required by the spaces served But then that might interfere with a proper simulation of mixed air temps going into the space. Thoughts? ***ERROR*********************************************************************** OSAU is not a legal SYSTEM-TYPE to be an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed. Jesse Eisenhart Energy Services | Project Manager [Description: LOGO_for_Email-4] VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 1186 bytes Desc: image001.png URL: From jesse at viridianusa.com Tue Apr 3 13:21:17 2012 From: jesse at viridianusa.com (Jesse Eisenhart) Date: Tue, 3 Apr 2012 20:21:17 +0000 Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units In-Reply-To: References: Message-ID: I guess I stumped everyone. :) Jesse Eisenhart Energy Services | Project Manager [Description: LOGO_for_Email-4] VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jesse Eisenhart Sent: Tuesday, April 03, 2012 11:07 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units Hello All! I am having an issue regarding a dedicated outside air unit that takes advantage of a condensing water loop. When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an error saying this system type is not eligible for "OA-FROM-SYSTEM". One of my thoughts is to * model all the units served by the outside air unit with no fresh air * model the dummy zone with a summation of the fresh air required by the spaces served But then that might interfere with a proper simulation of mixed air temps going into the space. Thoughts? ***ERROR*********************************************************************** OSAU is not a legal SYSTEM-TYPE to be an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed. Jesse Eisenhart Energy Services | Project Manager [Description: LOGO_for_Email-4]VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 1186 bytes Desc: image001.png URL: From dse at grummanbutkus.com Tue Apr 3 13:31:58 2012 From: dse at grummanbutkus.com (David Eldridge) Date: Tue, 3 Apr 2012 15:31:58 -0500 Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units In-Reply-To: References: Message-ID: <2c98ef31c4e51fc07d3f8ca03df593da@mail.gmail.com> Can you use PVVT, but configured as you would have setup the heat pump? David * * *David S. Eldridge, Jr.**, P**.**E**.**, LEED AP BD+C, BEMP, BEAP, HBDP* Project Manager Direct: (847) 316-9224 | Fax: (847) 328-4550 *Grumman/Butkus Associates* | 820 Davis Street, Suite 300 | Evanston, IL 60201 Energy Efficiency Consultants and Sustainable Design Engineers * * * * *From:* equest-users-bounces at lists.onebuilding.org [mailto: equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jesse Eisenhart *Sent:* Tuesday, April 03, 2012 3:21 PM *To:* equest-users at lists.onebuilding.org *Subject:* Re: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units I guess I stumped everyone. J Jesse Eisenhart Energy Services | Project Manager [image: Description: LOGO_for_Email-4]VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com *From:* equest-users-bounces at lists.onebuilding.org [mailto: equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jesse Eisenhart *Sent:* Tuesday, April 03, 2012 11:07 AM *To:* equest-users at lists.onebuilding.org *Subject:* [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units Hello All! I am having an issue regarding a dedicated outside air unit that takes advantage of a condensing water loop. When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an error saying this system type is not eligible for ?OA-FROM-SYSTEM?. One of my thoughts is to ? model all the units served by the outside air unit with no fresh air ? model the dummy zone with a summation of the fresh air required by the spaces served But then that might interfere with a proper simulation of mixed air temps going into the space. Thoughts? ***ERROR*********************************************************************** OSAU is not a legal SYSTEM-TYPE to be an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed. Jesse Eisenhart Energy Services | Project Manager [image: Description: LOGO_for_Email-4]VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 1186 bytes Desc: not available URL: From bbishop at pathfinder-ea.com Tue Apr 3 13:41:45 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Tue, 3 Apr 2012 20:41:45 +0000 Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units In-Reply-To: <2c98ef31c4e51fc07d3f8ca03df593da@mail.gmail.com> References: <2c98ef31c4e51fc07d3f8ca03df593da@mail.gmail.com> Message-ID: <90D829482BDEDB4CB264DE5060592B190486DDD6@lightning.pathfinderengineers.com> You can model a water-to-air heat pump using PSZ, PVAVS and PVVT by specifying a CONDENSER-TYPE -> WATER-COOLED and attaching a CIRCULATION-LOOP of type CW or WLHP. Best regards, Bill [cid:image002.png at 01CD11B8.1A0F08E0] From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge Sent: Tuesday, April 03, 2012 4:32 PM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units Can you use PVVT, but configured as you would have setup the heat pump? David David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP Project Manager Direct: (847) 316-9224 | Fax: (847) 328-4550 Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201 Energy Efficiency Consultants and Sustainable Design Engineers From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jesse Eisenhart Sent: Tuesday, April 03, 2012 3:21 PM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units I guess I stumped everyone. :) Jesse Eisenhart Energy Services | Project Manager [Description: LOGO_for_Email-4]VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jesse Eisenhart Sent: Tuesday, April 03, 2012 11:07 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Water Source Heat Pumps as Dedicated Outside Air Units Hello All! I am having an issue regarding a dedicated outside air unit that takes advantage of a condensing water loop. When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an error saying this system type is not eligible for "OA-FROM-SYSTEM". One of my thoughts is to * model all the units served by the outside air unit with no fresh air * model the dummy zone with a summation of the fresh air required by the spaces served But then that might interfere with a proper simulation of mixed air temps going into the space. Thoughts? ***ERROR*********************************************************************** OSAU is not a legal SYSTEM-TYPE to be an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed. Jesse Eisenhart Energy Services | Project Manager [Description: LOGO_for_Email-4]VIRIDIAN|Sustainable Building Consulting 100 Gamble Road, Little Rock, AR 72211 o: 501.227.0648, f: 501.227.8648 jesse at ViridianUSA.com | www.ViridianUSA.com -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.png Type: image/png Size: 21646 bytes Desc: image002.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.png Type: image/png Size: 1186 bytes Desc: image003.png URL: From xs2144 at gmail.com Tue Apr 3 17:25:39 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Tue, 3 Apr 2012 20:25:39 -0400 Subject: [Equest-users] download hourly temperature data Message-ID: Hi eQUEST Experts :), I downloade new york city central park hourly weather CSV file from Energy plus real-time weather data website from 20 http://apps1.eere.energy.gov/buildings/energyplus/weatherdata_download.cfm However, when I open these files from 2011 11 14- 2012 01 28, however, when I open this file, the data in the first two column TDbC and TDew is around 200, I cannnot figure out what the *unit* this file is using. Anyone can help me ? Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: KNYC_20111114-20120128 (2).CSV Type: text/csv Size: 264254 bytes Desc: not available URL: From aloysiusdecruz2004 at yahoo.com Tue Apr 3 22:52:22 2012 From: aloysiusdecruz2004 at yahoo.com (Aloysius Decruz) Date: Tue, 3 Apr 2012 22:52:22 -0700 (PDT) Subject: [Equest-users] SPAN email sent from this ID Message-ID: <1333518742.85982.YahooMailClassic@web161403.mail.bf1.yahoo.com> Dear all, It appears that a spam email has been circulated from my email (aloysiusdecruz2004 at yahoo.com) Sorry for the trouble. I am not sure how it happened except that strange things happen here in China. I have changed the password, so it should not happen again. Normally I will not send any email without an appropriate subject line. Thank you and regards Aloysius -------------- next part -------------- An HTML attachment was scrubbed... URL: From ADahlstrom at in-posse.com Wed Apr 4 06:07:21 2012 From: ADahlstrom at in-posse.com (Dahlstrom, Aaron) Date: Wed, 4 Apr 2012 09:07:21 -0400 Subject: [Equest-users] download hourly temperature data In-Reply-To: References: Message-ID: <22CE8791E7DE554FB00676D7248C6B5507DDFF7D94@AKFMAILPA.AKF-ENG.COM> I believe the KNYC data includes a "tenth of a degree" data without including the interposing decimal point. Eg 200 would be 20.0 deg. I am not sure if it is deg C or deg F although from the stated # I would imagine deg F. To know for sure, check the help guide at http://apps1.eere.energy.gov/buildings/energyplus/pdfs/weatherdata_guide_34303.pdf If that fails, the good folks at NREL have been pretty responsive to me when I clicked on the "help" link from the website you cited. Aaron Dahlstrom , PE, LEED(r) AP In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102 d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290 e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com | akf web: www.akfgroup.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of xiaoyang shi Sent: Tuesday, April 03, 2012 8:26 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] download hourly temperature data Hi eQUEST Experts :), I downloade new york city central park hourly weather CSV file from Energy plus real-time weather data website from 20http://apps1.eere.energy.gov/buildings/energyplus/weatherdata_download.cfm However, when I open these files from 2011 11 14- 2012 01 28, however, when I open this file, the data in the first two column TDbC and TDew is around 200, I cannnot figure out what the unit this file is using. Anyone can help me ? Thank you very much. Yang This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse. -------------- next part -------------- An HTML attachment was scrubbed... URL: From jason.e.quinn at gmail.com Wed Apr 4 12:04:49 2012 From: jason.e.quinn at gmail.com (Jason Quinn) Date: Thu, 5 Apr 2012 07:04:49 +1200 Subject: [Equest-users] Simplest way to turn off the cooling in PVVT and leave fans running Message-ID: I'd like to look at my system with the PVVVT providing no cooling but still using the fans to provide OA. What is the simplest way to do this? -- Jason From slv3sat at gmail.com Wed Apr 4 12:42:23 2012 From: slv3sat at gmail.com (R B) Date: Wed, 4 Apr 2012 14:42:23 -0500 Subject: [Equest-users] Simplest way to turn off the cooling in PVVT and leave fans running In-Reply-To: References: Message-ID: You could keep the fan min flow at the OA level. Have a fan on schedule that is always on. Thermostat schedule at 95 For so. This might work - look at the hourly report to see if the fan is consuming energy.-Rohini On Wed, Apr 4, 2012 at 2:04 PM, Jason Quinn wrote: > I'd like to look at my system with the PVVVT providing no cooling but > still using the fans to provide OA. What is the simplest way to do > this? > > -- > Jason > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -------------- next part -------------- An HTML attachment was scrubbed... URL: From CBosch at karpinskieng.com Wed Apr 4 12:49:27 2012 From: CBosch at karpinskieng.com (Bosch, Crina) Date: Wed, 4 Apr 2012 19:49:27 +0000 Subject: [Equest-users] BEPU/BEPS & LEED Template Message-ID: <6C6EB94FEA5D294E9393C628FE8A71F316F228@KE-EXCHANGE.BKAINC.local> I just received a comment on my energy model regarding the BEPS, BEPU & LEED Template as below: "The energy use values reported in Tables EAp2-4 and EAp2-5 of the form are inconsistent with the simulation output BEPU reports and the cost values reported in Table EAp2-7 of the form are inconsistent with the values shown in the Monthly Utility Bill simulation output reports. Please confirm the values entered in the form and revise as necessary. Ensure all values are consistent between the form and simulation documentation." After more research I found out that my inputs from BEPU reports are correct on the LEED template but in the end the template calculates the MMBtu/year with an error of 0.25 % when comparing the template with the BEPS which is carried on to the cost. Now, the difference is just a couple dollars and is insignificant for the savings between the models but the reviewer has a problem with this. I am thinking to just give an explanation to what I discovered with the LEED template. Did you guys have this kind of problem before? Any advice is appreciated. Thank you. Crina Bosch Designer, Sustainability karpinski ENGINEERING 3135 Euclid Avenue Cleveland, OH 44115 P 216.391.3700 ext 3087 F 216.391.0108 E cbosch at karpinskieng.com W www.karpinskieng.com -------------- next part -------------- An HTML attachment was scrubbed... URL: From slv3sat at gmail.com Wed Apr 4 12:51:56 2012 From: slv3sat at gmail.com (R B) Date: Wed, 4 Apr 2012 14:51:56 -0500 Subject: [Equest-users] Simplest way to turn off the cooling in PVVT and leave fans running In-Reply-To: References: Message-ID: You may have to set the temp control to warmest. Also, the max cooling coil supply temp is 70 F so you might end up cooling. So you could trick the system by having 0.01 cooling capacity. Let me know if this works. On Wed, Apr 4, 2012 at 2:42 PM, R B wrote: > > You could keep the fan min flow at the OA level. Have a fan on schedule > that is always on. Thermostat schedule at 95 For so. This might work - look > at the hourly report to see if the fan is consuming energy.-Rohini > > On Wed, Apr 4, 2012 at 2:04 PM, Jason Quinn wrote: > >> I'd like to look at my system with the PVVVT providing no cooling but >> still using the fans to provide OA. What is the simplest way to do >> this? >> >> -- >> Jason >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From Joey.Jiao at WSPGroup.com.cn Wed Apr 4 23:41:00 2012 From: Joey.Jiao at WSPGroup.com.cn (Jiao, Joey) Date: Thu, 5 Apr 2012 14:41:00 +0800 Subject: [Equest-users] =?gb2312?b?tPC4tDogIGVRVUVTVCB3ZWF0aGVyIGZvcm1h?= =?gb2312?b?dCBjb252ZXJ0b3I=?= Message-ID: <0F18FC782AAB044BADF94EA196DF1261FDAACA@exc03ahk1hk.asia.wspgroup.com> Hi, Yang: Try this: delete the the eQ_WthProc.INI (found in the EPW/Processor subdirectory) so that the program will create a new one upon startup. Joey ???: xiaoyang shi [mailto:xs2144 at gmail.com] ????: 2012?4?3? 7:12 ???: equest-users at lists.onebuilding.org ??: [Equest-users] eQUEST weather format convertor Hi guys, When I am trying to convert the csv file to bin file for weather data in software eQUEST Weather Format Convertor, after setting everything done, clicking "Convert" button. The software always say "invalid file name". Why? The file name I used is "NYTMY.BIN". Anybody knows about this question? Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: From smoret at ucdavis.edu Thu Apr 5 12:35:29 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Thu, 5 Apr 2012 19:35:29 +0000 Subject: [Equest-users] Schematic Design Wizard crashes with invalid path error Message-ID: <04B072E0E3317A4486513BB18D6579C00725DE8C@exmbx4.ex.ad3.ucdavis.edu> Dear Scott, I just installed E-quest on my Parallels XP virtual machine, and ran into the same issue as you did. Since the problem might be associated with the Parallels shared hard drive partition, I recommend you to uninstall the program and re-install it selecting the "all users" option instead of "just me". This way, the "data" and "projects" folder will be located in the C:\ partition of the virtual machine and not in the shared Parallels folders (//psf..). That did the trick for me. Regards, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu -------------- next part -------------- An HTML attachment was scrubbed... URL: From marwa1888 at hotmail.fr Thu Apr 5 13:59:58 2012 From: marwa1888 at hotmail.fr (marwa ot) Date: Thu, 5 Apr 2012 21:59:58 +0100 Subject: [Equest-users] Question marks in eQ-Refrig Message-ID: Dear all, I'm a new user of eQuest. I got the eQuest version 3.61 from the website www.doe2.com. I used this version toward using eQ-Refrig. But I got question marks in the button "Refrigeration" and in Refr System Tab (I tested this version in two operating systems : Windows 7 and XP). I have the same problem when I use eQuest 3.55.Please check the image attached to this mail for more information. Is there any solutions for this issue ? thanks in advance. Best RegardsMarwa -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: eqrerif-prob.jpg Type: image/jpeg Size: 249447 bytes Desc: not available URL: From smoret at ucdavis.edu Thu Apr 5 14:01:38 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Thu, 5 Apr 2012 21:01:38 +0000 Subject: [Equest-users] Window properties bug In-Reply-To: <04B072E0E3317A4486513BB18D6579C08655A6@exmbx10.ex.ad3.ucdavis.edu> References: <04B072E0E3317A4486513BB18D6579C08655A6@exmbx10.ex.ad3.ucdavis.edu> Message-ID: <04B072E0E3317A4486513BB18D6579C00725DFC0@exmbx4.ex.ad3.ucdavis.edu> Does anyone from the development side know how to fix this bug? Is a little bit annoying, since I'd need to use the switchable glazing option for some tests and I've no way of implementing it.. Thanks, Stefano From: Stefano Moret Sent: Wednesday, March 21, 2012 5:57 PM To: equest-users at lists.onebuilding.org Subject: Window properties bug Hi, I don't know if it happened already to you as well, but when I enter in window properties/switching, if I try to select the glazing to switch to, Equest crashes. I'm working on a 4GB RAM, 3.16Ghz, Intel core duo Window 7 pc. Stefano From: Stefano Moret Sent: Tuesday, March 20, 2012 12:32 PM To: 'mwilson at enerficiency.ca' Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Parametric runs Thanks, I see what you mean, I'll try and use the EMIT schedule generator for that. For what I see, with shades I can set set a schedule for solar heat gain, and from the daylight tab I can regulate visible light transmittance. It's nice that you can switch on daylight levels as control parameter, would be nice it to be adapting as electro-chromic windows and not 0/1 as it is here. Thanks for your inputs, Regards Stefano From: Michael Wilson [mailto:mwilson at enerficiency.ca] Sent: Tuesday, March 20, 2012 12:12 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Parametric runs Hi Stefano. Switching is under window properties, Blinds tab. See graphic below. To do it in Excel requires a bit of playing around with the formatting. Once you've done that you can save the Excel sheet as a prn file, which will turn it into text and it can be copied into the inp file and re-imported. But getting the formatting straight can be a bit of work. Mike [cid:image001.jpg at 01CD1334.9C736DD0] Michael Wilson, P.Eng., Enerficiency Consulting PO Box 1911 - 458 Abbs Rd., Gibsons, BC V0N 1V0 | 604-886-9864 | www.enerficiency.ca From: Stefano Moret [mailto:smoret at ucdavis.edu] Sent: March-20-12 11:58 AM To: mwilson at enerficiency.ca Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Parametric runs Dear Wesley and Michael, Thanks for your suggestions. I have been looking into the window/drapes functions, i.e. the possibility of changing blind positions over 3 different seasons. I didn't find, though, the possibility of switching on ambient conditions, as suggested by Michael. How can you do that? It's quite interesting the possibility of uploading an annual hourly schedule into the software. Do you think I can generate an excel schedule setting different values for some parameters (window properties such as VLT and SHGC) and import them into E-quest to run my model? It's not a perfect solution but I could have for sure a good estimate of the savings. Thanks, Stefano From: Michael Wilson [mailto:mwilson at enerficiency.ca] Sent: Sunday, March 18, 2012 10:18 AM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Parametric runs Hi Stefano. Within the Window, under Blinds/Drapes-Switching, there is an option for switching of window properties. This is to represent windows with electrochromic switching. As far as I know (I've never actually used it) it can only switch between two sets of window properties. But it can be switched on various ambient conditions (solar gain, temperature, etc). If thats not sophisticated enough, you could try using an 8760 hour schedule generated in Excel. Output all the data you need (OAT, solar gain, etc), then do your calculations in Excel to generate your shading schedule and import it into your file. Or if you really want a function, Doe2.1e allows them. But they're not very user friendly... Mike Michael Wilson, P.Eng., Enerficiency Consulting PO Box 1911 - 458 Abbs Rd., Gibsons, BC V0N 1V0 | 604-886-9864 | www.enerficiency.ca From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Stefano Moret Sent: March-15-12 2:12 PM To: Wesley S. Care; CleanTech Analytics; yjhuang at whiteboxtechnologies.com Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Parametric runs Thanks Wesley, Nice to know that I can schedule different window properties by schedule, this is a simplified approach that might give an estimate of the saving. I was wondering if the software already had a function reproducing basically what electro-chromic windows do, that's basically maintaining a constant illuminance level in a room, reducing solar heat gain and light transmittance accordingly. If not, then it might be an idea to try and implementing this function, as I reckon it might be useful in various application. Thanks, regards -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu From: Wesley S. Care [mailto:wesley.care at esdaz.com] Sent: Thursday, March 15, 2012 2:04 PM To: CleanTech Analytics; Stefano Moret; yjhuang at whiteboxtechnologies.com Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Parametric runs Hi Stefano, Before you start trying to recode eQUEST, you might see if the scheduling options in the Window Properties window will be close enough approximations for you. The Blinds/Drapes - Switching tab has several options that allow you to vary conductance, solar transmission, etc. during the course of a simulation. It's meant to represent variable shading, so you can decide if that's scientific enough for what you're doing. The only other "easy" way I can think of is to run the model with both (or all) of the skylight options, and stitch the results together (March through August with one, the remainder with the other for example). The effect would be the same as if a guy went up and swapped out the glass one day. You'd have to lock down equipment sizing and a few other things to make sure that's the only difference, but still easier than adding your own eQUEST feature. Maybe you're better with code than me though! Good luck however you decide to do it. Thanks, Wesley [Description: ESDGreenLogo]Mechanical Engineers + Electrical Engineers + Sustainable Design Wesley Care, EIT | Mechanical Project Engineer | * wesley.care at esdaz.com | * 480.481.4973 | 6 480.481.4903 From: CleanTech Analytics [mailto:jeremiah at cleantechanalytics.com] Sent: Wednesday, March 14, 2012 3:10 PM To: smoret at ucdavis.edu; yjhuang at whiteboxtechnologies.com Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Parametric runs You may wish to ask Joe Huang, as if there is anyone who could do this he would be the one, as he is one of the most knowledgeable in the world so far as the DOE2 computer code. Best of luck White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 On Wed, Mar 14, 2012 at 3:04 PM, Stefano Moret > wrote: Thanks Jeremiah, I actually don't want to change much to the model itself, I just want to give different properties to materials (or change components) in different times of the year. Let's say, I want to use a type of skylight in winter that's different from the one I use in summer, by changing the model of the skylight or some of its main parameters. Do you think this might be possible? Maybe adding some external script? Thanks, Stefano From: CleanTech Analytics [mailto:jeremiah at cleantechanalytics.com] Sent: Wednesday, March 14, 2012 2:51 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Parametric runs I do not believe so, but you can try lots of different configurations that you either draw, or trace from cad.. On Wed, Mar 14, 2012 at 2:38 PM, Stefano Moret > wrote: Hi, I'm new to the use of E-quest, I'm just starting to play around with it by performing some preliminary simulations. The reason why I started using it is because of its feature of managing skylight properties: for a research project I'd like to simulate an "ideal skylight" solution, which could basically adapt its main properties (VLT and SHGC) in order to minimize building energy consumption. I've seen there's a very interesting "parametric run" tool, which can make me able to perform simulations with different values of these parameters. My question is: does E-quest support the possibility of writing a function which changes this values over the run itself with a rule set by the user? Or, at least, can I set different values at different times of the day? Thanks for your attention, Best Regards Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu ________________________________ No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1913 / Virus Database: 2114/4866 - Release Date: 03/12/12 ________________________________ No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1913 / Virus Database: 2114/4882 - Release Date: 03/20/12 -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 60591 bytes Desc: image001.jpg URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.png Type: image/png Size: 11535 bytes Desc: image002.png URL: From msghaier at enerplus.com.tn Fri Apr 6 04:24:23 2012 From: msghaier at enerplus.com.tn (Mabrouk SGHAIER) Date: Fri, 6 Apr 2012 12:24:23 +0100 Subject: [Equest-users] Refrigeration model Message-ID: <000601cd13e7$d1f5c350$75e149f0$@com.tn> Dear Users, I want use the eQ-refrig 3-61 model, but when start the refrigeration model, I found ?the question marks? ( indicated in the following screen) Did you have a solution for this problem ? Best Regards Mabrouk Logo L?ENERGIE UTILSEE INTELLIGEMMENT Mabrouk SGHAIER,Eng Manager Espace SAFSAF, Bloc A, 2?me ?tage, bureau 2-3, 1073, Montplaisir, Tunis, Tunisie (: 216- 71 904 235 7: 216 - 71 791 785 ?: 216 - 98 270 547 *: msghaier at enerplus.com.tn Web Site: www.enerplus.com.tn P Afin de contribuer au respect de l'environnement, Merci de n'imprimer ce courrier qu'en cas de n?cessit? -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 29908 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 2742 bytes Desc: not available URL: From bfountain at greensim.com Fri Apr 6 04:45:57 2012 From: bfountain at greensim.com (bfountain at greensim.com) Date: Fri, 6 Apr 2012 11:45:57 +0000 Subject: [Equest-users] Refrigeration model In-Reply-To: <000601cd13e7$d1f5c350$75e149f0$@com.tn> References: <000601cd13e7$d1f5c350$75e149f0$@com.tn> Message-ID: <1356704246-1333712809-cardhu_decombobulator_blackberry.rim.net-353695568-@b5.c1.bise6.blackberry> It is not a problem. They simply did not spend time drawing the graphics for the refg elements. Brian Fountain bfountain at greensim.com -----Original Message----- From: "Mabrouk SGHAIER" Sender: equest-users-bounces at lists.onebuilding.orgDate: Fri, 6 Apr 2012 12:24:23 To: Subject: [Equest-users] Refrigeration model _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From dave.weigel at thewattdoctors.com Fri Apr 6 06:42:21 2012 From: dave.weigel at thewattdoctors.com (Dave Weigel) Date: Fri, 6 Apr 2012 09:42:21 -0400 Subject: [Equest-users] Process heat exchanger In-Reply-To: References: Message-ID: <5934EE0491054A7BA2E7E4F7C8407BB5@DaveHPDesktop> Hi again group, I must model a process heat exchanger (actually, several of them). They take chilled water from the building HVAC plant. I am considering modeling the loads as internal plug loads in a space of their own with no exposures, lights, people, or any other additional load. I will cool that space with a two-pipe fan coil unit, no outdoor air, to get the heat into the chilled water loop. I'll set up the fan power to match what the actual designed pump power will be for the heat exchanger. I'll explain this all with my LEED documentation and include the calculation of fan power versus pump power. The loads don't vary when they are on, so I don't have to worry about the differences in fan curve versus pump curve in eQuest. Do you think this is the best way to handle these heat-exchanger loads? Do you think it'll fly through a LEED review? Thanks for any experience or opinions! Dave David R. Weigel, PE Member / President The Watt Doctors, LLC 1189 Golden Circle SW Lilburn, GA 30047-1913 From jmcclanathan at CDiengineers.com Fri Apr 6 08:25:52 2012 From: jmcclanathan at CDiengineers.com (Jeremy McClanathan) Date: Fri, 6 Apr 2012 08:25:52 -0700 Subject: [Equest-users] Process heat exchanger In-Reply-To: <5934EE0491054A7BA2E7E4F7C8407BB5@DaveHPDesktop> References: <5934EE0491054A7BA2E7E4F7C8407BB5@DaveHPDesktop> Message-ID: Another option might be to create a secondary CHW loop and apply the process load directly to the loop. You could create a loop pump to serve the loop and match the head, flow, etc. Jeremy. ___________________________________________ Jeremy McClanathan, P.E., BEMP, HFDP, LEED? AP BD+C 4200 194th St SW, Ste 200, Lynnwood, WA 98036 P 425-672-1071 | F 425-778-8769 ??Please consider the environment before printing this email. -----Original Message----- From: Dave Weigel [mailto:dave.weigel at thewattdoctors.com] Sent: Friday, April 06, 2012 6:42 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Process heat exchanger Hi again group, I must model a process heat exchanger (actually, several of them). They take chilled water from the building HVAC plant. I am considering modeling the loads as internal plug loads in a space of their own with no exposures, lights, people, or any other additional load. I will cool that space with a two-pipe fan coil unit, no outdoor air, to get the heat into the chilled water loop. I'll set up the fan power to match what the actual designed pump power will be for the heat exchanger. I'll explain this all with my LEED documentation and include the calculation of fan power versus pump power. The loads don't vary when they are on, so I don't have to worry about the differences in fan curve versus pump curve in eQuest. Do you think this is the best way to handle these heat-exchanger loads? Do you think it'll fly through a LEED review? Thanks for any experience or opinions! Dave David R. Weigel, PE Member / President The Watt Doctors, LLC 1189 Golden Circle SW Lilburn, GA 30047-1913 _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies. From morteza.kasmai at gmail.com Fri Apr 6 09:06:52 2012 From: morteza.kasmai at gmail.com (Morteza Kasmai) Date: Fri, 6 Apr 2012 12:06:52 -0400 Subject: [Equest-users] Changing thermal zones in DDE mode. Message-ID: Hello all, I learned that in DDE mode under 2-D geometry we can select any floor area and switch between 2-D view and Polygon view and edit the selected polygon/floor. Is there any way to edit/add thermal zones in DDE mode? Your help would be greatly appreciated. -- *Morteza Kasmaei* Architect, LEED? AP BD+C -------------- next part -------------- An HTML attachment was scrubbed... URL: From smoret at ucdavis.edu Fri Apr 6 11:04:25 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Fri, 6 Apr 2012 18:04:25 +0000 Subject: [Equest-users] SRR error Message-ID: <04B072E0E3317A4486513BB18D6579C00725E65E@exmbx4.ex.ad3.ucdavis.edu> Dear all, When performing the Skylight Roof Ratio parametric run, evaluating energy consumption and daylight illuminance values for different SRR, I can't get in output the "energy and utility bill saving report". It just creates an empty srr.htm page without any graph on it. I'm sure that in previous simulations I could get those graphs, and I don't know what happened since I didn't change anything in my models. Any hint? Thanks, Regards Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu -------------- next part -------------- An HTML attachment was scrubbed... URL: From dave.weigel at thewattdoctors.com Fri Apr 6 13:54:36 2012 From: dave.weigel at thewattdoctors.com (Dave Weigel) Date: Fri, 6 Apr 2012 16:54:36 -0400 Subject: [Equest-users] Process heat exchanger In-Reply-To: References: <5934EE0491054A7BA2E7E4F7C8407BB5@DaveHPDesktop> Message-ID: <51ECA5A24B5D4CC78F9BA9A689BE9998@DaveHPDesktop> Thank you Jeremy, that makes more sense. I'll try it out. Dave David R. Weigel, PE Member / President The Watt Doctors, LLC 1189 Golden Circle SW Lilburn, GA 30047-1913 678-353-6394 office 901-619-1716 cell -----Original Message----- From: Jeremy McClanathan Sent: Friday, April 06, 2012 11:25 AM To: 'Dave Weigel' ; equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Process heat exchanger Another option might be to create a secondary CHW loop and apply the process load directly to the loop. You could create a loop pump to serve the loop and match the head, flow, etc. Jeremy. ___________________________________________ Jeremy McClanathan, P.E., BEMP, HFDP, LEED? AP BD+C 4200 194th St SW, Ste 200, Lynnwood, WA 98036 P 425-672-1071 | F 425-778-8769 ??Please consider the environment before printing this email. -----Original Message----- From: Dave Weigel [mailto:dave.weigel at thewattdoctors.com] Sent: Friday, April 06, 2012 6:42 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Process heat exchanger Hi again group, I must model a process heat exchanger (actually, several of them). They take chilled water from the building HVAC plant. I am considering modeling the loads as internal plug loads in a space of their own with no exposures, lights, people, or any other additional load. I will cool that space with a two-pipe fan coil unit, no outdoor air, to get the heat into the chilled water loop. I'll set up the fan power to match what the actual designed pump power will be for the heat exchanger. I'll explain this all with my LEED documentation and include the calculation of fan power versus pump power. The loads don't vary when they are on, so I don't have to worry about the differences in fan curve versus pump curve in eQuest. Do you think this is the best way to handle these heat-exchanger loads? Do you think it'll fly through a LEED review? Thanks for any experience or opinions! Dave David R. Weigel, PE Member / President The Watt Doctors, LLC 1189 Golden Circle SW Lilburn, GA 30047-1913 _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies. From jaya_mukho at yahoo.com Sun Apr 8 21:46:54 2012 From: jaya_mukho at yahoo.com (Jaya Mukhopadhyay) Date: Sun, 8 Apr 2012 21:46:54 -0700 (PDT) Subject: [Equest-users] Help on Modeling DOAS in eQUEST Message-ID: <1333946814.35564.YahooMailNeo@web121703.mail.ne1.yahoo.com> Hello: Can anybody share their experiences on modeling the DOAS using eQUEST? I am especially not clear about whether it is possible to model energy recovery, given the fact that we are defining a dummy zone with no loads. Thanks Jaya Mukhopadhyay -------------- next part -------------- An HTML attachment was scrubbed... URL: From laurafalk at hotmail.com Mon Apr 9 09:48:03 2012 From: laurafalk at hotmail.com (Laura Falk) Date: Mon, 9 Apr 2012 11:48:03 -0500 Subject: [Equest-users] (no subject) Message-ID: I am studying Equest in school, we are working on a group project. Is there a way to "bind" an Autocad drawing to an Equest file? Or does the .dwg file need to be loaded on whatever computer we are working on? Thank you Laura Falk-Helgemoe -------------- next part -------------- An HTML attachment was scrubbed... URL: From jra_sac at yahoo.com Mon Apr 9 09:55:26 2012 From: jra_sac at yahoo.com (John Aulbach) Date: Mon, 9 Apr 2012 09:55:26 -0700 (PDT) Subject: [Equest-users] (no subject) In-Reply-To: References: Message-ID: <1333990526.41240.YahooMailNeo@web126104.mail.ne1.yahoo.com> Hi Laura: ? You essentially have the .DWG file on your computer, fire up eQuest, and when you get to the drawing mode in the Wizard, call up the .DWG file and trace around it. I am unsure as to whether the image of the .DWG file follows the eQuest model around, or whether the program has to find it each time. Once you trace the building, you will actually not need the .DWG file again. ? John R. Aulbach, PE, CEM Senior Energy Engineer ________________________________ PartnerEnergy 2154 Torrance Blvd, Ste. 100, Torrance, CA 90501 W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745 www.ptrenergy.com| jaulbach at ptrenergy.com ? ? ________________________________ From: Laura Falk To: equest-users at lists.onebuilding.org Sent: Monday, April 9, 2012 9:48 AM Subject: [Equest-users] (no subject) I am studying Equest in school, we are working on a group project. Is there a way to "bind" an Autocad drawing to an Equest file? Or does the .dwg file need to be loaded on whatever computer we are working on? Thank you Laura Falk-Helgemoe _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From poleary1969 at gmail.com Mon Apr 9 10:01:53 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Mon, 09 Apr 2012 10:01:53 -0700 Subject: [Equest-users] (no subject) In-Reply-To: <1333990526.41240.YahooMailNeo@web126104.mail.ne1.yahoo.com> References: <1333990526.41240.YahooMailNeo@web126104.mail.ne1.yahoo.com> Message-ID: <4F831601.2040607@gmail.com> the path to the .dwg file is hard-coded into the equest file so if you move the .dwg the next time you open the simulation file you'll get a prompt that equest can't find it & would you like to locate it. alternatively you could just edit the .pd2 file and/or .inp file (using notepad) & change the hard-coded path to a moved .dwg file prior to opening the simulation file again. On 4/9/12 9:55 AM, John Aulbach wrote: > Hi Laura: > You essentially have the .DWG file on your computer, fire up eQuest, > and when you get to the drawing mode in the Wizard, call up the .DWG > file and trace around it. I am unsure as to whether the image of the > .DWG file follows the eQuest model around, or whether the program has > to find it each time. Once you trace the building, you will actually > not need the .DWG file again. > John R. Aulbach, PE, CEM > Senior Energy Engineer > ------------------------------------------------------------------------ > *Partner****Energy* > 2154 Torrance Blvd, Ste. 100, Torrance, CA 90501 > W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745 > www.ptrenergy.com| > jaulbach at ptrenergy.com > > *From:* Laura Falk > *To:* equest-users at lists.onebuilding.org > *Sent:* Monday, April 9, 2012 9:48 AM > *Subject:* [Equest-users] (no subject) > > I am studying Equest in school, we are working on a group project. Is > there a way to "bind" an Autocad drawing to an Equest file? Or does > the .dwg file need to be loaded on whatever computer we are working on? > Thank you > Laura Falk-Helgemoe > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From nirupamalnarasimhan at gmail.com Mon Apr 9 12:02:29 2012 From: nirupamalnarasimhan at gmail.com (nirupama lakshminarasimhan) Date: Mon, 9 Apr 2012 15:02:29 -0400 Subject: [Equest-users] model takes too long to load/open Message-ID: I am modeling a big public school with a lot of systems and custom windows. The equest file we have right now is taking too long to load. I've tried opening it from different locations- the default equest project folder on C: , the public server, external HDD, etc. It is just too slow in "importing project data" when it opens. The last time this happened, it was taking too long to load the BDL file and I ended up deleting a host of systems and starting from scratch. All my files- the .inp, .pd2, etc are in the same path. I just cannot get it to work faster. I'm trying to calibrate the model and it is an awfully long wait for each simulation. Does someone have any thoughts on how I could get this to work faster? Thank you. Nirupama -------------- next part -------------- An HTML attachment was scrubbed... URL: From yusuf at ytenterprises.com Mon Apr 9 12:24:20 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Tue, 10 Apr 2012 00:54:20 +0530 Subject: [Equest-users] Gated Community & Roof reflectivity Message-ID: Hello Group I have just started working on my first energy modeling project. I have two questions: - How do I model roof reflectivity. I want to model a roof of 4 inch concrete with 1 inch stucco at the bottom and top and cover the roof with cool roof tiles. I am not sure how I can account for the energy efficiency gains compared to base case through a high SRI roof. - I am trying to model a large gated community with 330 villas and 7 other common buildings. As someone suggested on this group I am modeling each building type separately and using excel to come up with a total energy usage. But I am not sure how to model the street lighting and landscape lighting at the exteriors. We plan to use solar street lights and I want to demonstrate the savings through use of solar energy. Many Thanks Yusuf Turab On 10 April 2012 00:32, nirupama lakshminarasimhan < nirupamalnarasimhan at gmail.com> wrote: > I am modeling a big public school with a lot of systems and custom > windows. The equest file we have right now is taking too long to load. I've > tried opening it from different locations- the default equest project > folder on C: , the public server, external HDD, etc. It is just too slow in > "importing project data" when it opens. The last time this happened, it was > taking too long to load the BDL file and I ended up deleting a host of > systems and starting from scratch. All my files- the .inp, .pd2, etc are in > the same path. I just cannot get it to work faster. I'm trying to calibrate > the model and it is an awfully long wait for each simulation. Does someone > have any thoughts on how I could get this to work faster? > > > > Thank you. > > Nirupama > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Mon Apr 9 12:38:37 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 9 Apr 2012 19:38:37 +0000 Subject: [Equest-users] (no subject) In-Reply-To: <4F831601.2040607@gmail.com> References: <1333990526.41240.YahooMailNeo@web126104.mail.ne1.yahoo.com> <4F831601.2040607@gmail.com> Message-ID: Hi Laura (and Laura's group!), welcome to the list! I run into this often as I move projects around and work on them from different locations. The .dwg file itself is never an "integral/imported" part of the project's files - only a path is defined, so eQuest will prompt you on starting up for the CAD file's location any time the project's files or the CAD file is moved around (to be expected if you're working with others on a thumb drive or similar). To re-emphasis John's point: This isn't something to lose sleep over =). The "CAD file not found" message is something you can safely ignore entirely once you are past zone/perimeter geometry definitions in the wizards. The CAD file is not actually used anywhere in eQuest beyond serving as a "reference" for the duration of those screens. Once you are finished defining zone/perimeter geometries in wizards, you can feel safe choosing "remove all" from the following dialog: [cid:image001.png at 01CD165C.FB457D50] For the duration where your group may wish to go back and revise those geometries using the CAD file, I'd advise keeping a copy of the .dwg file alongside other "reference" files to "browse" to as needed. As an organizational practice/suggestion, I commonly have a small "reference" directory that I'll save and move around alongside the actual model files containing items like this and other notes, PDF's, messages, and other electronic information I used while assembling the model. Keeping this stuff in one place can make many things easier down the road, even well after finishing the project-at-hand! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr. Sent: Monday, April 09, 2012 12:02 PM To: John Aulbach Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] (no subject) the path to the .dwg file is hard-coded into the equest file so if you move the .dwg the next time you open the simulation file you'll get a prompt that equest can't find it & would you like to locate it. alternatively you could just edit the .pd2 file and/or .inp file (using notepad) & change the hard-coded path to a moved .dwg file prior to opening the simulation file again. On 4/9/12 9:55 AM, John Aulbach wrote: Hi Laura: You essentially have the .DWG file on your computer, fire up eQuest, and when you get to the drawing mode in the Wizard, call up the .DWG file and trace around it. I am unsure as to whether the image of the .DWG file follows the eQuest model around, or whether the program has to find it each time. Once you trace the building, you will actually not need the .DWG file again. John R. Aulbach, PE, CEM Senior Energy Engineer ________________________________ Partner Energy 2154 Torrance Blvd, Ste. 100, Torrance, CA 90501 W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745 www.ptrenergy.com | jaulbach at ptrenergy.com From: Laura Falk To: equest-users at lists.onebuilding.org Sent: Monday, April 9, 2012 9:48 AM Subject: [Equest-users] (no subject) I am studying Equest in school, we are working on a group project. Is there a way to "bind" an Autocad drawing to an Equest file? Or does the .dwg file need to be loaded on whatever computer we are working on? Thank you Laura Falk-Helgemoe _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 8866 bytes Desc: image001.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.jpg Type: image/jpeg Size: 1459 bytes Desc: image002.jpg URL: From smoret at ucdavis.edu Mon Apr 9 13:57:59 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Mon, 9 Apr 2012 20:57:59 +0000 Subject: [Equest-users] Scale modeling Message-ID: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu -------------- next part -------------- An HTML attachment was scrubbed... URL: From kwalkerman at gmail.com Mon Apr 9 14:17:35 2012 From: kwalkerman at gmail.com (Karen Walkerman) Date: Mon, 9 Apr 2012 17:17:35 -0400 Subject: [Equest-users] Scale modeling In-Reply-To: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: > Dear all,**** > > ** ** > > I've recently played around quite a bit with E-quest to simulate the > effect of dynamic fenestration on building energy consumption. **** > > For these simulations I've been using a very simple office model with a > skylight on the top as a test-bed for my calculations (with default system > for HVAC and daylighting controls with dimming for lights) but, observing > the values I'm obtaining in output, I see that the values I obtain for > lighting, cooling and heating consumption make sense relatively, i.e. if > compared to themselves in different conditions, but are sometimes of > totally different order of magnitude if compared to each other > (lighting/cooling loads are often much higher than heating, by orders of > magnitude), especially when scaling up the model to bigger sizes. This way, > it's very difficult to see the effect of a variable change on the total > energy consumption. **** > > ** ** > > I know the model I'm using is very idealized, but is there any variable > that I can act on in order to obtain a model which has energy consumption > values more similar to a real building? For example, is there a "suggested" > size of the building that gives better results? Or maybe simulating a > single room in a large building gives more realistic results than the > single room alone? **** > > My point is that I would like to have a model whose results in scale might > be consistent when applied to bigger buildings. **** > > ** ** > > Thanks for your hints and suggestions, **** > > Stefano**** > > ** ** > > --**** > > ** ** > > Stefano Moret > California Lighting Technology Center > University of California, Davis > 633 Pena Drive > Davis, CA 95618 > > **** > > 530-747-3846 > smoret at ucdavis.edu **** > > ** ** > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From smoret at ucdavis.edu Mon Apr 9 14:41:04 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Mon, 9 Apr 2012 21:41:04 +0000 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: <04B072E0E3317A4486513BB18D6579C00725FF81@exmbx4.ex.ad3.ucdavis.edu> Dear Karen, Thanks for your quick reply. I've done plenty of simulation runs, which basically covered different types of buildings, of different sizes, in different locations. Of course different parameters grow with different laws, and if lighting wattage is strictly related to the building area, heating/cooling loads are influenced by the lateral surfaces and perimeter zones. This makes perfectly sense, and it was somehow what I expected to see. Said that, let me explain a little better my question: when I write about different results, I can probably show the point with an example. I take a 5x5x3m building with one skylight on the top (4% SRR) and I get certain values for lighting and HVAC loads. Then I simulate the same exact building with 50x50x6m dimensions, with 4% SRR for skylight, and I get lighting and cooling increasing by a factor of 100, heating by a factor of 10. I also have real data for this larger building, and I simulated it in Energyplus as well, and both these comparisons confirmed that heating and cooling should grow in a similar way in a temperate climate. So my question is, since I want to keep the model simple, especially on the HVAC side, which are the most important variables in Equest which might lead me to more consistent results without bringing excessive complexity into the model. Of course I'm not looking for a unique building which could be valid for all cases, but I'm caring about model consistency and validation. Thanks, Stefano From: Karen Walkerman [mailto:kwalkerman at gmail.com] Sent: Monday, April 09, 2012 2:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Mon Apr 9 15:57:01 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 9 Apr 2012 22:57:01 +0000 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: ...I see my response is arriving too late to the conversation but here are some further thoughts that might help Stefano and others: I have some parallel experience from which I can build/add to Karen's suggestions. I have performed studies with similar structure as Karen is suggesting (creating and adding "building blocks" to evaluate building massing options). However, for Stefano's purposes I would caution to carefully take stock of what questions you are trying to answer and whether an energy model is really the way to go about finding those answers. Using an energy model to develop generic guidelines with "arbitrary" buildings/spaces for something inherently site/climate/building-geometry-specific (such as "ideal window wall ratio" or "ideal window properties") is actually a terribly complex endeavor, as I'm sure you are appreciating. You can ultimately come up with a set of guidelines/spreadsheets/principles to use, but applying such developed guidelines to an actual project for decision-making will always be fraught with accuracy disclaimers (perhaps that is not the ultimate goal - I'm only throwing this out for consideration). Guidelines built around generic conditions are indeed useful and have their place (ASHRAE's advanced energy design guides are worth reviewing if you're at the outset of trying to find such results), but should only be relied upon in the context of "I don't want to invest in a site-specific study and the increased accuracy / differing suggestions that may produce." Evaluating how well any study applies to the project-at-hand is something to always keep in mind. To cut myself off: I think my response drafted so far is falling away from Stefano's original question as he's more recently clarifying it, but I'm ultimately driving towards furthering Karen's first line: Build project-specific models where you need a project-specific answer. To Stefano's issue of scaling - I am nodding my head vigorously as you're observing how spaces modeled in isolation do not always additively represent a group of spaces modeled together. It's possible for that to happen under certain circumstances, but the variables in play do not normally scale linearly between an isolated space and a whole building (consider the ratio of envelope surface area to conditioned volume, for one instance). A big part of "big picture" modeling differences when compared to "the smaller parts" is the tempering of various loads across spaces and the way that has energy saving effects on HVAC systems in particular . I would not spend too much time deliberating on such (expected) differences, and would emphasize focusing on the results of isolated or "whole building" models as appropriate to the purpose of your study =). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From smoret at ucdavis.edu Mon Apr 9 16:30:10 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Mon, 9 Apr 2012 23:30:10 +0000 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> Dear Nick, Thanks for your suggestions, I totally agree with your points, and I'm conscious of the issues about the "generic guidelines". I'm still surprised by some unexpected results in my models though: I'll work on my models to try to understand the reasons leading to results which are different from the measured ones. Thanks, Stefano From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 09, 2012 3:57 PM To: Karen Walkerman; Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Scale modeling ...I see my response is arriving too late to the conversation but here are some further thoughts that might help Stefano and others: I have some parallel experience from which I can build/add to Karen's suggestions. I have performed studies with similar structure as Karen is suggesting (creating and adding "building blocks" to evaluate building massing options). However, for Stefano's purposes I would caution to carefully take stock of what questions you are trying to answer and whether an energy model is really the way to go about finding those answers. Using an energy model to develop generic guidelines with "arbitrary" buildings/spaces for something inherently site/climate/building-geometry-specific (such as "ideal window wall ratio" or "ideal window properties") is actually a terribly complex endeavor, as I'm sure you are appreciating. You can ultimately come up with a set of guidelines/spreadsheets/principles to use, but applying such developed guidelines to an actual project for decision-making will always be fraught with accuracy disclaimers (perhaps that is not the ultimate goal - I'm only throwing this out for consideration). Guidelines built around generic conditions are indeed useful and have their place (ASHRAE's advanced energy design guides are worth reviewing if you're at the outset of trying to find such results), but should only be relied upon in the context of "I don't want to invest in a site-specific study and the increased accuracy / differing suggestions that may produce." Evaluating how well any study applies to the project-at-hand is something to always keep in mind. To cut myself off: I think my response drafted so far is falling away from Stefano's original question as he's more recently clarifying it, but I'm ultimately driving towards furthering Karen's first line: Build project-specific models where you need a project-specific answer. To Stefano's issue of scaling - I am nodding my head vigorously as you're observing how spaces modeled in isolation do not always additively represent a group of spaces modeled together. It's possible for that to happen under certain circumstances, but the variables in play do not normally scale linearly between an isolated space and a whole building (consider the ratio of envelope surface area to conditioned volume, for one instance). A big part of "big picture" modeling differences when compared to "the smaller parts" is the tempering of various loads across spaces and the way that has energy saving effects on HVAC systems in particular . I would not spend too much time deliberating on such (expected) differences, and would emphasize focusing on the results of isolated or "whole building" models as appropriate to the purpose of your study =). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From jeremiah at cleantechanalytics.com Mon Apr 9 18:28:17 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Mon, 9 Apr 2012 18:28:17 -0700 Subject: [Equest-users] Scale modeling In-Reply-To: <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> Message-ID: I had all to similar issues with eQuest, and and realized that eQuest is not really a reliable software. *I know the list is going to hate me.. The thing is that eQuest is deceptively easy, but when you want to find reliable results you basically have to find some "workaround"... The deal breaker for me in using eQuest for anything more then exploring early design options was: I had several real buildings complete with Energy Star portfolio manager data, as well as building audits, when I attempted to use eQuest discovered that eQuest was not capable of coming close to reality, in fact it wanted me to have something like zero insulation, and very poor U values to even come close. Given Energy Plus is not going to give exact results either but at least it comes close. Watch the lists, eQuest is full of "how do I come up with a work around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly "how does this feature work" I do not mean to insult eQuest users but my prospective is that it makes more since to use software that is harder to use, has better support and is updated regularly for such professional and high paid work, rather then the "workaround" Why eQuest is so popular is because it is easy, but for something like your project I suggest you use Energy Plus. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret wrote: > Dear Nick,**** > > ** ** > > Thanks for your suggestions, I totally agree with your points, and I?m > conscious of the issues about the ?generic guidelines?. I?m still surprised > by some unexpected results in my models though: I?ll work on my models to > try to understand the reasons leading to results which are different from > the measured ones.**** > > ** ** > > Thanks, Stefano**** > > ** ** > > *From:* Nick Caton [mailto:ncaton at smithboucher.com] > *Sent:* Monday, April 09, 2012 3:57 PM > *To:* Karen Walkerman; Stefano Moret > *Cc:* equest-users at lists.onebuilding.org > *Subject:* RE: [Equest-users] Scale modeling**** > > ** ** > > ?I see my response is arriving too late to the conversation but here are > some further thoughts that might help Stefano and others:**** > > ** ** > > I have some parallel experience from which I can build/add to Karen?s > suggestions.**** > > ** ** > > I have performed studies with similar structure as Karen is suggesting > (creating and adding ?building blocks? to evaluate building massing > options). However, for Stefano?s purposes I would caution to carefully > take stock of what questions you are trying to answer and whether an energy > model is really the way to go about finding those answers. **** > > ** ** > > Using an energy model to develop generic guidelines with ?arbitrary? > buildings/spaces for something inherently > site/climate/building-geometry-specific (such as ?ideal window wall ratio? > or ?ideal window properties?) is actually a terribly complex endeavor, as > I?m sure you are appreciating. You can ultimately come up with a set of > guidelines/spreadsheets/principles to use, but applying such developed > guidelines to an actual project for decision-making will always be fraught > with accuracy disclaimers (perhaps that is not the ultimate goal ? I?m > only throwing this out for consideration). **** > > ** ** > > Guidelines built around generic conditions are indeed useful and have > their place (ASHRAE?s advanced energy design guides are worth reviewing if > you?re at the outset of trying to find such results), but should only be > relied upon in the context of ?I don?t want to invest in a site-specific > study and the increased accuracy / differing suggestions that may > produce.? Evaluating how well any study applies to the project-at-hand is > something to always keep in mind.**** > > ** ** > > To cut myself off: I think my response drafted so far is falling away > from Stefano?s original question as he?s more recently clarifying it, but > I?m ultimately driving towards furthering Karen?s first line: Build > project-specific models where you need a project-specific answer.**** > > ** ** > > To Stefano?s issue of scaling ? I am nodding my head vigorously as you?re > observing how spaces modeled in isolation do not always additively > represent a group of spaces modeled together. It?s possible for that to > happen under certain circumstances, but the variables in play do not > normally scale linearly between an isolated space and a whole building > (consider the ratio of envelope surface area to conditioned volume, for one > instance). A big part of ?big picture? modeling differences when compared > to ?the smaller parts? is the tempering of various loads across spaces and > the way that has energy saving effects on HVAC systems in particular . ** > ** > > ** ** > > I would not spend too much time deliberating on such (expected) > differences, and would emphasize focusing on the results of isolated or > ?whole building? models as appropriate to the purpose of your study =).*** > * > > ** ** > > ~Nick**** > > ** ** > > [image: cid:489575314 at 22072009-0ABB]** > > * * > > *NICK CATON, P.E.* > > SENIOR ENGINEER**** > > ** ** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > ** ** > > *From:* equest-users-bounces at lists.onebuilding.org > [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Karen > Walkerman > *Sent:* Monday, April 09, 2012 4:18 PM > *To:* Stefano Moret > *Cc:* equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] Scale modeling**** > > ** ** > > The short answer is that every building is different, and there is no > "typical" model that will fit them all.**** > > ** ** > > As you mentioned, the ratio between lighting/cooling/heating changes > depending on the size of the building. I'm willing to guess that this is > because the core zones that have very little need for heat get much larger > in relation to the perimeter zones. Also, the building energy needs will > change depending on orientation and global location.**** > > ** ** > > I would suggest that you take a slightly different approach - try to come > up with values that are representative for different types of spaces. You > might do say:**** > > ** ** > > 1. A perimeter office space with XX% glazing (run for North, East, South > and West exposures)**** > > 2. A core office space with no skylights**** > > 3. A core office space with XX% of roof area as skylights**** > > 4. A core manufacturing space???**** > > 5,6,7....**** > > ** ** > > Run each model in the applicable climate. Then, if you have an office > building that is 70% core and 30% perimeter space, you'll have a better > understanding of the building. This is still a very rough approximation, > but should get you farther than trying to model one "typical" building.*** > * > > ** ** > > --**** > > Karen**** > > ** ** > > ** ** > > On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote:* > *** > > Dear all,**** > > **** > > I've recently played around quite a bit with E-quest to simulate the > effect of dynamic fenestration on building energy consumption. **** > > For these simulations I've been using a very simple office model with a > skylight on the top as a test-bed for my calculations (with default system > for HVAC and daylighting controls with dimming for lights) but, observing > the values I'm obtaining in output, I see that the values I obtain for > lighting, cooling and heating consumption make sense relatively, i.e. if > compared to themselves in different conditions, but are sometimes of > totally different order of magnitude if compared to each other > (lighting/cooling loads are often much higher than heating, by orders of > magnitude), especially when scaling up the model to bigger sizes. This way, > it's very difficult to see the effect of a variable change on the total > energy consumption. **** > > **** > > I know the model I'm using is very idealized, but is there any variable > that I can act on in order to obtain a model which has energy consumption > values more similar to a real building? For example, is there a "suggested" > size of the building that gives better results? Or maybe simulating a > single room in a large building gives more realistic results than the > single room alone? **** > > My point is that I would like to have a model whose results in scale might > be consistent when applied to bigger buildings. **** > > **** > > Thanks for your hints and suggestions, **** > > Stefano**** > > **** > > --**** > > **** > > Stefano Moret > California Lighting Technology Center > University of California, Davis > 633 Pena Drive > Davis, CA 95618**** > > 530-747-3846 > smoret at ucdavis.edu ** ** > > **** > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > ** ** > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From Joey.Jiao at WSPGroup.com.cn Mon Apr 9 20:51:13 2012 From: Joey.Jiao at WSPGroup.com.cn (Jiao, Joey) Date: Tue, 10 Apr 2012 11:51:13 +0800 Subject: [Equest-users] =?gb2312?b?tPC4tDogIEhlbHAgb24gTW9kZWxpbmcgRE9B?= =?gb2312?b?UyBpbiBlUVVFU1Q=?= Message-ID: <0F18FC782AAB044BADF94EA196DF1261FDAFE6@exc03ahk1hk.asia.wspgroup.com> Hi, Jaya. As I know, DOAS can't simulation a system with heat recovery. I made some test model before, it seems the system calculate the return air volume and temperature only include its own zone. I used single zone with reheat as the test system. But I made the test a long time ago, can't sure about it .If you want to check it , please make a simple model and check the SIM report to confirm it . Anyone else put some light on it? Thank you. Joey ???: Jaya Mukhopadhyay [mailto:jaya_mukho at yahoo.com] ????: 2012?4?9? 12:47 ???: equest-users at lists.onebuilding.org ??: [Equest-users] Help on Modeling DOAS in eQUEST Hello: Can anybody share their experiences on modeling the DOAS using eQUEST? I am especially not clear about whether it is possible to model energy recovery, given the fact that we are defining a dummy zone with no loads. Thanks Jaya Mukhopadhyay -------------- next part -------------- An HTML attachment was scrubbed... URL: From smoret at ucdavis.edu Mon Apr 9 23:05:12 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Tue, 10 Apr 2012 06:05:12 +0000 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> Message-ID: <3A795956-D0A0-4DFA-8BEF-DD499838BE7F@ucdavis.edu> Thanks all for your considerations, I much appreciate your recommendations. The nice thing about E-quest is that it support some elements, e.g. skylights, with many different features, while in Energyplus they are usually treated as normal windows. Thanks again, Cheers Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu On 09/apr/2012, at 18.28, CleanTech Analytics wrote: I had all to similar issues with eQuest, and and realized that eQuest is not really a reliable software. *I know the list is going to hate me.. The thing is that eQuest is deceptively easy, but when you want to find reliable results you basically have to find some "workaround"... The deal breaker for me in using eQuest for anything more then exploring early design options was: I had several real buildings complete with Energy Star portfolio manager data, as well as building audits, when I attempted to use eQuest discovered that eQuest was not capable of coming close to reality, in fact it wanted me to have something like zero insulation, and very poor U values to even come close. Given Energy Plus is not going to give exact results either but at least it comes close. Watch the lists, eQuest is full of "how do I come up with a work around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly "how does this feature work" I do not mean to insult eQuest users but my prospective is that it makes more since to use software that is harder to use, has better support and is updated regularly for such professional and high paid work, rather then the "workaround" Why eQuest is so popular is because it is easy, but for something like your project I suggest you use Energy Plus. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret > wrote: Dear Nick, Thanks for your suggestions, I totally agree with your points, and I?m conscious of the issues about the ?generic guidelines?. I?m still surprised by some unexpected results in my models though: I?ll work on my models to try to understand the reasons leading to results which are different from the measured ones. Thanks, Stefano From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 09, 2012 3:57 PM To: Karen Walkerman; Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Scale modeling ?I see my response is arriving too late to the conversation but here are some further thoughts that might help Stefano and others: I have some parallel experience from which I can build/add to Karen?s suggestions. I have performed studies with similar structure as Karen is suggesting (creating and adding ?building blocks? to evaluate building massing options). However, for Stefano?s purposes I would caution to carefully take stock of what questions you are trying to answer and whether an energy model is really the way to go about finding those answers. Using an energy model to develop generic guidelines with ?arbitrary? buildings/spaces for something inherently site/climate/building-geometry-specific (such as ?ideal window wall ratio? or ?ideal window properties?) is actually a terribly complex endeavor, as I?m sure you are appreciating. You can ultimately come up with a set of guidelines/spreadsheets/principles to use, but applying such developed guidelines to an actual project for decision-making will always be fraught with accuracy disclaimers (perhaps that is not the ultimate goal ? I?m only throwing this out for consideration). Guidelines built around generic conditions are indeed useful and have their place (ASHRAE?s advanced energy design guides are worth reviewing if you?re at the outset of trying to find such results), but should only be relied upon in the context of ?I don?t want to invest in a site-specific study and the increased accuracy / differing suggestions that may produce.? Evaluating how well any study applies to the project-at-hand is something to always keep in mind. To cut myself off: I think my response drafted so far is falling away from Stefano?s original question as he?s more recently clarifying it, but I?m ultimately driving towards furthering Karen?s first line: Build project-specific models where you need a project-specific answer. To Stefano?s issue of scaling ? I am nodding my head vigorously as you?re observing how spaces modeled in isolation do not always additively represent a group of spaces modeled together. It?s possible for that to happen under certain circumstances, but the variables in play do not normally scale linearly between an isolated space and a whole building (consider the ratio of envelope surface area to conditioned volume, for one instance). A big part of ?big picture? modeling differences when compared to ?the smaller parts? is the tempering of various loads across spaces and the way that has energy saving effects on HVAC systems in particular . I would not spend too much time deliberating on such (expected) differences, and would emphasize focusing on the results of isolated or ?whole building? models as appropriate to the purpose of your study =). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Tue Apr 10 00:20:02 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Tue, 10 Apr 2012 00:20:02 -0700 Subject: [Equest-users] Scale modeling In-Reply-To: <3A795956-D0A0-4DFA-8BEF-DD499838BE7F@ucdavis.edu> References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> <3A795956-D0A0-4DFA-8BEF-DD499838BE7F@ucdavis.edu> Message-ID: Thanks I will keep that in mind.. I kinda enjoy the eQuest interface, so it is good to know there are modeling tasks that it shines in! It has a nice parametric skylight tool and good libraries, so will now be my tool of choice when skylights are involved.. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Mon, Apr 9, 2012 at 11:05 PM, Stefano Moret wrote: > Thanks all for your considerations, I much appreciate your > recommendations. > The nice thing about E-quest is that it support some elements, e.g. > skylights, with many different features, while in Energyplus they are > usually treated as normal windows. > > Thanks again, Cheers > Stefano > > -- > > Stefano Moret > California Lighting Technology Center > University of California, Davis > 633 Pena Drive > Davis, CA 95618 > > 530-747-3846 > smoret at ucdavis.edu > > On 09/apr/2012, at 18.28, CleanTech Analytics wrote: > > I had all to similar issues with eQuest, and and realized that eQuest is > not really a reliable software. *I know the list is going to hate me.. The > thing is that eQuest is deceptively easy, but when you want to find > reliable results you basically have to find some "workaround"... > > The deal breaker for me in using eQuest for anything more then exploring > early design options was: > > I had several real buildings complete with Energy Star portfolio manager > data, as well as building audits, when I attempted to use eQuest discovered > that eQuest was not capable of coming close to reality, in fact it wanted > me to have something like zero insulation, and very poor U values to even > come close. Given Energy Plus is not going to give exact results either but > at least it comes close. > > Watch the lists, eQuest is full of "how do I come up with a work > around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly > "how does this feature work" > > I do not mean to insult eQuest users but my prospective is that it makes > more since to use software that is harder to use, has better support and is > updated regularly for such professional and high paid work, rather then the > "workaround" > Why eQuest is so popular is because it is easy, but for something like > your project I suggest you use Energy Plus. > > > *Jeremiah D. Crossett* > *CleanTech Analytics* > *503-688-8951* > *www.cleantechanalytics.com* > > > * > This document may contain valuable information proprietary to CleanTech > Analytics which is private and confidential. It may not be shared, copied, > stored or transmitted in any form without the prior written consent of > CleanTech Analytics > * > > > > On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret wrote: > >> Dear Nick,**** >> >> ** ** >> >> Thanks for your suggestions, I totally agree with your points, and I?m >> conscious of the issues about the ?generic guidelines?. I?m still surprised >> by some unexpected results in my models though: I?ll work on my models to >> try to understand the reasons leading to results which are different from >> the measured ones.**** >> >> ** ** >> >> Thanks, Stefano**** >> >> ** ** >> >> *From:* Nick Caton [mailto:ncaton at smithboucher.com] >> *Sent:* Monday, April 09, 2012 3:57 PM >> *To:* Karen Walkerman; Stefano Moret >> *Cc:* equest-users at lists.onebuilding.org >> *Subject:* RE: [Equest-users] Scale modeling**** >> >> ** ** >> >> ?I see my response is arriving too late to the conversation but here are >> some further thoughts that might help Stefano and others:**** >> >> ** ** >> >> I have some parallel experience from which I can build/add to Karen?s >> suggestions.**** >> >> ** ** >> >> I have performed studies with similar structure as Karen is suggesting >> (creating and adding ?building blocks? to evaluate building massing >> options). However, for Stefano?s purposes I would caution to carefully >> take stock of what questions you are trying to answer and whether an energy >> model is really the way to go about finding those answers. **** >> >> ** ** >> >> Using an energy model to develop generic guidelines with ?arbitrary? >> buildings/spaces for something inherently >> site/climate/building-geometry-specific (such as ?ideal window wall ratio? >> or ?ideal window properties?) is actually a terribly complex endeavor, as >> I?m sure you are appreciating. You can ultimately come up with a set of >> guidelines/spreadsheets/principles to use, but applying such developed >> guidelines to an actual project for decision-making will always be fraught >> with accuracy disclaimers (perhaps that is not the ultimate goal ? I?m >> only throwing this out for consideration). **** >> >> ** ** >> >> Guidelines built around generic conditions are indeed useful and have >> their place (ASHRAE?s advanced energy design guides are worth reviewing if >> you?re at the outset of trying to find such results), but should only be >> relied upon in the context of ?I don?t want to invest in a site-specific >> study and the increased accuracy / differing suggestions that may >> produce.? Evaluating how well any study applies to the project-at-hand is >> something to always keep in mind.**** >> >> ** ** >> >> To cut myself off: I think my response drafted so far is falling away >> from Stefano?s original question as he?s more recently clarifying it, but >> I?m ultimately driving towards furthering Karen?s first line: Build >> project-specific models where you need a project-specific answer.**** >> >> ** ** >> >> To Stefano?s issue of scaling ? I am nodding my head vigorously as you?re >> observing how spaces modeled in isolation do not always additively >> represent a group of spaces modeled together. It?s possible for that to >> happen under certain circumstances, but the variables in play do not >> normally scale linearly between an isolated space and a whole building >> (consider the ratio of envelope surface area to conditioned volume, for one >> instance). A big part of ?big picture? modeling differences when compared >> to ?the smaller parts? is the tempering of various loads across spaces and >> the way that has energy saving effects on HVAC systems in particular . * >> *** >> >> ** ** >> >> I would not spend too much time deliberating on such (expected) >> differences, and would emphasize focusing on the results of isolated or >> ?whole building? models as appropriate to the purpose of your study =).** >> ** >> >> ** ** >> >> ~Nick**** >> >> ** ** >> >> [image: cid:489575314 at 22072009-0ABB]** >> >> * * >> >> *NICK CATON, P.E.* >> >> SENIOR ENGINEER**** >> >> ** ** >> >> Smith & Boucher Engineers**** >> >> 25501 west valley parkway, suite 200**** >> >> olathe, ks 66061**** >> >> direct 913.344.0036**** >> >> fax 913.345.0617**** >> >> www.smithboucher.com* ***** >> >> ** ** >> >> *From:* equest-users-bounces at lists.onebuilding.org >> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Karen >> Walkerman >> *Sent:* Monday, April 09, 2012 4:18 PM >> *To:* Stefano Moret >> *Cc:* equest-users at lists.onebuilding.org >> *Subject:* Re: [Equest-users] Scale modeling**** >> >> ** ** >> >> The short answer is that every building is different, and there is no >> "typical" model that will fit them all.**** >> >> ** ** >> >> As you mentioned, the ratio between lighting/cooling/heating changes >> depending on the size of the building. I'm willing to guess that this is >> because the core zones that have very little need for heat get much larger >> in relation to the perimeter zones. Also, the building energy needs will >> change depending on orientation and global location.**** >> >> ** ** >> >> I would suggest that you take a slightly different approach - try to come >> up with values that are representative for different types of spaces. You >> might do say:**** >> >> ** ** >> >> 1. A perimeter office space with XX% glazing (run for North, East, South >> and West exposures)**** >> >> 2. A core office space with no skylights**** >> >> 3. A core office space with XX% of roof area as skylights**** >> >> 4. A core manufacturing space???**** >> >> 5,6,7....**** >> >> ** ** >> >> Run each model in the applicable climate. Then, if you have an office >> building that is 70% core and 30% perimeter space, you'll have a better >> understanding of the building. This is still a very rough approximation, >> but should get you farther than trying to model one "typical" building.** >> ** >> >> ** ** >> >> --**** >> >> Karen**** >> >> ** ** >> >> ** ** >> >> On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: >> **** >> >> Dear all,**** >> >> **** >> >> I've recently played around quite a bit with E-quest to simulate the >> effect of dynamic fenestration on building energy consumption. **** >> >> For these simulations I've been using a very simple office model with a >> skylight on the top as a test-bed for my calculations (with default system >> for HVAC and daylighting controls with dimming for lights) but, observing >> the values I'm obtaining in output, I see that the values I obtain for >> lighting, cooling and heating consumption make sense relatively, i.e. if >> compared to themselves in different conditions, but are sometimes of >> totally different order of magnitude if compared to each other >> (lighting/cooling loads are often much higher than heating, by orders of >> magnitude), especially when scaling up the model to bigger sizes. This way, >> it's very difficult to see the effect of a variable change on the total >> energy consumption. **** >> >> **** >> >> I know the model I'm using is very idealized, but is there any variable >> that I can act on in order to obtain a model which has energy consumption >> values more similar to a real building? For example, is there a "suggested" >> size of the building that gives better results? Or maybe simulating a >> single room in a large building gives more realistic results than the >> single room alone? **** >> >> My point is that I would like to have a model whose results in scale >> might be consistent when applied to bigger buildings. **** >> >> **** >> >> Thanks for your hints and suggestions, **** >> >> Stefano**** >> >> **** >> >> --**** >> >> **** >> >> Stefano Moret >> California Lighting Technology Center >> University of California, Davis >> 633 Pena Drive >> Davis, CA 95618**** >> >> 530-747-3846 >> smoret at ucdavis.edu * *** >> >> **** >> >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** >> >> ** ** >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> >> > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From Vikram.Sami at perkinswill.com Tue Apr 10 06:10:17 2012 From: Vikram.Sami at perkinswill.com (Sami, Vikram) Date: Tue, 10 Apr 2012 08:10:17 -0500 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> Message-ID: Good points Jeremiah. Yes - eQUEST is frustrating and it's a pain in the backside sometimes to try to make it do what you want it to. Maybe Energyplus is a better program to use for this. However - I don't think workarounds are necessarily a bad thing. In my experience - if you are experimenting with workarounds, it enhances your understanding of the process you are trying to model, and as a result makes you more thoughtful and allows you apply critical thinking to the process. Ultimately - most modeling is about that last item - critical thinking. Vikram Sami, LEED AP BD+C Sustainable Design Analyst 1315 Peachtree St. NE, Atlanta, GA 30309 t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com Perkins+Will. Ideas + buildings that honor the broader goals of society From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Monday, April 09, 2012 9:28 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling I had all to similar issues with eQuest, and and realized that eQuest is not really a reliable software. *I know the list is going to hate me.. The thing is that eQuest is deceptively easy, but when you want to find reliable results you basically have to find some "workaround"... The deal breaker for me in using eQuest for anything more then exploring early design options was: I had several real buildings complete with Energy Star portfolio manager data, as well as building audits, when I attempted to use eQuest discovered that eQuest was not capable of coming close to reality, in fact it wanted me to have something like zero insulation, and very poor U values to even come close. Given Energy Plus is not going to give exact results either but at least it comes close. Watch the lists, eQuest is full of "how do I come up with a work around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly "how does this feature work" I do not mean to insult eQuest users but my prospective is that it makes more since to use software that is harder to use, has better support and is updated regularly for such professional and high paid work, rather then the "workaround" Why eQuest is so popular is because it is easy, but for something like your project I suggest you use Energy Plus. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret > wrote: Dear Nick, Thanks for your suggestions, I totally agree with your points, and I'm conscious of the issues about the "generic guidelines". I'm still surprised by some unexpected results in my models though: I'll work on my models to try to understand the reasons leading to results which are different from the measured ones. Thanks, Stefano From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 09, 2012 3:57 PM To: Karen Walkerman; Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Scale modeling ...I see my response is arriving too late to the conversation but here are some further thoughts that might help Stefano and others: I have some parallel experience from which I can build/add to Karen's suggestions. I have performed studies with similar structure as Karen is suggesting (creating and adding "building blocks" to evaluate building massing options). However, for Stefano's purposes I would caution to carefully take stock of what questions you are trying to answer and whether an energy model is really the way to go about finding those answers. Using an energy model to develop generic guidelines with "arbitrary" buildings/spaces for something inherently site/climate/building-geometry-specific (such as "ideal window wall ratio" or "ideal window properties") is actually a terribly complex endeavor, as I'm sure you are appreciating. You can ultimately come up with a set of guidelines/spreadsheets/principles to use, but applying such developed guidelines to an actual project for decision-making will always be fraught with accuracy disclaimers (perhaps that is not the ultimate goal - I'm only throwing this out for consideration). Guidelines built around generic conditions are indeed useful and have their place (ASHRAE's advanced energy design guides are worth reviewing if you're at the outset of trying to find such results), but should only be relied upon in the context of "I don't want to invest in a site-specific study and the increased accuracy / differing suggestions that may produce." Evaluating how well any study applies to the project-at-hand is something to always keep in mind. To cut myself off: I think my response drafted so far is falling away from Stefano's original question as he's more recently clarifying it, but I'm ultimately driving towards furthering Karen's first line: Build project-specific models where you need a project-specific answer. To Stefano's issue of scaling - I am nodding my head vigorously as you're observing how spaces modeled in isolation do not always additively represent a group of spaces modeled together. It's possible for that to happen under certain circumstances, but the variables in play do not normally scale linearly between an isolated space and a whole building (consider the ratio of envelope surface area to conditioned volume, for one instance). A big part of "big picture" modeling differences when compared to "the smaller parts" is the tempering of various loads across spaces and the way that has energy saving effects on HVAC systems in particular . I would not spend too much time deliberating on such (expected) differences, and would emphasize focusing on the results of isolated or "whole building" models as appropriate to the purpose of your study =). ~Nick NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From bbishop at pathfinder-ea.com Tue Apr 10 06:30:26 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Tue, 10 Apr 2012 13:30:26 +0000 Subject: [Equest-users] Scale modeling - reliable software In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> <04B072E0E3317A4486513BB18D6579C0072600EA@exmbx4.ex.ad3.ucdavis.edu> Message-ID: <90D829482BDEDB4CB264DE5060592B190487626E@lightning.pathfinderengineers.com> Canon vs. Nikon. When you choose a photographer, do you ask to see their camera equipment? No, you look at their portfolio. There is no camera that reliably takes good pictures - you need a photographer that knows what they're doing. The best energy modeling program is the one you are most familiar with. ~Bill P.S. I can capture great shots with my Pentax K1000 35mm or my Nikon D40x digital SLR, but the Pentax collects dust because the Nikon is fast, inexpensive to use, and gives me immediate feedback. Sure, there are some qualities of film that are hard to reproduce with digital, but 9 times out of 10 you just work within the limitations. [cid:image001.png at 01CD16F8.E6E525D0] From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Monday, April 09, 2012 9:28 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling I had all to similar issues with eQuest, and and realized that eQuest is not really a reliable software. *I know the list is going to hate me.. The thing is that eQuest is deceptively easy, but when you want to find reliable results you basically have to find some "workaround"... The deal breaker for me in using eQuest for anything more then exploring early design options was: I had several real buildings complete with Energy Star portfolio manager data, as well as building audits, when I attempted to use eQuest discovered that eQuest was not capable of coming close to reality, in fact it wanted me to have something like zero insulation, and very poor U values to even come close. Given Energy Plus is not going to give exact results either but at least it comes close. Watch the lists, eQuest is full of "how do I come up with a work around", TRNSYS is mostly "how do I customize" and Energy Plus is mostly "how does this feature work" I do not mean to insult eQuest users but my prospective is that it makes more since to use software that is harder to use, has better support and is updated regularly for such professional and high paid work, rather then the "workaround" Why eQuest is so popular is because it is easy, but for something like your project I suggest you use Energy Plus. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Mon, Apr 9, 2012 at 4:30 PM, Stefano Moret > wrote: Dear Nick, Thanks for your suggestions, I totally agree with your points, and I'm conscious of the issues about the "generic guidelines". I'm still surprised by some unexpected results in my models though: I'll work on my models to try to understand the reasons leading to results which are different from the measured ones. Thanks, Stefano From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 09, 2012 3:57 PM To: Karen Walkerman; Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Scale modeling ...I see my response is arriving too late to the conversation but here are some further thoughts that might help Stefano and others: I have some parallel experience from which I can build/add to Karen's suggestions. I have performed studies with similar structure as Karen is suggesting (creating and adding "building blocks" to evaluate building massing options). However, for Stefano's purposes I would caution to carefully take stock of what questions you are trying to answer and whether an energy model is really the way to go about finding those answers. Using an energy model to develop generic guidelines with "arbitrary" buildings/spaces for something inherently site/climate/building-geometry-specific (such as "ideal window wall ratio" or "ideal window properties") is actually a terribly complex endeavor, as I'm sure you are appreciating. You can ultimately come up with a set of guidelines/spreadsheets/principles to use, but applying such developed guidelines to an actual project for decision-making will always be fraught with accuracy disclaimers (perhaps that is not the ultimate goal - I'm only throwing this out for consideration). Guidelines built around generic conditions are indeed useful and have their place (ASHRAE's advanced energy design guides are worth reviewing if you're at the outset of trying to find such results), but should only be relied upon in the context of "I don't want to invest in a site-specific study and the increased accuracy / differing suggestions that may produce." Evaluating how well any study applies to the project-at-hand is something to always keep in mind. To cut myself off: I think my response drafted so far is falling away from Stefano's original question as he's more recently clarifying it, but I'm ultimately driving towards furthering Karen's first line: Build project-specific models where you need a project-specific answer. To Stefano's issue of scaling - I am nodding my head vigorously as you're observing how spaces modeled in isolation do not always additively represent a group of spaces modeled together. It's possible for that to happen under certain circumstances, but the variables in play do not normally scale linearly between an isolated space and a whole building (consider the ratio of envelope surface area to conditioned volume, for one instance). A big part of "big picture" modeling differences when compared to "the smaller parts" is the tempering of various loads across spaces and the way that has energy saving effects on HVAC systems in particular . I would not spend too much time deliberating on such (expected) differences, and would emphasize focusing on the results of isolated or "whole building" models as appropriate to the purpose of your study =). ~Nick Error! Filename not specified. NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 21646 bytes Desc: image001.png URL: From bruce5 at bellnet.ca Tue Apr 10 07:59:07 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Tue, 10 Apr 2012 10:59:07 -0400 Subject: [Equest-users] =?utf-8?b?562U5aSNOiAgSGVscCBvbiBNb2RlbGluZyBET0FT?= =?utf-8?q?_in_eQUEST?= In-Reply-To: <0F18FC782AAB044BADF94EA196DF1261FDAFE6@exc03ahk1hk.asia.wspgroup.com> References: <0F18FC782AAB044BADF94EA196DF1261FDAFE6@exc03ahk1hk.asia.wspgroup.com> Message-ID: <4F844ABB.5010609@bellnet.ca> An HTML attachment was scrubbed... URL: From John.S.Eurek at usace.army.mil Tue Apr 10 09:31:08 2012 From: John.S.Eurek at usace.army.mil (Eurek, John S NWO) Date: Tue, 10 Apr 2012 16:31:08 +0000 Subject: [Equest-users] Scale modeling (UNCLASSIFIED) In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: Classification: UNCLASSIFIED Caveats: NONE Shrews must eat 80-90 % of their own body weight in food daily. An elephant eats about 5% of their own body weight in food daily. The surface area to mass ratios are vastly different. Heat loss, metabolism (internal loads) and fur are very different. If an elephant had the fur of a mouse it would die from overheating. You can't model a small building and try to extrapolate the results to a large building. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE From smartin at shaunmartinconsulting.com Tue Apr 10 10:16:41 2012 From: smartin at shaunmartinconsulting.com (Shaun Martin) Date: Tue, 10 Apr 2012 10:16:41 -0700 Subject: [Equest-users] Scale modeling In-Reply-To: References: <04B072E0E3317A4486513BB18D6579C00725FEE5@exmbx4.ex.ad3.ucdavis.edu> Message-ID: <5165ACA34C02491DB6215D8A63F0590B@SM> Hi Stefano, John's right on point (especially the elephant part). The results likely represent some sort of curve, and are probably multivariate. My suggestion would be to model large, medium and small scenarios and do hourly reports of the loads to see what is happening at different outside temperatures. Shaun Martin -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 10, 2012 9:31 AM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE Shrews must eat 80-90 % of their own body weight in food daily. An elephant eats about 5% of their own body weight in food daily. The surface area to mass ratios are vastly different. Heat loss, metabolism (internal loads) and fur are very different. If an elephant had the fur of a mouse it would die from overheating. You can't model a small building and try to extrapolate the results to a large building. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From joe at thespinnakergroupinc.com Tue Apr 10 10:44:40 2012 From: joe at thespinnakergroupinc.com (=?utf-8?B?am9lQHRoZXNwaW5uYWtlcmdyb3VwaW5jLmNvbQ==?=) Date: Tue, 10 Apr 2012 13:44:40 -0400 Subject: [Equest-users] =?utf-8?q?Scale_modeling?= Message-ID: <38.D8.12885.881748F4@cm-omr4> If the building is being scaled by some magnitude, then all dimensions need to be scaled equally. Otherwise, as has been mentioned in the previous emails, the ratio of envelope surface area to floor plan area will change. A 10x10x10 building, (heat/cool load-wise), will scale better to a 100x100x100 then it would to a 100x100x10, because the ratio of floor space to envelope area is maintained. Although only the top floor will have roof load. And a skylight will only effect the top floor of the larger scale building. Can you change from a skylight to a window with daylighting? This would scale better. Joe Fleming, PE, BEMP, LEED AP BD+C ----- Reply message ----- From: "Shaun Martin" To: Subject: [Equest-users] Scale modeling Date: Tue, Apr 10, 2012 1:16 pm Hi Stefano, John's right on point (especially the elephant part). The results likely represent some sort of curve, and are probably multivariate. My suggestion would be to model large, medium and small scenarios and do hourly reports of the loads to see what is happening at different outside temperatures. Shaun Martin -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 10, 2012 9:31 AM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE Shrews must eat 80-90 % of their own body weight in food daily. An elephant eats about 5% of their own body weight in food daily. The surface area to mass ratios are vastly different. Heat loss, metabolism (internal loads) and fur are very different. If an elephant had the fur of a mouse it would die from overheating. You can't model a small building and try to extrapolate the results to a large building. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From joe at thespinnakergroupinc.com Tue Apr 10 11:06:07 2012 From: joe at thespinnakergroupinc.com (=?utf-8?B?am9lQHRoZXNwaW5uYWtlcmdyb3VwaW5jLmNvbQ==?=) Date: Tue, 10 Apr 2012 14:06:07 -0400 Subject: [Equest-users] =?utf-8?q?Scale_modeling?= Message-ID: <62.36.27638.F86748F4@cm-omr2> And of course note you have multiple floors to deal with when you scale up... On second thought a better way to scale would he to maintain the ratio of length x width / height x ((2 x length) + (2 x width)) If height is constant then a 10x10 space scaled up ten times floor area would best scale to something like 194x5.1 (excuse calculations, no calculator doing this at red lights). Where other issues arise like the exposure of the long face will make a big impact. If building modeling could be scaled for certain constants this easily them we could do it with little paper wheels like ductulators. Fun to think about though! Joe Fleming, PE, BEMP, LEED AP BD+C ----- Reply message ----- From: "joe at thespinnakergroupinc.com" To: "Shaun Martin" , Subject: [Equest-users] Scale modeling Date: Tue, Apr 10, 2012 1:44 pm If the building is being scaled by some magnitude, then all dimensions need to be scaled equally. Otherwise, as has been mentioned in the previous emails, the ratio of envelope surface area to floor plan area will change. A 10x10x10 building, (heat/cool load-wise), will scale better to a 100x100x100 then it would to a 100x100x10, because the ratio of floor space to envelope area is maintained. Although only the top floor will have roof load. And a skylight will only effect the top floor of the larger scale building. Can you change from a skylight to a window with daylighting? This would scale better. Joe Fleming, PE, BEMP, LEED AP BD+C ----- Reply message ----- From: "Shaun Martin" To: Subject: [Equest-users] Scale modeling Date: Tue, Apr 10, 2012 1:16 pm Hi Stefano, John's right on point (especially the elephant part). The results likely represent some sort of curve, and are probably multivariate. My suggestion would be to model large, medium and small scenarios and do hourly reports of the loads to see what is happening at different outside temperatures. Shaun Martin -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 10, 2012 9:31 AM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE Shrews must eat 80-90 % of their own body weight in food daily. An elephant eats about 5% of their own body weight in food daily. The surface area to mass ratios are vastly different. Heat loss, metabolism (internal loads) and fur are very different. If an elephant had the fur of a mouse it would die from overheating. You can't model a small building and try to extrapolate the results to a large building. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From yusuf at ytenterprises.com Tue Apr 10 11:53:17 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Wed, 11 Apr 2012 00:23:17 +0530 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: Message-ID: Hello Group - Why do I get unmet hours even when I select the auto size option in the HVAC system? What is the point of auto sizing? - Is there a way to simulate all 4 orientations and get an average result for the base case? Thanks Yusuf Turab IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout ? R.S Puram ? Coimbatore - 641002 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 10 April 2012 00:54, Yusuf Turab wrote: > Hello Group > > I have just started working on my first energy modeling > project. I have two questions: > > - How do I model roof reflectivity. I want to model a roof of 4 inch > concrete with 1 inch stucco at the bottom and top and cover the roof with > cool roof tiles. I am not sure how I can account for the energy efficiency > gains compared to base case through a high SRI roof. > - I am trying to model a large gated community with 330 villas and 7 > other common buildings. As someone suggested on this group I am modeling > each building type separately and using excel to come up with a total > energy usage. But I am not sure how to model the street lighting and > landscape lighting at the exteriors. We plan to use solar street lights and > I want to demonstrate the savings through use of solar energy. > > Many Thanks > > Yusuf Turab > > > > On 10 April 2012 00:32, nirupama lakshminarasimhan < > nirupamalnarasimhan at gmail.com> wrote: > >> I am modeling a big public school with a lot of systems and custom >> windows. The equest file we have right now is taking too long to load. I've >> tried opening it from different locations- the default equest project >> folder on C: , the public server, external HDD, etc. It is just too slow in >> "importing project data" when it opens. The last time this happened, it was >> taking too long to load the BDL file and I ended up deleting a host of >> systems and starting from scratch. All my files- the .inp, .pd2, etc are in >> the same path. I just cannot get it to work faster. I'm trying to calibrate >> the model and it is an awfully long wait for each simulation. Does someone >> have any thoughts on how I could get this to work faster? >> >> >> >> Thank you. >> >> Nirupama >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> >> > -------------- next part -------------- An HTML attachment was scrubbed... URL: From bbishop at pathfinder-ea.com Tue Apr 10 14:29:18 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Tue, 10 Apr 2012 21:29:18 +0000 Subject: [Equest-users] Scroll chiller curves in DOE-2 library Message-ID: <90D829482BDEDB4CB264DE5060592B190487638F@lightning.pathfinderengineers.com> I am modeling a new air-cooled scroll chiller, but eQUEST doesn't have a "scroll" chiller type. I'm guessing the "screw" chiller type is the closest option. Out of curiosity, I searched the library and found the following performance curves: ScrollChlrAirCoolEIR-fPLR ScrollChlrAirCoolEIR-fCHW&OAT ScrollChlrAirCoolCap-fCHW&OAT Using these curves greatly reduced (by 33%) the cooling energy vs. the default ScrewAir-EIR and ScrewAir-Cap curves. Did I find the eQUEST version of a video game cheat code? (Any reason I shouldn't use these ScrollChlr curves?) Thanks, Bill [cid:image001.png at 01CD173D.066245C0] -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 21646 bytes Desc: image001.png URL: From Timothy.Howe at stantec.com Tue Apr 10 14:34:53 2012 From: Timothy.Howe at stantec.com (Howe, Timothy) Date: Tue, 10 Apr 2012 15:34:53 -0600 Subject: [Equest-users] Scroll chiller curves in DOE-2 library In-Reply-To: <90D829482BDEDB4CB264DE5060592B190487638F@lightning.pathfinderengineers.com> References: <90D829482BDEDB4CB264DE5060592B190487638F@lightning.pathfinderengineers.com> Message-ID: <145E7FBFC62D5F4588B01D7D765B02450B63958A36@CD1001-M310.corp.ads> Bill, If you have the time, why don't you get the vendor rep send you over some data which you can make into curves? See the attached docs if you have not already used/have them. Steven Gates created the word doc and Jeremy McClanathan the excel spreadsheet. I would not trust those curves unless someone on the eQUEST development team can validate them. Tim. Timothy Howe, MS, LEED? AP BD+C Mechanical Engineer Stantec 61 Commercial Street Rochester NY 14614 Ph: (585) 413-5347 Fx: (585) 272-1814 Cell: (585) 330-8681 stantec.com The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately. ? Please consider the environment before printing this email. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill Sent: Tuesday, April 10, 2012 5:29 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Scroll chiller curves in DOE-2 library I am modeling a new air-cooled scroll chiller, but eQUEST doesn't have a "scroll" chiller type. I'm guessing the "screw" chiller type is the closest option. Out of curiosity, I searched the library and found the following performance curves: ScrollChlrAirCoolEIR-fPLR ScrollChlrAirCoolEIR-fCHW&OAT ScrollChlrAirCoolCap-fCHW&OAT Using these curves greatly reduced (by 33%) the cooling energy vs. the default ScrewAir-EIR and ScrewAir-Cap curves. Did I find the eQUEST version of a video game cheat code? (Any reason I shouldn't use these ScrollChlr curves?) Thanks, Bill [cid:image001.png at 01CD1740.3C0E0530] -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 21646 bytes Desc: image001.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: Chiller Curves SDG Rev2 11-12-2010.doc Type: application/msword Size: 48128 bytes Desc: Chiller Curves SDG Rev2 11-12-2010.doc URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: eQuest Custom Chiller Curve v2.xls Type: application/vnd.ms-excel Size: 90624 bytes Desc: eQuest Custom Chiller Curve v2.xls URL: From adama at uw.edu Tue Apr 10 14:37:42 2012 From: adama at uw.edu (Adam Michael Aljets) Date: Tue, 10 Apr 2012 14:37:42 -0700 Subject: [Equest-users] Switchable glazing based on two criteria Message-ID: Hi all, I'm having difficulty implementing glazing that switches based on both direct solar incident and temperature. That is, I only want to allow switching when the outside dry bulb is over 60 F, and I want the switch to occur instantaneously when the glazing receives 15.9 BTU/hft^2 direct solar incident radiation. I don't have experience with user expressions/if statements in eQUEST. I've been successful in implementing switchable glazing based only on temperature or only on direct solar incident, but not on both. I tried something along the lines of this for the window in *.inp, but without success: SWITCH-CONTROL = ({if (#G("DRY-BULB TEMP")>60) GLASS-TYPE-SW = "ECW-switched" then "DIR-SOL-INC" else "NO-SWITCH" endif}) SWITCH-SET-LO = 15.9 SWITCH-SET-HI = 15.9 Thanks in advance, Adam -------------- next part -------------- An HTML attachment was scrubbed... URL: From deepika.khowal at gmail.com Tue Apr 10 14:49:39 2012 From: deepika.khowal at gmail.com (Deepika) Date: Tue, 10 Apr 2012 14:49:39 -0700 Subject: [Equest-users] Switchable glazing based on two criteria In-Reply-To: References: Message-ID: <2A736A30-99B3-48B8-9C19-F2DFEABB203D@gmail.com> Hi Unfortunately equest don't have the capability to use multiple triggers . . You might want to try this in energy plus On Apr 10, 2012, at 2:37 PM, Adam Michael Aljets wrote: > Hi all, > > I'm having difficulty implementing glazing that switches based on both direct solar incident and temperature. That is, I only want to allow switching when the outside dry bulb is over 60 F, and I want the switch to occur instantaneously when the glazing receives 15.9 BTU/hft^2 direct solar incident radiation. I don't have experience with user expressions/if statements in eQUEST. I've been successful in implementing switchable glazing based only on temperature or only on direct solar incident, but not on both. > > I tried something along the lines of this for the window in *.inp, but without success: > > SWITCH-CONTROL = ({if (#G("DRY-BULB TEMP")>60) > GLASS-TYPE-SW = "ECW-switched" > then "DIR-SOL-INC" > else "NO-SWITCH" > endif}) > SWITCH-SET-LO = 15.9 > SWITCH-SET-HI = 15.9 > > Thanks in advance, > > Adam > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From xs2144 at gmail.com Tue Apr 10 14:58:34 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Tue, 10 Apr 2012 17:58:34 -0400 Subject: [Equest-users] heat consumption breakdown Message-ID: Hi eQUEST experts :), I was trying to breakdown the amount of heat loss from a townhouse building by checking SIM file, "Building Monthly Load Component" Where I found, say, January, Walls: -6.673 MBTU (Wall R value is 10) *Roofs*: -20.543 MBTU (Top floor roof R value is 20, inside floor roofs R value is 2) I just want to ask, the *"Roofs" *here, means only the top floor roof, or all floor roofs (four floors of this townhouse) of this townhouse. Thank you very much. Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- modihouse2 DOE-2.2-47h2 4/04/2012 14:52:59 BDL RUN 9 REPORT- LS-F Building Monthly Load Component WEATHER FILE- 1 --------------------------------------------------------------------------------------------------------------------------------- (UNITS=MBTU) WALLS ROOFS INT SUR UND SUR INFIL WIN CON WIN SOL OCCUP LIGHTS EQUIP SOURCE TOTAL ----------------------------------------------------------------------------------------------------------------------- HEATNG -6.673 -20.543 0.000 0.000 -2.559 -4.548 1.897 0.794 1.984 1.601 0.000 -28.046 JAN SEN CL -0.025 -0.129 0.000 0.000 -0.095 -0.112 0.189 0.038 0.144 0.121 0.000 0.131 LAT CL 0.000 0.034 0.000 0.000 0.034 ----------------------------------------------------------------------------------------------------------------------- HEATNG -3.806 -12.137 0.000 0.000 -1.576 -2.610 1.867 0.598 1.450 1.169 0.000 -15.045 FEB SEN CL -0.061 -0.364 0.000 0.000 -0.166 -0.338 1.068 0.155 0.462 0.393 0.000 1.148 LAT CL 0.019 0.164 0.000 0.000 0.183 ----------------------------------------------------------------------------------------------------------------------- HEATNG -4.407 -13.952 0.000 0.000 -1.824 -2.985 2.366 0.663 1.581 1.290 0.000 -17.268 MAR SEN CL -0.101 -0.577 0.000 0.000 -0.215 -0.488 1.570 0.170 0.520 0.454 0.000 1.333 LAT CL 0.012 0.185 0.000 0.000 0.197 ----------------------------------------------------------------------------------------------------------------------- HEATNG -1.704 -5.622 0.000 0.000 -0.780 -1.200 1.389 0.424 0.913 0.713 0.000 -5.868 APR SEN CL 0.111 -1.130 0.000 0.000 -0.186 -0.423 3.568 0.382 1.138 0.959 0.000 4.418 LAT CL 0.005 0.426 0.000 0.000 0.431 ----------------------------------------------------------------------------------------------------------------------- HEATNG -0.189 -0.557 0.000 0.000 -0.127 -0.188 0.194 0.084 0.149 0.115 0.000 -0.519 MAY SEN CL 1.743 1.754 0.000 0.000 0.039 0.167 6.262 0.749 1.960 1.621 0.000 14.295 LAT CL 0.286 0.828 0.000 0.000 1.114 ----------------------------------------------------------------------------------------------------------------------- HEATNG -0.019 -0.051 0.000 0.000 -0.012 -0.020 0.019 0.010 0.020 0.015 0.000 -0.038 JUN SEN CL 3.003 5.145 0.000 0.000 0.487 0.893 6.732 0.796 2.015 1.670 0.000 20.740 LAT CL 1.271 0.877 0.000 0.000 2.147 ----------------------------------------------------------------------------------------------------------------------- HEATNG 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 JUL SEN CL 3.592 7.483 0.000 0.000 0.758 1.193 5.623 0.833 2.126 1.722 0.000 23.331 LAT CL 3.023 0.916 0.000 0.000 3.939 ----------------------------------------------------------------------------------------------------------------------- HEATNG -0.031 -0.072 0.000 0.000 -0.021 -0.033 0.031 0.017 0.032 0.024 0.000 -0.052 AUG SEN CL 2.504 4.780 0.000 0.000 0.445 0.651 4.722 0.815 2.068 1.719 0.000 17.704 LAT CL 2.349 0.900 0.000 0.000 3.248 ----------------------------------------------------------------------------------------------------------------------- HEATNG -0.283 -0.718 0.000 0.000 -0.173 -0.255 0.257 0.099 0.185 0.140 0.000 -0.747 SEP SEN CL 1.054 1.178 0.000 0.000 0.007 -0.060 4.112 0.707 1.866 1.532 0.000 10.395 LAT CL 0.573 0.784 0.000 0.000 1.356 ----------------------------------------------------------------------------------------------------------------------- HEATNG -2.797 -8.838 0.000 0.000 -1.170 -1.919 1.453 0.559 1.313 1.067 0.000 -10.332 OCT SEN CL -0.057 -0.693 0.000 0.000 -0.184 -0.380 1.640 0.274 0.806 0.662 0.000 2.067 LAT CL 0.052 0.311 0.000 0.000 0.364 ----------------------------------------------------------------------------------------------------------------------- HEATNG -5.936 -18.178 0.000 0.000 -2.315 -3.969 1.776 0.747 1.854 1.519 0.000 -24.501 NOV SEN CL -0.041 -0.175 0.000 0.000 -0.099 -0.139 0.267 0.059 0.197 0.151 0.000 0.220 LAT CL 0.000 0.057 0.000 0.000 0.057 ----------------------------------------------------------------------------------------------------------------------- HEATNG -8.717 -26.030 0.000 0.000 -3.358 -5.852 1.849 0.813 2.041 1.656 0.000 -37.598 DEC SEN CL -0.001 -0.088 0.000 0.000 -0.051 -0.003 0.006 0.020 0.084 0.067 0.000 0.033 LAT CL 0.000 0.019 0.000 0.000 0.019 ----------------------------------------------------------------------------------------------------------------------- HEATNG -34.560 -106.699 0.000 0.000 -13.915 -23.579 13.099 4.808 11.523 9.308 0.000 -140.016 TOT SEN CL 11.720 17.184 0.000 0.000 0.739 0.961 35.759 4.999 13.384 11.070 0.000 95.815 LAT CL 7.590 5.499 0.000 0.000 13.090 From BHall at karpinskieng.com Tue Apr 10 15:07:15 2012 From: BHall at karpinskieng.com (Hall, Brendan) Date: Tue, 10 Apr 2012 22:07:15 +0000 Subject: [Equest-users] Scroll chiller curves in DOE-2 library In-Reply-To: <145E7FBFC62D5F4588B01D7D765B02450B63958A36@CD1001-M310.corp.ads> References: <90D829482BDEDB4CB264DE5060592B190487638F@lightning.pathfinderengineers.com> <145E7FBFC62D5F4588B01D7D765B02450B63958A36@CD1001-M310.corp.ads> Message-ID: <96503702D289AE429D4575E6A764477D18F4B7@KE-EXCHANGE.BKAINC.local> Great idea in theory, but good luck getting that much data from a vendor. Also, I don't think there is a development team anymore, they all work on E+ now. I was just looking at this today, I had a job with scroll chillers. Just at a glance I noticed the EIR =f(PLR) curve is a lot more linear than the screw chiller curve. The limited part load data I had for my chiller seemed to suggest it was a lot more non linear. So your mileage may vary. Also make sure that you normalize any curves that you use to your design EIR. The default curve is EIR2(1) = .1305 . Elechour = Caphour * EIR * EIR1f(t1,t2) * EIR2f(PLR) / 3413 Btu/kW So if you don't normalize it is going to think it's using a fraction of the energy that it should be. Brendan Hall, M.Sc., LEED AP BD+C Engineer, Mechanical karpinski ENGINEERING 3135 Euclid Avenue Cleveland, OH 44115 P 216.391.3700 x 3111 E bhall at karpinskieng.com W www.karpinskieng.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Howe, Timothy Sent: Tuesday, April 10, 2012 5:35 PM To: Bishop, Bill; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scroll chiller curves in DOE-2 library Bill, If you have the time, why don't you get the vendor rep send you over some data which you can make into curves? See the attached docs if you have not already used/have them. Steven Gates created the word doc and Jeremy McClanathan the excel spreadsheet. I would not trust those curves unless someone on the eQUEST development team can validate them. Tim. Timothy Howe, MS, LEED? AP BD+C Mechanical Engineer Stantec 61 Commercial Street Rochester NY 14614 Ph: (585) 413-5347 Fx: (585) 272-1814 Cell: (585) 330-8681 stantec.com The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately. ? Please consider the environment before printing this email. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill Sent: Tuesday, April 10, 2012 5:29 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Scroll chiller curves in DOE-2 library I am modeling a new air-cooled scroll chiller, but eQUEST doesn't have a "scroll" chiller type. I'm guessing the "screw" chiller type is the closest option. Out of curiosity, I searched the library and found the following performance curves: ScrollChlrAirCoolEIR-fPLR ScrollChlrAirCoolEIR-fCHW&OAT ScrollChlrAirCoolCap-fCHW&OAT Using these curves greatly reduced (by 33%) the cooling energy vs. the default ScrewAir-EIR and ScrewAir-Cap curves. Did I find the eQUEST version of a video game cheat code? (Any reason I shouldn't use these ScrollChlr curves?) Thanks, Bill [cid:image001.png at 01CD1741.4CBFE550] -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 21646 bytes Desc: image001.png URL: From smoret at ucdavis.edu Tue Apr 10 15:19:03 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Tue, 10 Apr 2012 22:19:03 +0000 Subject: [Equest-users] Switchable glazing based on two criteria In-Reply-To: <2A736A30-99B3-48B8-9C19-F2DFEABB203D@gmail.com> References: <2A736A30-99B3-48B8-9C19-F2DFEABB203D@gmail.com> Message-ID: <6AE9941C-9907-4EB1-B4FE-ACA989163676@ucdavis.edu> E+ has some functions to control switchable glazings, for your case I would try the control "OnIfHighOutdoorTempAndHighSolarOnWindow", which seems to fit pretty well to your requirements. Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu On 10/apr/2012, at 14.49, Deepika wrote: Hi Unfortunately equest don't have the capability to use multiple triggers . . You might want to try this in energy plus On Apr 10, 2012, at 2:37 PM, Adam Michael Aljets > wrote: Hi all, I'm having difficulty implementing glazing that switches based on both direct solar incident and temperature. That is, I only want to allow switching when the outside dry bulb is over 60 F, and I want the switch to occur instantaneously when the glazing receives 15.9 BTU/hft^2 direct solar incident radiation. I don't have experience with user expressions/if statements in eQUEST. I've been successful in implementing switchable glazing based only on temperature or only on direct solar incident, but not on both. I tried something along the lines of this for the window in *.inp, but without success: SWITCH-CONTROL = ({if (#G("DRY-BULB TEMP")>60) GLASS-TYPE-SW = "ECW-switched" then "DIR-SOL-INC" else "NO-SWITCH" endif}) SWITCH-SET-LO = 15.9 SWITCH-SET-HI = 15.9 Thanks in advance, Adam _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From xs2144 at gmail.com Tue Apr 10 22:23:13 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Wed, 11 Apr 2012 01:23:13 -0400 Subject: [Equest-users] Question on "roof" Message-ID: Hi everyone, When I build a model as a whole shell, say 5 floor, the simulate results show: only the top floor roof is the whole building roof. But if I build this 5 floor building one floor by one floor, setting like: "position this shell: immediately above", the results show: every floor surface adds together is the whole building roof. So, the amount of heat loss from the roof will be different. Could anybody tell me the reason? Thank you. Best, yang ???????????? ??????5?????????????????roof? ???????????????????????position this shell: immediately above, ????room plan????????????????roof???????roof? ???equest??????roof??????????????????? ?????? ????? -------------- next part -------------- An HTML attachment was scrubbed... URL: From neeraj at kamalcogentenergy.com Wed Apr 11 00:12:13 2012 From: neeraj at kamalcogentenergy.com (Neeraj Arora) Date: Wed, 11 Apr 2012 12:42:13 +0530 Subject: [Equest-users] Removing unmet heating hours or the space heating consumption from the energy model Message-ID: <00c301cd17b2$6f23b100$4d6b1300$@kamalcogentenergy.com> Dear friends, I am doing an energy model and getting few unmet hours in heating. The air side system type is a Variable Air Volume and electric heating at system as well as at zone level. The water side is water cooled chillers with VFD secondary pumping. If I change the system type from VAV to Reheat Fan system, the unmet hours are gone but the model shows huge space heating consumption, which is not acceptable as per the location of the building. The building is located in New Delhi (India). I have tried everything possible to either remove the unmet hours or the space heating consumption but one goes and the other one comes. Is there any way to remove unmet heating hours and the space heating consumption simultaneously? I have used New Delhi weather file. Anyone please help me out to resolve the problem. Thanks in advance. Regards, Neeraj Arora -------------- next part -------------- An HTML attachment was scrubbed... URL: From bruce5 at bellnet.ca Wed Apr 11 05:46:14 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 11 Apr 2012 08:46:14 -0400 Subject: [Equest-users] heat consumption breakdown In-Reply-To: References: Message-ID: <4F857D16.1060600@bellnet.ca> An HTML attachment was scrubbed... URL: From bruce5 at bellnet.ca Wed Apr 11 06:08:22 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 11 Apr 2012 09:08:22 -0400 Subject: [Equest-users] Question on "roof" In-Reply-To: References: Message-ID: <4F858246.4080200@bellnet.ca> An HTML attachment was scrubbed... URL: From bruce5 at bellnet.ca Wed Apr 11 06:33:26 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 11 Apr 2012 09:33:26 -0400 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: Message-ID: <4F858826.3000106@bellnet.ca> An HTML attachment was scrubbed... URL: From bbishop at pathfinder-ea.com Wed Apr 11 06:46:13 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Wed, 11 Apr 2012 13:46:13 +0000 Subject: [Equest-users] Removing unmet heating hours or the space heating consumption from the energy model In-Reply-To: <00c301cd17b2$6f23b100$4d6b1300$@kamalcogentenergy.com> References: <00c301cd17b2$6f23b100$4d6b1300$@kamalcogentenergy.com> Message-ID: <90D829482BDEDB4CB264DE5060592B190487662B@lightning.pathfinderengineers.com> Neeraj, There are many adjustments you can make to address the performance of your VAV system in eQUEST. You didn't describe how many unmet hours you have or what you have tried already. Unmet heating hours can result from underheating, but also from overcooling. Depending on what you change in the model, you might end up increasing your heating energy, or you can end up reducing both cooling and heating energy. Here are a few things to try: ? Enter a value for the system REHEAT-DELTA-T. Leaving this blank can result in thousands of unmet heating hours. ? Set the system COOL-CONTROL to something other than CONSTANT, provided the system you are modeling has the controls capability. I have had success with WARMEST and RESET. ? If you change COOL-CONTROL to COLDEST or WARMEST, increase the zone THROTTLING-RANGE from the default 2?R (2?F). 4?-6? is recommended. You can start with 3? and increase by 0.5? to see how the unmet hours change. If you are comparing two models or two system types, keep the same throttling range in both models to make it a fair comparison. ? Adjust air flow rates, such as your system and/or zonal MIN-FLOW-RATIO. Search the archives here: http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/ You could always post your .inp and .pd2 files and someone might look at your model. Regards, Bill [cid:image001.png at 01CD17C3.1F2432E0] From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Neeraj Arora Sent: Wednesday, April 11, 2012 3:12 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Removing unmet heating hours or the space heating consumption from the energy model Dear friends, I am doing an energy model and getting few unmet hours in heating. The air side system type is a Variable Air Volume and electric heating at system as well as at zone level. The water side is water cooled chillers with VFD secondary pumping. If I change the system type from VAV to Reheat Fan system, the unmet hours are gone but the model shows huge space heating consumption, which is not acceptable as per the location of the building. The building is located in New Delhi (India). I have tried everything possible to either remove the unmet hours or the space heating consumption but one goes and the other one comes. Is there any way to remove unmet heating hours and the space heating consumption simultaneously? I have used New Delhi weather file. Anyone please help me out to resolve the problem. Thanks in advance. Regards, Neeraj Arora -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 21646 bytes Desc: image001.png URL: From bruce5 at bellnet.ca Wed Apr 11 07:16:04 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 11 Apr 2012 10:16:04 -0400 Subject: [Equest-users] Removing unmet heating hours or the space heating consumption from the energy model In-Reply-To: <00c301cd17b2$6f23b100$4d6b1300$@kamalcogentenergy.com> References: <00c301cd17b2$6f23b100$4d6b1300$@kamalcogentenergy.com> Message-ID: <4F859224.4020509@bellnet.ca> An HTML attachment was scrubbed... URL: From John.S.Eurek at usace.army.mil Wed Apr 11 07:49:15 2012 From: John.S.Eurek at usace.army.mil (Eurek, John S NWO) Date: Wed, 11 Apr 2012 14:49:15 +0000 Subject: [Equest-users] Gated Community & Roof reflectivity (UNCLASSIFIED) In-Reply-To: References: Message-ID: Classification: UNCLASSIFIED Caveats: NONE Consider you have 2 rooms, 1 room has 20 people for 1 hour a day, the other room has 1 person all day. If you select 1 piece of equipment using auto sizing, the equipment will make the 21 people comfortable for the one hour. The autosizing sizing is for the design condition. Since the auto sizing balances for the case of 20 in one room and 1 in the other. When there are 0 people in 1 room and 1 in the other, you will likely get unmet load hours. This is one of the many many many cases that cause unmet load hours, but a quick explanation of why you get unmet load hours using autosizing. Autosizing = design case for the worst hour Unmet load hours = does it work for the rest of the 8759 hours John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Yusuf Turab Sent: Tuesday, April 10, 2012 1:53 PM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Gated Community & Roof reflectivity Hello Group * Why do I get unmet hours even when I select the auto size option in the HVAC system? What is the point of auto sizing? * Is there a way to simulate all 4 orientations and get an average result for the base case? Thanks Yusuf Turab IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout | R.S Puram | Coimbatore - 641002 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 10 April 2012 00:54, Yusuf Turab wrote: Hello Group I have just started working on my first energy modeling project. I have two questions: * How do I model roof reflectivity. I want to model a roof of 4 inch concrete with 1 inch stucco at the bottom and top and cover the roof with cool roof tiles. I am not sure how I can account for the energy efficiency gains compared to base case through a high SRI roof. * I am trying to model a large gated community with 330 villas and 7 other common buildings. As someone suggested on this group I am modeling each building type separately and using excel to come up with a total energy usage. But I am not sure how to model the street lighting and landscape lighting at the exteriors. We plan to use solar street lights and I want to demonstrate the savings through use of solar energy. Many Thanks Yusuf Turab On 10 April 2012 00:32, nirupama lakshminarasimhan wrote: I am modeling a big public school with a lot of systems and custom windows. The equest file we have right now is taking too long to load. I've tried opening it from different locations- the default equest project folder on C: , the public server, external HDD, etc. It is just too slow in "importing project data" when it opens. The last time this happened, it was taking too long to load the BDL file and I ended up deleting a host of systems and starting from scratch. All my files- the .inp, .pd2, etc are in the same path. I just cannot get it to work faster. I'm trying to calibrate the model and it is an awfully long wait for each simulation. Does someone have any thoughts on how I could get this to work faster? Thank you. Nirupama _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE From ekaterina.tzekova at mail.utoronto.ca Wed Apr 11 09:50:53 2012 From: ekaterina.tzekova at mail.utoronto.ca (Ekaterina Tzekova) Date: Wed, 11 Apr 2012 16:50:53 +0000 Subject: [Equest-users] (no subject) Message-ID: Hello group, I am trying to model a building with no heating and cooling system to see how the interior temperature fluctuates based on exterior weather conditions. In particular I am concentrating on how hot it can get in a multi-unit residential building during the summer. My main two questions are: * Does eQuest do an average weather year, because I have tried to model different years but the solar radiation on the building is exactly the same. * Has anyone used or know of a report that looks at space temperature? Thank you! Ekaterina Tzekova -------------- next part -------------- An HTML attachment was scrubbed... URL: From yusuf at ytenterprises.com Wed Apr 11 11:30:07 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Thu, 12 Apr 2012 00:00:07 +0530 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: <4F858826.3000106@bellnet.ca> References: <4F858826.3000106@bellnet.ca> Message-ID: Thank you. I guess I have someway to go before I have system sizing and unmet hours fully figured out. One more question: - If I want to create multiple buildings of similar type, built up area and construction but different conditioned spaces, interior layouts and orientations. Can I simply make a copy of the old pd2 file and simply change the footprint zone and orientation in the new file? I tried to do this but I cannot see the 3D model of the new building. Does this mean every model has to be created from scratch? Many Thanks Yusuf On 11 April 2012 19:03, Bruce Easterbrook wrote: > Auto sizing is to ball park your system. There is no computer program > which with the press of a button will design your building for you. You > have unmet hours because you have conflicts in your design. You now have to > identify the conflicts and resolve them. eQuest works by prioritizing the > cooling system, hence when you have conflicts they show up mostly as > unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many > times is a good place to start. Depending on where you are 0.75 or 1.0 > could work better. You can also vary the flow to different zones > independently. You can't put 0.5 cfm into 20 spaces from the same AHU and > expect the heating and cooling needs of each space to be met 100% of the > time. Get into your sim file and figure out where the spaces are with > large unmet hours, figure out why and start adjusting the inputs to reduce > them. > There is no point to average the 4 orientations, nor is it allowed, just > LEED mumbo jumbo. It just illustrates how the orientation of your building > effects the energy consumption to run it. Most modellers get a building, a > street, a front and back with no option on orientation. That is your base > case. It can be handy to illustrate design flaws if there is a large > difference in energy consumption in different directions. Just don't call > it that when you are telling the architect a 20 story atrium is not a great > idea on the north side of a building. lol. > Bruce Easterbrook P.Eng. > Abode Engineering > > > On 10/04/2012 02:53 PM, Yusuf Turab wrote: > > Hello Group > > - Why do I get unmet hours even when I select the auto size option in > the HVAC system? What is the point of auto sizing? > - Is there a way to simulate all 4 orientations and get an average > result for the base case? > > Thanks > Yusuf Turab > IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer > Y T Enterprises > 18 A, Hamsa Layout ? R.S Puram ? Coimbatore - 641002 > > http://www.ytenterprises.com/ > > ***** Email confidentiality notice ***** > The information contained in this email and any attachments is intended > for the name recipients only. It may contain privileged and confidential > information and if you are not the intended recipient, you must not copy > distribute or take any action in reliance on it. If you have received this > email in error, please return it to the sender advising of the error and > delete all copies from your system. > > > On 10 April 2012 00:54, Yusuf Turab wrote: > >> Hello Group >> >> I have just started working on my first energy modeling >> project. I have two questions: >> >> - How do I model roof reflectivity. I want to model a roof of 4 inch >> concrete with 1 inch stucco at the bottom and top and cover the roof with >> cool roof tiles. I am not sure how I can account for the energy efficiency >> gains compared to base case through a high SRI roof. >> - I am trying to model a large gated community with 330 villas and 7 >> other common buildings. As someone suggested on this group I am modeling >> each building type separately and using excel to come up with a total >> energy usage. But I am not sure how to model the street lighting and >> landscape lighting at the exteriors. We plan to use solar street lights and >> I want to demonstrate the savings through use of solar energy. >> >> Many Thanks >> >> Yusuf Turab >> >> >> >> On 10 April 2012 00:32, nirupama lakshminarasimhan < >> nirupamalnarasimhan at gmail.com> wrote: >> >>> I am modeling a big public school with a lot of systems and custom >>> windows. The equest file we have right now is taking too long to load. I've >>> tried opening it from different locations- the default equest project >>> folder on C: , the public server, external HDD, etc. It is just too slow in >>> "importing project data" when it opens. The last time this happened, it was >>> taking too long to load the BDL file and I ended up deleting a host of >>> systems and starting from scratch. All my files- the .inp, .pd2, etc are in >>> the same path. I just cannot get it to work faster. I'm trying to calibrate >>> the model and it is an awfully long wait for each simulation. Does someone >>> have any thoughts on how I could get this to work faster? >>> >>> >>> >>> Thank you. >>> >>> Nirupama >>> >>> _______________________________________________ >>> Equest-users mailing list >>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>> To unsubscribe from this mailing list send a blank message to >>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >>> >>> >> > > > _______________________________________________ > Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Wed Apr 11 11:47:11 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Wed, 11 Apr 2012 18:47:11 +0000 Subject: [Equest-users] Occupany sensors In-Reply-To: <8C466C4FE44E5842A460083B66DF292E192CF9BD@HUBAM-MX-11.halcrow.com> References: <8C466C4FE44E5842A460083B66DF292E192CF9BD@HUBAM-MX-11.halcrow.com> Message-ID: Hi Fareed, There are multiple approaches to modeling occupancy sensors in eQuest... I assume you're in the context of lights. What's appropriate depends on how you have set up your model and to what degree their operation needs to be modeled explicitly. A few approaches, from simple to involved: * Established 90.1 Appendix G approach: Assign a flat % reduction to the installed LPD for the space(s) with occ sensors (only in those that don't already require them, if you're actually doing a proposed/baseline performance rating). * Define alternate fractional schedules that represent hourly operation of lights with and without occ sensors. This can be approached with a few variations to achieve the same result. Some choose to apply a % reduction to the schedules instead of the installed watts per space, achieving an identical result. * Redefine space occupancy schedules in a manner that makes them appropriate to assign to the lighting loads as well (i.e. setting 1.0 for occupied hours), and use the same schedules for both occupancy and lighting - if accuracy is critical, you'll want to consider moving away from a "whole building" fractional schedule as generated by the wizards and move towards "per space type" scheduling. In this scenario the hourly occupancy value is multiplied against the installed Watts for each space, so you could correctly account for an occ. sensor's time delay into an unoccupied hour with a fractional value. More creative (and potentially convoluted) solutions are out there that might fit your model on a case-by-case basis, but the three above are approaches I've used more than once. ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Syed, Fareed Sent: Wednesday, April 06, 2011 10:03 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Occupany sensors Hello All, Is there any way to model occupancy sensors in e-Quest? Thanks, Fareed Syed EIT LEED(r) AP Analytics Specialist Halcrow Yolles One South Dearborn 21st Floor Chicago, IL 60603 tel: +1 312 212 4430 fax: +1 312 212 4206 www.halcrowyolles.com Sustaining and improving the quality of people's lives Visit our website at http://www.halcrow.com ------------------------------------------------------------------------ The contents of this email are confidential, for the sole use of the intended recipient at the email address to which it has been addressed and do not give rise to any binding legal obligation upon Halcrow companies unless subsequently confirmed on headed business notepaper sent by fax, letter or as an email attachment. Whilst reasonable care has been taken to avoid virus transmission, no responsibility for viruses is taken and it is your responsibility to carry out such checks as you feel appropriate. Emails supplied are as found and there's no guarantee that the messages contained within the body of the email have not been edited after receipt. If you receive this email in error, please contact the sender immediately and delete the message from your system. Thank you. ------------------------------------------------------------------------- -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From smartin at shaunmartinconsulting.com Wed Apr 11 11:52:35 2012 From: smartin at shaunmartinconsulting.com (Shaun Martin) Date: Wed, 11 Apr 2012 11:52:35 -0700 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: <4F858826.3000106@bellnet.ca> References: <4F858826.3000106@bellnet.ca> Message-ID: <13D888D6070E443BAA164C4F5A687AD6@SM> Yusuf, Also check your thermostat throttling ranges and whether the unmet hours are occuring at system startup. Shaun Martin LEED AP Principal Shaun Martin Consulting 2060 Pine Street, Vancouver BC V6J 4P8 604-789-1095 smartin at shaunmartinconsulting.com member CAGBC, ASHRAE _____ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook Sent: Wednesday, April 11, 2012 6:33 AM To: Yusuf Turab Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Gated Community & Roof reflectivity Auto sizing is to ball park your system. There is no computer program which with the press of a button will design your building for you. You have unmet hours because you have conflicts in your design. You now have to identify the conflicts and resolve them. eQuest works by prioritizing the cooling system, hence when you have conflicts they show up mostly as unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many times is a good place to start. Depending on where you are 0.75 or 1.0 could work better. You can also vary the flow to different zones independently. You can't put 0.5 cfm into 20 spaces from the same AHU and expect the heating and cooling needs of each space to be met 100% of the time. Get into your sim file and figure out where the spaces are with large unmet hours, figure out why and start adjusting the inputs to reduce them. There is no point to average the 4 orientations, nor is it allowed, just LEED mumbo jumbo. It just illustrates how the orientation of your building effects the energy consumption to run it. Most modellers get a building, a street, a front and back with no option on orientation. That is your base case. It can be handy to illustrate design flaws if there is a large difference in energy consumption in different directions. Just don't call it that when you are telling the architect a 20 story atrium is not a great idea on the north side of a building. lol. Bruce Easterbrook P.Eng. Abode Engineering On 10/04/2012 02:53 PM, Yusuf Turab wrote: Hello Group * Why do I get unmet hours even when I select the auto size option in the HVAC system? What is the point of auto sizing? * Is there a way to simulate all 4 orientations and get an average result for the base case? Thanks Yusuf Turab IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout | R.S Puram | Coimbatore - 641002 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 10 April 2012 00:54, Yusuf Turab wrote: Hello Group I have just started working on my first energy modeling project. I have two questions: * How do I model roof reflectivity. I want to model a roof of 4 inch concrete with 1 inch stucco at the bottom and top and cover the roof with cool roof tiles. I am not sure how I can account for the energy efficiency gains compared to base case through a high SRI roof. * I am trying to model a large gated community with 330 villas and 7 other common buildings. As someone suggested on this group I am modeling each building type separately and using excel to come up with a total energy usage. But I am not sure how to model the street lighting and landscape lighting at the exteriors. We plan to use solar street lights and I want to demonstrate the savings through use of solar energy. Many Thanks Yusuf Turab On 10 April 2012 00:32, nirupama lakshminarasimhan wrote: I am modeling a big public school with a lot of systems and custom windows. The equest file we have right now is taking too long to load. I've tried opening it from different locations- the default equest project folder on C: , the public server, external HDD, etc. It is just too slow in "importing project data" when it opens. The last time this happened, it was taking too long to load the BDL file and I ended up deleting a host of systems and starting from scratch. All my files- the .inp, .pd2, etc are in the same path. I just cannot get it to work faster. I'm trying to calibrate the model and it is an awfully long wait for each simulation. Does someone have any thoughts on how I could get this to work faster? Thank you. Nirupama _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Wed Apr 11 12:04:04 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Wed, 11 Apr 2012 19:04:04 +0000 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: <4F858826.3000106@bellnet.ca> Message-ID: To Yusuf's more recent question below: What you're describing (varying the rotation/layout only with all else remaining constant) sounds most easily accomplished in a single file, within the wizard stage. Set up your first building (ideally as a single shell), then create new shells by copying the first - editing the rotation and internal layout as necessary. If/when you have everything set up, you can save multiple copies of the file and remove the shells you don't want for each case to isolate to the correct building. You shouldn't need re-enter the same information twice. To something Yusuf mentioned earlier: Modeling the savings of solar street/landscape lighting can be re-stated as determining the energy consumption of a "non-solar equivalent." This is a lot trickier than it may seem on the surface. Much of that complexity is tied up in what "non-solar equivalent" means in reality: Dig hard at the cutsheets of the solar equipment in question to come up with some hard numbers for photometrics and runtime realities. If you are not trained/familiar with photometric lighting design software you may want to engage someone who is to help you along the way. [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Yusuf Turab Sent: Wednesday, April 11, 2012 1:30 PM To: Bruce Easterbrook Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Gated Community & Roof reflectivity Thank you. I guess I have someway to go before I have system sizing and unmet hours fully figured out. One more question: * If I want to create multiple buildings of similar type, built up area and construction but different conditioned spaces, interior layouts and orientations. Can I simply make a copy of the old pd2 file and simply change the footprint zone and orientation in the new file? I tried to do this but I cannot see the 3D model of the new building. Does this mean every model has to be created from scratch? Many Thanks Yusuf On 11 April 2012 19:03, Bruce Easterbrook > wrote: Auto sizing is to ball park your system. There is no computer program which with the press of a button will design your building for you. You have unmet hours because you have conflicts in your design. You now have to identify the conflicts and resolve them. eQuest works by prioritizing the cooling system, hence when you have conflicts they show up mostly as unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many times is a good place to start. Depending on where you are 0.75 or 1.0 could work better. You can also vary the flow to different zones independently. You can't put 0.5 cfm into 20 spaces from the same AHU and expect the heating and cooling needs of each space to be met 100% of the time. Get into your sim file and figure out where the spaces are with large unmet hours, figure out why and start adjusting the inputs to reduce them. There is no point to average the 4 orientations, nor is it allowed, just LEED mumbo jumbo. It just illustrates how the orientation of your building effects the energy consumption to run it. Most modellers get a building, a street, a front and back with no option on orientation. That is your base case. It can be handy to illustrate design flaws if there is a large difference in energy consumption in different directions. Just don't call it that when you are telling the architect a 20 story atrium is not a great idea on the north side of a building. lol. Bruce Easterbrook P.Eng. Abode Engineering On 10/04/2012 02:53 PM, Yusuf Turab wrote: Hello Group * Why do I get unmet hours even when I select the auto size option in the HVAC system? What is the point of auto sizing? * Is there a way to simulate all 4 orientations and get an average result for the base case? Thanks Yusuf Turab IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout | R.S Puram | Coimbatore - 641002 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 10 April 2012 00:54, Yusuf Turab > wrote: Hello Group I have just started working on my first energy modeling project. I have two questions: * How do I model roof reflectivity. I want to model a roof of 4 inch concrete with 1 inch stucco at the bottom and top and cover the roof with cool roof tiles. I am not sure how I can account for the energy efficiency gains compared to base case through a high SRI roof. * I am trying to model a large gated community with 330 villas and 7 other common buildings. As someone suggested on this group I am modeling each building type separately and using excel to come up with a total energy usage. But I am not sure how to model the street lighting and landscape lighting at the exteriors. We plan to use solar street lights and I want to demonstrate the savings through use of solar energy. Many Thanks Yusuf Turab On 10 April 2012 00:32, nirupama lakshminarasimhan > wrote: I am modeling a big public school with a lot of systems and custom windows. The equest file we have right now is taking too long to load. I've tried opening it from different locations- the default equest project folder on C: , the public server, external HDD, etc. It is just too slow in "importing project data" when it opens. The last time this happened, it was taking too long to load the BDL file and I ended up deleting a host of systems and starting from scratch. All my files- the .inp, .pd2, etc are in the same path. I just cannot get it to work faster. I'm trying to calibrate the model and it is an awfully long wait for each simulation. Does someone have any thoughts on how I could get this to work faster? Thank you. Nirupama _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From bruce5 at bellnet.ca Wed Apr 11 12:27:56 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 11 Apr 2012 15:27:56 -0400 Subject: [Equest-users] Question on "roof", Archive list In-Reply-To: References: <4F858246.4080200@bellnet.ca> Message-ID: <4F85DB3C.9080406@bellnet.ca> An HTML attachment was scrubbed... URL: From yusuf at ytenterprises.com Wed Apr 11 12:41:38 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Thu, 12 Apr 2012 01:11:38 +0530 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: <4F858826.3000106@bellnet.ca> Message-ID: Thank you Nick I have only partially understood your response on multiple shells but I assume what you say is possible using the DD wizard. I will dig around a bit on that one. Creating multiple files does not seem to work. I do not understand why. With regards to your second suggestion, Indian Green Building Council have asked me not to waste time modeling the street lights. They asked me to use an excel sheet to calculate the total lighting consumption by multiplying the base case LPD of 2.4 W/Sq Mt with total area under lighting and average hrs of usage. In the proposed case I simply have to subtract the total outdoor lighting consumption from the overall energy consumption since it is powered using solar. I thought it makes sense. Thank You very much. Yusuf On 12 April 2012 00:34, Nick Caton wrote: > To Yusuf?s more recent question below:**** > > ** ** > > What you?re describing (varying the rotation/layout only with all else > remaining constant) sounds most easily accomplished in a single file, > within the wizard stage. Set up your first building (ideally as a single > shell), then create new shells by copying the first ? editing the rotation > and internal layout as necessary. If/when you have everything set up, you > can save multiple copies of the file and remove the shells you don?t want > for each case to isolate to the correct building. You shouldn?t need > re-enter the same information twice.**** > > ** ** > > To something Yusuf mentioned earlier:**** > > ** ** > > Modeling the savings of solar street/landscape lighting can be re-stated > as determining the energy consumption of a ?non-solar equivalent.? This is > a lot trickier than it may seem on the surface. Much of that complexity is > tied up in what ?non-solar equivalent? means in reality: Dig hard at the > cutsheets of the solar equipment in question to come up with some hard > numbers for photometrics and runtime realities. If you are not > trained/familiar with photometric lighting design software you may want to > engage someone who is to help you along the way.**** > > ** ** > > [image: cid:489575314 at 22072009-0ABB]** > > * * > > *NICK CATON, P.E.*** > > SENIOR ENGINEER**** > > ** ** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > ** ** > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Yusuf Turab > *Sent:* Wednesday, April 11, 2012 1:30 PM > *To:* Bruce Easterbrook > > *Cc:* equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] Gated Community & Roof reflectivity**** > > ** ** > > Thank you. I guess I have someway to go before I have system sizing and > unmet hours fully figured out. One more question:**** > > - If I want to create multiple buildings of similar type, built up > area and construction but different conditioned spaces, interior layouts > and orientations. Can I simply make a copy of the old pd2 file and simply > change the footprint zone and orientation in the new file? I tried to do > this but I cannot see the 3D model of the new building.**** > > Does this mean every model has to be created from scratch?**** > > Many Thanks**** > > Yusuf**** > > ** ** > > On 11 April 2012 19:03, Bruce Easterbrook wrote:**** > > Auto sizing is to ball park your system. There is no computer program > which with the press of a button will design your building for you. You > have unmet hours because you have conflicts in your design. You now have to > identify the conflicts and resolve them. eQuest works by prioritizing the > cooling system, hence when you have conflicts they show up mostly as > unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many > times is a good place to start. Depending on where you are 0.75 or 1.0 > could work better. You can also vary the flow to different zones > independently. You can't put 0.5 cfm into 20 spaces from the same AHU and > expect the heating and cooling needs of each space to be met 100% of the > time. Get into your sim file and figure out where the spaces are with > large unmet hours, figure out why and start adjusting the inputs to reduce > them. > There is no point to average the 4 orientations, nor is it allowed, just > LEED mumbo jumbo. It just illustrates how the orientation of your building > effects the energy consumption to run it. Most modellers get a building, a > street, a front and back with no option on orientation. That is your base > case. It can be handy to illustrate design flaws if there is a large > difference in energy consumption in different directions. Just don't call > it that when you are telling the architect a 20 story atrium is not a great > idea on the north side of a building. lol. > Bruce Easterbrook P.Eng. > Abode Engineering**** > > > > On 10/04/2012 02:53 PM, Yusuf Turab wrote: **** > > Hello Group**** > > - Why do I get unmet hours even when I select the auto size option in > the HVAC system? What is the point of auto sizing?**** > - Is there a way to simulate all 4 orientations and get an average > result for the base case?**** > > Thanks**** > > Yusuf Turab > IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer > Y T Enterprises > 18 A, Hamsa Layout ? R.S Puram ? Coimbatore - 641002 > > http://www.ytenterprises.com/ > > ***** Email confidentiality notice ***** > The information contained in this email and any attachments is intended > for the name recipients only. It may contain privileged and confidential > information and if you are not the intended recipient, you must not copy > distribute or take any action in reliance on it. If you have received this > email in error, please return it to the sender advising of the error and > delete all copies from your system. > > **** > > On 10 April 2012 00:54, Yusuf Turab wrote:**** > > Hello Group > > I have just started working on my first energy modeling > project. I have two questions:**** > > - How do I model roof reflectivity. I want to model a roof of 4 inch > concrete with 1 inch stucco at the bottom and top and cover the roof with > cool roof tiles. I am not sure how I can account for the energy efficiency > gains compared to base case through a high SRI roof.**** > - I am trying to model a large gated community with 330 villas and 7 > other common buildings. As someone suggested on this group I am modeling > each building type separately and using excel to come up with a total > energy usage. But I am not sure how to model the street lighting and > landscape lighting at the exteriors. We plan to use solar street lights and > I want to demonstrate the savings through use of solar energy.**** > > Many Thanks > > Yusuf Turab > > > **** > > On 10 April 2012 00:32, nirupama lakshminarasimhan < > nirupamalnarasimhan at gmail.com> wrote:**** > > I am modeling a big public school with a lot of systems and custom > windows. The equest file we have right now is taking too long to load. I've > tried opening it from different locations- the default equest project > folder on C: , the public server, external HDD, etc. It is just too slow in > "importing project data" when it opens. The last time this happened, it was > taking too long to load the BDL file and I ended up deleting a host of > systems and starting from scratch. All my files- the .inp, .pd2, etc are in > the same path. I just cannot get it to work faster. I'm trying to calibrate > the model and it is an awfully long wait for each simulation. Does someone > have any thoughts on how I could get this to work faster? **** > > **** > > Thank you.**** > > Nirupama**** > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > ** ** > > > > **** > > _______________________________________________**** > > Equest-users mailing list**** > > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org**** > > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > ** ** > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: From xs2144 at gmail.com Wed Apr 11 12:45:57 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Wed, 11 Apr 2012 15:45:57 -0400 Subject: [Equest-users] calibration models' accurate Message-ID: Hi guys, Based on your experience, if we simulate a real single-family, then compare the monthly gas consumption from ConEdison bill with our simulated data. What the error, or different will be ? 10% 15% 20% or almost exact same. Thank you. -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Wed Apr 11 13:07:11 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Wed, 11 Apr 2012 20:07:11 +0000 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: <4F858826.3000106@bellnet.ca> Message-ID: The complexity I was cautioning for a solar lighting baseline is much simpler when you're being given an installed wattage at least. Sounds like the only thing for you to nail down is operating hours of the solar lights. Regarding the DD wizard... I'm suggesting starting with one file then later splitting into multiple files, as you suggested for use with an external spreadsheet, to appropriately multiply the results without a massive model of the entire campus. Here is a quick illustration: [cid:image002.png at 01CD17F4.C52FDDC0] After completely finishing "Building A," defined as a single shell, click "create new shell" and choose to copy "Building A." You can then make only the necessary edits to orientation, space layout, window layout, etc... and other inputs will be repeated from the copied shell. Repeat that procedure for as many unique buildings as you require, then when finished you can proceed with saving the project a few times and in each project removing the shells you do not need to isolate to one building. Hope that helps get my suggestion across better! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: Yusuf Turab [mailto:yusuf at ytenterprises.com] Sent: Wednesday, April 11, 2012 2:42 PM To: Nick Caton Cc: Bruce Easterbrook; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Gated Community & Roof reflectivity Thank you Nick I have only partially understood your response on multiple shells but I assume what you say is possible using the DD wizard. I will dig around a bit on that one. Creating multiple files does not seem to work. I do not understand why. With regards to your second suggestion, Indian Green Building Council have asked me not to waste time modeling the street lights. They asked me to use an excel sheet to calculate the total lighting consumption by multiplying the base case LPD of 2.4 W/Sq Mt with total area under lighting and average hrs of usage. In the proposed case I simply have to subtract the total outdoor lighting consumption from the overall energy consumption since it is powered using solar. I thought it makes sense. Thank You very much. Yusuf On 12 April 2012 00:34, Nick Caton > wrote: To Yusuf's more recent question below: What you're describing (varying the rotation/layout only with all else remaining constant) sounds most easily accomplished in a single file, within the wizard stage. Set up your first building (ideally as a single shell), then create new shells by copying the first - editing the rotation and internal layout as necessary. If/when you have everything set up, you can save multiple copies of the file and remove the shells you don't want for each case to isolate to the correct building. You shouldn't need re-enter the same information twice. To something Yusuf mentioned earlier: Modeling the savings of solar street/landscape lighting can be re-stated as determining the energy consumption of a "non-solar equivalent." This is a lot trickier than it may seem on the surface. Much of that complexity is tied up in what "non-solar equivalent" means in reality: Dig hard at the cutsheets of the solar equipment in question to come up with some hard numbers for photometrics and runtime realities. If you are not trained/familiar with photometric lighting design software you may want to engage someone who is to help you along the way. [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Yusuf Turab Sent: Wednesday, April 11, 2012 1:30 PM To: Bruce Easterbrook Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Gated Community & Roof reflectivity Thank you. I guess I have someway to go before I have system sizing and unmet hours fully figured out. One more question: * If I want to create multiple buildings of similar type, built up area and construction but different conditioned spaces, interior layouts and orientations. Can I simply make a copy of the old pd2 file and simply change the footprint zone and orientation in the new file? I tried to do this but I cannot see the 3D model of the new building. Does this mean every model has to be created from scratch? Many Thanks Yusuf On 11 April 2012 19:03, Bruce Easterbrook > wrote: Auto sizing is to ball park your system. There is no computer program which with the press of a button will design your building for you. You have unmet hours because you have conflicts in your design. You now have to identify the conflicts and resolve them. eQuest works by prioritizing the cooling system, hence when you have conflicts they show up mostly as unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many times is a good place to start. Depending on where you are 0.75 or 1.0 could work better. You can also vary the flow to different zones independently. You can't put 0.5 cfm into 20 spaces from the same AHU and expect the heating and cooling needs of each space to be met 100% of the time. Get into your sim file and figure out where the spaces are with large unmet hours, figure out why and start adjusting the inputs to reduce them. There is no point to average the 4 orientations, nor is it allowed, just LEED mumbo jumbo. It just illustrates how the orientation of your building effects the energy consumption to run it. Most modellers get a building, a street, a front and back with no option on orientation. That is your base case. It can be handy to illustrate design flaws if there is a large difference in energy consumption in different directions. Just don't call it that when you are telling the architect a 20 story atrium is not a great idea on the north side of a building. lol. Bruce Easterbrook P.Eng. Abode Engineering On 10/04/2012 02:53 PM, Yusuf Turab wrote: Hello Group * Why do I get unmet hours even when I select the auto size option in the HVAC system? What is the point of auto sizing? * Is there a way to simulate all 4 orientations and get an average result for the base case? Thanks Yusuf Turab IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout | R.S Puram | Coimbatore - 641002 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 10 April 2012 00:54, Yusuf Turab > wrote: Hello Group I have just started working on my first energy modeling project. I have two questions: * How do I model roof reflectivity. I want to model a roof of 4 inch concrete with 1 inch stucco at the bottom and top and cover the roof with cool roof tiles. I am not sure how I can account for the energy efficiency gains compared to base case through a high SRI roof. * I am trying to model a large gated community with 330 villas and 7 other common buildings. As someone suggested on this group I am modeling each building type separately and using excel to come up with a total energy usage. But I am not sure how to model the street lighting and landscape lighting at the exteriors. We plan to use solar street lights and I want to demonstrate the savings through use of solar energy. Many Thanks Yusuf Turab On 10 April 2012 00:32, nirupama lakshminarasimhan > wrote: I am modeling a big public school with a lot of systems and custom windows. The equest file we have right now is taking too long to load. I've tried opening it from different locations- the default equest project folder on C: , the public server, external HDD, etc. It is just too slow in "importing project data" when it opens. The last time this happened, it was taking too long to load the BDL file and I ended up deleting a host of systems and starting from scratch. All my files- the .inp, .pd2, etc are in the same path. I just cannot get it to work faster. I'm trying to calibrate the model and it is an awfully long wait for each simulation. Does someone have any thoughts on how I could get this to work faster? Thank you. Nirupama _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.png Type: image/png Size: 22473 bytes Desc: image002.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.jpg Type: image/jpeg Size: 1459 bytes Desc: image003.jpg URL: From yusuf at ytenterprises.com Wed Apr 11 14:35:32 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Thu, 12 Apr 2012 03:05:32 +0530 Subject: [Equest-users] Gated Community & Roof reflectivity In-Reply-To: References: <4F858826.3000106@bellnet.ca> Message-ID: Oh Yes!! I get it now. Many thanks Nick. Regards Yusuf Turab Managing Director IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer Y T Enterprises 18 A, Hamsa Layout ? R.S Puram ? Coimbatore - 641002 Tel: +91 (0)422 4368896 Fax: +91 (0)422 2473697 http://www.ytenterprises.com/ ***** Email confidentiality notice ***** The information contained in this email and any attachments is intended for the name recipients only. It may contain privileged and confidential information and if you are not the intended recipient, you must not copy distribute or take any action in reliance on it. If you have received this email in error, please return it to the sender advising of the error and delete all copies from your system. On 12 April 2012 01:37, Nick Caton wrote: > The complexity I was cautioning for a solar lighting baseline is much > simpler when you?re being given an installed wattage at least. Sounds like > the only thing for you to nail down is operating hours of the solar lights. > **** > > ** ** > > Regarding the DD wizard? I?m suggesting starting with one file then later > splitting into multiple files, as you suggested for use with an external > spreadsheet, to appropriately multiply the results without a massive model > of the entire campus. Here is a quick illustration:**** > > **** > > After completely finishing ?Building A,? defined as a single shell, click > ?create new shell? and choose to copy ?Building A.? You can then make only > the necessary edits to orientation, space layout, window layout, etc? and > other inputs will be repeated from the copied shell. Repeat that procedure > for as many unique buildings as you require, then when finished you can > proceed with saving the project a few times and in each project removing > the shells you do not need to isolate to one building.**** > > ** ** > > Hope that helps get my suggestion across better!**** > > ** ** > > ~Nick**** > > ** ** > > [image: cid:489575314 at 22072009-0ABB]** > > * * > > *NICK CATON, P.E.*** > > SENIOR ENGINEER**** > > ** ** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > ** ** > > *From:* Yusuf Turab [mailto:yusuf at ytenterprises.com] > *Sent:* Wednesday, April 11, 2012 2:42 PM > *To:* Nick Caton > *Cc:* Bruce Easterbrook; equest-users at lists.onebuilding.org > > *Subject:* Re: [Equest-users] Gated Community & Roof reflectivity**** > > ** ** > > Thank you Nick > > I have only partially understood your response on multiple shells but I > assume what you say is possible using the DD wizard. I will dig around a > bit on that one. Creating multiple files does not seem to work. I do not > understand why. > > With regards to your second suggestion, Indian Green Building Council have > asked me not to waste time modeling the street lights. They asked me to use > an excel sheet to calculate the total lighting consumption by multiplying > the base case LPD of 2.4 W/Sq Mt with total area under lighting and average > hrs of usage. In the proposed case I simply have to subtract the total > outdoor lighting consumption from the overall energy consumption since it > is powered using solar. I thought it makes sense. > > Thank You very much. > > Yusuf > **** > > On 12 April 2012 00:34, Nick Caton wrote:**** > > To Yusuf?s more recent question below:**** > > **** > > What you?re describing (varying the rotation/layout only with all else > remaining constant) sounds most easily accomplished in a single file, > within the wizard stage. Set up your first building (ideally as a single > shell), then create new shells by copying the first ? editing the rotation > and internal layout as necessary. If/when you have everything set up, you > can save multiple copies of the file and remove the shells you don?t want > for each case to isolate to the correct building. You shouldn?t need > re-enter the same information twice.**** > > **** > > To something Yusuf mentioned earlier:**** > > **** > > Modeling the savings of solar street/landscape lighting can be re-stated > as determining the energy consumption of a ?non-solar equivalent.? This is > a lot trickier than it may seem on the surface. Much of that complexity is > tied up in what ?non-solar equivalent? means in reality: Dig hard at the > cutsheets of the solar equipment in question to come up with some hard > numbers for photometrics and runtime realities. If you are not > trained/familiar with photometric lighting design software you may want to > engage someone who is to help you along the way.**** > > **** > > [image: cid:489575314 at 22072009-0ABB]**** > > * ***** > > *NICK CATON, P.E.***** > > SENIOR ENGINEER**** > > **** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > **** > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Yusuf Turab > *Sent:* Wednesday, April 11, 2012 1:30 PM > *To:* Bruce Easterbrook**** > > > *Cc:* equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] Gated Community & Roof reflectivity**** > > **** > > Thank you. I guess I have someway to go before I have system sizing and > unmet hours fully figured out. One more question:**** > > - If I want to create multiple buildings of similar type, built up > area and construction but different conditioned spaces, interior layouts > and orientations. Can I simply make a copy of the old pd2 file and simply > change the footprint zone and orientation in the new file? I tried to do > this but I cannot see the 3D model of the new building.**** > > Does this mean every model has to be created from scratch?**** > > Many Thanks**** > > Yusuf**** > > **** > > On 11 April 2012 19:03, Bruce Easterbrook wrote:**** > > Auto sizing is to ball park your system. There is no computer program > which with the press of a button will design your building for you. You > have unmet hours because you have conflicts in your design. You now have to > identify the conflicts and resolve them. eQuest works by prioritizing the > cooling system, hence when you have conflicts they show up mostly as > unheated hours. eQuest has a low default on airflow, 0.5 cfm/SF, this many > times is a good place to start. Depending on where you are 0.75 or 1.0 > could work better. You can also vary the flow to different zones > independently. You can't put 0.5 cfm into 20 spaces from the same AHU and > expect the heating and cooling needs of each space to be met 100% of the > time. Get into your sim file and figure out where the spaces are with > large unmet hours, figure out why and start adjusting the inputs to reduce > them. > There is no point to average the 4 orientations, nor is it allowed, just > LEED mumbo jumbo. It just illustrates how the orientation of your building > effects the energy consumption to run it. Most modellers get a building, a > street, a front and back with no option on orientation. That is your base > case. It can be handy to illustrate design flaws if there is a large > difference in energy consumption in different directions. Just don't call > it that when you are telling the architect a 20 story atrium is not a great > idea on the north side of a building. lol. > Bruce Easterbrook P.Eng. > Abode Engineering**** > > > > On 10/04/2012 02:53 PM, Yusuf Turab wrote: **** > > Hello Group**** > > - Why do I get unmet hours even when I select the auto size option in > the HVAC system? What is the point of auto sizing?**** > - Is there a way to simulate all 4 orientations and get an average > result for the base case?**** > > Thanks**** > > Yusuf Turab > IGBC Accredited Professional, LEED Green Associate & GRIHA Trainer > Y T Enterprises > 18 A, Hamsa Layout ? R.S Puram ? Coimbatore - 641002 > > http://www.ytenterprises.com/ > > ***** Email confidentiality notice ***** > The information contained in this email and any attachments is intended > for the name recipients only. It may contain privileged and confidential > information and if you are not the intended recipient, you must not copy > distribute or take any action in reliance on it. If you have received this > email in error, please return it to the sender advising of the error and > delete all copies from your system.**** > > On 10 April 2012 00:54, Yusuf Turab wrote:**** > > Hello Group > > I have just started working on my first energy modeling > project. I have two questions:**** > > - How do I model roof reflectivity. I want to model a roof of 4 inch > concrete with 1 inch stucco at the bottom and top and cover the roof with > cool roof tiles. I am not sure how I can account for the energy efficiency > gains compared to base case through a high SRI roof.**** > - I am trying to model a large gated community with 330 villas and 7 > other common buildings. As someone suggested on this group I am modeling > each building type separately and using excel to come up with a total > energy usage. But I am not sure how to model the street lighting and > landscape lighting at the exteriors. We plan to use solar street lights and > I want to demonstrate the savings through use of solar energy.**** > > Many Thanks > > Yusuf Turab > > **** > > On 10 April 2012 00:32, nirupama lakshminarasimhan < > nirupamalnarasimhan at gmail.com> wrote:**** > > I am modeling a big public school with a lot of systems and custom > windows. The equest file we have right now is taking too long to load. I've > tried opening it from different locations- the default equest project > folder on C: , the public server, external HDD, etc. It is just too slow in > "importing project data" when it opens. The last time this happened, it was > taking too long to load the BDL file and I ended up deleting a host of > systems and starting from scratch. All my files- the .inp, .pd2, etc are in > the same path. I just cannot get it to work faster. I'm trying to calibrate > the model and it is an awfully long wait for each simulation. Does someone > have any thoughts on how I could get this to work faster? **** > > **** > > Thank you.**** > > Nirupama**** > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > **** > > ** ** > > _______________________________________________**** > > Equest-users mailing list**** > > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org**** > > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > **** > > ** ** > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 22473 bytes Desc: not available URL: From jason.e.quinn at gmail.com Wed Apr 11 15:35:57 2012 From: jason.e.quinn at gmail.com (Jason Quinn) Date: Thu, 12 Apr 2012 10:35:57 +1200 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: Message-ID: Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: From akrickx at seriousenergy.com Wed Apr 11 15:42:46 2012 From: akrickx at seriousenergy.com (Alex Krickx) Date: Wed, 11 Apr 2012 15:42:46 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: Message-ID: Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: From yjhuang at whiteboxtechnologies.com Wed Apr 11 17:03:41 2012 From: yjhuang at whiteboxtechnologies.com (Joe Huang) Date: Wed, 11 Apr 2012 17:03:41 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: Message-ID: <4F861BDD.6090207@whiteboxtechnologies.com> This is a topic that I have explored. Although DOE-2 (the core engine for eQUEST) does not explicitly solve for the inside surface temperatures, researchers at EMPA in Switzerland back in the late 90's added a routine to DOE-2.1E to back-calculate the inside surface temperatures (think of it as doing a heat balance calculation in reverse). This featured is documented in DOE-2.1E update package 2 (version 107), but I only have a hard copy of the report. In 2003, I used this feature to do exactly what Jason is asking, i.e., calculate the PMV for naturally ventilated buildings in Egypt. Recently, I've also used the same feature to estimate the amount of radiant heat transfer from attics to the conditioned space, something that is ignored in the weighting factor model in DOE-2. The bad news, though, is that this feature has not been carried over from DOE-2.1E to DOE-2.2, although I've had some discussions with members of the development team about resurrecting it. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/11/2012 3:42 PM, Alex Krickx wrote: > > Hi Jason, > > I'm under the impression that eQUEST can't output surface temperatures which are needed > to calculate PMV values. > > I think an EnergyPlus based program might be a better place to look. I would ask on the > Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST > specific). > > Good luck, > > Alex > > Alex Krickx, LEED AP > > Building Energy Specialist > > Serious Energy, Inc. > > 1250 Elko Dr, Sunnyvale, CA 94089 > > (t) 408.541.8124 > > akrickx at seriousenergy.com > > /The information contained in this e-mail and any attachments may be confidential, > proprietary and/or privileged. If you are not the intended recipient then you have > received it in error and any review, distribution or copying of this message and any > attachments is prohibited and you are to notify the sender immediately by reply e-mail > and delete immediately this message and any attachments./ > > *From:*equest-users-bounces at lists.onebuilding.org > [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jason Quinn > *Sent:* Wednesday, April 11, 2012 3:36 PM > *To:* equest-users at lists.onebuilding.org > *Subject:* [Equest-users] Can you use eQuest for PMV calculations? > > Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) > calculations per ASHRAE 55/RP884? > > If not are there any recommendations? > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From thomasv at iit.edu Thu Apr 12 07:06:25 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Thu, 12 Apr 2012 09:06:25 -0500 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: <4F861BDD.6090207@whiteboxtechnologies.com> References: <4F861BDD.6090207@whiteboxtechnologies.com> Message-ID: DOE-2 Supplement Version 21E December 1993 Appendix A Hourly Report Variables Page A10 LOADS Variable-Type = u-name of EXTERIOR-WALL Variable List Number 5 Q Heat transfer from wall to the zone un-weighted (Btu/hr) Variable List Number 6 T Outside surface temperature (Rankine) The outside surface temp was used to calculate the inside surface temp in this example http://bepan.info/contents http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt ?Proj-22 - Kuwait-Envelope-Temps-MRT-Systems-Study? -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- This is a topic that I have explored. Although DOE-2 (the core engine for eQUEST) does not explicitly solve for the inside surface temperatures, researchers at EMPA in Switzerland back in the late 90's added a routine to DOE-2.1E to back-calculate the inside surface temperatures (think of it as doing a heat balance calculation in reverse). This featured is documented in DOE-2.1E update package 2 (version 107), but I only have a hard copy of the report. In 2003, I used this feature to do exactly what Jason is asking, i.e., calculate the PMV for naturally ventilated buildings in Egypt. Recently, I've also used the same feature to estimate the amount of radiant heat transfer from attics to the conditioned space, something that is ignored in the weighting factor model in DOE-2. The bad news, though, is that this feature has not been carried over from DOE-2.1E to DOE-2.2, although I've had some discussions with members of the development team about resurrecting it. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/11/2012 3:42 PM, Alex Krickx wrote: > > Hi Jason, > > I'm under the impression that eQUEST can't output surface temperatures which are needed > to calculate PMV values. > > I think an EnergyPlus based program might be a better place to look. I would ask on the > Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST > specific). > > Good luck, > > Alex > > Alex Krickx, LEED AP > > Building Energy Specialist > > Serious Energy, Inc. > > 1250 Elko Dr, Sunnyvale, CA 94089 > > (t) 408.541.8124 > > akrickx at seriousenergy.com > > /The information contained in this e-mail and any attachments may be confidential, > proprietary and/or privileged. If you are not the intended recipient then you have > received it in error and any review, distribution or copying of this message and any > attachments is prohibited and you are to notify the sender immediately by reply e-mail > and delete immediately this message and any attachments./ > > *From:*equest-users-bounces at lists.onebuilding.org > [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jason Quinn > *Sent:* Wednesday, April 11, 2012 3:36 PM > *To:* equest-users at lists.onebuilding.org > *Subject:* [Equest-users] Can you use eQuest for PMV calculations? > > Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) > calculations per ASHRAE 55/RP884? > > If not are there any recommendations? > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From kathryn.kerns at bceengineers.com Thu Apr 12 08:57:45 2012 From: kathryn.kerns at bceengineers.com (Kathryn Kerns) Date: Thu, 12 Apr 2012 08:57:45 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? References: Message-ID: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. Check the ASHRAE website for things to purchase. ________________________________ From: equest-users-bounces at lists.onebuilding.org on behalf of Alex Krickx Sent: Wed 4/11/2012 3:42 PM To: Jason Quinn; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: From akrickx at seriousenergy.com Thu Apr 12 09:12:42 2012 From: akrickx at seriousenergy.com (Alex Krickx) Date: Thu, 12 Apr 2012 09:12:42 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: I'll second the suggestion to purchase the Thermal Comfort tool. It is easy to use. I believe that a newer version was recently released - we're still using the 1994 version. However, I'm not sure that it solves Jason's problem - it still requires a user-entered Mean Radiant Temperature which I don't believe eQUEST gives as an output. When we use the tool (specifically for perimeter comfort analysis understanding the impact of different glazing options on comfort) we make some assumptions on wall/floor/ceiling temps, some calculations on glass-temperatures, and some further assumptions on the ratio of glass-to-other surfaces from the occupant's perspective. Based on that we can calculate the PMV for that single point time with those conditions. I've used software in the past that was able to calculate PMV for every hour of the year (so every hour it would combine air temp, a calculated MRT based on surface temps, humidity, etc) and then give an output for how comfortable the space was throughout the year (with hourly outputs of PMV for different spaces). I don't believe that eQUEST gives the necessary information (surface temps) to do this type of analysis. I included Jeremiah's response below which suggests that Energy Plus can do these calculations. This was my impression, however I have never used E+ to do them. Kind regards, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. ________________________________ Energy Plus does PMV and inside surface temperatures as well... Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com From: Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] Sent: Thursday, April 12, 2012 8:58 AM To: Alex Krickx Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Can you use eQuest for PMV calculations? Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. Check the ASHRAE website for things to purchase. ________________________________ From: equest-users-bounces at lists.onebuilding.org on behalf of Alex Krickx Sent: Wed 4/11/2012 3:42 PM To: Jason Quinn; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Thu Apr 12 09:38:26 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Thu, 12 Apr 2012 09:38:26 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: I use both Energy Plus and eQuest, and try to choose between the two for features not preference. Energy Plus can produce many comfort calculations, including PMV, eQuest can not. I spent a moment and went through an Energy Plus file I am working on and copied most of the possible variations of comfort objects, and published them to this google spreadsheet: https://docs.google.com/spreadsheet/ccc?key=0Ak5Rfmjyon9idHJLUW8tbjhHOWpNUE9nMkhrdDdBTGc Hope this helps, and if you decide to use and need some help with Energy Plus please let me know. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 12, 2012 at 9:12 AM, Alex Krickx wrote: > I?ll second the suggestion to purchase the Thermal Comfort tool. It is > easy to use. I believe that a newer version was recently released ? we?re > still using the 1994 version.**** > > ** ** > > However, I?m not sure that it solves Jason?s problem ? it still requires a > user-entered Mean Radiant Temperature which I don?t believe eQUEST gives as > an output.**** > > ** ** > > When we use the tool (specifically for perimeter comfort analysis > understanding the impact of different glazing options on comfort) we make > some assumptions on wall/floor/ceiling temps, some calculations on > glass-temperatures, and some further assumptions on the ratio of > glass-to-other surfaces from the occupant?s perspective. Based on that we > can calculate the PMV for that single point time with those conditions.*** > * > > ** ** > > I?ve used software in the past that was able to calculate PMV for every > hour of the year (so every hour it would combine air temp, a calculated MRT > based on surface temps, humidity, etc) and then give an output for how > comfortable the space was throughout the year (with hourly outputs of PMV > for different spaces). I don?t believe that eQUEST gives the necessary > information (surface temps) to do this type of analysis.**** > > ** ** > > I included Jeremiah?s response below which suggests that Energy Plus can > do these calculations. This was my impression, however I have never used E+ > to do them.**** > > ** ** > > Kind regards,**** > > Alex**** > > ** ** > > Alex Krickx, LEED AP**** > > Building Energy Specialist**** > > Serious Energy, Inc.**** > > 1250 Elko Dr, Sunnyvale, CA 94089**** > > (t) 408.541.8124**** > > akrickx at seriousenergy.com**** > > ** ** > > *The information contained in this e-mail and any attachments may be > confidential, proprietary and/or privileged. If you are not the intended > recipient then you have received it in error and any review, distribution > or copying of this message and any attachments is prohibited and you are to > notify the sender immediately by reply e-mail and delete immediately this > message and any attachments.***** > > ** ** > > ** ** > > ** ** > ------------------------------ > > Energy Plus does PMV and inside surface temperatures as well...**** > > > **** > > *Jeremiah D. Crossett***** > > *CleanTech Analytics***** > > *503-688-8951***** > > *www.cleantechanalytics.com* **** > > ** ** > > ** ** > > *From:* Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] > *Sent:* Thursday, April 12, 2012 8:58 AM > *To:* Alex Krickx > *Cc:* equest-users at lists.onebuilding.org > *Subject:* RE: [Equest-users] Can you use eQuest for PMV calculations?**** > > ** ** > > Alex, ASHRAE sells a Thermal Comfort program which will do these > calculations for you based on temperature, humidity, air speed, etc. It > doesn't cost much and is easy to use. Check the ASHRAE website for things > to purchase.**** > > ** ** > ------------------------------ > > *From:* equest-users-bounces at lists.onebuilding.org on behalf of Alex > Krickx > *Sent:* Wed 4/11/2012 3:42 PM > *To:* Jason Quinn; equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] Can you use eQuest for PMV calculations?**** > > Hi Jason,**** > > **** > > I?m under the impression that eQUEST can?t output surface temperatures > which are needed to calculate PMV values.**** > > **** > > I think an EnergyPlus based program might be a better place to look. I > would ask on the Bldg-Sim list for recommendations as it has a broader > user-base (this list is eQUEST specific).**** > > **** > > Good luck,**** > > Alex**** > > **** > > Alex Krickx, LEED AP**** > > Building Energy Specialist**** > > Serious Energy, Inc.**** > > 1250 Elko Dr, Sunnyvale, CA 94089**** > > (t) 408.541.8124**** > > akrickx at seriousenergy.com**** > > **** > > *The information contained in this e-mail and any attachments may be > confidential, proprietary and/or privileged. If you are not the intended > recipient then you have received it in error and any review, distribution > or copying of this message and any attachments is prohibited and you are to > notify the sender immediately by reply e-mail and delete immediately this > message and any attachments.***** > > **** > > **** > > *From:* equest-users-bounces at lists.onebuilding.org [ > mailto:equest-users-bounces at lists.onebuilding.org] > *On Behalf Of *Jason Quinn > *Sent:* Wednesday, April 11, 2012 3:36 PM > *To:* equest-users at lists.onebuilding.org > *Subject:* [Equest-users] Can you use eQuest for PMV calculations?**** > > **** > > Is it possible to use an eQuest model to do thermal comfort PMV (Predicted > Mean Vote) calculations per ASHRAE 55/RP884?**** > > If not are there any recommendations?**** > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From yjhuang at whiteboxtechnologies.com Thu Apr 12 12:11:33 2012 From: yjhuang at whiteboxtechnologies.com (Joe Huang) Date: Thu, 12 Apr 2012 12:11:33 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: <4F861BDD.6090207@whiteboxtechnologies.com> Message-ID: <4F8728E5.50901@whiteboxtechnologies.com> Varkie, That's interesting, so at least there are three people who've used the the EMPA surface temperature calculation in DOE-2.1E (EMPA, you, and me) :-) In case anyone's interested, I'm attaching some more information on this feature in 2.1E: (1) original documentation by Markus Koschenz of EMPA from the 2.1 Update, Version 107 (2) my description of the comfort calculator that I implemented in 2003 as a User Function to 2.1E. Call me old style, but I really like the User Function in DOE-2.1E, because it allowed me to add features and tweaks to the program to get the information that I need, instead of just waiting for the next release of whatever program you're using. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/12/2012 7:06 AM, Varkie C Thomas wrote: > > *DOE-2 Supplement Version 21E* > > December 1993 > > Appendix A > > Hourly Report Variables > > PageA10 > > LOADS > > Variable-Type = u-name of EXTERIOR-WALL > > Variable List Number5QHeat transfer from wall to the zone un-weighted (Btu/hr) > > Variable List Number6TOutside surface temperature (Rankine) > > > The outside surface temp was used to calculate the inside surface temp in this example > > http://bepan.info/contents > > http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt > > ?Proj-22 - Kuwait-Envelope-Temps-MRT-Systems-Study? > > > > > > > > This is a topic that I have explored. Although DOE-2 (the core engine for eQUEST) does > not explicitly solve for the inside surface temperatures, researchers at EMPA in > Switzerland back in the late 90's added a routine to DOE-2.1E to back-calculate the > inside surface temperatures (think of it as doing a heat balance calculation in > reverse). This featured is documented in DOE-2.1E update package 2 (version 107), but I > only have a hard copy of the report. In 2003, I used this feature to do exactly what > Jason is asking, i.e., calculate > the PMV for naturally ventilated buildings in Egypt. Recently, I've also used the same > feature to estimate the amount of radiant heat > transfer from attics to the conditioned space, something that is ignored in the > weighting factor model in DOE-2. > > The bad news, though, is that this feature has not been carried over from DOE-2.1E to > DOE-2.2, although I've had some discussions > with members of the development team about resurrecting it. > > Joe > Joe Huang > White Box Technologies, Inc. > 346 Rheem Blvd., Suite 108D > Moraga CA 94556 > yjhuang at whiteboxtechnologies.com > www.whiteboxtechnologies.com > (o) (925)388-0265 > (c) (510)928-2683 > "building energy simulations at your fingertips" > > On 4/11/2012 3:42 PM, Alex Krickx wrote: >> >> Hi Jason, >> >> I'm under the impression that eQUEST can't output surface temperatures which are needed >> to calculate PMV values. >> >> I think an EnergyPlus based program might be a better place to look. I would ask on the >> Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST >> specific). >> >> Good luck, >> >> Alex >> >> Alex Krickx, LEED AP >> >> Building Energy Specialist >> >> Serious Energy, Inc. >> >> 1250 Elko Dr, Sunnyvale, CA 94089 >> >> (t) 408.541.8124 >> >> akrickx at seriousenergy.com >> >> /The information contained in this e-mail and any attachments may be confidential, >> proprietary and/or privileged. If you are not the intended recipient then you have >> received it in error and any review, distribution or copying of this message and any >> attachments is prohibited and you are to notify the sender immediately by reply e-mail >> and delete immediately this message and any attachments./ >> >> *From:*equest-users-bounces at lists.onebuilding.org >> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jason Quinn >> *Sent:* Wednesday, April 11, 2012 3:36 PM >> *To:* equest-users at lists.onebuilding.org >> *Subject:* [Equest-users] Can you use eQuest for PMV calculations? >> >> Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) >> calculations per ASHRAE 55/RP884? >> >> If not are there any recommendations? >> >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: EMPA_Surface_Temp_Routine_fr_21e_update2.pdf Type: application/pdf Size: 55974 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: 03.YJH_DOE2_user_news_article.pdf Type: application/pdf Size: 349540 bytes Desc: not available URL: From adama at uw.edu Thu Apr 12 16:01:43 2012 From: adama at uw.edu (Adam Aljets) Date: Thu, 12 Apr 2012 16:01:43 -0700 Subject: [Equest-users] Zone cooling/heating hourly data Message-ID: Hello all, I'm looking for some hourly report data. In the simulation results view I see the electric consumption for space cooling for the entire building as well as the gas consumption for space heating the entire building. I'm looking for zone-specific data. Is this possible? I couldn't find a good option in the hourly reports. There's a space gas option, but it provides no data. I've only found "space total load." The HVAC system is a packaged multizone with furnace. Thanks in advance, Adam -------------- next part -------------- An HTML attachment was scrubbed... URL: From nbulger at integralgroup.com Fri Apr 13 13:19:19 2012 From: nbulger at integralgroup.com (Neil Bulger) Date: Fri, 13 Apr 2012 13:19:19 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: Alex you are correct, eQuest does not know the surface temperatures required to calculate the Mean Radiant Temperature. eQuest /DOE2 uses the Cooling Load Temperature Difference (CLTD) method to arrive at heat loads in a space. This approach makes approximations of the radiant component of heat transfer and does not directly calculate radiant gains or losses. Because of this, any DOE2 based software at best can predict air temperature and moisture needed for a PMV calc. EnergyPlus or IES are the only engines that can produce hourly surface temp information and therefore, mean radiant temperature averages. If you are interested in providing comfort feedback of envelope changes and not HVAC changes, learning EnergyPlus using OpenStudio from NREL is well worth the time and effort. Their workflow takes some practice to adopt but once you get the hang of things, creating buildings is very easy. Their youtube channel is best for explaining this, search for OpenStudio and NREL. Neil Bulger Project Engineer ________________________________ I N T E G R A L GROUP 427 13th Street, Oakland CA 94612 510 663 2070 x 235 nbulger at integralgroup.com www.integralgroup.com DEEP GREEN Engineering. ________________________________ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx Sent: Thursday, April 12, 2012 9:13 AM To: Kathryn Kerns Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? I'll second the suggestion to purchase the Thermal Comfort tool. It is easy to use. I believe that a newer version was recently released - we're still using the 1994 version. However, I'm not sure that it solves Jason's problem - it still requires a user-entered Mean Radiant Temperature which I don't believe eQUEST gives as an output. When we use the tool (specifically for perimeter comfort analysis understanding the impact of different glazing options on comfort) we make some assumptions on wall/floor/ceiling temps, some calculations on glass-temperatures, and some further assumptions on the ratio of glass-to-other surfaces from the occupant's perspective. Based on that we can calculate the PMV for that single point time with those conditions. I've used software in the past that was able to calculate PMV for every hour of the year (so every hour it would combine air temp, a calculated MRT based on surface temps, humidity, etc) and then give an output for how comfortable the space was throughout the year (with hourly outputs of PMV for different spaces). I don't believe that eQUEST gives the necessary information (surface temps) to do this type of analysis. I included Jeremiah's response below which suggests that Energy Plus can do these calculations. This was my impression, however I have never used E+ to do them. Kind regards, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. ________________________________ Energy Plus does PMV and inside surface temperatures as well... Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com From: Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] Sent: Thursday, April 12, 2012 8:58 AM To: Alex Krickx Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Can you use eQuest for PMV calculations? Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. Check the ASHRAE website for things to purchase. ________________________________ From: equest-users-bounces at lists.onebuilding.org on behalf of Alex Krickx Sent: Wed 4/11/2012 3:42 PM To: Jason Quinn; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: From yjhuang at whiteboxtechnologies.com Fri Apr 13 17:24:09 2012 From: yjhuang at whiteboxtechnologies.com (Joe Huang) Date: Fri, 13 Apr 2012 17:24:09 -0700 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: <4F88C3A9.2070107@whiteboxtechnologies.com> Neil, eQUEST/DOE-2 does not use the CLTD method, which is a quasi-steady state method from the late 70's for calculating heat gain through the envelope. It uses Weighting Factors (also known as Room Response Factors) that characterize the dynamic response of a space for a given input of heat flow. Envelope heat flows are similarly calculated using Response Factors that are also dynamic, i.e., they capture the thermal lag and capacitance of the materials. Radiant heat gains are taken into account in both response factors (using the sol-air temperature method) and weighting factors (there are different weighting factors for different types of heat gain). However, radiant heat gains are ignored in interzone heat transfer. Although DOE-2 doesn't compute inside surface temperatures, they can be output (in DOE-2.1E at least) and I've that little-known feature to do PMV calculations. Lastly, DOE-2 has always been able to model the humidity of the indoor air. What it doesn't do (which may be what you're thinking) is that it doesn't model the absorption/desorption of moisture in the building fabric. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/13/2012 1:19 PM, Neil Bulger wrote: > > Alex you are correct, eQuest does not know the surface temperatures required to > calculate the Mean Radiant Temperature. eQuest /DOE2 uses the Cooling Load Temperature > Difference (CLTD) method to arrive at heat loads in a space. This approach makes > approximations of the radiant component of heat transfer and does not directly calculate > radiant gains or losses. Because of this, any DOE2 based software at best can predict > air temperature and moisture needed for a PMV calc. > > EnergyPlus or IES are the only engines that can produce hourly surface temp information > and therefore, mean radiant temperature averages. > > If you are interested in providing comfort feedback of envelope changes and not HVAC > changes, learning EnergyPlus using OpenStudio from NREL is well worth the time and > effort. Their workflow takes some practice to adopt but once you get the hang of things, > creating buildings is very easy. Their youtube channel is best for explaining this, > search for OpenStudio and NREL. > > *Neil Bulger* > Project Engineer > > *________________________________* > > I N T E G R A L > > *****GROUP* > > 427 13th Street, Oakland CA 94612 > 510 663 2070 x 235 > nbulger at integralgroup.com > www.integralgroup.com > > *DEEP GREEN Engineering. * > > *________________________________ * > > *From:*equest-users-bounces at lists.onebuilding.org > [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Alex Krickx > *Sent:* Thursday, April 12, 2012 9:13 AM > *To:* Kathryn Kerns > *Cc:* equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] Can you use eQuest for PMV calculations? > > I'll second the suggestion to purchase the Thermal Comfort tool. It is easy to use. I > believe that a newer version was recently released -- we're still using the 1994 version. > > However, I'm not sure that it solves Jason's problem -- it still requires a user-entered > Mean Radiant Temperature which I don't believe eQUEST gives as an output. > > When we use the tool (specifically for perimeter comfort analysis understanding the > impact of different glazing options on comfort) we make some assumptions on > wall/floor/ceiling temps, some calculations on glass-temperatures, and some further > assumptions on the ratio of glass-to-other surfaces from the occupant's perspective. > Based on that we can calculate the PMV for that single point time with those conditions. > > I've used software in the past that was able to calculate PMV for every hour of the year > (so every hour it would combine air temp, a calculated MRT based on surface temps, > humidity, etc) and then give an output for how comfortable the space was throughout the > year (with hourly outputs of PMV for different spaces). I don't believe that eQUEST > gives the necessary information (surface temps) to do this type of analysis. > > I included Jeremiah's response below which suggests that Energy Plus can do these > calculations. This was my impression, however I have never used E+ to do them. > > Kind regards, > > Alex > > Alex Krickx, LEED AP > > Building Energy Specialist > > Serious Energy, Inc. > > 1250 Elko Dr, Sunnyvale, CA 94089 > > (t) 408.541.8124 > > akrickx at seriousenergy.com > > /The information contained in this e-mail and any attachments may be confidential, > proprietary and/or privileged. If you are not the intended recipient then you have > received it in error and any review, distribution or copying of this message and any > attachments is prohibited and you are to notify the sender immediately by reply e-mail > and delete immediately this message and any attachments./ > > Energy Plus does PMV and inside surface temperatures as well... > > > /Jeremiah D. Crossett/ > > /CleanTech Analytics/ > > /503-688-8951/ > > /www.cleantechanalytics.com/ > > *From:*Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] > *Sent:* Thursday, April 12, 2012 8:58 AM > *To:* Alex Krickx > *Cc:* equest-users at lists.onebuilding.org > *Subject:* RE: [Equest-users] Can you use eQuest for PMV calculations? > > Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you > based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. > Check the ASHRAE website for things to purchase. > > *From:*equest-users-bounces at lists.onebuilding.org > on behalf of Alex Krickx > *Sent:* Wed 4/11/2012 3:42 PM > *To:* Jason Quinn; equest-users at lists.onebuilding.org > > *Subject:* Re: [Equest-users] Can you use eQuest for PMV calculations? > > Hi Jason, > > I'm under the impression that eQUEST can't output surface temperatures which are needed > to calculate PMV values. > > I think an EnergyPlus based program might be a better place to look. I would ask on the > Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST > specific). > > Good luck, > > Alex > > Alex Krickx, LEED AP > > Building Energy Specialist > > Serious Energy, Inc. > > 1250 Elko Dr, Sunnyvale, CA 94089 > > (t) 408.541.8124 > > akrickx at seriousenergy.com > > /The information contained in this e-mail and any attachments may be confidential, > proprietary and/or privileged. If you are not the intended recipient then you have > received it in error and any review, distribution or copying of this message and any > attachments is prohibited and you are to notify the sender immediately by reply e-mail > and delete immediately this message and any attachments./ > > *From:*equest-users-bounces at lists.onebuilding.org > > [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jason Quinn > *Sent:* Wednesday, April 11, 2012 3:36 PM > *To:* equest-users at lists.onebuilding.org > *Subject:* [Equest-users] Can you use eQuest for PMV calculations? > > Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) > calculations per ASHRAE 55/RP884? > > If not are there any recommendations? > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From modeling at jeisenhart.com Fri Apr 13 18:43:53 2012 From: modeling at jeisenhart.com (modeling at jeisenhart.com) Date: Fri, 13 Apr 2012 19:43:53 -0600 Subject: [Equest-users] Heating in Summer Message-ID: Hello Everyone! Here's a puzzle for the email group. (I hope you're having a better weekend than me!) I've searched the archived emails to find a solution, but most seem to ask for the PD2 and INP file so that makes me think that the solutions will mostly be unique. I'm attaching a zip file of my model. I have packaged single zone units with electric resistence heat. I'm seeing a significant load in the summer on all units. I've dropped the thermostat in the summer months on the heating and am still getting a load. Any ideas on why there would be a load? Thanks, Ben -------------- next part -------------- A non-text attachment was scrubbed... Name: Equest 01.zip Type: application/zip Size: 56118 bytes Desc: not available URL: From charu_0011 at yahoo.com Sun Apr 15 00:44:08 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Sun, 15 Apr 2012 00:44:08 -0700 (PDT) Subject: [Equest-users] Urgent request Message-ID: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> Dear Sir, I started working on?E-quest?for my thesis model in an attempt to simulate the effects of a green roof with different soil thickness and vegetation for Mumbai region (India) for my thesis. And I have a few queries regarding it: 1.?I wish to create a very simple 4 storied rectangular model building as a comparative model (file has been attached- MODULE1) but on running the?perform compliance analysis, it?gives an error ?''?Table look-up failed: A901-07_Envelope(1, 4) evaluating rule: Look up and default C-FACTOR for slabs.'' Also, when i go on Project and?site> site data properties, it?doesn't?accept the latitude and longitude and gives the same as an error. Also please guide me the action report from where I can get the?Annual energy consumption( Since there is no electric utility and gas utility file rates?available here, can we get it in terms of unit, which can be multiplied with the rate and rate analysis can be found);?space load component( total building?load);?peak load component(total building load);?sensible cooling load & ?roof thermal transfer value?(RTTV ) 2. Secondly, please guide me on how can one?add up layers?to just the top of this building of varying soil thickness and green cover ( I have the data on their?R-values and thickness) and simulate the same without having errors. 3.?Is there a way by which the?outside ambient temperature?of the building with green roof ( & its micro-climatic features) can be found?I basically need?the temperature variation in the top 3 meters of the building. It will be really helpful for me if you could take out some time from your busy schedule and guide me for the above mentioned queries.? Waiting for your reply in anticipation,? Thanking you Regards, Charu Sharma X Semester, B.Arch National Institute of Technology India -------------- next part -------------- An HTML attachment was scrubbed... URL: From charu_0011 at yahoo.com Sun Apr 15 05:48:07 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Sun, 15 Apr 2012 05:48:07 -0700 (PDT) Subject: [Equest-users] Fw: Urgent request In-Reply-To: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> Message-ID: <1334494087.22758.YahooMailNeo@web114606.mail.gq1.yahoo.com> ----- Forwarded Message ----- From: sharma charu To: "equest-users at lists.onebuilding.org" Sent: Sunday, April 15, 2012 1:14 PM Subject: Urgent request Dear Sir, I started working on?E-quest?for my thesis model in an attempt to simulate the effects of a green roof with different soil thickness and vegetation for Mumbai region (India) for my thesis. And I have a few queries regarding it: 1.?I wish to create a very simple 4 storied rectangular model building as a comparative model (file has been attached- MODULE1) but on running the?perform compliance analysis, it?gives an error ?''?Table look-up failed: A901-07_Envelope(1, 4) evaluating rule: Look up and default C-FACTOR for slabs.'' Also, when i go on Project and?site> site data properties, it?doesn't?accept the latitude and longitude and gives the same as an error. Also please guide me the action report from where I can get the?Annual energy consumption( Since there is no electric utility and gas utility file rates?available here, can we get it in terms of unit, which can be multiplied with the rate and rate analysis can be found);?space load component( total building?load);?peak load component(total building load);?sensible cooling load & ?roof thermal transfer value?(RTTV ) 2. Secondly, please guide me on how can one?add up layers?to just the top of this building of varying soil thickness and green cover ( I have the data on their?R-values and thickness) and simulate the same without having errors. 3.?Is there a way by which the?outside ambient temperature?of the building with green roof ( & its micro-climatic features) can be found?I basically need?the temperature variation in the top 3 meters of the building. It will be really helpful for me if you could take out some time from your busy schedule and guide me for the above mentioned queries.? Waiting for your reply in anticipation,? Thanking you Regards, Charu Sharma X Semester, B.Arch National Institute of Technology India -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: MODULE 1.pd2 Type: application/octet-stream Size: 5020 bytes Desc: not available URL: From bedriye at live.dk Sun Apr 15 06:16:16 2012 From: bedriye at live.dk (Bedriye K.) Date: Sun, 15 Apr 2012 15:16:16 +0200 Subject: [Equest-users] Simulation in eQUEST Message-ID: Hey, I performed a quick simple simulation in eQUEST, but don't know how I can see how much energy consumption is for the building, I mean amount of kWh/m2 ? The electric and gas consumptions are given like x000..Please look at the attached file. Best, Bedriye -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: PINE CONE RIDGERS 2.pdf Type: application/pdf Size: 51251 bytes Desc: not available URL: From YJHuang at whiteboxtechnologies.com Sun Apr 15 12:15:16 2012 From: YJHuang at whiteboxtechnologies.com (Joe Huang) Date: Sun, 15 Apr 2012 12:15:16 -0700 Subject: [Equest-users] Urgent request In-Reply-To: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> Message-ID: <4F8B1E44.40106@whiteboxtechnologies.com> Sharma, eQUEST is a program developed in the US, so its compliance rule set might not work for locations outside of the US. Or the rule set might be failing because it doesn't know the ASHRAE climate region for your location (Mumbai). I assume that you have a weather file for Mumbai. I recently created last year a set of weather files for 38 Indian locations for ISHRAE, so if you have any problems there, just give me a holler. However, even if you get these practical problems resolved, I question the logic of creating an ASHRAE-90 building as the reference or comparison building for your study, which would set all the building conditions to ASHRAE-90 requirements. I would recommend that, instead, you create a reference building based on India's ECBC, or if you don't think that's being widely followed yet, on what you think are the typical construction and operating conditions in Mumbai. I can also think of several friends in India, even Mumbai, that I could recommend if you need help. It seems that you're thinking of modeling a green roof as an additional soil layer. That's okay for starters, but if that's the topic of your thesis, you should do a more careful job and incorporate the following characteristics that makes a green roof differ from just 20 cm of dirt on top: (1) changing soil moisture depending on the time of year and rainfall, and (2) evaporatranspiration that would keep the soil surface temperature low on sunny days. This is not a marketing pitch, but in DOE-2.1E (an earlier version of the DOE-2.2 engine in eQUEST) that I still use, there is a feature called "Functions" that would allow users to insert additional code in pseudo-Fortran to model processes not covered by the program. If you're interested, we can discuss more offline. Again, this is not a marketing pitch. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/15/2012 12:44 AM, sharma charu wrote: > Dear Sir, > I started working on E-quest for my thesis model in an attempt to > simulate the effects of a green roof with different soil thickness and > vegetation for Mumbai region (India) for my thesis. And I have a few > queries regarding it: > > 1. I wish to create a very simple 4 storied rectangular model building > as a comparative model (file has been attached- MODULE1) but on > running the perform compliance analysis, it gives an error > '' Table look-up failed: A901-07_Envelope(1, 4) evaluating rule: Look > up and default C-FACTOR for slabs.'' Also, when i go on Project and > site> site data properties, it doesn't accept the latitude and > longitude and gives the same as an error. > Also please guide me the action report from where I can get the Annual > energy consumption( Since there is no electric utility and gas utility > file rates available here, can we get it in terms of unit, which can > be multiplied with the rate and rate analysis can be found); space > load component( total building load); peak load component(total > building load); sensible cooling load & roof thermal transfer value > (RTTV ) > > 2. Secondly, please guide me on how can one add up layers to just the > top of this building of varying soil thickness and green cover ( I > have the data on their R-values and thickness) and simulate the same > without having errors. > > 3. Is there a way by which the outside ambient temperature of the > building with green roof ( & its micro-climatic features) can be > found?I basically need the temperature variation in the top 3 meters > of the building. > > It will be really helpful for me if you could take out some time from > your busy schedule and guide me for the above mentioned queries. > > Waiting for your reply in anticipation, > Thanking you > Regards, > Charu Sharma > X Semester, B.Arch > National Institute of Technology > India > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From Joey.Jiao at WSPGroup.com.cn Mon Apr 16 02:26:40 2012 From: Joey.Jiao at WSPGroup.com.cn (Jiao, Joey) Date: Mon, 16 Apr 2012 17:26:40 +0800 Subject: [Equest-users] Infiltration of Baseline model Message-ID: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> Hi, Everyone: Is there any request about baseline model's infiltration? I have check all appendix G items, but it seems this area is blank. If the infiltration must be the same between baseline & purposed? Any light on it will be appreciated. Thank you. Joey. ------------------------------------------------------------------------ --- Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. -------------- next part -------------- An HTML attachment was scrubbed... URL: From rsg4999 at gmail.com Mon Apr 16 03:36:21 2012 From: rsg4999 at gmail.com (Bobby Sy) Date: Mon, 16 Apr 2012 18:36:21 +0800 Subject: [Equest-users] Building Shade (attached file for reference) In-Reply-To: References: Message-ID: Hi everyone, We would like to ask for your thoughts on how to set up building shade in eQuest specifically for this type. I attached a picture of how the building shade (metal tube louver) would look like. Placing un-even building shade is hard enough for a building with elliptical footprint; it?s even more challenging because the area of each level reduces as it reaches the top. We?re thinking of averaging the shade but this would definitely affect the result. Anyone had the same facade design modeled? How did the reviewer react on the work around used? Thanks a lot for your time! -Bob -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: facade.pdf Type: application/pdf Size: 94283 bytes Desc: not available URL: From ELO at MichaelsEnergy.com Mon Apr 16 06:37:29 2012 From: ELO at MichaelsEnergy.com (Eric O'Neill) Date: Mon, 16 Apr 2012 08:37:29 -0500 Subject: [Equest-users] Heating in Summer In-Reply-To: References: Message-ID: Hi Ben, In this case, it looks like the usual suspect: reheat. If you shut off your dehumidification limit of 50%, it eliminates the summer heating issue. Also, I don?t know how much control you have over your economizer settings, but if you haven?t read this article , I?d strongly suggest it. As an interesting aside ? that author?s comments on RH sensor reliability matches well with what I?ve found on a recent project. Here?s a little data I?ve gathered from a college campus. I harvested 24hr trend data from all the buildings that were measuring OA humidity (y-axis in %). The fat blue line is what I got from the National Weather Service for the area and each other line represents a building?s OA humidity sensor. I think in total these sensors control at least 25 AHU?s enthalpy economizers. From what I can tell, they don?t have a regular PM routine for calibrating/replacing these sensors. Just something to consider? Eric O'Neill 608.785.3328 | MICHAELS ENERGY -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of modeling at jeisenhart.com Sent: Friday, April 13, 2012 8:44 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Heating in Summer Hello Everyone! Here's a puzzle for the email group. (I hope you're having a better weekend than me!) I've searched the archived emails to find a solution, but most seem to ask for the PD2 and INP file so that makes me think that the solutions will mostly be unique. I'm attaching a zip file of my model. I have packaged single zone units with electric resistence heat. I'm seeing a significant load in the summer on all units. I've dropped the thermostat in the summer months on the heating and am still getting a load. Any ideas on why there would be a load? Thanks, Ben -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 99922 bytes Desc: image003.png URL: From thomasv at iit.edu Mon Apr 16 06:50:37 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Mon, 16 Apr 2012 08:50:37 -0500 Subject: [Equest-users] Can you use eQuest for PMV calculations? In-Reply-To: References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: 8760 hourly inside zone wall surface temp and MRT at a point in space is not very useful. It might be useful in Loads program based on design day conditions in summer and winter. See http://bepan.info/engg-calcs - 3a - Design-Weather-Generator DOE2.1E uses the Transfer Function method to calculate envelope heat transfer. I think Trane-TRACE and Carrier-HAP use the same method. The CLTD-SCL-CLF method is still very useful for teaching envelope heat transfer. See http://bepan.info/class-notes/e4-project-loads The Total Equivalent Temperature Difference (TETD) method is also useful for teaching. See - http://bepan.info/hvac-prog/x1-apec-hccv-loads It is difficult to explain the heat storage capacity and time lag concepts of the envelope with the other methods although all Loads calculations are done by computer today. The APEC (Automated Procedure for Engineering Consultants) HCC-V Loads program can be downloaded and used. If you don?t know what the ?decrement factor? is, use 0.5 since the range is between 0 and 1. An estimate for ?time-lag? depends on the type of bldg. In design loads calculation for commercial buildings it is important NOT to underestimate the loads. The hourly Fortran Variable report of the DOE2 based programs include outside wall surface temp. In the DOE2 Loads section choose (1) Variable-Type = u-name of EXTERIOR-WALL (2) Variable List Number 5 Q Heat transfer from wall to the zone un-weighted (Btu/hr) (3) Variable List Number 6 T Outside surface temperature (Rankine). Transfer the values of Q and T to an Excel spreadsheet and calculate the inside wall surface temps. Examples of calculating inside surface temp using outside surface temp. http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt Proj-22 - Kuwait-Envelope-Temps-MRT-Systems-Study? I have found the hourly Fortran Variable report by the DOE2 program very helpful. Transfer the hourly data to an Excel spreadsheet and do the rest yourself. Example of using hourly solar data is: http://bepan.info/proj-doe21e/p21_beijing-solar-pv Proj-21 - Beijing-Solar-Radiation-PV-Study - PDF-Report? Example of using cooling coil data is: http://bepan.info/proj-doe21e/p27_dubai-condens-recov Proj-27 - Dubai- Cooling-Coils-Condensate-Recovery Files recently added to the website: 4b ? Tall-Bldgs - Stack Effect, Wind Press and 4c - High-Rise-Apt-Bldgs-Pressurization Varkie -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- Alex you are correct, eQuest does not know the surface temperatures required to calculate the Mean Radiant Temperature. eQuest /DOE2 uses the Cooling Load Temperature Difference (CLTD) method to arrive at heat loads in a space. This approach makes approximations of the radiant component of heat transfer and does not directly calculate radiant gains or losses. Because of this, any DOE2 based software at best can predict air temperature and moisture needed for a PMV calc. EnergyPlus or IES are the only engines that can produce hourly surface temp information and therefore, mean radiant temperature averages. If you are interested in providing comfort feedback of envelope changes and not HVAC changes, learning EnergyPlus using OpenStudio from NREL is well worth the time and effort. Their workflow takes some practice to adopt but once you get the hang of things, creating buildings is very easy. Their youtube channel is best for explaining this, search for OpenStudio and NREL. Neil Bulger Project Engineer ________________________________ I N T E G R A L GROUP 427 13th Street, Oakland CA 94612 510 663 2070 x 235 nbulger at integralgroup.com www.integralgroup.com DEEP GREEN Engineering. ________________________________ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx Sent: Thursday, April 12, 2012 9:13 AM To: Kathryn Kerns Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? I'll second the suggestion to purchase the Thermal Comfort tool. It is easy to use. I believe that a newer version was recently released - we're still using the 1994 version. However, I'm not sure that it solves Jason's problem - it still requires a user-entered Mean Radiant Temperature which I don't believe eQUEST gives as an output. When we use the tool (specifically for perimeter comfort analysis understanding the impact of different glazing options on comfort) we make some assumptions on wall/floor/ceiling temps, some calculations on glass-temperatures, and some further assumptions on the ratio of glass-to-other surfaces from the occupant's perspective. Based on that we can calculate the PMV for that single point time with those conditions. I've used software in the past that was able to calculate PMV for every hour of the year (so every hour it would combine air temp, a calculated MRT based on surface temps, humidity, etc) and then give an output for how comfortable the space was throughout the year (with hourly outputs of PMV for different spaces). I don't believe that eQUEST gives the necessary information (surface temps) to do this type of analysis. I included Jeremiah's response below which suggests that Energy Plus can do these calculations. This was my impression, however I have never used E+ to do them. Kind regards, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. ________________________________ Energy Plus does PMV and inside surface temperatures as well... Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com From: Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] Sent: Thursday, April 12, 2012 8:58 AM To: Alex Krickx Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Can you use eQuest for PMV calculations? Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. Check the ASHRAE website for things to purchase. ________________________________ From: equest-users-bounces at lists.onebuilding.org on behalf of Alex Krickx Sent: Wed 4/11/2012 3:42 PM To: Jason Quinn; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From thomasv at iit.edu Mon Apr 16 07:02:17 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Mon, 16 Apr 2012 09:02:17 -0500 Subject: [Equest-users] DOE2.1E Re: Urgent request In-Reply-To: <4F8B1E44.40106@whiteboxtechnologies.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> <4F8B1E44.40106@whiteboxtechnologies.com> Message-ID: My views on DOE2.1E: I would support the development of an open source DOE2.1E so that it can be used for academic thesis research. See http://www.whiteboxtechnologies.com/ Click here for the Open Letter to Lawrence Berkeley National Lab (LBNL) on Open Source DOE-2.1E.) DOE2.1E is particularly suited for academic thesis research for the following reasons: 1. It is a mature computer program that has been in extensive use for nearly 30 years. In fact, its latest proprietary version (DOE-2.2/eQUEST) is clearly the most widely used building energy simulation program in the US, if not the entire world. 2. Compared to other simulation programs, DOE-2 runs very quickly. 3. Since DOE-2.1E has been in effect abandoned by DOE and LBNL, its code can be made open source, and be freely available to students and researchers 4. DOE-2.1E contains a User Function option that allows users to develop additional modules or tweak existing calculations without having to change and recompile the existing source code. User Functions are ideal for student applications. Those that are promising can then later be incorporated into the source code itself. Here are suggestions of how to fix DOE-2.1E so that it can be used for academic thesis research 1. Provide better documentation and examples of building models and User Functions. 2. Develop teaching materials on how to use the DOE-2 program, including how to extract hourly data, use macros to manage sensitivity analyses, and available open-source user interfaces. 3. Freeze the existing code since it is error-free and make it possible for research students to add/attach independent sub programs to expand the features of DOE-2.1E. The independent (or dependent) sub-programs that can be interfaced with DOE-2.1E should include PV-modules, GSHP, UFAD, DOAS, Radiant-ceilings and other features not included in DOE-2.1E. There could be multiple versions of each sub-program by different authors. 4. A DOE-2.1E committee should establish common output reports for them. You can expect advanced program development using an open source DOE2.1E as the base launching pad from enterprising architects, engineers, academics in the areas renewable energy and also in testing new concepts. The analogy is countries like socialist India and communist Russia & China opening up development to individual free enterprise. All the economies are now booming after 15 years. Their economies stagnated during the previous 50 years of the government doing everything. Trane & Carrier have their own energy programs (TRACE and HAP) based on their equipment and systems. Other manufacturers can now create energy programs starting with the open source DOE2.1E and base it on their own equipment. These would be program developers that are involved with real buildings from design through construction and operation and understand the business. Equipment consumes energy in buildings, not the envelope or people. Manufacturers would therefore have vested interest in making sure that their energy programs produced results that are close to the building in operation. ----- Original Message ----- From: Joe Huang Date: Sunday, April 15, 2012 2:15 pm Subject: Re: [Equest-users] Urgent request > Sharma, > > eQUEST is a program developed in the US, so its compliance rule > set > might not work for locations outside of the US. > Or the rule set might be failing because it doesn't know the > ASHRAE > climate region for your location (Mumbai). etc > This is not a marketing pitch, but in DOE-2.1E (an earlier version > of > the DOE-2.2 engine in eQUEST) that I still use, there > is a feature called "Functions" that would allow users to insert > additional code in pseudo-Fortran to model processes > not covered by the program. If you're interested, we can discuss > more > offline. Again, this is not a marketing pitch. > > Joe > > Joe Huang > White Box Technologies, Inc. > 346 Rheem Blvd., Suite 108D > Moraga CA 94556 > yjhuang at whiteboxtechnologies.com > www.whiteboxtechnologies.com > (o) (925)388-0265 > (c) (510)928-2683 > "building energy simulations at your fingertips" > > > On 4/15/2012 12:44 AM, sharma charu wrote: > > Dear Sir, > > I started working on E-quest for my thesis model in an attempt > to > > simulate the effects of a green roof with different soil > thickness and > > vegetation for Mumbai region (India) for my thesis. And I have a > few > > queries regarding it: > > > > 1. I wish to create a very simple 4 storied rectangular model > building > > as a comparative model (file has been attached- MODULE1) but on > > running the perform compliance analysis, it gives an error > > '' Table look-up failed: A901-07_Envelope(1, 4) evaluating > rule: Look > > up and default C-FACTOR for slabs.'' Also, when i go on Project > and > > site> site data properties, it doesn't accept the latitude and > > longitude and gives the same as an error. > > Also please guide me the action report from where I can get the > Annual > > energy consumption( Since there is no electric utility and gas > utility > > file rates available here, can we get it in terms of unit, which > can > > be multiplied with the rate and rate analysis can be found); > space > > load component( total building load); peak load component(total > > building load); sensible cooling load & roof thermal transfer > value > > (RTTV ) > > > > 2. Secondly, please guide me on how can one add up layers to > just the > > top of this building of varying soil thickness and green cover ( > I > > have the data on their R-values and thickness) and simulate the > same > > without having errors. > > > > 3. Is there a way by which the outside ambient temperature of > the > > building with green roof ( & its micro-climatic features) can be > > found?I basically need the temperature variation in the top 3 > meters > > of the building. > > > > It will be really helpful for me if you could take out some time > from > > your busy schedule and guide me for the above mentioned queries. > > > > Waiting for your reply in anticipation, > > Thanking you > > Regards, > > Charu Sharma > > X Semester, B.Arch > > National Institute of Technology > > India > > > > > > > > _______________________________________________ > > Equest-users mailing list > > http://lists.onebuilding.org/listinfo.cgi/equest-users- > onebuilding.org> To unsubscribe from this mailing list send a > blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From jeremiah at cleantechanalytics.com Mon Apr 16 09:58:52 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Mon, 16 Apr 2012 09:58:52 -0700 Subject: [Equest-users] DOE2.1E Re: Urgent request In-Reply-To: References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> <4F8B1E44.40106@whiteboxtechnologies.com> Message-ID: Agreed! *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Mon, Apr 16, 2012 at 7:02 AM, Varkie C Thomas wrote: > My views on DOE2.1E: > > I would support the development of an open source DOE2.1E so that it can > be used for academic thesis research. See > http://www.whiteboxtechnologies.com/ Click here for the Open Letter to > Lawrence Berkeley National Lab (LBNL) on Open Source DOE-2.1E.) > > DOE2.1E is particularly suited for academic thesis research for the > following reasons: > > 1. It is a mature computer program that has been in extensive use for > nearly 30 years. In fact, its latest proprietary version (DOE-2.2/eQUEST) > is clearly the most widely used building energy simulation program in the > US, if not the entire world. > 2. Compared to other simulation programs, DOE-2 runs very quickly. > 3. Since DOE-2.1E has been in effect abandoned by DOE and LBNL, its code > can be made open source, and be freely available to students and researchers > 4. DOE-2.1E contains a User Function option that allows users to develop > additional modules or tweak existing calculations without having to change > and recompile the existing source code. User Functions are ideal for > student applications. Those that are promising can then later be > incorporated into the source code itself. > > Here are suggestions of how to fix DOE-2.1E so that it can be used for > academic thesis research > > 1. Provide better documentation and examples of building models and User > Functions. > 2. Develop teaching materials on how to use the DOE-2 program, including > how to extract hourly data, use macros to manage sensitivity analyses, and > available open-source user interfaces. > 3. Freeze the existing code since it is error-free and make it possible > for research students to add/attach independent sub programs to expand the > features of DOE-2.1E. The independent (or dependent) sub-programs that can > be interfaced with DOE-2.1E should include PV-modules, GSHP, UFAD, DOAS, > Radiant-ceilings and other features not included in DOE-2.1E. There could > be multiple versions of each sub-program by different authors. > 4. A DOE-2.1E committee should establish common output reports for them. > > You can expect advanced program development using an open source DOE2.1E > as the base launching pad from enterprising architects, engineers, > academics in the areas renewable energy and also in testing new concepts. > > The analogy is countries like socialist India and communist Russia & China > opening up development to individual free enterprise. All the economies > are now booming after 15 years. Their economies stagnated during the > previous 50 years of the government doing everything. > > Trane & Carrier have their own energy programs (TRACE and HAP) based on > their equipment and systems. Other manufacturers can now create energy > programs starting with the open source DOE2.1E and base it on their own > equipment. These would be program developers that are involved with real > buildings from design through construction and operation and understand the > business. > > Equipment consumes energy in buildings, not the envelope or people. > Manufacturers would therefore have vested interest in making sure that > their energy programs produced results that are close to the building in > operation. > > > > > > ----- Original Message ----- > From: Joe Huang > Date: Sunday, April 15, 2012 2:15 pm > Subject: Re: [Equest-users] Urgent request > > > Sharma, > > > > eQUEST is a program developed in the US, so its compliance rule > > set > > might not work for locations outside of the US. > > Or the rule set might be failing because it doesn't know the > > ASHRAE > > climate region for your location (Mumbai). > etc > > This is not a marketing pitch, but in DOE-2.1E (an earlier version > > of > > the DOE-2.2 engine in eQUEST) that I still use, there > > is a feature called "Functions" that would allow users to insert > > additional code in pseudo-Fortran to model processes > > not covered by the program. If you're interested, we can discuss > > more > > offline. Again, this is not a marketing pitch. > > > > Joe > > > > Joe Huang > > White Box Technologies, Inc. > > 346 Rheem Blvd., Suite 108D > > Moraga CA 94556 > > yjhuang at whiteboxtechnologies.com > > www.whiteboxtechnologies.com > > (o) (925)388-0265 > > (c) (510)928-2683 > > "building energy simulations at your fingertips" > > > > > > On 4/15/2012 12:44 AM, sharma charu wrote: > > > Dear Sir, > > > I started working on E-quest for my thesis model in an attempt > > to > > > simulate the effects of a green roof with different soil > > thickness and > > > vegetation for Mumbai region (India) for my thesis. And I have a > > few > > > queries regarding it: > > > > > > 1. I wish to create a very simple 4 storied rectangular model > > building > > > as a comparative model (file has been attached- MODULE1) but on > > > running the perform compliance analysis, it gives an error > > > '' Table look-up failed: A901-07_Envelope(1, 4) evaluating > > rule: Look > > > up and default C-FACTOR for slabs.'' Also, when i go on Project > > and > > > site> site data properties, it doesn't accept the latitude and > > > longitude and gives the same as an error. > > > Also please guide me the action report from where I can get the > > Annual > > > energy consumption( Since there is no electric utility and gas > > utility > > > file rates available here, can we get it in terms of unit, which > > can > > > be multiplied with the rate and rate analysis can be found); > > space > > > load component( total building load); peak load component(total > > > building load); sensible cooling load & roof thermal transfer > > value > > > (RTTV ) > > > > > > 2. Secondly, please guide me on how can one add up layers to > > just the > > > top of this building of varying soil thickness and green cover ( > > I > > > have the data on their R-values and thickness) and simulate the > > same > > > without having errors. > > > > > > 3. Is there a way by which the outside ambient temperature of > > the > > > building with green roof ( & its micro-climatic features) can be > > > found?I basically need the temperature variation in the top 3 > > meters > > > of the building. > > > > > > It will be really helpful for me if you could take out some time > > from > > > your busy schedule and guide me for the above mentioned queries. > > > > > > Waiting for your reply in anticipation, > > > Thanking you > > > Regards, > > > Charu Sharma > > > X Semester, B.Arch > > > National Institute of Technology > > > India > > > > > > > > > > > > _______________________________________________ > > > Equest-users mailing list > > > http://lists.onebuilding.org/listinfo.cgi/equest-users- > > onebuilding.org> To unsubscribe from this mailing list send a > > blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > _______________________________________________ > > Equest-users mailing list > > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > > To unsubscribe from this mailing list send a blank message to > > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From David_Fishel at rlfae.com Mon Apr 16 11:07:44 2012 From: David_Fishel at rlfae.com (David C. Fishel) Date: Mon, 16 Apr 2012 18:07:44 +0000 Subject: [Equest-users] Importing window 6 file Message-ID: Hi Group, I am trying to model glazing with a silk screen frit of 50%. I can do this in NLBL window 6 program but I am getting the following error message when I try to import this into eQuest: "Invalid U-value Conditions - likely due to non-NFRC conditions being specified in the Window program" Is it possible to import Window 6 data to eQuest? If not is there a better way to model this 50% opening which reduced the visible transmittance of the glazing? Thanks -David David C. Fishel, PE, LEED AP BD+C Senior Energy Analyst RLF | architecture engineering interiors 4750 New Broad Street, Orlando, FL 32814 p 407.730-8600 | f 407.730-3603| www.rlfarchitects.com AIA Florida's 2010 Firm of the Year P Please consider the environment before printing this e-mail -------------- next part -------------- An HTML attachment was scrubbed... URL: From dave.weigel at thewattdoctors.com Mon Apr 16 11:49:23 2012 From: dave.weigel at thewattdoctors.com (Dave Weigel) Date: Mon, 16 Apr 2012 14:49:23 -0400 Subject: [Equest-users] Fw: Heating in Summer Message-ID: Hi Ben, Your question intrigued me. I have not been in great detail through your model, but I saw right away that you have specified humidity control on your packaged unit, with a 50 percent maximum. I believe that your cooling system will be running in the summer for dehumidification quite often when the space temperature is already satisfied. The electric heat will have to come on to re-heat the air. This will show as a load on the heating coil. Hope this helps! If not, I look forward to hearing what's causing your summertime heating. Dave David R. Weigel, PE Managing Member The Watt Doctors, LLC 1189 Golden Circle SW, Lilburn GA 30047 678-353-6941 office 901-619-1716 cell -----Original Message----- From: modeling at jeisenhart.com Sent: Friday, April 13, 2012 9:43 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Heating in Summer Hello Everyone! Here's a puzzle for the email group. (I hope you're having a better weekend than me!) I've searched the archived emails to find a solution, but most seem to ask for the PD2 and INP file so that makes me think that the solutions will mostly be unique. I'm attaching a zip file of my model. I have packaged single zone units with electric resistence heat. I'm seeing a significant load in the summer on all units. I've dropped the thermostat in the summer months on the heating and am still getting a load. Any ideas on why there would be a load? Thanks, Ben From smoret at ucdavis.edu Mon Apr 16 12:34:24 2012 From: smoret at ucdavis.edu (Stefano Moret) Date: Mon, 16 Apr 2012 19:34:24 +0000 Subject: [Equest-users] Scale modeling In-Reply-To: <62.36.27638.F86748F4@cm-omr2> References: <62.36.27638.F86748F4@cm-omr2> Message-ID: <04B072E0E3317A4486513BB18D6579C007271784@exmbx10.ex.ad3.ucdavis.edu> Dear all, I?ve proceeded in the last days in my research for model validation and building prototypes which could serve as reference models for my research. I finally found what I was looking for, and it looks like this has been the goal of a DOE project concluded in 2008. In the website I linked below, there are listed some models of commercial building prototypes which have demonstrated to fit most of the commercial buildings in the US, and which could serve as a starting point for modeling energy efficiency measures without the risk of having results dependent on the specific modeling assumptions, of course within reasonable ranges. There are also the IDF files which serve as input for E+. To recall the elephant and the mouse metaphor, here there?s probably a good reference for consistent mice and elephants prototypes, and that was exactly what I was looking for. Here?s the website for your interest: http://www1.eere.energy.gov/buildings/commercial_initiative/reference_buildings.html Thanks again for your hints, and best regards Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of joe at thespinnakergroupinc.com Sent: Tuesday, April 10, 2012 11:06 AM To: joe at thespinnakergroupinc.com; Shaun Martin; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling And of course note you have multiple floors to deal with when you scale up... On second thought a better way to scale would he to maintain the ratio of length x width / height x ((2 x length) + (2 x width)) If height is constant then a 10x10 space scaled up ten times floor area would best scale to something like 194x5.1 (excuse calculations, no calculator doing this at red lights). Where other issues arise like the exposure of the long face will make a big impact. If building modeling could be scaled for certain constants this easily them we could do it with little paper wheels like ductulators. Fun to think about though! Joe Fleming, PE, BEMP, LEED AP BD+C ----- Reply message ----- From: "joe at thespinnakergroupinc.com" > To: "Shaun Martin" >, > Subject: [Equest-users] Scale modeling Date: Tue, Apr 10, 2012 1:44 pm If the building is being scaled by some magnitude, then all dimensions need to be scaled equally. Otherwise, as has been mentioned in the previous emails, the ratio of envelope surface area to floor plan area will change. A 10x10x10 building, (heat/cool load-wise), will scale better to a 100x100x100 then it would to a 100x100x10, because the ratio of floor space to envelope area is maintained. Although only the top floor will have roof load. And a skylight will only effect the top floor of the larger scale building. Can you change from a skylight to a window with daylighting? This would scale better. Joe Fleming, PE, BEMP, LEED AP BD+C ----- Reply message ----- From: "Shaun Martin" > To: > Subject: [Equest-users] Scale modeling Date: Tue, Apr 10, 2012 1:16 pm Hi Stefano, John's right on point (especially the elephant part). The results likely represent some sort of curve, and are probably multivariate. My suggestion would be to model large, medium and small scenarios and do hourly reports of the loads to see what is happening at different outside temperatures. Shaun Martin -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 10, 2012 9:31 AM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE Shrews must eat 80-90 % of their own body weight in food daily. An elephant eats about 5% of their own body weight in food daily. The surface area to mass ratios are vastly different. Heat loss, metabolism (internal loads) and fur are very different. If an elephant had the fur of a mouse it would die from overheating. You can't model a small building and try to extrapolate the results to a large building. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman Sent: Monday, April 09, 2012 4:18 PM To: Stefano Moret Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Scale modeling The short answer is that every building is different, and there is no "typical" model that will fit them all. As you mentioned, the ratio between lighting/cooling/heating changes depending on the size of the building. I'm willing to guess that this is because the core zones that have very little need for heat get much larger in relation to the perimeter zones. Also, the building energy needs will change depending on orientation and global location. I would suggest that you take a slightly different approach - try to come up with values that are representative for different types of spaces. You might do say: 1. A perimeter office space with XX% glazing (run for North, East, South and West exposures) 2. A core office space with no skylights 3. A core office space with XX% of roof area as skylights 4. A core manufacturing space??? 5,6,7.... Run each model in the applicable climate. Then, if you have an office building that is 70% core and 30% perimeter space, you'll have a better understanding of the building. This is still a very rough approximation, but should get you farther than trying to model one "typical" building. -- Karen On Mon, Apr 9, 2012 at 4:57 PM, Stefano Moret > wrote: Dear all, I've recently played around quite a bit with E-quest to simulate the effect of dynamic fenestration on building energy consumption. For these simulations I've been using a very simple office model with a skylight on the top as a test-bed for my calculations (with default system for HVAC and daylighting controls with dimming for lights) but, observing the values I'm obtaining in output, I see that the values I obtain for lighting, cooling and heating consumption make sense relatively, i.e. if compared to themselves in different conditions, but are sometimes of totally different order of magnitude if compared to each other (lighting/cooling loads are often much higher than heating, by orders of magnitude), especially when scaling up the model to bigger sizes. This way, it's very difficult to see the effect of a variable change on the total energy consumption. I know the model I'm using is very idealized, but is there any variable that I can act on in order to obtain a model which has energy consumption values more similar to a real building? For example, is there a "suggested" size of the building that gives better results? Or maybe simulating a single room in a large building gives more realistic results than the single room alone? My point is that I would like to have a model whose results in scale might be consistent when applied to bigger buildings. Thanks for your hints and suggestions, Stefano -- Stefano Moret California Lighting Technology Center University of California, Davis 633 Pena Drive Davis, CA 95618 530-747-3846 smoret at ucdavis.edu _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From pasha.pkconsulting at gmail.com Mon Apr 16 13:38:28 2012 From: pasha.pkconsulting at gmail.com (Pasha Korber-Gonzalez) Date: Mon, 16 Apr 2012 14:38:28 -0600 Subject: [Equest-users] Munters units in eQuest Message-ID: Hi, has anybody had any successful experience modeling Munters heat recovery units in eQuest? and for LEED compliance? I could use some guidance please. Thanks, Pasha :) pasha at korberenergy.com -------------- next part -------------- An HTML attachment was scrubbed... URL: From arpanbakshi at gmail.com Mon Apr 16 18:06:56 2012 From: arpanbakshi at gmail.com (Arpan Bakshi) Date: Mon, 16 Apr 2012 21:06:56 -0400 Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone Message-ID: Fixed and Building Shades are presently defined in DOE2/eQUEST using: X-REF Y-REF Z-REF HEIGHT WIDTH AZIMUTH Has anyone come across an alternate specification method using coordinates only? For example: Point 1 (x,y,z) Point 2 (x,y,z) Point 3 (x,y,z) Point 4 (x,y,z) Arpan Bakshi, LEED AP BD+C -------------- next part -------------- An HTML attachment was scrubbed... URL: From 546751190 at qq.com Mon Apr 16 20:27:04 2012 From: 546751190 at qq.com (=?ISO-8859-1?B?YWFyb24=?=) Date: Tue, 17 Apr 2012 11:27:04 +0800 Subject: [Equest-users] How to decide HVAC type Message-ID: Dear all I find contradiction between ASHRAE90.1-2007 Standard and ASHRAE 90.1-2007 User's Manual when deciding the baseline's HVAC system. Table G3.1.1A in Appendix G is used to decide the baseline HVAC as shown below The note under the table which i have underline say "Where attributes make a building eligible for more than one baseline system type, use the predominant condition to determine the system type for the entire building." It seems that only one HVAC system will be used in baseline. However, in ASHRAE 90.1-2007 User's Manual , there is no explaination about the note. While the Case Study in Page G-37 of User's Manual tell us that two different types of HVAC system should be used respectively for the Residential part and office part as shown below. So I think this conflict with the ASHRAE90.1-2007 Standard Table G3.1.1A. what about your views? If a hospital building includes mainly wards in 3~7 floors with an area of 132000ft2 and therapy zone in 1~2 floors with an area of 52000ft2, the proposed building is FCU served by chiller and boiler, I tend to the PTAC system (system 1) for 3~7 floors and system 5 for 1~2 floors. what about your opinion? Thank you for any comments and directions. Aaron -------------- next part -------------- An HTML attachment was scrubbed... URL: From 546751190 at qq.com Mon Apr 16 20:34:56 2012 From: 546751190 at qq.com (=?gbk?B?QWFyb24=?=) Date: Tue, 17 Apr 2012 11:34:56 +0800 Subject: [Equest-users] How to decied HVAC system type(with picture) Message-ID: Dear all I find contradiction between ASHRAE90.1-2007 Standard and ASHRAE 90.1-2007 User's Manual when deciding the baseline's HVAC system. Table G3.1.1A in Appendix G is used to decide the baseline HVAC as shown below The note under the table which i have underline say "Where attributes make a building eligible for more than one baseline system type, use the predominant condition to determine the system type for the entire building." It seems that only one HVAC system will be used in baseline. However, in ASHRAE 90.1-2007 User's Manual , there is no explaination about the note. While the Case Study in Page G-37 of User's Manual tell us that two different types of HVAC system should be usedrespectively forthe Residential part and office part as shown below.So I think this conflict with the ASHRAE90.1-2007 StandardTable G3.1.1A. what about your views? If a hospital building includes mainly wards in 3~7 floors with an area of 132000ft2 and therapy zone in 1~2 floors with an area of 52000ft2, the proposed building is FCU served by chiller and boiler, I tend to the PTAC system (system 1) for 3~7 floors and system 5 for 1~2 floors. what about your opinion? Thank you for any comments and directions. Aaron -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 32276 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 48441 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: application/octet-stream Size: 174 bytes Desc: not available URL: From jenny.zhang at arup.com Tue Apr 17 00:31:47 2012 From: jenny.zhang at arup.com (Jenny Zhang) Date: Tue, 17 Apr 2012 15:31:47 +0800 Subject: [Equest-users] How to decied HVAC system type(with picture) In-Reply-To: References: Message-ID: Hi Aaron, you could refer to G3.1.1 Exceptions a ? use additional system types for non-predominant conditions, if those conditions apply to more than 1900 sqm of conditioned floor area. It is not conflict. For you case, could the hospital floors can be considered as residential area? you should check it. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Aaron Sent: 2012?4?17? 11:35 To: equest-users Subject: [Equest-users] How to decied HVAC system type(with picture) Dear all I find contradiction between ASHRAE90.1-2007 Standard and ASHRAE 90.1-2007 User's Manual when deciding the baseline's HVAC system. Table G3.1.1A in Appendix G is used to decide the baseline HVAC as shown below [cid:image001.png at 01CD1CAE.51567440][cid:image002.jpg at 01CD1CAE.51567440] The note under the table which i have underline say "Where attributes make a building eligible for more than one baseline system type, use the predominant condition to determine the system type for the entire building." It seems that only one HVAC system will be used in baseline. However, in ASHRAE 90.1-2007 User's Manual , there is no explaination about the note. While the Case Study in Page G-37 of User's Manual tell us that two different types of HVAC system should be usedrespectively forthe Residential part and office part as shown below.So I think this conflict with the ASHRAE90.1-2007 StandardTable G3.1.1A. what about your views? [cid:image001.png at 01CD1CAE.51567440][cid:image003.jpg at 01CD1CAE.51567440] If a hospital building includes mainly wards in 3~7 floors with an area of 132000ft2 and therapy zone in 1~2 floors with an area of 52000ft2, the proposed building is FCU served by chiller and boiler, I tend to the PTAC system (system 1) for 3~7 floors and system 5 for 1~2 floors. what about your opinion? Thank you for any comments and directions. Aaron ____________________________________________________________ Electronic mail messages entering and leaving Arup business systems are scanned for acceptability of content and viruses -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.png Type: image/png Size: 174 bytes Desc: image001.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.jpg Type: image/jpeg Size: 48441 bytes Desc: image002.jpg URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.jpg Type: image/jpeg Size: 32276 bytes Desc: image003.jpg URL: From jenny.zhang at arup.com Tue Apr 17 00:34:21 2012 From: jenny.zhang at arup.com (Jenny Zhang) Date: Tue, 17 Apr 2012 15:34:21 +0800 Subject: [Equest-users] Infiltration of Baseline model In-Reply-To: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> References: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> Message-ID: Joey, you are correct! I have receive comments from GBCI on a LEED EA project. The baseline model?s infiltration should be the same as the proposed model. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jiao, Joey Sent: 2012?4?16? 17:27 To: Equest-users at lists.onebuilding.org Subject: [Equest-users] Infiltration of Baseline model Hi, Everyone: Is there any request about baseline model?s infiltration? I have check all appendix G items, but it seems this area is blank. If the infiltration must be the same between baseline & purposed? Any light on it will be appreciated. Thank you. Joey. --------------------------------------------------------------------------- Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. ____________________________________________________________ Electronic mail messages entering and leaving Arup business systems are scanned for acceptability of content and viruses -------------- next part -------------- An HTML attachment was scrubbed... URL: From Joey.Jiao at WSPGroup.com.cn Tue Apr 17 01:56:01 2012 From: Joey.Jiao at WSPGroup.com.cn (Jiao, Joey) Date: Tue, 17 Apr 2012 16:56:01 +0800 Subject: [Equest-users] Demand charge & 25% Process Cost rule. Message-ID: <0F18FC782AAB044BADF94EA196DF1261010504B1@exc03ahk1hk.asia.wspgroup.com> Hi, everyone: If there is a project with demand charge, how should we deal with the rule of 25% process cost. Assume one building annual cost like below: total demand cost?by $/kw?=1$ total energy cost ?by $/kwh) =3$ SUM = 4$ How much dollar this building need to pay for the process cost when this building comply with the 25% rule? Thank you very much for any suggestion. Joey --------------------------------------------------------------------------- Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. -------------- next part -------------- An HTML attachment was scrubbed... URL: From 503271081 at qq.com Tue Apr 17 03:15:17 2012 From: 503271081 at qq.com (=?gbk?B?wOTD5rqux7k=?=) Date: Tue, 17 Apr 2012 18:15:17 +0800 Subject: [Equest-users] Can you use eQuest for Ice storage air Conditioning system stimulation Message-ID: Hi Everyone , I am a abecedarian of eQuest. Who can tell me how use eQuest for Ice storage air Conditioning system stimulation. thank you ! zhao -------------- next part -------------- An HTML attachment was scrubbed... URL: From BradH at BVHis.com Tue Apr 17 06:14:26 2012 From: BradH at BVHis.com (Brad L. Huff) Date: Tue, 17 Apr 2012 09:14:26 -0400 Subject: [Equest-users] DCV - Z Fraction Message-ID: Modelers, In e-Quest, it is frustrating that the z fraction equation is defined properly within the help documentation but there is no way to define the maximum z fraction (As you can in Trace) in the model, resulting in systems that tend to use 100% OA for 100% of the time. Does anyone know if this will be a feature added in the future? Does everyone tend to model DCV by scheduling the OA to follow the occupancy schedule? Brad Huff, EIT, LEED Green Associate, Mechanical Engineer I BVH Integrated Services, Inc. 50 Griffin Road South, Bloomfield, CT 06002 I 860.286.9171 One Gateway Center, Suite 701, Newton, MA 02458 I 617.658.9008 bvhis.com I twitter.com/bvhis -------------- next part -------------- An HTML attachment was scrubbed... URL: From John.S.Eurek at usace.army.mil Tue Apr 17 07:32:30 2012 From: John.S.Eurek at usace.army.mil (Eurek, John S NWO) Date: Tue, 17 Apr 2012 14:32:30 +0000 Subject: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) In-Reply-To: References: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> Message-ID: Classification: UNCLASSIFIED Caveats: NONE So LEED doesn't want to promote building built with strict air tightness? Did the air tightness industry not pony up as much cash as the bike rack industry? Our architects have been working on writing up an air tightness spec and researching best construction methods and air testing methods. I'll let them know they can stop. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jenny Zhang Sent: Tuesday, April 17, 2012 2:34 AM To: Jiao, Joey; Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model Joey, you are correct! I have receive comments from GBCI on a LEED EA project. The baseline model?s infiltration should be the same as the proposed model. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jiao, Joey Sent: 2012?4?16? 17:27 To: Equest-users at lists.onebuilding.org Subject: [Equest-users] Infiltration of Baseline model Hi, Everyone: Is there any request about baseline model?s infiltration? I have check all appendix G items, but it seems this area is blank. If the infiltration must be the same between baseline & purposed? Any light on it will be appreciated. Thank you. Joey. --------------------------------------------------------------------------- Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. ____________________________________________________________ Electronic mail messages entering and leaving Arup business systems are scanned for acceptability of content and viruses Classification: UNCLASSIFIED Caveats: NONE From ncaton at smithboucher.com Tue Apr 17 07:37:38 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 17 Apr 2012 14:37:38 +0000 Subject: [Equest-users] Munters units in eQuest In-Reply-To: References: Message-ID: Hi Pasha, I haven't yet, but multiple approaches have surfaced before on the lists and I understand it to be a significant challenge - see attached discussions. If these discussions leave any questions unanswered, I would suggest following up directly with one or more of the 4 familiar names asking/answering all the questions in these threads for their thoughts/experience: Vikram, Eric, Shuichi, Kyle. I'm appointing this team the title of onebuilding.org's "Fantastic 4" for eQuest Munters units - add that to your business cards guys. ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez Sent: Monday, April 16, 2012 3:38 PM To: eQUEST Users List Subject: [Equest-users] Munters units in eQuest Hi, has anybody had any successful experience modeling Munters heat recovery units in eQuest? and for LEED compliance? I could use some guidance please. Thanks, Pasha :) pasha at korberenergy.com -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: -------------- next part -------------- An embedded message was scrubbed... From: Eric Studer Subject: Re: [Equest-users] Desiccant Wheel with Gas-fired Regeneration Date: Mon, 8 Feb 2010 14:45:17 +0000 Size: 109402 URL: -------------- next part -------------- An embedded message was scrubbed... From: Shuichi Hendrickson Subject: Re: [Equest-users] Modeling Munters ERV in Equest Date: Fri, 4 Mar 2011 06:28:29 +0000 Size: 36733 URL: From nathanm at rushingco.com Tue Apr 17 08:13:25 2012 From: nathanm at rushingco.com (Nathan Miller) Date: Tue, 17 Apr 2012 08:13:25 -0700 (PDT) Subject: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) In-Reply-To: References: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> Message-ID: <065901cd1cad$04ab5670$0e020350$@com> Oh please, what an over reaction. As an industry we are very in the dark about reasonable/typical infiltration rates. I suspect any model reviewer, GBCI or otherwise would have a difficult time assessing if the claimed savings due to improved air barrier, or whatever strategy is implemented, are reasonable, especially given that there is no clear baseline established by 90.1. However, you could always put forward a well reasoned argument with back up data and studies and it is possible that the reviewer will allow you take credit. Cite some reputable sources. Submit it as an Exceptional Calculation Methodology with the claimed savings separated out from the rest of your model so it can be discretely evaluated. Here is Seattle the city is requiring new projects to conduct full building air leakage testing prior to occupancy with the city receiving the results as part of a data collection effort, presumably so that they can set reasonable requirements for air leakage in the future. Maybe this data can work its way into an upcoming 90.1 cycle and we can all have a more reasonable approach for modeling air leakage. Nathan Miller, PE, LEED AP BD+C Mechanical Engineer/Senior Energy Analyst O 206-285-7100 | D 206-788-4577 www.rushingco.com -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 17, 2012 7:33 AM To: Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE So LEED doesn't want to promote building built with strict air tightness? Did the air tightness industry not pony up as much cash as the bike rack industry? Our architects have been working on writing up an air tightness spec and researching best construction methods and air testing methods. I'll let them know they can stop. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jenny Zhang Sent: Tuesday, April 17, 2012 2:34 AM To: Jiao, Joey; Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model Joey, you are correct! I have receive comments from GBCI on a LEED EA project. The baseline model?s infiltration should be the same as the proposed model. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jiao, Joey Sent: 2012?4?16? 17:27 To: Equest-users at lists.onebuilding.org Subject: [Equest-users] Infiltration of Baseline model Hi, Everyone: Is there any request about baseline model?s infiltration? I have check all appendix G items, but it seems this area is blank. If the infiltration must be the same between baseline & purposed? Any light on it will be appreciated. Thank you. Joey. -------------------------------------------------------------------------- - Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. ____________________________________________________________ Electronic mail messages entering and leaving Arup business systems are scanned for acceptability of content and viruses Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From ncaton at smithboucher.com Tue Apr 17 13:56:22 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 17 Apr 2012 20:56:22 +0000 Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone In-Reply-To: References: Message-ID: Hi Arpan, I'd hate to lead you into an unnecessarily time-consuming path, but I have on rare occasion found it helpful to approach defining complex building shades as exterior wall sections under a dummy space, which themselves can be defined referencing a polygon, which in turn can be defined in (relative) XYZ point coordinates... What you functionally lose along the way is the ability to assign a shading schedule or otherwise alter the opacity of the resulting "shade." Disclaimer: Defining shades with exterior wall sections is likely going to be time consuming, however you slice it. Like anything worth doing, right =)? If you're interested in pursuing this, you should first consider whether the shade you're emulating can be represented/approximated in 2D. I did a writeup once (full discussion attached) showing how one can apply the concept above to represent a complex, repeating shape to pick up the shading of a superstructure. Here's an illustration showing the end-result: [cid:image005.png at 01CB5978.13595400] To up the ante, with another tier of effort you can approach approximating 3D shapes with polygonal exterior wall sections... but I would sooner advise strongly considering whether a 2D equivalent can be defined, or if you might better invest your time learning a more complex-geometry-compliant energy modeling software (I keep meaning to do this!). Following is a visual of using polygonal exterior wall sections as shades to achieve a 3D shape - this was not a small amount of work: [cid:image002.png at 01CD1CAC.4CC51730] A couple folks have, in years past, developed impressive looking export tools (from the likes of sketchup, revit and so forth) that at least appear to automate production of polygons for complex geometries in eQuest... I've never seen any of these freely distributed nor test-driven any such tool/process myself, so I can't endorse further other than to note they're out there and might be available, for a cost. Best of luck! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Arpan Bakshi Sent: Monday, April 16, 2012 8:07 PM To: equest-users Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone Fixed and Building Shades are presently defined in DOE2/eQUEST using: X-REF Y-REF Z-REF HEIGHT WIDTH AZIMUTH Has anyone come across an alternate specification method using coordinates only? For example: Point 1 (x,y,z) Point 2 (x,y,z) Point 3 (x,y,z) Point 4 (x,y,z) Arpan Bakshi, LEED AP BD+C -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.png Type: image/png Size: 139092 bytes Desc: image002.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.png Type: image/png Size: 150727 bytes Desc: image003.png URL: -------------- next part -------------- An embedded message was scrubbed... From: Nick Caton Subject: Re: [Equest-users] Simple Building Shade Question Date: Tue, 21 Sep 2010 15:34:19 +0000 Size: 400612 URL: From arpanbakshi at gmail.com Tue Apr 17 14:06:22 2012 From: arpanbakshi at gmail.com (Arpan Bakshi) Date: Tue, 17 Apr 2012 17:06:22 -0400 Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone In-Reply-To: References: Message-ID: Nick, these examples are quite impressive and DO look like a lot of work! A question about the dummy zone approach--my understanding is that any geometry which is a subset of a zone or window only shades the parent object, whereas a building & fixed shade element shades all geometry in the model. How did you bypass this issue? Thank you! Arpan Bakshi, LEED AP BD+C On Tue, Apr 17, 2012 at 4:56 PM, Nick Caton wrote: > Hi Arpan,**** > > ** ** > > I?d hate to lead you into an unnecessarily time-consuming path, but I have > on rare occasion found it helpful to approach defining complex building > shades as exterior wall sections under a dummy space, which themselves can > be defined referencing a polygon, which in turn can be defined in > (relative) XYZ point coordinates? What you functionally lose along the way > is the ability to assign a shading schedule or otherwise alter the opacity > of the resulting ?shade.?**** > > ** ** > > Disclaimer: Defining shades with exterior wall sections is likely going > to be time consuming, however you slice it. Like anything worth doing, > right =)?**** > > ** ** > > If you?re interested in pursuing this, you should first consider whether > the shade you?re emulating can be represented/approximated in 2D. I did a > writeup once (full discussion attached) showing how one can apply the > concept above to represent a complex, repeating shape to pick up the > shading of a superstructure. Here?s an illustration showing the end-result: > **** > > ** ** > > [image: cid:image005.png at 01CB5978.13595400]**** > > ** ** > > To up the ante, with another tier of effort you can approach approximating > 3D shapes with polygonal exterior wall sections? but I would sooner advise > strongly considering whether a 2D equivalent can be defined, or if you > might better invest your time learning a more complex-geometry-compliant > energy modeling software (I keep meaning to do this!). Following is a > visual of using polygonal exterior wall sections as shades to achieve a 3D > shape ? this was not a small amount of work:**** > > ** ** > > **** > > ** ** > > A couple folks have, in years past, developed impressive looking export > tools (from the likes of sketchup, revit and so forth) that at least appear > to automate production of polygons for complex geometries in eQuest? I?ve > never seen any of these freely distributed nor test-driven any such > tool/process myself, so I can?t endorse further other than to note they?re > out there and might be available, for a cost.**** > > ** ** > > Best of luck!**** > > ** ** > > ~Nick**** > > ** ** > > [image: cid:489575314 at 22072009-0ABB]** > > * * > > *NICK CATON, P.E.*** > > SENIOR ENGINEER**** > > ** ** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > ** ** > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Arpan Bakshi > *Sent:* Monday, April 16, 2012 8:07 PM > *To:* equest-users > *Subject:* [Equest-users] Defining Building and Fixed Shades using > Coordinates Alone**** > > ** ** > > Fixed and Building Shades are presently defined in DOE2/eQUEST using:**** > > **** > > X-REF **** > > Y-REF **** > > Z-REF **** > > HEIGHT **** > > WIDTH **** > > AZIMUTH**** > > **** > > Has anyone come across an alternate specification method using coordinates > only? **** > > For example:**** > > **** > > Point 1 (x,y,z)**** > > Point 2 (x,y,z)**** > > Point 3 (x,y,z)**** > > Point 4 (x,y,z)**** > > **** > > **** > > **** > > **** > > Arpan Bakshi, LEED AP BD+C**** > > **** > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 139092 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 150727 bytes Desc: not available URL: From ncaton at smithboucher.com Tue Apr 17 15:48:05 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 17 Apr 2012 22:48:05 +0000 Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone In-Reply-To: References: Message-ID: Our understandings differ a bit - I can affirm that I and others have tested and shades defined as I'm describing/showing do their job and shade other surfaces that are components of other spaces/shells. Here's my understanding bulleted out for clarity... I might be off here so feel free to correct me: - Building shades: Shade everything - External surfaces (roofs, walls) generally: Shade everything as well, unless you set the "self shading" input to "no" - Shades defined as a child components of a window (fins/overhangs): Shade only that window, not the surrounding wall surfaces or adjacent windows [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: Arpan Bakshi [mailto:arpanbakshi at gmail.com] Sent: Tuesday, April 17, 2012 4:06 PM To: Nick Caton Cc: equest-users Subject: Re: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone Nick, these examples are quite impressive and DO look like a lot of work! A question about the dummy zone approach--my understanding is that any geometry which is a subset of a zone or window only shades the parent object, whereas a building & fixed shade element shades all geometry in the model. How did you bypass this issue? Thank you! Arpan Bakshi, LEED AP BD+C On Tue, Apr 17, 2012 at 4:56 PM, Nick Caton > wrote: Hi Arpan, I'd hate to lead you into an unnecessarily time-consuming path, but I have on rare occasion found it helpful to approach defining complex building shades as exterior wall sections under a dummy space, which themselves can be defined referencing a polygon, which in turn can be defined in (relative) XYZ point coordinates... What you functionally lose along the way is the ability to assign a shading schedule or otherwise alter the opacity of the resulting "shade." Disclaimer: Defining shades with exterior wall sections is likely going to be time consuming, however you slice it. Like anything worth doing, right =)? If you're interested in pursuing this, you should first consider whether the shade you're emulating can be represented/approximated in 2D. I did a writeup once (full discussion attached) showing how one can apply the concept above to represent a complex, repeating shape to pick up the shading of a superstructure. Here's an illustration showing the end-result: [cid:image005.png at 01CB5978.13595400] To up the ante, with another tier of effort you can approach approximating 3D shapes with polygonal exterior wall sections... but I would sooner advise strongly considering whether a 2D equivalent can be defined, or if you might better invest your time learning a more complex-geometry-compliant energy modeling software (I keep meaning to do this!). Following is a visual of using polygonal exterior wall sections as shades to achieve a 3D shape - this was not a small amount of work: [cid:image004.png at 01CD1CC2.1BBE9380] A couple folks have, in years past, developed impressive looking export tools (from the likes of sketchup, revit and so forth) that at least appear to automate production of polygons for complex geometries in eQuest... I've never seen any of these freely distributed nor test-driven any such tool/process myself, so I can't endorse further other than to note they're out there and might be available, for a cost. Best of luck! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Arpan Bakshi Sent: Monday, April 16, 2012 8:07 PM To: equest-users Subject: [Equest-users] Defining Building and Fixed Shades using Coordinates Alone Fixed and Building Shades are presently defined in DOE2/eQUEST using: X-REF Y-REF Z-REF HEIGHT WIDTH AZIMUTH Has anyone come across an alternate specification method using coordinates only? For example: Point 1 (x,y,z) Point 2 (x,y,z) Point 3 (x,y,z) Point 4 (x,y,z) Arpan Bakshi, LEED AP BD+C -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.png Type: image/png Size: 150727 bytes Desc: image003.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image004.png Type: image/png Size: 139092 bytes Desc: image004.png URL: From jenny.zhang at arup.com Tue Apr 17 20:12:09 2012 From: jenny.zhang at arup.com (Jenny Zhang) Date: Wed, 18 Apr 2012 11:12:09 +0800 Subject: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) In-Reply-To: <065901cd1cad$04ab5670$0e020350$@com> References: <0F18FC782AAB044BADF94EA196DF1261010500AD@exc03ahk1hk.asia.wspgroup.com> <065901cd1cad$04ab5670$0e020350$@com> Message-ID: Interesting topic! In ASHRAE 90.1 5.4.3.3 Fenestration and doors: air leakage shall not exceed 2.0L/s m2 for all other products(curtain walls I think). I refer to NFRC400 and the test delta pressure is 75pa. In China the grading standard of curtain wall air tightness is under 10 delta pressure. The 2.0L/s m2(75Pa) is equal to 0.522L/Sm2(10[a) which is much worse than China GB standard(0.278L/sm2, 10pa) However in other sections like chiller cop or lighting Power ASHRAE standard are much more strict than China GB code. Do American people prefer to live with more air infiltration? It confuse me for a long time. Jie Z -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nathan Miller Sent: 2012?4?17? 23:13 To: 'Eurek, John S NWO'; Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) Oh please, what an over reaction. As an industry we are very in the dark about reasonable/typical infiltration rates. I suspect any model reviewer, GBCI or otherwise would have a difficult time assessing if the claimed savings due to improved air barrier, or whatever strategy is implemented, are reasonable, especially given that there is no clear baseline established by 90.1. However, you could always put forward a well reasoned argument with back up data and studies and it is possible that the reviewer will allow you take credit. Cite some reputable sources. Submit it as an Exceptional Calculation Methodology with the claimed savings separated out from the rest of your model so it can be discretely evaluated. Here is Seattle the city is requiring new projects to conduct full building air leakage testing prior to occupancy with the city receiving the results as part of a data collection effort, presumably so that they can set reasonable requirements for air leakage in the future. Maybe this data can work its way into an upcoming 90.1 cycle and we can all have a more reasonable approach for modeling air leakage. Nathan Miller, PE, LEED AP BD+C Mechanical Engineer/Senior Energy Analyst O 206-285-7100 | D 206-788-4577 www.rushingco.com -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO Sent: Tuesday, April 17, 2012 7:33 AM To: Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model (UNCLASSIFIED) Classification: UNCLASSIFIED Caveats: NONE So LEED doesn't want to promote building built with strict air tightness? Did the air tightness industry not pony up as much cash as the bike rack industry? Our architects have been working on writing up an air tightness spec and researching best construction methods and air testing methods. I'll let them know they can stop. John Eurek -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jenny Zhang Sent: Tuesday, April 17, 2012 2:34 AM To: Jiao, Joey; Equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Infiltration of Baseline model Joey, you are correct! I have receive comments from GBCI on a LEED EA project. The baseline model?s infiltration should be the same as the proposed model. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jiao, Joey Sent: 2012?4?16? 17:27 To: Equest-users at lists.onebuilding.org Subject: [Equest-users] Infiltration of Baseline model Hi, Everyone: Is there any request about baseline model?s infiltration? I have check all appendix G items, but it seems this area is blank. If the infiltration must be the same between baseline & purposed? Any light on it will be appreciated. Thank you. Joey. -------------------------------------------------------------------------- - Joey Jiao Graduate Engineer Shanghai WSP Consulting Ltd. (Shenzhen Branch) Room 406, Wan Tong Da Sha, 3002 Sun Gang Road East, Luo Hu, Shenzhen, 518023, PRC Tel: +86 755 25860686 Fax: +86 755 25860680 Website: www.wspgroup.hk We are WSP. United by our difference. WSP is one of the world's fastest-growing design, engineering and management consultancies. Specialising in property, transport and environmental projects, we work with clients to create built and natural environments for the future. CONFIDENTIAL This e-mail is confidential to the named recipient. If you have received a copy in error, please destroy it. You may not use or disclose the contents of this e-mail to anyone, nor take copies of it. The only copies permitted are (1) by the named recipient and (2) for the purposes of completing successful electronic transmission to the named recipient and then only on the condition that these copies, with this notice attached, are kept confidential until destruction. ____________________________________________________________ Electronic mail messages entering and leaving Arup business systems are scanned for acceptability of content and viruses Classification: UNCLASSIFIED Caveats: NONE _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From charu_0011 at yahoo.com Wed Apr 18 02:13:36 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Wed, 18 Apr 2012 02:13:36 -0700 (PDT) Subject: [Equest-users] Regarding installation of Doe2.1 In-Reply-To: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> Message-ID: <1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com> I'm not able to install doe2.1 version on my windows7 64 bit, even after i changed to compatibility mode Windows XP Please help Regards, Charu Sharma -------------- next part -------------- An HTML attachment was scrubbed... URL: From charu_0011 at yahoo.com Wed Apr 18 02:48:51 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Wed, 18 Apr 2012 02:48:51 -0700 (PDT) Subject: [Equest-users] Regarding installation of Doe2.1 In-Reply-To: <1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> <1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com> Message-ID: <1334742531.11957.YahooMailNeo@web114616.mail.gq1.yahoo.com> It shows, runtime error 303 Please help! ________________________________ From: sharma charu To: "equest-users at lists.onebuilding.org" Sent: Wednesday, April 18, 2012 2:43 PM Subject: Regarding installation of Doe2.1 I'm not able to install doe2.1 version on my windows7 64 bit, even after i changed to compatibility mode Windows XP Please help Regards, Charu Sharma -------------- next part -------------- An HTML attachment was scrubbed... URL: From charu_0011 at yahoo.com Wed Apr 18 03:27:15 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Wed, 18 Apr 2012 03:27:15 -0700 (PDT) Subject: [Equest-users] Regarding installation of Doe2.1 In-Reply-To: References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> <1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com> <1334742531.11957.YahooMailNeo@web114616.mail.gq1.yahoo.com> <009001cd1d49$1542a640$3fc7f2c0$@kamalcogentenergy.com> <1334743772.95892.YahooMailNeo@web114615.mail.gq1.yahoo.com> Message-ID: <1334744835.96065.YahooMailNeo@web114604.mail.gq1.yahoo.com> > >I'm not able to install doe2.1 version on my windows7 64 bit, even after i changed to compatibility mode Windows XP. It shows the errors (attached) >Please help >? >Regards, >Charu Sharma >? > > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: error 2.png Type: image/png Size: 238371 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: error 3.png Type: image/png Size: 238124 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: error floppy drive.png Type: image/png Size: 253453 bytes Desc: not available URL: From ramesh at greenevolution.in Wed Apr 18 04:15:16 2012 From: ramesh at greenevolution.in (ramesh buddhi) Date: Wed, 18 Apr 2012 19:15:16 +0800 (SGT) Subject: [Equest-users] Load unmet hours In-Reply-To: <1334747560.14342.YahooMailNeo@web2712.biz.mail.sg3.yahoo.com> References: <1334747560.14342.YahooMailNeo@web2712.biz.mail.sg3.yahoo.com> Message-ID: <1334747716.94318.YahooMailNeo@web2710.biz.mail.sg3.yahoo.com> Dear Folks I am running an multistorey two bedroom apartment house, I considered two bedroom in each unit (Flat) as air-conditioned, I had separated conditioned and non-conditioned into two separate zones and arrived at an overall tonnage of about 120. When i tried to check the Load unmet hours in the detailed report for conditioned zone it shows some x hours as unmet, then i increased the tonnage so that i can get into an stage where there will not have any unmet hours but even i increased the total tonnage the results shows the same amount of unmet hours. Can any one help me out on this, I had attached the eQuest file for your reference. Thanks a lot in advance. Regards Ramesh BR -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: Belvedere_2Bhk_Baseline.rar Type: application/octet-stream Size: 1490329 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: Sample Report - Load unmet hours.jpg Type: image/jpeg Size: 101235 bytes Desc: not available URL: From bruce5 at bellnet.ca Wed Apr 18 05:18:51 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 18 Apr 2012 08:18:51 -0400 Subject: [Equest-users] Load unmet hours In-Reply-To: <1334747716.94318.YahooMailNeo@web2710.biz.mail.sg3.yahoo.com> References: <1334747560.14342.YahooMailNeo@web2712.biz.mail.sg3.yahoo.com> <1334747716.94318.YahooMailNeo@web2710.biz.mail.sg3.yahoo.com> Message-ID: <4F8EB12B.7000004@bellnet.ca> An HTML attachment was scrubbed... URL: From smartin at shaunmartinconsulting.com Wed Apr 18 08:06:16 2012 From: smartin at shaunmartinconsulting.com (Shaun Martin) Date: Wed, 18 Apr 2012 08:06:16 -0700 Subject: [Equest-users] Regarding installation of Doe2.1 In-Reply-To: <1334744835.96065.YahooMailNeo@web114604.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com><1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com><1334742531.11957.YahooMailNeo@web114616.mail.gq1.yahoo.com><009001cd1d49$1542a640$3fc7f2c0$@kamalcogentenergy.com><1334743772.95892.YahooMailNeo@web114615.mail.gq1.yahoo.com> <1334744835.96065.YahooMailNeo@web114604.mail.gq1.yahoo.com> Message-ID: <6F39422E9A624F4595811EB9AD42ED60@SM> Install windows virtual pc/XP mode. Windows 7 compatibility mode doesn't work. Shaun _____ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sharma charu Sent: Wednesday, April 18, 2012 3:27 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Regarding installation of Doe2.1 I'm not able to install doe2.1 version on my windows7 64 bit, even after i changed to compatibility mode Windows XP. It shows the errors (attached) Please help Regards, Charu Sharma -------------- next part -------------- An HTML attachment was scrubbed... URL: From thomasv at iit.edu Wed Apr 18 09:18:40 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Wed, 18 Apr 2012 11:18:40 -0500 Subject: [Equest-users] Running APEC HCCV and DOE2.1E In-Reply-To: References: <07BF4294A620CF4C9BF3280086050EE10186EC59@camaro.BCE.local> Message-ID: Thanks for letting me know about the problems of installing and running the APEC-HCCV program. I added a folder HCCV.zip? containing the executable program HCCV.EXE. http://bepan.info/hvac-prog/x1-apec-hccv-loads . Let me know if it works. It runs in Windows 7 32-bit computer or earlier hardware, but it will not run on a 64-bit computer. You have to install Windows XP Virtuual Mode on 64-bit. The same applies for the DOE2.1E program http://bepan.info/doe2inp http://www.microsoft.com/windows/virtual-pc/download.aspx How to install Windows XP Mode on Windows 7 Home Premium or lower http://www.youtube.com/watch?v=CbEK0jD6GlE&feature=related Windows Virtual PC Windows XP Mode For Windows 7 http://www.youtube.com/watch?v=8RcSZqAnYLo How to Install Windows XP on Virtual PC http://www.youtube.com/watch?v=n24oQdgTdZs&feature=related -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- 8760 hourly inside zone wall surface temp and MRT at a point in space is not very useful. It might be useful in Loads program based on design day conditions in summer and winter. See http://bepan.info/engg-calcs - 3a - Design-Weather-Generator DOE2.1E uses the Transfer Function method to calculate envelope heat transfer. I think Trane-TRACE and Carrier-HAP use the same method. The CLTD-SCL-CLF method is still very useful for teaching envelope heat transfer. See http://bepan.info/class-notes/e4-project-loads The Total Equivalent Temperature Difference (TETD) method is also useful for teaching. See - http://bepan.info/hvac-prog/x1-apec-hccv-loads It is difficult to explain the heat storage capacity and time lag concepts of the envelope with the other methods although all Loads calculations are done by computer today. The APEC (Automated Procedure for Engineering Consultants) HCC-V Loads program can be downloaded and used. If you don?t know what the ?decrement factor? is, use 0.5 since the range is between 0 and 1. An estimate for ?time-lag? depends on the type of bldg. In design loads calculation for commercial buildings it is important NOT to underestimate the loads. The hourly Fortran Variable report of the DOE2 based programs include outside wall surface temp. In the DOE2 Loads section choose (1) Variable-Type = u-name of EXTERIOR-WALL (2) Variable List Number 5 Q Heat transfer from wall to the zone un-weighted (Btu/hr) (3) Variable List Number 6 T Outside surface temperature (Rankine). Transfer the values of Q and T to an Excel spreadsheet and calculate the inside wall surface temps. Examples of calculating inside surface temp using outside surface temp. http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt Proj-22 - Kuwait-Envelope-Temps-MRT-Systems-Study? I have found the hourly Fortran Variable report by the DOE2 program very helpful. Transfer the hourly data to an Excel spreadsheet and do the rest yourself. Example of using hourly solar data is: http://bepan.info/proj-doe21e/p21_beijing-solar-pv Proj-21 - Beijing-Solar-Radiation-PV-Study - PDF-Report? Example of using cooling coil data is: http://bepan.info/proj-doe21e/p27_dubai-condens-recov Proj-27 - Dubai- Cooling-Coils-Condensate-Recovery Files recently added to the website: 4b ? Tall-Bldgs - Stack Effect, Wind Press and 4c - High-Rise-Apt-Bldgs-Pressurization Varkie -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- Alex you are correct, eQuest does not know the surface temperatures required to calculate the Mean Radiant Temperature. eQuest /DOE2 uses the Cooling Load Temperature Difference (CLTD) method to arrive at heat loads in a space. This approach makes approximations of the radiant component of heat transfer and does not directly calculate radiant gains or losses. Because of this, any DOE2 based software at best can predict air temperature and moisture needed for a PMV calc. EnergyPlus or IES are the only engines that can produce hourly surface temp information and therefore, mean radiant temperature averages. If you are interested in providing comfort feedback of envelope changes and not HVAC changes, learning EnergyPlus using OpenStudio from NREL is well worth the time and effort. Their workflow takes some practice to adopt but once you get the hang of things, creating buildings is very easy. Their youtube channel is best for explaining this, search for OpenStudio and NREL. Neil Bulger Project Engineer ________________________________ I N T E G R A L GROUP 427 13th Street, Oakland CA 94612 510 663 2070 x 235 nbulger at integralgroup.com www.integralgroup.com DEEP GREEN Engineering. ________________________________ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx Sent: Thursday, April 12, 2012 9:13 AM To: Kathryn Kerns Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? I'll second the suggestion to purchase the Thermal Comfort tool. It is easy to use. I believe that a newer version was recently released - we're still using the 1994 version. However, I'm not sure that it solves Jason's problem - it still requires a user-entered Mean Radiant Temperature which I don't believe eQUEST gives as an output. When we use the tool (specifically for perimeter comfort analysis understanding the impact of different glazing options on comfort) we make some assumptions on wall/floor/ceiling temps, some calculations on glass-temperatures, and some further assumptions on the ratio of glass-to-other surfaces from the occupant's perspective. Based on that we can calculate the PMV for that single point time with those conditions. I've used software in the past that was able to calculate PMV for every hour of the year (so every hour it would combine air temp, a calculated MRT based on surface temps, humidity, etc) and then give an output for how comfortable the space was throughout the year (with hourly outputs of PMV for different spaces). I don't believe that eQUEST gives the necessary information (surface temps) to do this type of analysis. I included Jeremiah's response below which suggests that Energy Plus can do these calculations. This was my impression, however I have never used E+ to do them. Kind regards, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. ________________________________ Energy Plus does PMV and inside surface temperatures as well... Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com From: Kathryn Kerns [mailto:kathryn.kerns at bceengineers.com] Sent: Thursday, April 12, 2012 8:58 AM To: Alex Krickx Cc: equest-users at lists.onebuilding.org Subject: RE: [Equest-users] Can you use eQuest for PMV calculations? Alex, ASHRAE sells a Thermal Comfort program which will do these calculations for you based on temperature, humidity, air speed, etc. It doesn't cost much and is easy to use. Check the ASHRAE website for things to purchase. ________________________________ From: equest-users-bounces at lists.onebuilding.org on behalf of Alex Krickx Sent: Wed 4/11/2012 3:42 PM To: Jason Quinn; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Can you use eQuest for PMV calculations? Hi Jason, I'm under the impression that eQUEST can't output surface temperatures which are needed to calculate PMV values. I think an EnergyPlus based program might be a better place to look. I would ask on the Bldg-Sim list for recommendations as it has a broader user-base (this list is eQUEST specific). Good luck, Alex Alex Krickx, LEED AP Building Energy Specialist Serious Energy, Inc. 1250 Elko Dr, Sunnyvale, CA 94089 (t) 408.541.8124 akrickx at seriousenergy.com The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason Quinn Sent: Wednesday, April 11, 2012 3:36 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Can you use eQuest for PMV calculations? Is it possible to use an eQuest model to do thermal comfort PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? If not are there any recommendations? -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From YJHuang at whiteboxtechnologies.com Wed Apr 18 09:27:07 2012 From: YJHuang at whiteboxtechnologies.com (Joe Huang) Date: Wed, 18 Apr 2012 09:27:07 -0700 Subject: [Equest-users] Regarding installation of Doe2.1 In-Reply-To: <1334744835.96065.YahooMailNeo@web114604.mail.gq1.yahoo.com> References: <1334475848.10211.YahooMailNeo@web114604.mail.gq1.yahoo.com> <1334740416.84359.YahooMailNeo@web114603.mail.gq1.yahoo.com> <1334742531.11957.YahooMailNeo@web114616.mail.gq1.yahoo.com> <009001cd1d49$1542a640$3fc7f2c0$@kamalcogentenergy.com> <1334743772.95892.YahooMailNeo@web114615.mail.gq1.yahoo.com> <1334744835.96065.YahooMailNeo@web114604.mail.gq1.yahoo.com> Message-ID: <4F8EEB5B.3060903@whiteboxtechnologies.com> Sharma, Where did you get the install version of DOE-2.1E ? (you can reply by e-mail if necessary :-)). I've never had this problem, and I've been running DOE-2.1E on Window 7 64-bit for at least two years. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang at whiteboxtechnologies.com www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 4/18/2012 3:27 AM, sharma charu wrote: > > > I'm not able to install doe2.1 version on my windows7 64 bit, even > after i changed to compatibility mode Windows XP. It shows the > errors (attached) > Please help > Regards, > Charu Sharma > > > > > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From omoltay at mimtarch.com Wed Apr 18 09:54:59 2012 From: omoltay at mimtarch.com (=?ISO-8859-9?Q?=D6mer_Moltay?=) Date: Wed, 18 Apr 2012 19:54:59 +0300 Subject: [Equest-users] Floor Convectors Message-ID: <4F8EF1E3.9040307@mimtarch.com> Hi, I have to model floor convectors in a multifamily residential, but the mechanical designer is foreeseing the following mode of operation: The convector fans will not run during normal heating and air from the convectors will rise by natural convection into the room. Only when this kind of heating is not sufficient for loads will the fans in the convector units start working. This will be controlled by an outside air thermostat. Which system would be the most suitable for this in eQuest and how to tell the software that fans will only be operational below a certain temperature (FYI: cooling in the same spaces will be by VRF units). Thank you, Omer Moltay Mimta From ekaterina.tzekova at mail.utoronto.ca Wed Apr 18 11:38:35 2012 From: ekaterina.tzekova at mail.utoronto.ca (Ekaterina Tzekova) Date: Wed, 18 Apr 2012 18:38:35 +0000 Subject: [Equest-users] Interior Space Temperature Message-ID: Hello everyone, I am trying to model a building with no heating and cooling system to see how the interior temperature fluctuates based on exterior weather conditions during the summer. Does anyone know if eQuest looks at space temperature when the heating/cooling systems are not on? So far I've only been able to track solar radiation on the building facade.... Thank you! Ekaterina Tzekova -------------- next part -------------- An HTML attachment was scrubbed... URL: From bfountain at greensim.com Wed Apr 18 12:08:17 2012 From: bfountain at greensim.com (bfountain at greensim.com) Date: Wed, 18 Apr 2012 19:08:17 +0000 Subject: [Equest-users] Interior Space Temperature In-Reply-To: References: Message-ID: <863799387-1334776098-cardhu_decombobulator_blackberry.rim.net-891114784-@b5.c1.bise6.blackberry> If the fan schedule is off (and fan control isn't cycle at night) eQUEST doesn't really look at space temp. My inclination would be to create a psz system serving your space with very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize) an an 'always on' fan schedule. Fan volume would depend on whether you wanted to introduce OA. Brian Fountain bfountain at greensim.com -----Original Message----- From: Ekaterina Tzekova Sender: equest-users-bounces at lists.onebuilding.orgDate: Wed, 18 Apr 2012 18:38:35 To: equest-users at lists.onebuilding.org Subject: [Equest-users] Interior Space Temperature _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From baude.jim at gmail.com Wed Apr 18 12:48:14 2012 From: baude.jim at gmail.com (Jim Baude) Date: Wed, 18 Apr 2012 15:48:14 -0400 Subject: [Equest-users] Urgent : maximum number of expression dependency Message-ID: Hi everyone, I would like to know how it is possible to modify BDL source code to increase the limit of exp dep lists. I have a large hospital model and I've been facing some size limit difficulties with it. Thanks in advance, Jim -------------- next part -------------- An HTML attachment was scrubbed... URL: From rdh4176 at gmail.com Wed Apr 18 13:02:07 2012 From: rdh4176 at gmail.com (Rob Hudson) Date: Wed, 18 Apr 2012 16:02:07 -0400 Subject: [Equest-users] Interior Space Temperature In-Reply-To: <863799387-1334776098-cardhu_decombobulator_blackberry.rim.net-891114784-@b5.c1.bise6.blackberry> References: <863799387-1334776098-cardhu_decombobulator_blackberry.rim.net-891114784-@b5.c1.bise6.blackberry> Message-ID: If you leave the thermostats in the space as undefined and the fan schedule in the HVAC tab, the results should show that the HVAC never turns on, and give you the results you are wishing to see. Hope this helps, Rob On Wed, Apr 18, 2012 at 3:08 PM, wrote: > If the fan schedule is off (and fan control isn't cycle at night) eQUEST > doesn't really look at space temp. > > My inclination would be to create a psz system serving your space with > very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize) > an an 'always on' fan schedule. Fan volume would depend on whether you > wanted to introduce OA. > Brian Fountain > bfountain at greensim.com > > -----Original Message----- > From: Ekaterina Tzekova > Sender: equest-users-bounces at lists.onebuilding.orgDate: Wed, 18 Apr 2012 > 18:38:35 > To: equest-users at lists.onebuilding.org > Subject: [Equest-users] Interior Space Temperature > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -- Rob Hudson -------------- next part -------------- An HTML attachment was scrubbed... URL: From thomasv at iit.edu Wed Apr 18 13:32:05 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Wed, 18 Apr 2012 15:32:05 -0500 Subject: [Equest-users] Interior Space Temperature In-Reply-To: References: Message-ID: See - http://bepan.info/engg-calcs Excel File - 16 - Project Space-Temp-Rise The DOE2 programs do not have a Space or Room level below the Zone level. Zone is a group of rooms controlled by a thermostat in one of the rooms. The temp of the room with the thermostat is maintained and the temps of the other rooms float. A Loads program should show the temps in the rooms that have no thermostat. The SOM-IBM-AES loads program developed in the late 1980s (and died in the early 1990s) did have this feature. See - http://bepan.info/hvac-prog/x2-som-ibm-aes-hvac I think the TRACE program has a room level but I am not sure it calculates the temp in the rooms without a thermostat. If it does, then provide no HVAC to a room without a thermostat to get the resulting temp. But then such rooms would have windows open in summer. -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- Hello everyone, I am trying to model a building with no heating and cooling system to see how the interior temperature fluctuates based on exterior weather conditions during the summer. Does anyone know if eQuest looks at space temperature when the heating/cooling systems are not on? So far I've only been able to track solar radiation on the building facade.... Thank you! Ekaterina Tzekova -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From hongjing.shirley at gmail.com Wed Apr 18 14:53:16 2012 From: hongjing.shirley at gmail.com (Jing Hong) Date: Wed, 18 Apr 2012 16:53:16 -0500 Subject: [Equest-users] How to get the hearing and cooling load individually? Message-ID: <184043CC-B410-4873-AE14-04AED7DED27B@gmail.com> The outcomes if equest is energy consumption. How could we get the hearing and cooling loads for each zone? Thanks! Jing From tiwari.sambhav at gmail.com Wed Apr 18 23:40:38 2012 From: tiwari.sambhav at gmail.com (sambhav tiwari) Date: Thu, 19 Apr 2012 12:10:38 +0530 Subject: [Equest-users] Error Message-ID: Hi All, I was done with model and was simulating it ,in between simulation i am having program run terminated due to error but when i checked the building description it is showing no error neither while opening the pd2 file any error is coming then what can be the reason. Only it shown when the run terminated" standard file writing" error but i dont know what is that. please if someone can respond its very urgent. attached the file also Thanks Sambhav -------------- next part -------------- A non-text attachment was scrubbed... Name: Project17april-5.rar Type: application/rar Size: 563059 bytes Desc: not available URL: From eee.javed at gmail.com Thu Apr 19 00:20:48 2012 From: eee.javed at gmail.com (Javed Iqbal) Date: Thu, 19 Apr 2012 12:50:48 +0530 Subject: [Equest-users] Error In-Reply-To: References: Message-ID: Dear Sambhav, You have specified Duct losses without a *DUCT-LOSS-ZONE*. Find revised file as an attachment. DUCT-AIR-LOSS Fraction of the supply air that is lost from the ductwork, thereby reducing the design supply air at the zones. Air lost from the ductwork will change the temperature of the zone specified by DUCT-ZONE, which must be a plenum or unconditioned space. If the DUCT-ZONE is a plenum, then the duct air loss changes the temperature of the return air entering the plenum. If the DUCT-ZONE is an unconditioned space the duct air loss acts to change the temperature of the zone. The program does not currently simulate duct losses to conditioned spaces. ***ERROR*********************************************************************** Duct losses are specified without a DUCT-LOSS-ZONE; No plenum exists for default duct losses. I hope some senior HVAC/Modeling consultant can shed some light on this. Thanks! On Thu, Apr 19, 2012 at 12:10 PM, sambhav tiwari wrote: > Hi All, > I was done with model and was simulating it ,in between > simulation i am having program run terminated due to error but when i > checked the building description it is showing no error neither while > opening the pd2 file any error is coming then what can be the reason. > > Only it shown when the run terminated" standard file writing" error > but i dont know what is that. > > please if someone can respond its very urgent. attached the file also > > > Thanks > Sambhav > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -- Javed Iqbal, LEED AP, CEA Energy Analyst -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: Bagmane WTC9_Revised.zip Type: application/zip Size: 39961 bytes Desc: not available URL: From yusuf at ytenterprises.com Thu Apr 19 02:06:45 2012 From: yusuf at ytenterprises.com (Yusuf Turab) Date: Thu, 19 Apr 2012 14:36:45 +0530 Subject: [Equest-users] Window wall ratios Message-ID: Hello Group I am simulating a single storey villa. On the DD wizard scree for exterior windows I selected custom window and door placements and individually marked each window and door with their respective dimensions. But I found that the % of WWR on the main screen still remained the default value. Why is that happening? and what is eQuest simulating the default values or the custom windows and doors? Many Thanks Yusuf Turab -------------- next part -------------- An HTML attachment was scrubbed... URL: From bfountain at greensim.com Thu Apr 19 05:26:50 2012 From: bfountain at greensim.com (bfountain at greensim.com) Date: Thu, 19 Apr 2012 12:26:50 +0000 Subject: [Equest-users] Window wall ratios In-Reply-To: References: Message-ID: <1760261323-1334838411-cardhu_decombobulator_blackberry.rim.net-1262455781-@b5.c1.bise6.blackberry> When you enter custom windows, the percentage values on the window screen do not get updated. Look at the summary at the bottom of report LV-D for your window and wall areas. Brian Fountain bfountain at greensim.com -----Original Message----- From: Yusuf Turab Sender: equest-users-bounces at lists.onebuilding.orgDate: Thu, 19 Apr 2012 14:36:45 To: Subject: [Equest-users] Window wall ratios _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From oscar664 at hotmail.com Thu Apr 19 07:23:05 2012 From: oscar664 at hotmail.com (Oscar B.) Date: Thu, 19 Apr 2012 15:23:05 +0100 Subject: [Equest-users] CO sensors parking Message-ID: Hello guys. I'm trying to claim credits from using CO sensors with VAV fans in underground parking. Does any body know which is the bes way to do it. Many Thanks -------------- next part -------------- An HTML attachment was scrubbed... URL: From brianlo8 at yahoo.com Thu Apr 19 07:44:40 2012 From: brianlo8 at yahoo.com (Brian Lo) Date: Thu, 19 Apr 2012 07:44:40 -0700 (PDT) Subject: [Equest-users] Load Profiles Message-ID: <1334846680.77833.YahooMailNeo@web120306.mail.ne1.yahoo.com> Hi, I am having problems finding the loads for office equipment, motors and air compressors. In the office equipment loads and profile page, it asks for office Eq (w/sqft) for the office, corridor, ect. Am I supposed to be able to calculate this from building plans or is there a standard value I should be using? Thanks, Brian -------------- next part -------------- An HTML attachment was scrubbed... URL: From ablue at sustainable-solutions.ca Thu Apr 19 08:01:54 2012 From: ablue at sustainable-solutions.ca (Alex Blue) Date: Thu, 19 Apr 2012 08:01:54 -0700 Subject: [Equest-users] Load Profiles In-Reply-To: <1334846680.77833.YahooMailNeo@web120306.mail.ne1.yahoo.com> References: <1334846680.77833.YahooMailNeo@web120306.mail.ne1.yahoo.com> Message-ID: Hi Brian, It is possible to calculate it by counting workstations and finding some reasonable values online for the office equipment. ASHRAE also publishes some values you can use in the Handbook and in the pocket guide. Alex From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Lo Sent: April 19, 2012 9:45 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Load Profiles Hi, I am having problems finding the loads for office equipment, motors and air compressors. In the office equipment loads and profile page, it asks for office Eq (w/sqft) for the office, corridor, ect. Am I supposed to be able to calculate this from building plans or is there a standard value I should be using? Thanks, Brian -------------- next part -------------- An HTML attachment was scrubbed... URL: From danielk at arborus.ca Thu Apr 19 08:54:59 2012 From: danielk at arborus.ca (Daniel Knapp) Date: Thu, 19 Apr 2012 11:54:59 -0400 Subject: [Equest-users] CO sensors parking In-Reply-To: References: Message-ID: Hi Oscar, One way to do it would be to assume a run-time for the Proposed Case which could depend on some estimates of the CO produced in the parking garage. I know the Canadian standard is to use a run-time of 6 hours (2 morning, 2 mid-day and 2 evening) for ventilation control. One thing to keep in mind for LEED is that you will need to demonstrate that CO control is not standard practice in your jurisdiction. I know it's required by the building code here in Ontario, so it can't be claimed for credit. All the best, Dan ? Daniel Knapp, PhD, LEED? AP O+M danielk at arborus.ca Arborus Consulting Energy Strategies for the Built Environment www.arborus.ca 76 Chamberlain Avenue Ottawa, ON, K1S 1V9 Phone: (613) 234-7178 ext. 113 Fax: (613) 234-0740 On 2012-04-19, at 10:23 AM, Oscar B. wrote: > > Hello guys. > > I'm trying to claim credits from using CO sensors with VAV fans in underground parking. Does any body know which is the bes way to do it. > > Many Thanks > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From robbyoylear at gmail.com Thu Apr 19 09:27:09 2012 From: robbyoylear at gmail.com (Robby Oylear) Date: Thu, 19 Apr 2012 09:27:09 -0700 Subject: [Equest-users] CO sensors parking In-Reply-To: References: Message-ID: Oscar, For multifamily projects, the ENERGYSTAR Multifamily Highrise Simulation Guidelines includes a simple method of reducing scheduled operation of the exhaust fans. This is how it is typically done. Outside of multifamily, you will need to provide some additional backup documentation for reducing the operation of the fans. The guidelines can be found here: http://www.energystar.gov/ia/partners/bldrs_lenders_raters/downloads/mfhr/ENERGY_STAR_MFHR_Simulation_Guidelines_V1.0.pdf Refer to page 26 of the document. -Robby On Thu, Apr 19, 2012 at 8:54 AM, Daniel Knapp wrote: > Hi Oscar, > > One way to do it would be to assume a run-time for the Proposed Case which > could depend on some estimates of the CO produced in the parking garage. I > know the Canadian standard is to use a run-time of 6 hours (2 morning, 2 > mid-day and 2 evening) for ventilation control. > > One thing to keep in mind for LEED is that you will need to demonstrate > that CO control is not standard practice in your jurisdiction. I know it's > required by the building code here in Ontario, so it can't be claimed for > credit. > > All the best, > > Dan > > > > ? > Daniel Knapp, PhD, LEED? AP O+M > danielk at arborus.ca > > Arborus Consulting > Energy Strategies for the Built Environment > www.arborus.ca > 76 Chamberlain Avenue > Ottawa, ON, K1S 1V9 > Phone: (613) 234-7178 ext. 113 > Fax: (613) 234-0740 > > > > On 2012-04-19, at 10:23 AM, Oscar B. wrote: > > > Hello guys. > > > I'm trying to claim credits from using CO sensors with VAV fans in underground parking. Does any body know which is the bes way to do it. > > Many Thanks > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From tiwari.sambhav at gmail.com Thu Apr 19 21:55:00 2012 From: tiwari.sambhav at gmail.com (sambhav tiwari) Date: Fri, 20 Apr 2012 10:25:00 +0530 Subject: [Equest-users] Cooling design day Message-ID: Hi All, Where can we create cooling design day . Thanks Sambhav From cic at jci.com Fri Apr 20 00:24:20 2012 From: cic at jci.com (cic at jci.com) Date: Fri, 20 Apr 2012 12:54:20 +0530 Subject: [Equest-users] Compliance simulation errors In-Reply-To: References: Message-ID: An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/gif Size: 8803 bytes Desc: not available URL: From eee.javed at gmail.com Fri Apr 20 05:15:20 2012 From: eee.javed at gmail.com (Javed Iqbal) Date: Fri, 20 Apr 2012 05:15:20 -0700 Subject: [Equest-users] Cooling design day In-Reply-To: References: Message-ID: Hi, Please find following post on the same. Hope this Helps! "You can tell eQUEST to run multiple Design Days by setting the start day and the number of days in the Design Day Properties dialog box in the detailed interface (don't know about the wizard). For example I normally set the start day to 6/1 and the number of days to 120. That way it will cover all the solar angles from June - September combined with the ASHRAE Cooling DB / WB, and will use the heating/cooling design day schedules specified in the Week Schedules. I figure this should pretty much cover it, although as Carol said there is usually a peak in the weather file that exceeds the ASHRAE conditions." ( http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2008-September/000365.html) Before equest will use the Design Day information in the schedules you need to setup actual design days for the simulation to use. You need to do this in the *detailed edit under the Project & Site tab*. You need to create both a heating and cooling design day and then input the desired temperature extremes and duration that you wish to simulate. Reference the climate design data in the ASHRAE Fundamentals Handbook for your location. Once you create the design days equest will use them for equipment sizing rather than the peak heating & cooling loads calculated from the TMY weather data. (http://www.gard.com/ml/bldg-sim-archive/msg04540.html) Thanks On Thu, Apr 19, 2012 at 9:55 PM, sambhav tiwari wrote: > Hi All, > Where can we create cooling design day . > > > Thanks > Sambhav > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -- Javed Iqbal, LEED AP, CEA Energy Analyst -------------- next part -------------- An HTML attachment was scrubbed... URL: From bjowkar at fluentgroup.com Fri Apr 20 11:24:36 2012 From: bjowkar at fluentgroup.com (Behnam Jowkar) Date: Fri, 20 Apr 2012 18:24:36 +0000 Subject: [Equest-users] Modelling an exhaust fan Message-ID: Hi Guys, I am modelling an AHU with exhaust fan, which comes on only during economizing, but I can not figure out how to properly model it in eQuest. Can anyone help me with this? Regards, -- Behnam Jowkar, MASc Energy Services Associate Fluent Group Consulting Engineers Inc. 295A Broadway Avenue, Second Floor P.O. Box 188, Orangeville, Ontario, L9W 2Z6 t 888.358.3683 x704 f 866.620.7502 c 519.938.7657 www.fluentgroup.com -------------- next part -------------- An HTML attachment was scrubbed... URL: From slv3sat at gmail.com Fri Apr 20 12:04:36 2012 From: slv3sat at gmail.com (R B) Date: Fri, 20 Apr 2012 14:04:36 -0500 Subject: [Equest-users] Modelling an exhaust fan In-Reply-To: References: Message-ID: Set is as relief fan in the systems-fan tab -Rohini On Fri, Apr 20, 2012 at 1:24 PM, Behnam Jowkar wrote: > Hi Guys, > > I am modelling an AHU with exhaust fan, which comes on only during > economizing, but I can not figure out how to properly model it in eQuest. > Can anyone help me with this? > > Regards, > > -- > *Behnam Jowkar, MASc > *Energy Services Associate > > Fluent Group Consulting Engineers Inc. > 295A Broadway Avenue, Second Floor > P.O. Box 188, Orangeville, Ontario, L9W 2Z6 > *t* 888.358.3683 x704 *f* 866.620.7502 *c* 519.938.7657 > www.fluentgroup.com > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From 546751190 at qq.com Sat Apr 21 00:09:14 2012 From: 546751190 at qq.com (=?gbk?B?0rvStrHi1ts=?=) Date: Sat, 21 Apr 2012 15:09:14 +0800 Subject: [Equest-users] how to decide the effficency of HVAC equipment Message-ID: Dear all When using appendix G of ASHRAE 90.1-2007 to build baseline, If the baseline system is system 3 (PSZ-AC) , 4 (PSZ-HP) or 5 (Packaged VAV with reheat) ,which table in ASHRAE90.1-2007 should be used to decide the Equipment efficiency separately? Table 6.8.1A or 6.8.1D? Thank you for your help Aarron -------------- next part -------------- An HTML attachment was scrubbed... URL: From charu_0011 at yahoo.com Sat Apr 21 17:44:12 2012 From: charu_0011 at yahoo.com (sharma charu) Date: Sat, 21 Apr 2012 17:44:12 -0700 (PDT) Subject: [Equest-users] (no subject) In-Reply-To: References: Message-ID: <1335055452.44582.YahooMailNeo@web114613.mail.gq1.yahoo.com> ? Hey, ??Keeping all the parameters same,so as to check the differences in energy consumption(sensible cooling load& peak load) between different roofs (by feeding different R values), not much variation is shown(which it should)! ? ? Files attached ? ? Results are as follows ? ? R typical grass=4.755 ? ? R typical shrubs= 12.5699 ? ? R typical trees= 8.1033 ? ?? ? Annual Energy Peak Demand ? ? ? Type Energy Units Demand Units ? ? typical grass? ? ? ? ? ? Elec (utility) 186903 KWH 72.9168 KW ? ? ? Elec (utility) 186903 KWH 72.9168 KW ? ? typical trees? ? ? ? ? ? Elec (utility) 187059 KWH 73.0736 KW ? ? ? Elec (utility) 187059 KWH 73.0736 KW ? ? typical shrubs? ? ? ? ? ? Elec (utility) 187095 KWH 73.0925 KW ? ? ? Elec (utility) 187095 KWH 73.0925 KW ? ? Please help! Urgent.. -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: typical-grass.pd2 Type: application/octet-stream Size: 15 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: typical+trees.pd2 Type: application/octet-stream Size: 6618 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: typical+shrubs.pd2 Type: application/octet-stream Size: 6527 bytes Desc: not available URL: From dave.weigel at thewattdoctors.com Sun Apr 22 06:32:25 2012 From: dave.weigel at thewattdoctors.com (Dave Weigel) Date: Sun, 22 Apr 2012 09:32:25 -0400 Subject: [Equest-users] how to decide the effficency of HVAC equipment In-Reply-To: References: Message-ID: <86CF482133924991BC78C31E391C5AD3@DaveHPDesktop> 6.8.1A is appropriate for packaged systems. The other table (6.8.1D) applies to single-room air conditioners. Best to you, Dave From: ???? Sent: Saturday, April 21, 2012 3:09 AM To: equest-users Subject: [Equest-users] how to decide the effficency of HVAC equipment Dear all When using appendix G of ASHRAE 90.1-2007 to build baseline, If the baseline system is system 3 (PSZ-AC) , 4 (PSZ-HP) or 5 (Packaged VAV with reheat) ,which table in ASHRAE90.1-2007 should be used to decide the Equipment efficiency separately? Table 6.8.1A or 6.8.1D? Thank you for your help Aarron -------------- next part -------------- An HTML attachment was scrubbed... URL: From tiwari.sambhav at gmail.com Sun Apr 22 21:25:40 2012 From: tiwari.sambhav at gmail.com (sambhav tiwari) Date: Mon, 23 Apr 2012 09:55:40 +0530 Subject: [Equest-users] ERV Message-ID: Hi All, Whether the Energy recovery wheel should only reduce the cooling kwh or fan kwh also along with cooling kwh . as far as cooling energy is concern it is sure it will come down but i am not sure about fan energy effect by ERV. Thanks Sambhav From poleary1969 at gmail.com Mon Apr 23 04:50:09 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Mon, 23 Apr 2012 04:50:09 -0700 Subject: [Equest-users] ERV In-Reply-To: References: Message-ID: <4F9541F1.8090905@gmail.com> depends on how you control the erv. an uncontrolled erv (i.e. erv fans on all the time when unit supply fan is on) will probably use more fan energy than is saved in cooling or heating energy. at a minimum setting the erv fans to operate based on a delta t w/the outdoor air is required to demonstrate erv energy savings. or delta enthalpy depending on your wheel type. if you look at the march issue of ashrae journal it has an article on how to control a total enthalpy wheel and save money - and it makes the point of having the fans (supply/exhaust) and wheel run all the time can/will add energy cost to your building. On 4/22/12 9:25 PM, sambhav tiwari wrote: > Hi All, > Whether the Energy recovery wheel should only reduce the > cooling kwh or fan kwh also along with cooling kwh . as far as cooling > energy is concern it is sure it will come down but i am not sure about > fan energy effect by ERV. > > > Thanks > Sambhav > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > From dkim96 at illinois.edu Mon Apr 23 09:00:12 2012 From: dkim96 at illinois.edu (Kim, Donghwa) Date: Mon, 23 Apr 2012 16:00:12 +0000 Subject: [Equest-users] eQuest Weather data for 2011 Message-ID: <8E454C47D2CAF44496D4C954AC8C2E580CD5937E@CHIMBX6.ad.uillinois.edu> Good Morning, I am trying to find the 2011 weather data for Illinois(near Chicago area), but I can find only 2008 data from http://doe2.com/index_wth.html . Is there any way I can find the 2011 weather data? Thanks in advance! Kim From jonabroadway at gmail.com Mon Apr 23 08:52:20 2012 From: jonabroadway at gmail.com (Jon Broadway) Date: Mon, 23 Apr 2012 10:52:20 -0500 Subject: [Equest-users] CO sensors parking In-Reply-To: References: Message-ID: Oscar: I agree that the key issue for you is determining if your 'base building" requires CO sensors.(based on local codes). If required, you can't get credit, if not required, that opens the possibility to seeking credit. Good luck, Jon Broadway From: Oscar B. [mailto:oscar664 at hotmail.com] Sent: Thursday, April 19, 2012 9:23 AM To: eQuest Users Subject: [Equest-users] CO sensors parking Hello guys. I'm trying to claim credits from using CO sensors with VAV fans in underground parking. Does any body know which is the bes way to do it. Many Thanks -------------- next part -------------- An HTML attachment was scrubbed... URL: From thomasv at iit.edu Mon Apr 23 09:46:22 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Mon, 23 Apr 2012 11:46:22 -0500 Subject: [Equest-users] eQuest Weather data for 2011 In-Reply-To: <8E454C47D2CAF44496D4C954AC8C2E580CD5937E@CHIMBX6.ad.uillinois.edu> References: <8E454C47D2CAF44496D4C954AC8C2E580CD5937E@CHIMBX6.ad.uillinois.edu> Message-ID: Instructions http://bepan.info/weather Open 9 - Weather _NCDC.tpe to DOE2.bin to Tables-Charts ----- Original Message ----- From: "Kim, Donghwa" Date: Monday, April 23, 2012 11:00 am Subject: [Equest-users] eQuest Weather data for 2011 > Good Morning, > > I am trying to find the 2011 weather data for Illinois(near > Chicago area), but I can find only 2008 data from > http://doe2.com/index_wth.html . Is there any way I can find the > 2011 weather data? > > Thanks in advance! > Kim > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From obuchely at ses-ingenieria.com Mon Apr 23 09:50:01 2012 From: obuchely at ses-ingenieria.com (Oscar Buchely L.) Date: Mon, 23 Apr 2012 11:50:01 -0500 Subject: [Equest-users] how to decide the effficency of HVAC equipment In-Reply-To: <86CF482133924991BC78C31E391C5AD3@DaveHPDesktop> References: <86CF482133924991BC78C31E391C5AD3@DaveHPDesktop> Message-ID: <4F958839.5050501@ses-ingenieria.com> I have a similar question, If my system is 2 (PTHP) can I use table 6.8.1B or 6.8.1D and why? thanks Oscar. On 22/04/2012 08:32 a.m., Dave Weigel wrote: > 6.8.1A is appropriate for packaged systems. > The other table (6.8.1D) applies to single-room air conditioners. > Best to you, > Dave > *From:* ???? > *Sent:* Saturday, April 21, 2012 3:09 AM > *To:* equest-users > *Subject:* [Equest-users] how to decide the effficency of HVAC equipment > > Dear all > > When using appendix G of ASHRAE 90.1-2007 to build baseline, If the > baseline system is system 3 (PSZ-AC) , 4 (PSZ-HP) or 5 (Packaged VAV > with reheat) ,which table in ASHRAE90.1-2007 should be used to decide > the Equipment efficiency separately? Table 6.8.1A or 6.8.1D? > > Thank you for your help > > Aarron > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From mclough at kme-inc.com Mon Apr 23 11:59:22 2012 From: mclough at kme-inc.com (Matt Clough) Date: Mon, 23 Apr 2012 18:59:22 +0000 Subject: [Equest-users] EEM vs. new model Message-ID: <6F3694F71FCF0D4A89F7337180F2049E08514988@KME3.kme.local> Salutations eQuesters, I'm doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Mon Apr 23 14:39:35 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 23 Apr 2012 21:39:35 +0000 Subject: [Equest-users] EEM vs. new model In-Reply-To: <6F3694F71FCF0D4A89F7337180F2049E08514988@KME3.kme.local> References: <6F3694F71FCF0D4A89F7337180F2049E08514988@KME3.kme.local> Message-ID: By context, I gather by 'baseline' you mean something other than your proposed design, such as an 90.1 Appendix G baseline or similar. If that's the case, my general advice is that you should much more heavily weight the comparative results using your "actual/proposed" model. A baseline per above inherently diverges from the actual building materials, lighting power densities, solar load shading, and so forth. It's not the same building. Best to choose systems that most efficiently handle your actual project. Don't get too hung up what works best for an imaginary building ;). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Clough Sent: Monday, April 23, 2012 1:59 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] EEM vs. new model Salutations eQuesters, I'm doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From xs2144 at gmail.com Mon Apr 23 23:54:20 2012 From: xs2144 at gmail.com (xiaoyang shi) Date: Tue, 24 Apr 2012 02:54:20 -0400 Subject: [Equest-users] infiltration rate Message-ID: Hi guys, Could I ask what is the about infiltration rate of old townhouse in NYC? Where could I find the standard? 0.2cfm/ft2? Is it correct? Thanks Yang -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Tue Apr 24 00:31:35 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Tue, 24 Apr 2012 00:31:35 -0700 Subject: [Equest-users] infiltration rate In-Reply-To: References: Message-ID: .35 ACH is the BPI standard, any tighter and mechanical ventilation is required.. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Mon, Apr 23, 2012 at 11:54 PM, xiaoyang shi wrote: > Hi guys, > > Could I ask what is the about infiltration rate of old townhouse in NYC? > Where could I find the standard? > > 0.2cfm/ft2? Is it correct? > > Thanks > > Yang > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From mclough at kme-inc.com Tue Apr 24 05:36:52 2012 From: mclough at kme-inc.com (Matt Clough) Date: Tue, 24 Apr 2012 12:36:52 +0000 Subject: [Equest-users] EEM vs. new model In-Reply-To: Message-ID: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> I suppose I should have been more specific in my description: By baseline I mean the proposed design. So the program outputs 2 sim files - the base(proposed, CHW) case and the iterated (DX) case We want to use eQuest to validate the system choice on this particular project. This is work that was started before I joined, but I have been selected to try and use eQuest to compare the performance of a chilled water system and a DX system. I'm not the most experienced energy modeler, but it seems like a task that would be a good application for eQuest. My approach was to simulate the energy consumption of a building that is similar to the actual design in orientation, shape, and square footage. I initially built the model in the SD wizard, using most of the default values (building envelope, activity usage, etc.), autosize the equipment, and use the EEM to compare the two systems. The idea was that when the building construction and geometry are equal, we can look at the relative energy consumption of the two systems. This initial simulation reported that the DX system would be more efficient, which is not what I had expected based on the design that had been selected. So I figured that maybe my model was too generic, too simple. I created zones based on the plans, and made the geometry more representative of the actual building. These changes produced reports that suggest the chilled water system is more efficient than the DX. I realized that the EEM was incorrectly modeling the change - it was treating the chilled water system as having all 8 air handlers, but was modeling the DX system as one AHU. So I created a duplicate model that has a DX system (autosized and using equest defaults). The comparison of these two models suggests the DX system is slightly more efficient. Unfortunately, my lack of experience makes me doubt the validity of this comparison - especially considering that the engineers selected a chilled water system for this project. So I suppose my questions are: Does my approach seem valid? Is this an appropriate use of the software? After taking some time to write this note, and with a little rest, I wonder if comparing the proposed design to an ASHRAE 90.1 baseline would have been a better approach. Regards, Matt Clough ________________________________ From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 23, 2012 3:40 PM To: Matt Clough; equest-users at lists.onebuilding.org Subject: RE: EEM vs. new model By context, I gather by 'baseline' you mean something other than your proposed design, such as an 90.1 Appendix G baseline or similar. If that's the case, my general advice is that you should much more heavily weight the comparative results using your "actual/proposed" model. A baseline per above inherently diverges from the actual building materials, lighting power densities, solar load shading, and so forth. It's not the same building. Best to choose systems that most efficiently handle your actual project. Don't get too hung up what works best for an imaginary building ;). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Clough Sent: Monday, April 23, 2012 1:59 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] EEM vs. new model Salutations eQuesters, I'm doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From ncaton at smithboucher.com Tue Apr 24 08:01:17 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 24 Apr 2012 15:01:17 +0000 Subject: [Equest-users] EEM vs. new model In-Reply-To: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> References: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> Message-ID: Hi Matt! If your primary goal is to compare the relative performance of two systems on the same building, then you can rest assured you've made fine decisions so far. That you're simultaneously tasked with "validating" one choice over another might complicate things in presentation of your results - it depends on how the cookies crumble. More later. eQuest is a capable tool to this end, but I might have cautioned you at the outset that eQuest can quickly become unwieldy for "a simple comparison" when trying to compare certain system types, especially for newer/intermediate users. That said, you are clearly well-invested into this model, and why would anyone want to miss a learning opportunity, right =)? General rule: A more representative model will always produce a 'better' result - the corollary is that 'better' is not always what you're hoping for. "Degree-of-accuracy" is always a balancing act for any model - it's clear you're taking an active role in deciding when/how to improve the model's degree of detail, however. That's enough to satisfy me. So long as you personally feel the model is "representative enough," that's the key litmus test when you're the one presenting the results ;). I would not suggest stopping and building a 90.1 baseline model provided with this extra context, but you could use 90.1 as a broader reference to ensure you are making a fair comparison. For example, 90.1 Appendix G has a section discussing unmet hours and establishes a threshold for both the (90.1) baseline and proposed models. Have you made a similar check between your chiller and DX models to ensure they're on similar footing? I almost always build my models from DD wizards instead of SD so my usual workflow may produce different "normal fixes," but I commonly need to spend extra time reviewing the hydronic inputs in detailed mode to ensure any chiller system is being correctly modeled. Give your chiller, pump, and loop inputs a good scour, particularly pump operation/scheduling inputs. You mentioned also changing the quantity of airside systems for the DX model - it might be worthwhile to review the schedules applicable to the consolidated system to ensure its operating as a single large AHU would. When all is said and done if you still feel uncomfortable with your inputs, I've often found it productive to have the responsible mechanical designer scan through typical waterside/airside inputs alongside me to identify anything that appears off. I have found pulling other designers in is a good QC practice for all skill levels where the modeler didn't do all the work him/herself. I find it easiest to plan on missing some nuances along the way (Murphy's law), and allow those most intimate with the design to collaborate with me to pick any loose threads up. So full-circle... regarding your 'intended' results: Accept that the "right" answer can ultimately swing either way. Whenever performing a comparative study, keep in mind all such results are built on unknowns/assumptions. Where the results are close, it's not uncommon to conclude there are multiple right answers. ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: Matt Clough [mailto:mclough at kme-inc.com] Sent: Tuesday, April 24, 2012 7:37 AM To: Nick Caton; equest-users at lists.onebuilding.org Subject: RE: EEM vs. new model I suppose I should have been more specific in my description: By baseline I mean the proposed design. So the program outputs 2 sim files - the base(proposed, CHW) case and the iterated (DX) case We want to use eQuest to validate the system choice on this particular project. This is work that was started before I joined, but I have been selected to try and use eQuest to compare the performance of a chilled water system and a DX system. I'm not the most experienced energy modeler, but it seems like a task that would be a good application for eQuest. My approach was to simulate the energy consumption of a building that is similar to the actual design in orientation, shape, and square footage. I initially built the model in the SD wizard, using most of the default values (building envelope, activity usage, etc.), autosize the equipment, and use the EEM to compare the two systems. The idea was that when the building construction and geometry are equal, we can look at the relative energy consumption of the two systems. This initial simulation reported that the DX system would be more efficient, which is not what I had expected based on the design that had been selected. So I figured that maybe my model was too generic, too simple. I created zones based on the plans, and made the geometry more representative of the actual building. These changes produced reports that suggest the chilled water system is more efficient than the DX. I realized that the EEM was incorrectly modeling the change - it was treating the chilled water system as having all 8 air handlers, but was modeling the DX system as one AHU. So I created a duplicate model that has a DX system (autosized and using equest defaults). The comparison of these two models suggests the DX system is slightly more efficient. Unfortunately, my lack of experience makes me doubt the validity of this comparison - especially considering that the engineers selected a chilled water system for this project. So I suppose my questions are: Does my approach seem valid? Is this an appropriate use of the software? After taking some time to write this note, and with a little rest, I wonder if comparing the proposed design to an ASHRAE 90.1 baseline would have been a better approach. Regards, Matt Clough ________________________________ From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 23, 2012 3:40 PM To: Matt Clough; equest-users at lists.onebuilding.org Subject: RE: EEM vs. new model By context, I gather by 'baseline' you mean something other than your proposed design, such as an 90.1 Appendix G baseline or similar. If that's the case, my general advice is that you should much more heavily weight the comparative results using your "actual/proposed" model. A baseline per above inherently diverges from the actual building materials, lighting power densities, solar load shading, and so forth. It's not the same building. Best to choose systems that most efficiently handle your actual project. Don't get too hung up what works best for an imaginary building ;). ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Clough Sent: Monday, April 23, 2012 1:59 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] EEM vs. new model Salutations eQuesters, I'm doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From ramana.koti at gmail.com Tue Apr 24 09:23:04 2012 From: ramana.koti at gmail.com (Ramana Koti) Date: Tue, 24 Apr 2012 12:23:04 -0400 Subject: [Equest-users] outside air flow during unoccupied/setback hours Message-ID: Dear All, One of the LEED review comments on a university building project I'm working on suggests to verify that all systems in baseline and proposed models contain zero outside air flow when fans are cycled on to meet setback temperatures during unoccupied hours. What is the best way to go about verifying this? In the 'Hourly Report Block' options under a system, I find 'Hourly summed zone OA CFM for DCV calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation (cfm/cf/). Is one or both of these options under an hourly report, the way to go or is there a better way of doing it? Thanks, Ramana. -------------- next part -------------- An HTML attachment was scrubbed... URL: From bfountain at greensim.com Tue Apr 24 09:24:42 2012 From: bfountain at greensim.com (Brian Fountain) Date: Tue, 24 Apr 2012 12:24:42 -0400 Subject: [Equest-users] FINAL WEEK: 2012 eSim Building Simulation Conference - Register Now! In-Reply-To: References: Message-ID: <026901cd2236$c37a4140$4a6ec3c0$@greensim.com> ONE WEEK UNTIL THE CONFERENCE - eSim Building Simulation Conference 1-4 May 2012. http://esim.ca Complete programme with abstracts and technical session speaker schedule is on the website. The 2012 eSim Building Simulation Conference in Halifax, Canada is hosted by Dalhousie University and features an exciting slate of speakers, social events, workshops, and tours. Major themes include: building performance modeling, innovative technology control methods, simulations tools, and quality control approaches. We invite you to explore our new website which contains all the information http://esim.ca . image.png Forty two full papers will be presented forming a full two-days of parallel technical sessions (a detailed schedule is available under Conference Information at http://esim.ca ). Several exciting features of the eSim conference are (complete descriptions at http://esim.ca/): . Conference venue is the Pier 21 Immigration Museum on the Halifax Waterfront where over a million immigrants entered Canada. . Keynote speakers are Christoph Reinhart (MIT Architecture) and Mark Riley (former Sustainable Buildings Director at CanmetEnergy). . Technical tour of the NSCC Centre for the Built Environment (LEED Silver) . Social events at the Seaport Farmers Market (LEED Platinum) and banquet at the historic Waterfront Warehouse. . Half and full-day workshops on modeling and simulation, communities, and certification tools. . Reduced rate accommodations at the Westin Hotel are within a 10 minute walk from all events. Schedule overview of eSim 2012: image.png Keynote speakers of eSim 2012: Christoph Reinhart is an Associate Professor of Building Technology in Architecture at MIT. He has built design tools such as DIVA-for-Rhino and Daysim. Dr. Reinhart's address is titled Building Performance Simulation - >From Evaluating Performance To Suggesting New Forms. Mark Riley was the S&T Director of the Sustainable Buildings and Communities Group within CanmetENERGY. He now consults on projects related to sustainable housing, buildings and communities. Mr. Riley's address is titled Housing for a Changing World: A Sustainable Housing Technology Roadmap for Canada. Workshop overview of eSim 2012: We have 8 great workshops on a variety of building simulation software and methods. image.png Partners and sponsors of eSim 2012: image.png About the eSim 2012 Conference: eSim brings together professionals, academics and students interested in building performance simulation advancements and applications. The 2012 conference is hosted by Dalhousie University in collaboration with Natural Resources Canada. It will be held in the beautiful port city of Halifax, Canada on May 2 and 3, 2012, with workshops held one day pre and post the conference. Themes of the eSim conference surround the modeling and simulation of processes and performance of the built environment. This includes all aspects of building simulation ranging from the simulators themselves to results of unique and innovative models. Coverage includes modeling physical processes (energy, occupant comfort, daylighting, etc.), control methods, community energy systems, building simulator tools, use of tools with building code/incentive programs, and performance visualization/validation. We hope you will join us for the 2012 eSim Building Simulation Conference on 1-4 May. We invite you to explore our website at http://esim.ca/. Dr. Lukas Swan and Prof. Richard Kroeker Dalhousie University - Faculties of Engineering and Architecture Halifax, NS Canada _____ -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 64791 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 111338 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 50521 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/png Size: 150774 bytes Desc: not available URL: From dse at grummanbutkus.com Tue Apr 24 09:35:20 2012 From: dse at grummanbutkus.com (David Eldridge) Date: Tue, 24 Apr 2012 11:35:20 -0500 Subject: [Equest-users] EEM vs. new model In-Reply-To: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> References: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> Message-ID: <3eed67866c98f3a3c29f5ca197ce9c57@mail.gmail.com> eQUEST?s defaults will be important here for pressure drop in the two systems, ability to modulate airflow or chilled water flow, ability to economize (although Google shows your company near the Gulf, so if this is a local auto dealer then maybe economizer won?t be important). The use of the chiller system?s cooling efficiency and pump power will be important since these are known, and may vary from the wizard?s suggestion. You?ll also need to make sure the DX system efficiency and fan power is realistic. The part-load performance of the system could also be important if the hours for the shop and show room are different ? this could be a case where two or more right-sized DX systems may be a better match than one chiller, depending on the magnitude for the loads and if the zones have wildly different hours of operation. My suggestion would be to set eQUEST aside for a half hour, and just run through a table for the fan power, pump power, and cooling efficiency for each of the two cases and see if the answer jumps out at you. If you get pointed strongly in one direction, then review the eQuest files more closely to be sure you are capturing all of the part-load effects. Regarding your ASHRAE 90.1 baseline suggestions, that might be your best ?baseline? and then compare the proposed CHW and an enhanced DX system against that, but shouldn?t be necessary other than as Nick suggests for a QA reference. David * * David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP *Grumman/Butkus Associates* * * *From:* equest-users-bounces at lists.onebuilding.org [mailto: equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Matt Clough *Sent:* Tuesday, April 24, 2012 7:37 AM *To:* Nick Caton; equest-users at lists.onebuilding.org *Subject:* Re: [Equest-users] EEM vs. new model I suppose I should have been more specific in my description: By baseline I mean the proposed design. So the program outputs 2 sim files ? the base(proposed, CHW) case and the iterated (DX) case We want to use eQuest to validate the system choice on this particular project. This is work that was started before I joined, but I have been selected to try and use eQuest to compare the performance of a chilled water system and a DX system. I?m not the most experienced energy modeler, but it seems like a task that would be a good application for eQuest. My approach was to simulate the energy consumption of a building that is similar to the actual design in orientation, shape, and square footage. I initially built the model in the SD wizard, using most of the default values (building envelope, activity usage, etc.), autosize the equipment, and use the EEM to compare the two systems. The idea was that when the building construction and geometry are equal, we can look at the relative energy consumption of the two systems. This initial simulation reported that the DX system would be more efficient, which is not what I had expected based on the design that had been selected. So I figured that maybe my model was too generic, too simple. I created zones based on the plans, and made the geometry more representative of the actual building. These changes produced reports that suggest the chilled water system is more efficient than the DX. I realized that the EEM was incorrectly modeling the change ? it was treating the chilled water system as having all 8 air handlers, but was modeling the DX system as one AHU. So I created a duplicate model that has a DX system (autosized and using equest defaults). The comparison of these two models suggests the DX system is slightly more efficient. Unfortunately, my lack of experience makes me doubt the validity of this comparison ? especially considering that the engineers selected a chilled water system for this project. So I suppose my questions are: Does my approach seem valid? Is this an appropriate use of the software? After taking some time to write this note, and with a little rest, I wonder if comparing the proposed design to an ASHRAE 90.1 baseline would have been a better approach. Regards, Matt Clough ------------------------------ *From:* Nick Caton [mailto:ncaton at smithboucher.com] *Sent:* Monday, April 23, 2012 3:40 PM *To:* Matt Clough; equest-users at lists.onebuilding.org *Subject:* RE: EEM vs. new model By context, I gather by ?baseline? you mean something other than your proposed design, such as an 90.1 Appendix G baseline or similar. If that?s the case, my general advice is that you should *much* more heavily weight the comparative results using your ?actual/proposed? model. A baseline per above inherently diverges from the actual building materials, lighting power densities, solar load shading, and so forth. It?s not the same building. Best to choose systems that most efficiently handle your actual project. Don?t get too hung up what works best for an imaginary building ;). ~Nick [image: cid:489575314 at 22072009-0ABB]** * * *NICK CATON, P.E.* SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com* * *From:* equest-users-bounces at lists.onebuilding.org [mailto: equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Matt Clough *Sent:* Monday, April 23, 2012 1:59 PM *To:* equest-users at lists.onebuilding.org *Subject:* [Equest-users] EEM vs. new model Salutations eQuesters, I?m doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: From slv3sat at gmail.com Tue Apr 24 09:54:25 2012 From: slv3sat at gmail.com (R B) Date: Tue, 24 Apr 2012 11:54:25 -0500 Subject: [Equest-users] outside air flow during unoccupied/setback hours In-Reply-To: References: Message-ID: I normally have a min sch specified at the zone level - 0 for unoccupied hours and -999 for other hours that takes care of this comment. There is an hourly report for fan coming on during night cycle flag (or something similar). If you do not have the fan coming on or do not have the night cycle control, you should be ok. You can also look at the hourly report for OA ratio and whether fan is on/off during the unoccupied time. -Rohini On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti wrote: > Dear All, > > One of the LEED review comments on a university building project I'm > working on suggests to verify that all systems in baseline and proposed > models contain zero outside air flow when fans are cycled on to meet > setback temperatures during unoccupied hours. > > What is the best way to go about verifying this? In the 'Hourly Report > Block' options under a system, I find 'Hourly summed zone OA CFM for DCV > calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation > (cfm/cf/). Is one or both of these options under an hourly report, the way > to go or is there a better way of doing it? > > Thanks, > Ramana. > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Tue Apr 24 10:07:57 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Tue, 24 Apr 2012 17:07:57 +0000 Subject: [Equest-users] infiltration rate In-Reply-To: References: Message-ID: For an "old townhouse," I think you may want to reference the ASHRAE fundamentals table for residential constructions (Fundamentals 2001, Ch28, Table 7)... they surveyed a bunch of homes that were up to a few decades old to come up with a table that shows varying ACH rates, for "tight" to "loose" construction, varying with the OADT. The tightest value given is 0.41. Again this isn't a standard but rather based on real-world measurements. A very good (and long) discussion thread is in the equest-users archives discussing alternate infiltration resources as well: thread title was "Basic stuff - Infiltration" ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Tuesday, April 24, 2012 2:32 AM To: xiaoyang shi Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] infiltration rate .35 ACH is the BPI standard, any tighter and mechanical ventilation is required.. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Mon, Apr 23, 2012 at 11:54 PM, xiaoyang shi > wrote: Hi guys, Could I ask what is the about infiltration rate of old townhouse in NYC? Where could I find the standard? 0.2cfm/ft2? Is it correct? Thanks Yang _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From jeremiah at cleantechanalytics.com Tue Apr 24 12:46:54 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Tue, 24 Apr 2012 12:46:54 -0700 Subject: [Equest-users] infiltration rate In-Reply-To: References: Message-ID: When doing blower door tests I have found ACH 2 or 3 to be commonplace. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Tue, Apr 24, 2012 at 10:07 AM, Nick Caton wrote: > For an ?old townhouse,? I think you may want to reference the ASHRAE > fundamentals table for residential constructions (Fundamentals 2001, Ch28, > Table 7)? they surveyed a bunch of homes that were up to a few decades old > to come up with a table that shows varying ACH rates, for ?tight? to > ?loose? construction, varying with the OADT. *The tightest value given > is 0.41*. Again this isn?t a standard but rather based on real-world > measurements.**** > > ** ** > > A very good (and long) discussion thread is in the equest-users archives > discussing alternate infiltration resources as well: thread title was > ?Basic stuff ? Infiltration?**** > > ** ** > > ~Nick**** > > ** ** > > [image: cid:489575314 at 22072009-0ABB]** > > * * > > *NICK CATON, P.E.*** > > SENIOR ENGINEER**** > > ** ** > > Smith & Boucher Engineers**** > > 25501 west valley parkway, suite 200**** > > olathe, ks 66061**** > > direct 913.344.0036**** > > fax 913.345.0617**** > > www.smithboucher.com* ***** > > ** ** > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *CleanTech > Analytics > *Sent:* Tuesday, April 24, 2012 2:32 AM > *To:* xiaoyang shi > *Cc:* equest-users at lists.onebuilding.org > *Subject:* Re: [Equest-users] infiltration rate**** > > ** ** > > .35 ACH is the BPI standard, any tighter and mechanical ventilation is > required..**** > > > **** > > *Jeremiah D. Crossett***** > > *CleanTech Analytics***** > > *503-688-8951***** > > *www.cleantechanalytics.com* **** > > ** ** > > **** > > *This document may contain valuable information proprietary to CleanTech > Analytics which is private and confidential. It may not be shared, copied, > stored or transmitted in any form without the prior written consent of > CleanTech Analytics*** > > ** ** > > ** ** > > On Mon, Apr 23, 2012 at 11:54 PM, xiaoyang shi wrote:** > ** > > Hi guys,**** > > ** ** > > Could I ask what is the about infiltration rate of old townhouse in NYC? > Where could I find the standard?**** > > ** ** > > 0.2cfm/ft2? Is it correct?**** > > ** ** > > Thanks**** > > ** ** > > Yang**** > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG**** > > ** ** > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: From poleary1969 at gmail.com Tue Apr 24 16:52:15 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Tue, 24 Apr 2012 16:52:15 -0700 Subject: [Equest-users] outside air flow during unoccupied/setback hours In-Reply-To: References: Message-ID: <4F973CAF.90205@gmail.com> is this a leed 2.2 or 3.0 project? i'm guessing, without looking in my leed manuals, this is a usgbc requirement for at least 2.2. for leed 3, 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically states the "hvac fans that provide outdoor air for ventilation shall run continuously whenever spaces are occupied and shall be cycled on and off to meet heating and cooling loads during unoccupied hours." 90.1-2004 doesn't specify fans specifically for outdoor air for ventilation, it just says hvac fans - which is the same as the system supply fan in a non-doas/economizer capable of completely closing the outdoor air damper system so the outdoor air can't be shut off. so the comment is contrary to the 90.1-2007 (and/or 2004 depending on systems) simulation requirement. the 90.1-2004 user's manual appendix g section doesn't address the scheduling for hvac fans during unoccupied modes. On 4/24/12 9:54 AM, R B wrote: > I normally have a min sch specified at the zone level - 0 for > unoccupied hours and -999 for other hours that takes care of this comment. > There is an hourly report for fan coming on during night cycle flag > (or something similar). If you do not have the fan coming on or do not > have the night cycle control, you should be ok. You can also look at > the hourly report for OA ratio and whether fan is on/off during the > unoccupied time. > -Rohini > > > On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti > wrote: > > Dear All, > One of the LEED review comments on a university building project > I'm working on suggests to verify that all systems in baseline and > proposed models contain zero outside air flow when fans are cycled > on to meet setback temperatures during unoccupied hours. > What is the best way to go about verifying this? In the 'Hourly > Report Block' options under a system, I find 'Hourly summed zone > OA CFM for DCV calculation (cfm)' and 'Hourly max zone OA/total > flow for DCV calculation (cfm/cf/). Is one or both of these > options under an hourly report, the way to go or is there a better > way of doing it? > Thanks, > Ramana. > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > > > > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From 546751190 at qq.com Tue Apr 24 21:25:58 2012 From: 546751190 at qq.com (=?gb18030?B?QWFyb24=?=) Date: Wed, 25 Apr 2012 12:25:58 +0800 Subject: [Equest-users] how to simulate PTAC reasonably Message-ID: Dear all If baseline is system 1 (PTAC), the equipment is decided according to table 6.8.1D which is for the whole equipment, while 90.1 Manual says the supply fan energy (0.3W/cfm for system 1&2) should be separate from cooling system energy, shown as the picture below About how to calculate the COP except supply fan energy, the manual also gives the equation as shown below: I try to find the Cooling Capacity for every PTAC system in SV-A report and calculate the COP for the cooling section(Compressor and condenser), while when I input the cooling EIP (1/COP) in cooling uni and 0.3W/cfm for supply fan, the energy consumption is much higher than inputting the whole EER for the cooling EIR and 0 W/cfm for the supply fan before. From the energy breakdown contrast, what surprises me is that the energy for cooling is more than before. When I try to change the fan delta t from 0.93 to 0 and find the cooling energy is decreasing than inputting the whole EER, but the sum of cooling and fan is still more than inputting the whole EER , have anyone met the same confusion before and tell me the reason and how to simulate PTAC reasonably. Thanks a lot -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: application/octet-stream Size: 28229 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: application/octet-stream Size: 72037 bytes Desc: not available URL: From tiwari.sambhav at gmail.com Tue Apr 24 21:55:41 2012 From: tiwari.sambhav at gmail.com (sambhav tiwari) Date: Wed, 25 Apr 2012 10:25:41 +0530 Subject: [Equest-users] Vegetated roof Message-ID: Hi All, Ho to model vegetated roof whether the effect of vegetation shall be considered in roof reflectivity or in U value of roof. If someone did it before kindly can share the method. Thanks Sambhav. From bruce5 at bellnet.ca Wed Apr 25 06:06:42 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Wed, 25 Apr 2012 09:06:42 -0400 Subject: [Equest-users] infiltration rate In-Reply-To: References: Message-ID: <4F97F6E2.8070708@bellnet.ca> An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: From calebsfreeman at gmail.com Wed Apr 25 08:00:09 2012 From: calebsfreeman at gmail.com (Caleb Freeman) Date: Wed, 25 Apr 2012 11:00:09 -0400 Subject: [Equest-users] Parallel Boxes for Packaged RTU Message-ID: I am modeling an ASHRAE system type 6 and cannot seem to get equest to model this system type. I have tried to user override the VAV to parallel but that does not work. The default expression is set up to only allow parallel piu boxes for a piu system, but the only available piu system type is chilled water. Any suggestions to override the VAV box type or the system type to DX from CHW would be helpful. Thanks in advance, Caleb -------------- next part -------------- An HTML attachment was scrubbed... URL: From dbastow at mcclure-engineering.com Wed Apr 25 08:05:48 2012 From: dbastow at mcclure-engineering.com (Dave Bastow) Date: Wed, 25 Apr 2012 09:05:48 -0600 Subject: [Equest-users] EEM vs. new model In-Reply-To: <3eed67866c98f3a3c29f5ca197ce9c57@mail.gmail.com> References: <6F3694F71FCF0D4A89F7337180F2049E085149C7@KME3.kme.local> <3eed67866c98f3a3c29f5ca197ce9c57@mail.gmail.com> Message-ID: You just need to make sure and get all the inputs input equally realistic for both models to get a true comparison. Often times you will find that a DX system is more efficient, in particular, if you are using a VRF system that utilizes VFD's on all the fans and the compressors, with HRV/DCV outdoor air system utilizing design economizer and with tight DDC variable control of all zones and systems. A chiller/boiler system always has pump power, that uses additional power, that has to be overcome. That said, a chiller system, if put together with an evaporative condenser or cooling tower, with evaporative, so called, "free cooling", economizer, with VFD's on pumps/fans/compressors, VAV system, great variable control of chilled water and hot water for zone control, might have equal or lower energy use than a VRF system and may have great control. Often the first cost of chiller boiler system is higher. Both can be great systems, depending on how they are set up and controlled. David A. Bastow McClure Engineering, Inc. From: David Eldridge [mailto:dse at grummanbutkus.com] Sent: Tuesday, April 24, 2012 10:35 AM To: equest-users at lists.onebuilding.org Cc: Matt Clough Subject: Re: [Equest-users] EEM vs. new model eQUEST's defaults will be important here for pressure drop in the two systems, ability to modulate airflow or chilled water flow, ability to economize (although Google shows your company near the Gulf, so if this is a local auto dealer then maybe economizer won't be important). The use of the chiller system's cooling efficiency and pump power will be important since these are known, and may vary from the wizard's suggestion. You'll also need to make sure the DX system efficiency and fan power is realistic. The part-load performance of the system could also be important if the hours for the shop and show room are different - this could be a case where two or more right-sized DX systems may be a better match than one chiller, depending on the magnitude for the loads and if the zones have wildly different hours of operation. My suggestion would be to set eQUEST aside for a half hour, and just run through a table for the fan power, pump power, and cooling efficiency for each of the two cases and see if the answer jumps out at you. If you get pointed strongly in one direction, then review the eQuest files more closely to be sure you are capturing all of the part-load effects. Regarding your ASHRAE 90.1 baseline suggestions, that might be your best "baseline" and then compare the proposed CHW and an enhanced DX system against that, but shouldn't be necessary other than as Nick suggests for a QA reference. David David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP Grumman/Butkus Associates From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Clough Sent: Tuesday, April 24, 2012 7:37 AM To: Nick Caton; equest-users at lists.onebuilding.org Subject: Re: [Equest-users] EEM vs. new model I suppose I should have been more specific in my description: By baseline I mean the proposed design. So the program outputs 2 sim files - the base(proposed, CHW) case and the iterated (DX) case We want to use eQuest to validate the system choice on this particular project. This is work that was started before I joined, but I have been selected to try and use eQuest to compare the performance of a chilled water system and a DX system. I'm not the most experienced energy modeler, but it seems like a task that would be a good application for eQuest. My approach was to simulate the energy consumption of a building that is similar to the actual design in orientation, shape, and square footage. I initially built the model in the SD wizard, using most of the default values (building envelope, activity usage, etc.), autosize the equipment, and use the EEM to compare the two systems. The idea was that when the building construction and geometry are equal, we can look at the relative energy consumption of the two systems. This initial simulation reported that the DX system would be more efficient, which is not what I had expected based on the design that had been selected. So I figured that maybe my model was too generic, too simple. I created zones based on the plans, and made the geometry more representative of the actual building. These changes produced reports that suggest the chilled water system is more efficient than the DX. I realized that the EEM was incorrectly modeling the change - it was treating the chilled water system as having all 8 air handlers, but was modeling the DX system as one AHU. So I created a duplicate model that has a DX system (autosized and using equest defaults). The comparison of these two models suggests the DX system is slightly more efficient. Unfortunately, my lack of experience makes me doubt the validity of this comparison - especially considering that the engineers selected a chilled water system for this project. So I suppose my questions are: Does my approach seem valid? Is this an appropriate use of the software? After taking some time to write this note, and with a little rest, I wonder if comparing the proposed design to an ASHRAE 90.1 baseline would have been a better approach. Regards, Matt Clough _____ From: Nick Caton [mailto:ncaton at smithboucher.com] Sent: Monday, April 23, 2012 3:40 PM To: Matt Clough; equest-users at lists.onebuilding.org Subject: RE: EEM vs. new model By context, I gather by 'baseline' you mean something other than your proposed design, such as an 90.1 Appendix G baseline or similar. If that's the case, my general advice is that you should much more heavily weight the comparative results using your "actual/proposed" model. A baseline per above inherently diverges from the actual building materials, lighting power densities, solar load shading, and so forth. It's not the same building. Best to choose systems that most efficiently handle your actual project. Don't get too hung up what works best for an imaginary building ;). ~Nick cid:489575314 at 22072009-0ABB NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Clough Sent: Monday, April 23, 2012 1:59 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] EEM vs. new model Salutations eQuesters, I'm doing a simple comparison between a chilled water and DX system. It would seem that this is a great opportunity to use the EEM, and the simulation predicted that the CHW configuration would be more energy efficient than the DX system. To be conservative, I also made a copy of the baseline model and changed the system from chilled water to DX. Using this method, the simulation predicts that the DX system would be more efficient (although not by much). Which result is most accurate? The building is a car dealership with a large showroom and an air-conditioned parts storage area. The geometry and building envelope are not exact, but I made this decision because we are doing this for comparison purposes, so the geometry and construction will be the same. I have let eQuest autosize both systems. Sincerely, Matt Clough -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: not available Type: image/jpeg Size: 1459 bytes Desc: not available URL: From slv3sat at gmail.com Wed Apr 25 09:06:45 2012 From: slv3sat at gmail.com (R B) Date: Wed, 25 Apr 2012 11:06:45 -0500 Subject: [Equest-users] Parallel Boxes for Packaged RTU In-Reply-To: References: Message-ID: Use Powered induction for the system type, and in the cooling source under the cooling->coil capacity/control tab cool source as electric DX. If eQuest is not allowing that, maybe you don't have the latest version (actually this has been possible for quite some time). -Rohini On Wed, Apr 25, 2012 at 10:00 AM, Caleb Freeman wrote: > I am modeling an ASHRAE system type 6 and cannot seem to get equest to > model this system type. I have tried to user override the VAV to parallel > but that does not work. The default expression is set up to only allow > parallel piu boxes for a piu system, but the only available piu system type > is chilled water. Any suggestions to override the VAV box type or the > system type to DX from CHW would be helpful. > > Thanks in advance, > > Caleb > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From slv3sat at gmail.com Wed Apr 25 09:12:10 2012 From: slv3sat at gmail.com (R B) Date: Wed, 25 Apr 2012 11:12:10 -0500 Subject: [Equest-users] outside air flow during unoccupied/setback hours In-Reply-To: References: Message-ID: I should have written min OA sch (at the OA tab, system level) instead of the min sch at the zone level. Thanks to Ramana for pointing this out. -Rohini On Tue, Apr 24, 2012 at 11:54 AM, R B wrote: > I normally have a min sch specified at the zone level - 0 for unoccupied > hours and -999 for other hours that takes care of this comment. > There is an hourly report for fan coming on during night cycle flag (or > something similar). If you do not have the fan coming on or do not have the > night cycle control, you should be ok. You can also look at the hourly > report for OA ratio and whether fan is on/off during the unoccupied time. > -Rohini > > > > On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti wrote: > >> Dear All, >> >> One of the LEED review comments on a university building project I'm >> working on suggests to verify that all systems in baseline and proposed >> models contain zero outside air flow when fans are cycled on to meet >> setback temperatures during unoccupied hours. >> >> What is the best way to go about verifying this? In the 'Hourly Report >> Block' options under a system, I find 'Hourly summed zone OA CFM for DCV >> calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation >> (cfm/cf/). Is one or both of these options under an hourly report, the way >> to go or is there a better way of doing it? >> >> Thanks, >> Ramana. >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> >> > -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Wed Apr 25 10:01:51 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Wed, 25 Apr 2012 17:01:51 +0000 Subject: [Equest-users] Vegetated roof In-Reply-To: References: Message-ID: Hi Sambhav, Best single piece of advice I can offer is to invest some time to peruse the [equest-users] and [bldg-sim] archives. There have been many discussions centered around green roofs, but nobody has established a "best practice" to my knowledge. You will have to ultimately define for yourself what course of action is most appropriate for your current project. Limitations to how eQuest handles constructions have led many to recommend EnergyPlus and it's brethren (such as Designbuilder), where approximations such as assuming a constant soil dampness are unacceptable. If a specific end-goal is to model a green roof as accurately as possible, it seems reasonable to consider other software options. I can't speak much further to exactly how to get started with EnergyPlus - something I'm still working on myself. If you're comfortable with approximations inherent to using eQuest, you could optionally account for the shading effects of vegetation with a building shade + shading schedule appropriate to the seasonal shading effects. Thermal mass/conductivity of the soil, assuming a certain constant dampness, should be represented in a custom layered construction. For that construction, reflectivity should be representative of the soil surface. Consider increasing the roof surface area beyond its actual boundaries to account for thermal conduction of the vegetation. Hmm - maybe I've just set a standard? Some have suggested the net thermal effects of green roofs, inclusive of nuances eQuest cannot account for, are rendered negligible when the layers & thermal mass comprising a green roof are situated external to (above) a significant layer of insulation. I haven't heard of any studies investigating this, but it's very much worth considering from an energy modeling perspective. If the net thermal effects turn out to be negligible, that's reasonable grounds for deciding to not include the green roof at all in the model - it may be time-efficient to build a separate model to explore this specific possibility for your project's local climate and green roof properties. ~Nick NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sambhav tiwari Sent: Tuesday, April 24, 2012 11:56 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Vegetated roof Hi All, Ho to model vegetated roof whether the effect of vegetation shall be considered in roof reflectivity or in U value of roof. If someone did it before kindly can share the method. Thanks Sambhav. _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From jeremy at renewage.com Wed Apr 25 10:07:15 2012 From: jeremy at renewage.com (Jeremy Morlas) Date: Wed, 25 Apr 2012 10:07:15 -0700 Subject: [Equest-users] eQuest Auditor / Engineer Needed Message-ID: Energy Solutions Company is seeking experienced eQUEST Modeling Energy Efficiency Engineer to build energy modeling for commercial buildings in San Francisco. The qualified engineer will have experience in conducting a site survey that identifies all energy efficiency measure (EEM) opportunities within commercial buildings and then you must identify the energy savings and utility company rebates associated with each individual EEM. Please reply to this email with your experience in achieving the above requirements. Thank you. -------------- next part -------------- An HTML attachment was scrubbed... URL: From cland at geo-marine.com Wed Apr 25 10:25:35 2012 From: cland at geo-marine.com (Charles Land) Date: Wed, 25 Apr 2012 12:25:35 -0500 Subject: [Equest-users] Parallel Boxes for Packaged RTU In-Reply-To: References: Message-ID: When you first specify the system as a PIU it does have to have the cooling specified as chilled water, but once you create the system you can go under the cooling tab and change it to DX. Then you can delete out your chilled water system. From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B Sent: Wednesday, April 25, 2012 12:07 PM To: Caleb Freeman Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Parallel Boxes for Packaged RTU Use Powered induction for the system type, and in the cooling source under the cooling->coil capacity/control tab cool source as electric DX. If eQuest is not allowing that, maybe you don't have the latest version (actually this has been possible for quite some time). -Rohini On Wed, Apr 25, 2012 at 10:00 AM, Caleb Freeman > wrote: I am modeling an ASHRAE system type 6 and cannot seem to get equest to model this system type. I have tried to user override the VAV to parallel but that does not work. The default expression is set up to only allow parallel piu boxes for a piu system, but the only available piu system type is chilled water. Any suggestions to override the VAV box type or the system type to DX from CHW would be helpful. Thanks in advance, Caleb _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From thomasv at iit.edu Wed Apr 25 11:04:12 2012 From: thomasv at iit.edu (Varkie C Thomas) Date: Wed, 25 Apr 2012 13:04:12 -0500 Subject: [Equest-users] eQUEST & PV Message-ID: Below is my answer to eQUEST PV questions that I received directly. I am not an expert on eQUEST. I used DOE2.1E to estimate the performance of PV as described below. The results may be questionable. I would like to have case studies of modeling PV with eQUEST. PV Case Studies Projects on http://bepan.info/ Proj-8 - eQ-Tutor - CCGT (modified) - DL+GSHP+PV http://bepan.info/projequest/p8-ccgt-pv-gshp Proj-8 used the PV option of eQUEST-DOE22. I have not tried to understand the PV theory and how it converts solar light energy to electricity. I am not sure whether I modeled the input right because I copied the input described in: http://bepan.info/iit-eq-sem-08/q5-pv-gshp DOE22-eQUEST PV-Documentation Proj-11 - DOE21E - Chicago Center for Green Tech - DL+GSHP+PV http://bepan.info/proj-bldgs/p11-ccgt-doe21e Proj-11 used DOE2.1E (does not have PV option) and uses the hourly report of radiation (direct, diffuse, total) falling on a surface. It assumes the light energy falling on PV is the same (??). Create a bldg with a wall (or roof surface) with an azimuth and tilt angle of the proposed PV panel and the area of the PV panel. 10 years ago when the study was done the efficiency of PV was about 9% to 12%. Now the manufacturers claim up to 17%. In the study 10% (I think) of the total btuh radiation falling on the surface was assumed can be converted to kwh electricity. Proj-12 - eQ-DOE21E - MSCC - Middle-School + Community-Center http://bepan.info/proj-bldgs/p12-middle-school Proj-12 applies the renewable energy savings (PV, GSHP, day-lighting) options of Proj-11 CCGT and creates a bldg (design criteria based on a RFP from client) that enhances the performance. Proj-21 ? DOE21E - Beijing - Solar-Radiation ? PhotoVoltaics ? Study http://bepan.info/proj-doe21e/p21_beijing-solar-pv Proj-21 also analyzes solar data using DOE2.1E. Proj-13 - eQ-DOE21E - HRMU - High-Rise Mixed-Use Bldg http://bepan.info/proj-bldgs/p13-high-rise-bldg Note that the PERCENT energy savings (base Std90) for a low-rise bldg in a suburban location with land for GSHP can be 50% but for a high-rise bldg in an urban location with high land costs and surrounded by tall bldgs the percent energy savings is small. Compare Proj-12 & Proj-13. There are plans to create a database of case studies. Statistical analysis of existing bldgs can be used to estimate the energy performance of new bldgs. See http://bepan.info/contents ???2 -Building Energy Performance Analysis Resources (BEPAR) Database - Proposed??? Varkie http://www.iit.edu/arch/faculty/thomas_varkie.shtml $------Hourly Reports for Loads---Choose specific days to check results--------$ $ Variable-Type=Global Variable-Type=Building Variable-Type= Wall-Name $ $ -------------------- ---------------------- ------------------------ $ $ 1 = Clearness No. 1 = Heating Sensible 1 = Total Solar on Wall $ $ 2 = Ground-T (R) 18 = Infltr Heating Latent 4 = PD by Wind & Stack $ $ 3 = WB Temp 19 = Cooling Sensible 5 = Heat Transfer $ $ 4 = DB Temp 20 = Cooling Latent 6 = Surface Temp $ $ 5 = Atm Press 25 = Cooling Infltr Sensib 7 = Infltr CFM by Crack $ $ 6 = Cloud Cover 36 = Cooling Infltr Latent $ $ 7 = Snow Flag Variable-Type= Wndw-Name $ $ 8 = Rain Flag Variable-Type = Space-Name ------------------------ $ $ 9 = Wind Dir -------------------------- 10 = Shaded Fraction $ $ 10 = Humidity Ratio 31 = Infltr Latent 11 = Dir Solar Incident $ $ 12 = Enthalpy 37 = Infltr Sensible 12 = Diff Solar Incident $ $ 18 = Dew Point 39 = Infltr CFM 15 = Solar Heat Gain $ $ 27 = Hour Angle 42 = Space Sensible 18 = Infltr CFM by Crack $ $ 36 = Direct Rad 43 = Space Latent $ $ 37 = Diffuse Rad 44 = Space Total Variable-Type= Door-Name $ $ 50 = Solar Altitude 49 = Daylight (FC) Ref-1 ------------------------ $ $ 51 = Solar Azimuth 50 = Daylight (FC) Ref-2 6 = Infltr CFM by Crack $ $------------------------------------------------------------------------------$ SCH-HOURLY-LOADS = SCHEDULE $ Hourly Report 21st of each month $ THRU JAN 20 (ALL) (1,24) = (0) THRU JAN 21 (ALL) (1,24) = (1) THRU FEB 20 (ALL) (1,24) = (0) THRU FEB 21 (ALL) (1,24) = (1) THRU MAR 20 (ALL) (1,24) = (0) THRU MAR 21 (ALL) (1,24) = (1) THRU APR 20 (ALL) (1,24) = (0) THRU APR 21 (ALL) (1,24) = (1) THRU MAY 20 (ALL) (1,24) = (0) THRU MAY 21 (ALL) (1,24) = (1) THRU JUN 20 (ALL) (1,24) = (0) THRU JUN 21 (ALL) (1,24) = (1) THRU JUL 20 (ALL) (1,24) = (0) THRU JUL 21 (ALL) (1,24) = (1) THRU AUG 20 (ALL) (1,24) = (0) THRU AUG 21 (ALL) (1,24) = (1) THRU SEP 20 (ALL) (1,24) = (0) THRU SEP 21 (ALL) (1,24) = (1) THRU OCT 20 (ALL) (1,24) = (0) THRU OCT 21 (ALL) (1,24) = (1) THRU NOV 20 (ALL) (1,24) = (0) THRU NOV 21 (ALL) (1,24) = (1) THRU DEC 20 (ALL) (1,24) = (0) THRU DEC 21 (ALL) (1,24) = (1) THRU DEC 31 (ALL) (1,24) = (0) .. $-------------------------------------Hourly Global & Building-----------------$ LDS-WEATHER = REPORT-BLOCK $ VARIABLE-TYPE = GLOBAL $ VARIABLE-TYPE = GLOBAL VARIABLE-LIST = (3,4,10,12,18,36,37,50,51) $ WB,DB,W,H,DP,Dir,Diff,Azm,Alt $ .. $---------------------------------------------- Space, Wall, Window -----------$ LDS-SPACE-S3 = REPORT-BLOCK $ VARIABLE-TYPE = User-Name of SPACE $ VARIABLE-TYPE = S-3 $ User-Name of Space $ VARIABLE-LIST = (42,43,44) $ Space Sensible, Latent, Total $ .. LDS-WALL-S3 = REPORT-BLOCK $ VARIABLE-TYPE = User-Name of EXTERIOR-WALL $ VARIABLE-TYPE = S-EW $ User-Name of EXTERIOR-WALL $ VARIABLE-LIST = (1,17,18,6) $ Wall Solar: Total, Direct, Diffuse $ $ 6 = Wall Outside Surface Temp $ .. LDS-WNDW-S3 = REPORT-BLOCK $ VARIABLE-TYPE = User-Name of WINDOW $ VARIABLE-TYPE = S-WN $ User-Name of WINDOW $ VARIABLE-LIST = (11,12) $ I-dir, I-diff $ .. $-------------------------------------------------Print Selected Report Blocks $ LOADS-HOUR-REP = HOURLY-REPORT $ REPORT-SCHEDULE = SCH-HOURLY-LOADS $ REPORT-BLOCK = (LDS-WEATHER ) .. $------------------------------------------------------------------------------$ END .. $ End of INPUT FOR LOADS $ COMPUTE LOADS .. SAVE-FILES .. STOP .. -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: thomasv.vcf Type: text/x-vcard Size: 308 bytes Desc: Card for Varkie C Thomas URL: From edmund1017 at gmail.com Wed Apr 25 11:28:39 2012 From: edmund1017 at gmail.com (Edmund Wong) Date: Wed, 25 Apr 2012 11:28:39 -0700 Subject: [Equest-users] Historical building with no OA supply Message-ID: Hi everyone, I am currently trying to develop a model in eQuest for a 100 year old commerical building. The building has floor ACU and heat pumps. The challenge is that there is no dedicated OA supply system (OA supply only via infiltration). Air is supplied and returned from ducts in phenum. What is the best way to model this in eQuest? Any suggestions is appreciated. -- Edmund From ramana.koti at gmail.com Wed Apr 25 12:53:23 2012 From: ramana.koti at gmail.com (Ramana Koti) Date: Wed, 25 Apr 2012 15:53:23 -0400 Subject: [Equest-users] outside air flow during unoccupied/setback hours In-Reply-To: References: Message-ID: That worked, thanks. It took me while to figure out the schedule type was Frac/Design but the results showed that my model was using OA during unoccupied hours. Ramana. On Wed, Apr 25, 2012 at 12:12 PM, R B wrote: > I should have written min OA sch (at the OA tab, system level) instead of > the min sch at the zone level. Thanks to Ramana for pointing this out. > -Rohini > > On Tue, Apr 24, 2012 at 11:54 AM, R B wrote: > >> I normally have a min sch specified at the zone level - 0 for unoccupied >> hours and -999 for other hours that takes care of this comment. >> There is an hourly report for fan coming on during night cycle flag (or >> something similar). If you do not have the fan coming on or do not have the >> night cycle control, you should be ok. You can also look at the hourly >> report for OA ratio and whether fan is on/off during the unoccupied time. >> -Rohini >> >> >> >> On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti wrote: >> >>> Dear All, >>> >>> One of the LEED review comments on a university building project I'm >>> working on suggests to verify that all systems in baseline and proposed >>> models contain zero outside air flow when fans are cycled on to meet >>> setback temperatures during unoccupied hours. >>> >>> What is the best way to go about verifying this? In the 'Hourly Report >>> Block' options under a system, I find 'Hourly summed zone OA CFM for DCV >>> calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation >>> (cfm/cf/). Is one or both of these options under an hourly report, the way >>> to go or is there a better way of doing it? >>> >>> Thanks, >>> Ramana. >>> >>> _______________________________________________ >>> Equest-users mailing list >>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>> To unsubscribe from this mailing list send a blank message to >>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >>> >>> >> > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From omoltay at mimtarch.com Wed Apr 25 13:56:44 2012 From: omoltay at mimtarch.com (=?ISO-8859-9?Q?=D6mer_Moltay?=) Date: Wed, 25 Apr 2012 23:56:44 +0300 Subject: [Equest-users] Modeling Convectors for Heating Message-ID: <4F98650C.3070706@mimtarch.com> Dear All, My previous message did not get any answers, so with the hope that maybe I catch the attention of some expert modelers with knowledge on this subject, I am repeating my question. Any help would be appreciated. A multifamily high rise residential will be heated by floor convectors with both natural and forced convection. In most cases, natural convection will be sufficient (this is the experience of the mechanical engineer) and warmed air will rise from these convectors into the spaces. In colder weather, the convectors will operate their fans for more airflow. I have not been able to find much about modelling such a device. My intuition tells me that system Fan Coil would be the best candidate, but with fan power and airflow tied to a schedule that is dependent on outside air temperatures. Is this possible in eQuest? The difficult part is that in warmer weather fan power will be zero and there will be some airflow, while in colder weather fan power will appear and there will be higher airflows. Thanks for any help, Omer Moltay Mimta From ncaton at smithboucher.com Wed Apr 25 14:38:12 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Wed, 25 Apr 2012 21:38:12 +0000 Subject: [Equest-users] how to simulate PTAC reasonably In-Reply-To: References: Message-ID: Hi there, Sounds like you are getting yourself turned around... There are a few schools of thought out there regarding exactly how cooling EIR should be derived from a fan-inclusive energy rating (it's my understanding future versions/addenda to 90.1 may address/clarify this with a sort of generic set of "non-fan cooling/heating efficiency factors"), but you should not be entering 0.0 energy for your fan in any case. Presently, one can choose to figure a baseline system cooling EIR using either the baseline Pfan or ARI procedure fan power figures... I have used both without consequence, and the two methods (usually) produce similar results, but I have gathered over time approaches based on ARI fan energies are easier to pick up and may be more widely practiced, so I'll describe that approach here. The archives contain a few discussions (look for my name) describing Pfan-based methods as well: - Use the modeled capacity (SV-A) and prescribed EER to determine the Total system energy at full capacity. - Determine the fan power as specified by the ARI rating procedures (365W/CFM) using the modeled baseline system airflow (SV-A). This is distinct from Pfan. - Subtract the ARI fan energy from the total system energy. The result is the non-fan energy. - Divide this remainder (non-fan energy) by the capacity (SV-A) and adjust/convert as necessary to make the ratio unitless - now you've found cooling EIR. Interesting to note: I've learned HAP's baseline automation tools use an ARI-based procedure much like the above, but further tweaks the numbers to account for local design conditions differing from ARI test conditions. In practice this makes the same baseline system in very hot design conditions like Arizona cool less efficiently than in more temperate design conditions... It took me awhile but I've come to wrap my head around the logic. Does anybody using eQuest or otherwise doing these baseline calcs "by hand" perform a similar efficiency 'de-rating' in their spreadsheet calcs? ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Aaron Sent: Tuesday, April 24, 2012 11:26 PM To: equest-users Subject: [Equest-users] how to simulate PTAC reasonably Dear all If baseline is system 1 (PTAC), the equipment is decided according to table 6.8.1D which is for the whole equipment, while 90.1 Manual says the supply fan energy (0.3W/cfm for system 1&2) should be separate from cooling system energy, shown as the picture below [cid:image002.png at 01CD22F8.8BB28A20] About how to calculate the COP except supply fan energy, the manual also gives the equation as shown below: [cid:image003.png at 01CD22F8.8BB28A20] I try to find the Cooling Capacity for every PTAC system in SV-A report and calculate the COP for the cooling section(Compressor and condenser), while when I input the cooling EIP (1/COP) in cooling uni and 0.3W/cfm for supply fan, the energy consumption is much higher than inputting the whole EER for the cooling EIR and 0 W/cfm for the supply fan before. From the energy breakdown contrast, what surprises me is that the energy for cooling is more than before. When I try to change the fan delta t from 0.93 to 0 and find the cooling energy is decreasing than inputting the whole EER, but the sum of cooling and fan is still more than inputting the whole EER , have anyone met the same confusion before and tell me the reason and how to simulate PTAC reasonably. Thanks a lot -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image002.png Type: image/png Size: 72037 bytes Desc: image002.png URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image003.png Type: image/png Size: 28229 bytes Desc: image003.png URL: From bbishop at pathfinder-ea.com Wed Apr 25 14:52:58 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Wed, 25 Apr 2012 21:52:58 +0000 Subject: [Equest-users] Modeling Convectors for Heating In-Reply-To: <4F98650C.3070706@mimtarch.com> References: <4F98650C.3070706@mimtarch.com> Message-ID: <90D829482BDEDB4CB264DE5060592B19048823EC@lightning.pathfinderengineers.com> ?mer, There are different ways you could include the fan energy in the model, depending on the following: How are these convectors controlled? What controls the heat output, and what triggers the fans to come on? Are the convectors electric heating or hot water? Is there a separate air handler for ventilation? How about modeling the convector heating as hot water (regardless of whether or not they are). Assign two boilers (electric if the convectors are electric), one with a separate boiler pump to represent the convector fan, and one without. Create an equipment control that uses the boiler without pump as the first stage of heating, and the boiler with pump as the second stage. This method models the fans as coming on at a certain stage of heating load, instead of them coming on per a time schedule or OA schedule. Some other ideas: If the convectors are hot water, you could model them as hot water baseboards, and add a miscellaneous load with a schedule that mimics the hours that the convector fan would run. If the convectors are electric, you could model them as hot water baseboards with an electric boiler, and the HW loop pump can represent the fan. Add a miscellaneous load with a schedule that mimics the hours that the convectors are natural convection only. You could also try to model the convectors as variable volume, so that the fan curve results in lower fan power at lower loads. Regards, Bill -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of ?mer Moltay Sent: Wednesday, April 25, 2012 4:57 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Modeling Convectors for Heating Dear All, My previous message did not get any answers, so with the hope that maybe I catch the attention of some expert modelers with knowledge on this subject, I am repeating my question. Any help would be appreciated. A multifamily high rise residential will be heated by floor convectors with both natural and forced convection. In most cases, natural convection will be sufficient (this is the experience of the mechanical engineer) and warmed air will rise from these convectors into the spaces. In colder weather, the convectors will operate their fans for more airflow. I have not been able to find much about modelling such a device. My intuition tells me that system Fan Coil would be the best candidate, but with fan power and airflow tied to a schedule that is dependent on outside air temperatures. Is this possible in eQuest? The difficult part is that in warmer weather fan power will be zero and there will be some airflow, while in colder weather fan power will appear and there will be higher airflows. Thanks for any help, Omer Moltay Mimta _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From soldattm at gmail.com Wed Apr 25 15:09:44 2012 From: soldattm at gmail.com (Maria Elena Soldatti) Date: Wed, 25 Apr 2012 19:09:44 -0300 Subject: [Equest-users] Question about Units Message-ID: Can I use metric units? when and where I can make the change in units? Thanks. Maria Elena.. -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios! -------------- next part -------------- An HTML attachment was scrubbed... URL: From rp.esdc at gmail.com Wed Apr 25 15:19:28 2012 From: rp.esdc at gmail.com (Ron Pecarina) Date: Wed, 25 Apr 2012 16:19:28 -0600 Subject: [Equest-users] Modeling Convectors for Heating In-Reply-To: <90D829482BDEDB4CB264DE5060592B19048823EC@lightning.pathfinderengineers.com> References: <4F98650C.3070706@mimtarch.com> <90D829482BDEDB4CB264DE5060592B19048823EC@lightning.pathfinderengineers.com> Message-ID: One method that I have used is to use a fan coil or unit heater system (depending on if cooling or outdoor air is required) with baseboard heat. A fan powered convector will provide much more heat than one without the fan. Typically I set the baseboard capacity to10-15% of the heat capacity of the fan powered convector. This will vary for hot water heating systems based on the HW and space temperatures. The balance of the heating capacity is then used for the fan coil or unit heater. On Wed, Apr 25, 2012 at 3:52 PM, Bishop, Bill wrote: > ?mer, > > There are different ways you could include the fan energy in the model, > depending on the following: > How are these convectors controlled? What controls the heat output, and > what triggers the fans to come on? > Are the convectors electric heating or hot water? > Is there a separate air handler for ventilation? > > How about modeling the convector heating as hot water (regardless of > whether or not they are). Assign two boilers (electric if the convectors > are electric), one with a separate boiler pump to represent the convector > fan, and one without. Create an equipment control that uses the boiler > without pump as the first stage of heating, and the boiler with pump as the > second stage. This method models the fans as coming on at a certain stage > of heating load, instead of them coming on per a time schedule or OA > schedule. > > Some other ideas: > If the convectors are hot water, you could model them as hot water > baseboards, and add a miscellaneous load with a schedule that mimics the > hours that the convector fan would run. > If the convectors are electric, you could model them as hot water > baseboards with an electric boiler, and the HW loop pump can represent the > fan. Add a miscellaneous load with a schedule that mimics the hours that > the convectors are natural convection only. > You could also try to model the convectors as variable volume, so that the > fan curve results in lower fan power at lower loads. > > Regards, > Bill > > > -----Original Message----- > From: equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] On Behalf Of ?mer Moltay > Sent: Wednesday, April 25, 2012 4:57 PM > To: equest-users at lists.onebuilding.org > Subject: [Equest-users] Modeling Convectors for Heating > > Dear All, > > My previous message did not get any answers, so with the hope that maybe > I catch the attention of some expert modelers with knowledge on this > subject, I am repeating my question. Any help would be appreciated. > > A multifamily high rise residential will be heated by floor convectors > with both natural and forced convection. In most cases, natural > convection will be sufficient (this is the experience of the mechanical > engineer) and warmed air will rise from these convectors into the > spaces. In colder weather, the convectors will operate their fans for > more airflow. > > I have not been able to find much about modelling such a device. My > intuition tells me that system Fan Coil would be the best candidate, but > with fan power and airflow tied to a schedule that is dependent on > outside air temperatures. Is this possible in eQuest? > > The difficult part is that in warmer weather fan power will be zero and > there will be some airflow, while in colder weather fan power will > appear and there will be higher airflows. > > Thanks for any help, > > Omer Moltay > Mimta > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > -- Ron Pecarina, PE, CEM, LEED-AP BD&C Energy and Sustainable Design Consultants, Inc. 1128 Noblewood Drive Billings, MT 59101 406-208-0227 -------------- next part -------------- An HTML attachment was scrubbed... URL: From ablue at sustainable-solutions.ca Thu Apr 26 06:49:53 2012 From: ablue at sustainable-solutions.ca (Alex Blue) Date: Thu, 26 Apr 2012 06:49:53 -0700 Subject: [Equest-users] Question about Units In-Reply-To: References: Message-ID: Hi Maria Elena, eQuest doesn't have metric units available yet, though that's one of the major features the Canadian version (called CanQuest) that is under development will add. It has been "soon to be released" for a couple of years now, though, so I would get used to manual unit conversions for the moment. Alex From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Maria Elena Soldatti Sent: April 25, 2012 5:10 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Question about Units Can I use metric units? when and where I can make the change in units? Thanks. Maria Elena.. -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios! -------------- next part -------------- An HTML attachment was scrubbed... URL: From poleary1969 at gmail.com Thu Apr 26 07:16:04 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Thu, 26 Apr 2012 07:16:04 -0700 Subject: [Equest-users] outside air flow during unoccupied/setback hours In-Reply-To: References: <4F973CAF.90205@gmail.com> Message-ID: <4F9958A4.3070904@gmail.com> just looking in the advanced energy modeling for leed manual (from aug 2010) i can't find anything about the reviewer's comment, though it does mention 90.1-2004 addenda for appendix g did change the language for schedules, outside air, to match the 90.1-2007 appendix requirement i quoted below. have you tried contacting the review team thru the project resources? for leed 3/2009 there is an option buried in the submittal process that allows some communication w/the review team so either you, or the project lead, should be able to ask the reviewer to clarify the source of the comment requirement prior to marking your comment responses as done & possibly getting the same comment again. i've found it useful to respond to reviewer's comments by referring to ashrae chapter, section, and verse (90.1-2007 in this case) and quoting the relevant text so if there's a usgbc interpretation that is different from the ashrae text, addenda, or interpretations the reviewer ends up telling what the source of the comment is. there could be a usgbc cir addressing the subject, does anyone know? the usgbc position on simulating non-tradable exterior lighting the same in both proposed and baseline cases is in an old cir only - not in the usgbc modeling guide, not in 90.1, not in the usgbc handbooks. On 4/26/12 6:16 AM, Ramana Koti wrote: > Patrick, it is a LEED 2009 (v3) project. I'm slightly confused by this > one but trying to follow the reviewer's suggestion. Thanks for > pointing this out. > RK. > > On Tue, Apr 24, 2012 at 7:52 PM, Patrick J. O'Leary, Jr. > > wrote: > > is this a leed 2.2 or 3.0 project? > > i'm guessing, without looking in my leed manuals, this is a usgbc > requirement for at least 2.2. for leed 3, 90.1-2007, appendix g, > table 3.1, no. 4 schedules, specifically states the "hvac fans > that provide outdoor air for ventilation shall run continuously > whenever spaces are occupied and shall be cycled on and off to > meet heating and cooling loads during unoccupied hours." > 90.1-2004 doesn't specify fans specifically for outdoor air for > ventilation, it just says hvac fans - which is the same as the > system supply fan in a non-doas/economizer capable of completely > closing the outdoor air damper system so the outdoor air can't be > shut off. > > so the comment is contrary to the 90.1-2007 (and/or 2004 depending > on systems) simulation requirement. the 90.1-2004 user's manual > appendix g section doesn't address the scheduling for hvac fans > during unoccupied modes. > > > On 4/24/12 9:54 AM, R B wrote: >> I normally have a min sch specified at the zone level - 0 for >> unoccupied hours and -999 for other hours that takes care of this >> comment. >> There is an hourly report for fan coming on during night cycle >> flag (or something similar). If you do not have the fan coming on >> or do not have the night cycle control, you should be ok. You can >> also look at the hourly report for OA ratio and whether fan is >> on/off during the unoccupied time. >> -Rohini >> >> >> On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti >> > wrote: >> >> Dear All, >> One of the LEED review comments on a university building >> project I'm working on suggests to verify that all systems >> in baseline and proposed models contain zero outside air flow >> when fans are cycled on to meet setback temperatures during >> unoccupied hours. >> What is the best way to go about verifying this? In the >> 'Hourly Report Block' options under a system, I find 'Hourly >> summed zone OA CFM for DCV calculation (cfm)' and 'Hourly max >> zone OA/total flow for DCV calculation (cfm/cf/). Is one or >> both of these options under an hourly report, the way to go >> or is there a better way of doing it? >> Thanks, >> Ramana. >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message >> to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> >> >> >> >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Thu Apr 26 09:16:09 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Thu, 26 Apr 2012 09:16:09 -0700 Subject: [Equest-users] Question about Units In-Reply-To: References: Message-ID: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue wrote: > Hi Maria Elena,**** > > ** ** > > eQuest doesn?t have metric units available yet, though that?s one of the > major features the Canadian version (called CanQuest) that is under > development will add. It has been ?soon to be released? for a couple of > years now, though, so I would get used to manual unit conversions for the > moment.**** > > ** ** > > Alex**** > > ** ** > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Maria Elena > Soldatti > *Sent:* April 25, 2012 5:10 PM > *To:* equest-users at lists.onebuilding.org > *Subject:* [Equest-users] Question about Units**** > > ** ** > > > **** > > Can I use metric units? when and where I can make the change in units?**** > > ** ** > > Thanks. Maria Elena..**** > > -- > La vida te da sorpresas, sorpresas te da la vida. Ay Dios!**** > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From ssavich at systemswestengineers.com Thu Apr 26 09:28:58 2012 From: ssavich at systemswestengineers.com (Steven Savich) Date: Thu, 26 Apr 2012 09:28:58 -0700 Subject: [Equest-users] Question about Units In-Reply-To: References: Message-ID: <002d01cd23c9$b0b7da10$12278e30$@com> I've heard this assertion a few times now, but have seen no verification. Got an email from Hirsch, Gates, Criswell, or Addison confirming that eQuest will no longer be developed? Steven From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 9:16 AM To: Alex Blue Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Question about Units The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue wrote: Hi Maria Elena, eQuest doesn't have metric units available yet, though that's one of the major features the Canadian version (called CanQuest) that is under development will add. It has been "soon to be released" for a couple of years now, though, so I would get used to manual unit conversions for the moment. Alex From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Maria Elena Soldatti Sent: April 25, 2012 5:10 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Question about Units Can I use metric units? when and where I can make the change in units? Thanks. Maria Elena.. -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios! _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Thu Apr 26 09:50:14 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Thu, 26 Apr 2012 09:50:14 -0700 Subject: [Equest-users] Is eQuest still under development ? Message-ID: List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer wrote: > I am not upset. I just couldn't tell if you meant to just send that to > Maria Elena. My guess is you are going to generate some controversy but > that is ok with me. > > Jason > > > On 4/26/2012 11:28 AM, CleanTech Analytics wrote: > >> Sorry Jason, could you please school me-- what is going on >> with CanQuest? Why is it that the well documented complience >> tools can not be used? What should I not say to not upset >> the modarater? I only said what I think is true >> from research and use of the tool. >> >> >> >> >> >> /Jeremiah D. Crossett/ >> /CleanTech Analytics/ >> /503-688-8951/ >> /www.cleantechanalytics.com/ >> > >> >> >> * >> >> This document may contain valuable information proprietary >> to CleanTech Analytics which is private and confidential. It >> may not be shared, copied, stored or transmitted in any form >> without the prior written consent of CleanTech Analytics >> >> * >> >> >> >> On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer >> > wrote: >> >> Jeremiah, >> >> Did you mean to send this to the mailing list? >> >> Jason >> >> >> On 4/26/2012 11:16 AM, CleanTech Analytics wrote: >> >> The eQuest project is dead, anything that is current >> is what >> there is, and there is not more development going >> into the >> code. There many are issues, and no support other >> then this >> list. To use eQuest you must be comfortable with >> developing >> workflows to work around issues you may come across. >> CanQuest will never be finished, so don't hold your >> breath, >> also do not use the compliance tools if you expect >> to create >> a compliant building, as they do not work. >> >> You could allwees use a spreadsheet to convert, but >> the text >> files are very time consuming to convert to spreadsheet. >> >> >> >> >> >> /Jeremiah D. Crossett/ >> /CleanTech Analytics/ >> /503-688-8951 / >> /www.cleantechanalytics.com/ >> >> > >> >> >> >> >> >> >> >> >> * >> >> This document may contain valuable information >> proprietary >> to CleanTech Analytics which is private and >> confidential. It >> may not be shared, copied, stored or transmitted in >> any form >> without the prior written consent of CleanTech Analytics >> >> * >> >> >> >> On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue >> > >> > >> >> >> >>> >> wrote: >> >> Hi Maria Elena,____ >> >> __ __ >> >> >> eQuest doesn?t have metric units available yet, >> though >> that?s one of the major features the Canadian >> version >> (called CanQuest) that is under development will >> add. >> It has been ?soon to be released? for a couple >> of years >> now, though, so I would get used to manual unit >> conversions for the moment.____ >> >> __ __ >> >> Alex____ >> >> __ __ >> >> >> *From:*equest-users-bounces at __**lists.onebuilding.org> equest-users-bounces@**lists.onebuilding.org >> > >> > >> >> >> >> [mailto:equest-users-bounces at _**_lists.onebuilding.org > equest-users-bounces@**lists.onebuilding.org >> > >> > >> >>] >> *On >> Behalf Of *Maria Elena Soldatti >> *Sent:* April 25, 2012 5:10 PM >> *To:* equest-users at lists.__onebuildi**ng.org >> >> > >> >> >> >> >> >> *Subject:* [Equest-users] Question about Units____ >> >> __ __ >> >> >> ____ >> >> Can I usemetric units? when andwhere I can makethe >> change in units?____ >> >> __ __ >> >> Thanks. Maria Elena..____ >> >> >> -- >> La vida te da sorpresas, sorpresas te da la vida. Ay >> Dios!____ >> >> >> ______________________________**___________________ >> Equest-users mailing list >> http://lists.onebuilding.org/_**_listinfo.cgi/equest-users-__** >> onebuilding.org >> >> > onebuilding.org >> > >> To unsubscribe from this mailing list send a blank >> message to >> EQUEST-USERS-UNSUBSCRIBE at __ONE**BUILDING.ORG >> >> > >> >> >> >> >> >> >> >> >> >> ______________________________**___________________ >> Equest-users mailing list >> http://lists.onebuilding.org/_**_listinfo.cgi/equest-users-__** >> onebuilding.org >> >> > onebuilding.org >> > >> To unsubscribe from this mailing list send a blank >> message to >> EQUEST-USERS-UNSUBSCRIBE at __ONE**BUILDING.ORG >> >> > >> >> >> >> -- >> Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair >> Admin for onebuilding.org >> building performance mailing lists >> >> >> > -- > Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair > Admin for onebuilding.org building performance mailing lists > -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: PAKtech 0 Degree Rotation.pd2 Type: application/octet-stream Size: 19501 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: PAKtech Two Hundred Seventy Degree Rotation.pd2 Type: application/octet-stream Size: 18857 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: PAKtech One Hundred Eighty Degree Rotation.pd2 Type: application/octet-stream Size: 18843 bytes Desc: not available URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: PAKtech Ninety Degree Rotation.pd2 Type: application/octet-stream Size: 18830 bytes Desc: not available URL: From cbalbach at psdconsulting.com Thu Apr 26 10:05:19 2012 From: cbalbach at psdconsulting.com (Chris Balbach) Date: Thu, 26 Apr 2012 17:05:19 +0000 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: References: Message-ID: <6692B6E504A5054682FDE225163A6E6F0EC121A3@mbx027-e1-nj-10.exch027.domain.local> All: I think it was Mark Twain who said "The reports of my death are greatly exaggerated." I note a (presumably working) demonstration of the CanQuest software is on the slate for the ESim conference in Halifax next week. See page 14 of the ESim Program posted here: http://esim.ca/ All the Best, _Chris Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP Vice President of Research and Development Performance Systems Development of NY,LLC 124 Brindley Street, Suite 4,Ithaca, NY 14850 http://www.psdconsulting.com ph: (607)-327-1647 From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 12:50 PM To: jglazer at gard.com; equest-users at lists.onebuilding.org; jeff.hirsch at doe2.com Subject: Re: [Equest-users] Is eQuest still under development ? List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer > wrote: I am not upset. I just couldn't tell if you meant to just send that to Maria Elena. My guess is you are going to generate some controversy but that is ok with me. Jason On 4/26/2012 11:28 AM, CleanTech Analytics wrote: Sorry Jason, could you please school me-- what is going on with CanQuest? Why is it that the well documented complience tools can not be used? What should I not say to not upset the modarater? I only said what I think is true from research and use of the tool. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951/ /www.cleantechanalytics.com/ * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer >> wrote: Jeremiah, Did you mean to send this to the mailing list? Jason On 4/26/2012 11:16 AM, CleanTech Analytics wrote: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951 >/ /www.cleantechanalytics.com/ > * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue > >>> wrote: Hi Maria Elena,____ __ __ eQuest doesn't have metric units available yet, though that's one of the major features the Canadian version (called CanQuest) that is under development will add. It has been "soon to be released" for a couple of years now, though, so I would get used to manual unit conversions for the moment.____ __ __ Alex____ __ __ *From:*equest-users-bounces at __lists.onebuilding.org > __lists.onebuilding.org >> [mailto:equest-users-bounces@__lists.onebuilding.org > __lists.onebuilding.org >>] *On Behalf Of *Maria Elena Soldatti *Sent:* April 25, 2012 5:10 PM *To:* equest-users at lists.__onebuilding.org > __onebuilding.org >> *Subject:* [Equest-users] Question about Units____ __ __ ____ Can I usemetric units? when andwhere I can makethe change in units?____ __ __ Thanks. Maria Elena..____ -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios!____ _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > >> _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists IMPORTANT NOTICE: This email message is intended to be received only by persons entitled to receive the confidential information it may contain. Email messages to clients of Performance Systems Development may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. -------------- next part -------------- An HTML attachment was scrubbed... URL: From Jeff.Hirsch at DOE2.com Thu Apr 26 19:52:24 2012 From: Jeff.Hirsch at DOE2.com (Jeff Hirsch) Date: Thu, 26 Apr 2012 19:52:24 -0700 Subject: [Equest-users] Is eQuest still under development ? Message-ID: The Mark Twain quote is most appropriate. Thank you Chris. Our group rarely participates in these forums, but I felt some response to this somewhat annoying rumor was needed. Some of the discussion also brings to mind another familiar proverb: a bad workman always blames his tools. But also I am reminded that, if all you have is a hammer everything looks like a nail. So I add to the ?controversy? here. eQUEST and DOE-2 are alive and well and our combined development efforts are at an equal or higher funding and effort level than ever before. However, we will continue to provide all our DOE-2 and eQUEST products as freeware to the simulation communities around the world. We support the overall community activities so that the community can offer analysis and support services to derive income based upon use of our products. We tend not to compete with the community by offering those same analyses and support services ourselves with the exception of providing eQUEST and DOE-2 training. Thus we as a group do not normally offer fee based support services except to a small group of our long-term clients who also generally support our development efforts ? we leave those fee based support service opportunities to you, the user community, as an income source. With thousands of eQUEST and DOE-2 installation around the world, we receive too many emails per day to possibly respond. We especially cannot respond to standard support requests as that request should be directed to those offering fee based support services. We try to pay attention and examine requests when program bugs or errors are suspected. But quite often we need to delay any fixes to the next program release. Our focus on DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 has slowed our releases for the past two years. That will change this year, so be patient please. We do not develop eQUEST or DOE-2 using a license fee income based model. Rather we develop our tools to support the analysis needs of our major clients and the general user community. We have no plans to change our model. Like all software, eQUEST and DOE-2 will have quirks, bugs and limitations. No realistic or truthful company offering software could claim otherwise. However, we plan to continue making improvements and have the resources to do so. What is coming? Several things are coming in the next year. DOE-2.3 has been in beta for some time. We will release that new version when we are confident it can be used in production work in place of DOE-2.2. A version of eQUEST that fully supports DOE-2.3 that will be released at the same time. DOE-2.2 is also still under development, but we tend to implement all major new features in DOE-2.3 rather than DOE-2.2. We expect to release an update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version later. The DOE-2.2 refrigeration version development continues, however more priority has been placed on DOE-2.3 recently; however, we will also release an update to that application as well and we consider that version an important product to continue to upgrade well into the future. I am not sure why rumors of the impending death of DOE-2, that started in the late 1990?s, continue to persist since the evidence for the past fifteen years should have proven those rumors wrong. Similarly, the rumors about the death of eQUEST that have appeared more recently can be also similarly be ignored as completely false. The real history shows that our DOE-2 and eQUEST products have proven to have more funding and longevity ?legs? than any other existing similar software. While other development groups struggle to advance one simulation program or one user interface we have shown that our group can do both the engine and interface with major advances to both for decades and as freeware. I see no change coming in our ability to continue the upgrade of both in the current decade. You should, as a community, be more concerned with the long term viability of other groups making big claims that have a long way to go before they can claim to be offering the simulation community the mature, stable, reliable capabilities free as you get from our products. It is much easier for a developer to claim their product can do amazing things than it is for the user community to realize those possible gains while maintaining the ability to deliver services to their clients competitively in a timely manner. We plan to do our best to continue to offer you products that allow you to perform your job or earn a living, and keep your clients satisfied. In return we ask for your continued support, patience and generally good vibes. We also ask that you continue to support one another in this and other forums, as the freeware nature of our products requires the user community to hang together and exchange information and ideas. With that, I return to my observation deck. ps ? For some reason I and others in my group do not get all the emails from this forum ? of the multiple emails Mr. Crossett sent to the forum and myself below I received none but I did, obviously see the one I am now responding to. Not sure of the cause, but I do get hundreds of emails per day and cannot even open many. -------------------------------------------------------------------------------- Jeff Hirsch James J. Hirsch & Associates From: Chris Balbach Sent: Thursday, April 26, 2012 10:05 AM To: CleanTech Analytics ; jglazer at gard.com ; equest-users at lists.onebuilding.org ; jeff.hirsch at doe2.com Subject: RE: [Equest-users] Is eQuest still under development ? All: I think it was Mark Twain who said ?The reports of my death are greatly exaggerated." I note a (presumably working) demonstration of the CanQuest software is on the slate for the ESim conference in Halifax next week. See page 14 of the ESim Program posted here: http://esim.ca/ All the Best, _Chris Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP Vice President of Research and Development Performance Systems Development of NY,LLC 124 Brindley Street, Suite 4,Ithaca, NY 14850 http://www.psdconsulting.com ph: (607)-327-1647 From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 12:50 PM To: jglazer at gard.com; equest-users at lists.onebuilding.org; jeff.hirsch at doe2.com Subject: Re: [Equest-users] Is eQuest still under development ? List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer wrote: I am not upset. I just couldn't tell if you meant to just send that to Maria Elena. My guess is you are going to generate some controversy but that is ok with me. Jason On 4/26/2012 11:28 AM, CleanTech Analytics wrote: Sorry Jason, could you please school me-- what is going on with CanQuest? Why is it that the well documented complience tools can not be used? What should I not say to not upset the modarater? I only said what I think is true from research and use of the tool. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951/ /www.cleantechanalytics.com/ * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer > wrote: Jeremiah, Did you mean to send this to the mailing list? Jason On 4/26/2012 11:16 AM, CleanTech Analytics wrote: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951 / /www.cleantechanalytics.com/ > * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue >> wrote: Hi Maria Elena,____ __ __ eQuest doesn?t have metric units available yet, though that?s one of the major features the Canadian version (called CanQuest) that is under development will add. It has been ?soon to be released? for a couple of years now, though, so I would get used to manual unit conversions for the moment.____ __ __ Alex____ __ __ *From:*equest-users-bounces at __lists.onebuilding.org > [mailto:equest-users-bounces at __lists.onebuilding.org >] *On Behalf Of *Maria Elena Soldatti *Sent:* April 25, 2012 5:10 PM *To:* equest-users at lists.__onebuilding.org > *Subject:* [Equest-users] Question about Units____ __ __ ____ Can I usemetric units? when andwhere I can makethe change in units?____ __ __ Thanks. Maria Elena..____ -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios!____ _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists IMPORTANT NOTICE: This email message is intended to be received only by persons entitled to receive the confidential information it may contain. Email messages to clients of Performance Systems Development may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. -------------- next part -------------- An HTML attachment was scrubbed... URL: From jeremiah at cleantechanalytics.com Thu Apr 26 20:30:47 2012 From: jeremiah at cleantechanalytics.com (CleanTech Analytics) Date: Thu, 26 Apr 2012 20:30:47 -0700 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: References: Message-ID: Many apologies Jeff- Glad to see the project is still alive- and then back to my original question, does the LEED Complacence manager to the best of your knowledge work? I was told not to use it, and and have had troubles with it. My original question is intact, does it work and I must have made some error, or is there "issues" with it, so it should not be used? Many thanks and sorry if my statements where out of line. Best regards- *Jeremiah D. Crossett* *CleanTech Analytics* *503-688-8951* *www.cleantechanalytics.com* * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 7:52 PM, Jeff Hirsch wrote: > The Mark Twain quote is most appropriate. Thank you Chris. Our group > rarely participates in these forums, but I felt some response to this > somewhat annoying rumor was needed. Some of the discussion also brings to > mind another familiar proverb: a bad workman always blames his tools. But > also I am reminded that, if all you have is a hammer everything looks like > a nail. So I add to the ?controversy? here. > > > > eQUEST and DOE-2 are alive and well and our combined development efforts > are at an equal or higher funding and effort level than ever before. > However, we will continue to provide all our DOE-2 and eQUEST products as > freeware to the simulation communities around the world. We support the > overall community activities so that the community can offer analysis and > support services to derive income based upon use of our products. > > > > We tend not to compete with the community by offering those same analyses > and support services ourselves with the exception of providing eQUEST and > DOE-2 training. Thus we as a group do not normally offer fee based support > services except to a small group of our long-term clients who also > generally support our development efforts ? we leave those fee based > support service opportunities to you, the user community, as an income > source. > > > > With thousands of eQUEST and DOE-2 installation around the world, we > receive too many emails per day to possibly respond. We especially cannot > respond to standard support requests as that request should be directed to > those offering fee based support services. We try to pay attention and > examine requests when program bugs or errors are suspected. But quite often > we need to delay any fixes to the next program release. Our focus on > DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 > has slowed our releases for the past two years. That will change this year, > so be patient please. > > > > We do not develop eQUEST or DOE-2 using a license fee income based model. > Rather we develop our tools to support the analysis needs of our major > clients and the general user community. We have no plans to change our > model. Like all software, eQUEST and DOE-2 will have quirks, bugs and > limitations. No realistic or truthful company offering software could claim > otherwise. However, we plan to continue making improvements and have the > resources to do so. > > > > What is coming? Several things are coming in the next year. DOE-2.3 has > been in beta for some time. We will release that new version when we are > confident it can be used in production work in place of DOE-2.2. A version > of eQUEST that fully supports DOE-2.3 that will be released at the same > time. DOE-2.2 is also still under development, but we tend to implement all > major new features in DOE-2.3 rather than DOE-2.2. We expect to release an > update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version > later. The DOE-2.2 refrigeration version development continues, however > more priority has been placed on DOE-2.3 recently; however, we will also > release an update to that application as well and we consider that version > an important product to continue to upgrade well into the future. > > > > I am not sure why rumors of the impending death of DOE-2, that started in > the late 1990?s, continue to persist since the evidence for the past > fifteen years should have proven those rumors wrong. Similarly, the rumors > about the death of eQUEST that have appeared more recently can be also > similarly be ignored as completely false. The real history shows that our > DOE-2 and eQUEST products have proven to have more funding and longevity > ?legs? than any other existing similar software. While other development > groups struggle to advance one simulation program or one user interface we > have shown that our group can do both the engine and interface with major > advances to both for decades and as freeware. I see no change coming in our > ability to continue the upgrade of both in the current decade. > > > > You should, as a community, be more concerned with the long term viability > of other groups making big claims that have a long way to go before they > can claim to be offering the simulation community the mature, stable, > reliable capabilities free as you get from our products. It is much easier > for a developer to claim their product can do amazing things than it is for > the user community to realize those possible gains while maintaining the > ability to deliver services to their clients competitively in a timely > manner. We plan to do our best to continue to offer you products that allow > you to perform your job or earn a living, and keep your clients satisfied. > In return we ask for your continued support, patience and generally good > vibes. We also ask that you continue to support one another in this and > other forums, as the freeware nature of our products requires the user > community to hang together and exchange information and ideas. > > > > With that, I return to my observation deck. > > ps ? For some reason I and others in my group do not get all the emails > from this forum ? of the multiple emails Mr. Crossett sent to the forum and > myself below I received none but I did, obviously see the one I am now > responding to. Not sure of the cause, but I do get hundreds of emails per > day and cannot even open many. > > ------------------------------ > Jeff Hirsch > James J. Hirsch & Associates > > *From:* Chris Balbach > *Sent:* Thursday, April 26, 2012 10:05 AM > *To:* CleanTech Analytics ; > jglazer at gard.com ; equest-users at lists.onebuilding.org ; > jeff.hirsch at doe2.com > *Subject:* RE: [Equest-users] Is eQuest still under development ? > > > All: > > > > I think it was Mark Twain who said ?The reports of my death are greatly > exaggerated." > > > > I note a (presumably working) demonstration of the CanQuest software is on > the slate for the ESim conference in Halifax next week. See page 14 of the > ESim Program posted here: http://esim.ca/ > > > > All the Best, > > > > _Chris > > > > Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP > > Vice President of Research and Development > > Performance Systems Development of NY,LLC > > 124 Brindley Street, Suite 4,Ithaca, NY 14850 > > http://www.psdconsulting.com > > ph: (607)-327-1647 > > > > > > > > > > > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *CleanTech > Analytics > > *Sent:* Thursday, April 26, 2012 12:50 PM > *To:* jglazer at gard.com; equest-users at lists.onebuilding.org; > jeff.hirsch at doe2.com > *Subject:* Re: [Equest-users] Is eQuest still under development ? > > > > List, I do not mean to cause controversy but I am going to re-post this to > see if it gets a response this time. > > > > > > When I had an issue I tracked down the phone number for the Hirsch's of > 805-532-1045, and left a voicemail, then was texted back the message > "please send email to jeff.hirsch at doe2.com and when I emailed the below I > never got a response, and after that as well as after much research showed > there is no DOE funding, or sales revenue to fund the eQuest project > assumed that the project is "dead"....If I am wrong, someone from the > eQuest development team please respond to my questions? > > > > > Jeff, > I am working on a LEED compliance building model in eQUEST, and have to > ask you a question. So I created a building that has zero insulation, > standard lighting watts/sqft and ran the compliance analysis. The building > that is not at code energy costs are in the sixty thousand range, and the > 0,90,180,270 average that should be at code is in the ninty thousand > range.This %30 savings for the building that has zero insulation over the > building that has been auto generated to be complaint with ASHRAE/LEED > shows that for some reason the building that is not at code (zero > insulation) uses 30% less then the building that is suppose to be at code, > and I am sure that the software is wrong. > > Now I have read the PDF published on the subject, and am very curios if the > compliance analysis tool is something that you believe to work correctly? > (I would be happy to find out I made some error, but can not find any such > errors on my part, and someone told me that the tool does not work so I > doubt it is error on my part) > > > *Jeremiah D. Crossett* > > *CleanTech Analytics* > > *503-688-8951* > > *www.cleantechanalytics.com* > > > > *This document may contain valuable information proprietary to CleanTech > Analytics which is private and confidential. It may not be shared, copied, > stored or transmitted in any form without the prior written consent of > CleanTech Analytics*** > > > > > > On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer wrote: > > I am not upset. I just couldn't tell if you meant to just send that to > Maria Elena. My guess is you are going to generate some controversy but > that is ok with me. > > Jason > > > > On 4/26/2012 11:28 AM, CleanTech Analytics wrote: > > Sorry Jason, could you please school me-- what is going on > with CanQuest? Why is it that the well documented complience > tools can not be used? What should I not say to not upset > the modarater? I only said what I think is true > from research and use of the tool. > > > > > /Jeremiah D. Crossett/ > /CleanTech Analytics/ > /503-688-8951/ > /www.cleantechanalytics.com/ > > > * > > This document may contain valuable information proprietary > to CleanTech Analytics which is private and confidential. It > may not be shared, copied, stored or transmitted in any form > without the prior written consent of CleanTech Analytics > > * > > > On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer > > > wrote: > > Jeremiah, > > Did you mean to send this to the mailing list? > > Jason > > > On 4/26/2012 11:16 AM, CleanTech Analytics wrote: > > The eQuest project is dead, anything that is current > is what > there is, and there is not more development going > into the > code. There many are issues, and no support other > then this > list. To use eQuest you must be comfortable with > developing > workflows to work around issues you may come across. > CanQuest will never be finished, so don't hold your > breath, > also do not use the compliance tools if you expect > to create > a compliant building, as they do not work. > > You could allwees use a spreadsheet to convert, but > the text > files are very time consuming to convert to spreadsheet. > > > > > > /Jeremiah D. Crossett/ > /CleanTech Analytics/ > > /503-688-8951 / > /www.cleantechanalytics.com/ > > > > > > > > > * > > This document may contain valuable information > proprietary > to CleanTech Analytics which is private and > confidential. It > may not be shared, copied, stored or transmitted in > any form > without the prior written consent of CleanTech Analytics > > * > > > > On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue > > > > > >> wrote: > > Hi Maria Elena,____ > > __ __ > > > eQuest doesn?t have metric units available yet, > though > that?s one of the major features the Canadian > version > (called CanQuest) that is under development will > add. > It has been ?soon to be released? for a couple > of years > now, though, so I would get used to manual unit > conversions for the moment.____ > > __ __ > > Alex____ > > __ __ > > *From:*equest-users-bounces at __lists.onebuilding.org equest-users-bounces at lists.onebuilding.org> > > > > [mailto:equest-users-bounces at __lists.onebuilding.org equest-users-bounces at lists.onebuilding.org> > > > >] *On > Behalf Of *Maria Elena Soldatti > *Sent:* April 25, 2012 5:10 PM > > *To:* equest-users at lists.__onebuilding.org > > > > > > *Subject:* [Equest-users] Question about Units____ > > __ __ > > > ____ > > Can I usemetric units? when andwhere I can makethe > change in units?____ > > __ __ > > Thanks. Maria Elena..____ > > > -- > La vida te da sorpresas, sorpresas te da la vida. Ay > Dios!____ > > _________________________________________________ > Equest-users mailing list > > http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org > > > < > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org> > To unsubscribe from this mailing list send a blank > message to > > EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > > > > > > > > > _________________________________________________ > Equest-users mailing list > > http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org > > > < > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org> > To unsubscribe from this mailing list send a blank > message to > > EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > > > > > > -- > Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair > > Admin for onebuilding.org > building performance mailing lists > > > -- > Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair > Admin for onebuilding.org building performance mailing lists > > > IMPORTANT NOTICE: This email message is intended to be received only by > persons entitled to receive the confidential information it may contain. > Email messages to clients of Performance Systems Development may contain > information that is confidential and legally privileged. Please do not > read, copy, forward, or store this message unless you are an intended > recipient of it. If you have received this message in error, please forward > it to the sender and delete it completely from your computer system. > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From sachin5787 at gmail.com Fri Apr 27 00:49:37 2012 From: sachin5787 at gmail.com (Sachin Sharma) Date: Fri, 27 Apr 2012 13:19:37 +0530 Subject: [Equest-users] zone monthly relative humidity details Message-ID: <00f901cd244a$4ec07cf0$ec4176d0$@com> Hi, Where can I find monthly relative humidity of each zone in eQuest output file. Thanks, With regards, Sachin Sharma GRIHA T&E Department of Mechanical Engineering NIT Jaipur +91 9983912512 -------------- next part -------------- An HTML attachment was scrubbed... URL: From cj at enersave.ca Fri Apr 27 06:00:53 2012 From: cj at enersave.ca (Chris Jones) Date: Fri, 27 Apr 2012 09:00:53 -0400 Subject: [Equest-users] Software development In-Reply-To: <6692B6E504A5054682FDE225163A6E6F0EC121A3@mbx027-e1-nj-10.e xch027.domain.local> References: <6692B6E504A5054682FDE225163A6E6F0EC121A3@mbx027-e1-nj-10.exch027.domain.local> Message-ID: <20120427130059.104308DB13D2@zapata.dreamhost.com> While your waiting for the release of canQuest, or any other piece of software, entertain yourself by reading "The Mythical Man-Month", Fred Brooks, ISBN 0-201-83595-9 At 01:05 PM 26/04/2012, Chris Balbach wrote: >Content-Language: en-US >Content-Type: multipart/alternative; > >boundary="_000_6692B6E504A5054682FDE225163A6E6F0EC121A3mbx027e1nj10exc_" > >All: > >I think it was Mark Twain who said "The reports of my death are >greatly exaggerated." > >I note a (presumably working) demonstration of the CanQuest software >is on the slate for the ESim conference in Halifax next week. See >page 14 of the ESim Program posted here: http://esim.ca/ > >All the Best, > >_Chris > >Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP >Vice President of Research and Development >Performance Systems Development of NY,LLC >124 Brindley Street, Suite 4,Ithaca, NY 14850 >http://www.psdconsulting.com >ph: (607)-327-1647 > > > > > >G >> Christopher Jones, P.Eng. Suite 1801, 1 Yonge Street Toronto, ON M5E1W7 Tel. 416-203-7465 Fax. 416-946-1005 email cj at enersave.ca -------------- next part -------------- An HTML attachment was scrubbed... URL: From cj at enersave.ca Fri Apr 27 06:39:16 2012 From: cj at enersave.ca (Chris Jones) Date: Fri, 27 Apr 2012 09:39:16 -0400 Subject: [Equest-users] Thanks Jeff In-Reply-To: References: Message-ID: <20120427133921.5DEC398403F@zapata.dreamhost.com> Thanks Jeff, it would be impossible to meet the demands of the building energy simulation needs without the "free" versions of DOE2. The price for a free, open box engine is quirkiness but you get the power of control if you take the time to understand the abilities and limitations of the tool. >> Christopher Jones, P.Eng. Suite 1801, 1 Yonge Street Toronto, ON M5E1W7 Tel. 416-203-7465 Fax. 416-946-1005 email cj at enersave.ca From tiwari.sambhav at gmail.com Fri Apr 27 09:44:35 2012 From: tiwari.sambhav at gmail.com (sambhav tiwari) Date: Fri, 27 Apr 2012 22:14:35 +0530 Subject: [Equest-users] OA schedule Message-ID: Hi All, It is necessary to specify the min OA schedule as -999 for occupied and 0 for unoccupied hrs at either system or zone level or it can be skipped. Thanks Sambhav From jmcclanathan at CDiengineers.com Fri Apr 27 09:57:03 2012 From: jmcclanathan at CDiengineers.com (Jeremy McClanathan) Date: Fri, 27 Apr 2012 09:57:03 -0700 Subject: [Equest-users] OA schedule In-Reply-To: References: Message-ID: -999 means use input values rather than scheduled values. If you want the program to use input values for a period of time, then override the input with 0 for another period of time, you have to use -999 for the times you want the program to use input values. Blank may not mean the same thing as -999. Jeremy ___________________________________________ Jeremy McClanathan, P.E., BEMP, HFDP, LEED? AP BD+C 4200 194th St SW, Ste 200, Lynnwood, WA 98036 P 425-672-1071 | F 425-778-8769 ??Please consider the environment before printing this email. -----Original Message----- From: sambhav tiwari [mailto:tiwari.sambhav at gmail.com] Sent: Friday, April 27, 2012 9:45 AM To: equest-users at lists.onebuilding.org Subject: [Equest-users] OA schedule Hi All, It is necessary to specify the min OA schedule as -999 for occupied and 0 for unoccupied hrs at either system or zone level or it can be skipped. Thanks Sambhav _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies. From poleary1969 at gmail.com Fri Apr 27 09:57:58 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Fri, 27 Apr 2012 09:57:58 -0700 Subject: [Equest-users] OA schedule In-Reply-To: References: Message-ID: <4F9AD016.6030001@gmail.com> depends on the modeling requirements. 90.1? owner requirement? leed? something else? for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically states the "hvac fans that provide outdoor air for ventilation shall run continuously whenever spaces are occupied and shall be cycled on and off to meet heating and cooling loads during unoccupied hours." 90.1-2004 doesn't specify fans specifically for outdoor air for ventilation, it just says hvac fans - which is the same as the system supply fan in a non-doas/economizer capable of completely closing the outdoor air damper system so the outdoor air can't be shut off. so for a 90.1-2007 simulation the minimum oa should not be zero during unoccupied hours. On 4/27/12 9:44 AM, sambhav tiwari wrote: > Hi All, > It is necessary to specify the min OA schedule as -999 for > occupied and 0 for unoccupied hrs at either system or zone level or it > can be skipped. > > > Thanks > Sambhav > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > From ncaton at smithboucher.com Fri Apr 27 10:11:08 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Fri, 27 Apr 2012 17:11:08 +0000 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: References: Message-ID: Jeremiah to your original query: If you'll look to the archives you'll see many have asked the same question. I and others have responded to many of these repeat queries with a cohesive answer: those of us who have invested the time to explore the 90.1 compliance tool have concluded it is a work in progress at best. The documentation specific to using the compliance ruleset says as much, and it is quite true. If you asked the mailing lists in the past and got no response, I'm personally sorry if that caused any bad feelings but that unfortunately is the nature of the beast at times: the supply/demand ratio for individuals with enough time to help out a stranger doesn't always favor those with the questions - that's a primary reason the archives are so important as a support resource. Everyone: Knowing what the compliance tools presently accomplish, I have myself resolved to generally advise others to avoid using it entirely in its current state, for any project on a tight deadline. Newer users especially are better off and will save time focusing on learning to build their own baselines from their proposed models, until this set of features is further along. I would encourage more intermediate/advanced users to give these compliance options a try, explore the implicit workflow adaptations, and draw/learn from how baselines are put together in an automated fashion - but *not* on a real project with a pending deadline. You might very well pick up a few "aha!" tips along the way that save yourself time and improve/enlighten your understanding of modeling for LEED, but don't count on the compliance tools to be a timesaver or even totally function for a given project. A LEED feature I DO recommend all users trying, whether you are using the compliance ruleset or not: File -> Export File -> LEED Results This is something everyone should stop and experience once with a completed project. Depending on how long you've been working with LEED+eQuest - this could be a real timesaver if adapted into your workflow. The time in a workflow you would use this in an active project would be upon finishing your proposed and baseline models (with rotations), and before beginning to tackle the LEED templates. The resulting file pulls a lot of inputs together I am used to printing a stack of reports to draw from. I hope development of LEED features in future eQuest releases fleshes this area out further - exporting a "LEED input report" for uploading to LEED Online would be great. At first I thought this would be unreasonable/unwieldy, but I have input to share on this front if this seems within reason for the development team. ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 10:31 PM To: Jeff Hirsch Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Is eQuest still under development ? Many apologies Jeff- Glad to see the project is still alive- and then back to my original question, does the LEED Complacence manager to the best of your knowledge work? I was told not to use it, and and have had troubles with it. My original question is intact, does it work and I must have made some error, or is there "issues" with it, so it should not be used? Many thanks and sorry if my statements where out of line. Best regards- Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 7:52 PM, Jeff Hirsch > wrote: The Mark Twain quote is most appropriate. Thank you Chris. Our group rarely participates in these forums, but I felt some response to this somewhat annoying rumor was needed. Some of the discussion also brings to mind another familiar proverb: a bad workman always blames his tools. But also I am reminded that, if all you have is a hammer everything looks like a nail. So I add to the "controversy" here. eQUEST and DOE-2 are alive and well and our combined development efforts are at an equal or higher funding and effort level than ever before. However, we will continue to provide all our DOE-2 and eQUEST products as freeware to the simulation communities around the world. We support the overall community activities so that the community can offer analysis and support services to derive income based upon use of our products. We tend not to compete with the community by offering those same analyses and support services ourselves with the exception of providing eQUEST and DOE-2 training. Thus we as a group do not normally offer fee based support services except to a small group of our long-term clients who also generally support our development efforts - we leave those fee based support service opportunities to you, the user community, as an income source. With thousands of eQUEST and DOE-2 installation around the world, we receive too many emails per day to possibly respond. We especially cannot respond to standard support requests as that request should be directed to those offering fee based support services. We try to pay attention and examine requests when program bugs or errors are suspected. But quite often we need to delay any fixes to the next program release. Our focus on DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 has slowed our releases for the past two years. That will change this year, so be patient please. We do not develop eQUEST or DOE-2 using a license fee income based model. Rather we develop our tools to support the analysis needs of our major clients and the general user community. We have no plans to change our model. Like all software, eQUEST and DOE-2 will have quirks, bugs and limitations. No realistic or truthful company offering software could claim otherwise. However, we plan to continue making improvements and have the resources to do so. What is coming? Several things are coming in the next year. DOE-2.3 has been in beta for some time. We will release that new version when we are confident it can be used in production work in place of DOE-2.2. A version of eQUEST that fully supports DOE-2.3 that will be released at the same time. DOE-2.2 is also still under development, but we tend to implement all major new features in DOE-2.3 rather than DOE-2.2. We expect to release an update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version later. The DOE-2.2 refrigeration version development continues, however more priority has been placed on DOE-2.3 recently; however, we will also release an update to that application as well and we consider that version an important product to continue to upgrade well into the future. I am not sure why rumors of the impending death of DOE-2, that started in the late 1990's, continue to persist since the evidence for the past fifteen years should have proven those rumors wrong. Similarly, the rumors about the death of eQUEST that have appeared more recently can be also similarly be ignored as completely false. The real history shows that our DOE-2 and eQUEST products have proven to have more funding and longevity "legs' than any other existing similar software. While other development groups struggle to advance one simulation program or one user interface we have shown that our group can do both the engine and interface with major advances to both for decades and as freeware. I see no change coming in our ability to continue the upgrade of both in the current decade. You should, as a community, be more concerned with the long term viability of other groups making big claims that have a long way to go before they can claim to be offering the simulation community the mature, stable, reliable capabilities free as you get from our products. It is much easier for a developer to claim their product can do amazing things than it is for the user community to realize those possible gains while maintaining the ability to deliver services to their clients competitively in a timely manner. We plan to do our best to continue to offer you products that allow you to perform your job or earn a living, and keep your clients satisfied. In return we ask for your continued support, patience and generally good vibes. We also ask that you continue to support one another in this and other forums, as the freeware nature of our products requires the user community to hang together and exchange information and ideas. With that, I return to my observation deck. ps - For some reason I and others in my group do not get all the emails from this forum - of the multiple emails Mr. Crossett sent to the forum and myself below I received none but I did, obviously see the one I am now responding to. Not sure of the cause, but I do get hundreds of emails per day and cannot even open many. ________________________________ Jeff Hirsch James J. Hirsch & Associates From: Chris Balbach Sent: Thursday, April 26, 2012 10:05 AM To: CleanTech Analytics ; jglazer at gard.com ; equest-users at lists.onebuilding.org ; jeff.hirsch at doe2.com Subject: RE: [Equest-users] Is eQuest still under development ? All: I think it was Mark Twain who said "The reports of my death are greatly exaggerated." I note a (presumably working) demonstration of the CanQuest software is on the slate for the ESim conference in Halifax next week. See page 14 of the ESim Program posted here: http://esim.ca/ All the Best, _Chris Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP Vice President of Research and Development Performance Systems Development of NY,LLC 124 Brindley Street, Suite 4,Ithaca, NY 14850 http://www.psdconsulting.com ph: (607)-327-1647 From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 12:50 PM To: jglazer at gard.com; equest-users at lists.onebuilding.org; jeff.hirsch at doe2.com Subject: Re: [Equest-users] Is eQuest still under development ? List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer > wrote: I am not upset. I just couldn't tell if you meant to just send that to Maria Elena. My guess is you are going to generate some controversy but that is ok with me. Jason On 4/26/2012 11:28 AM, CleanTech Analytics wrote: Sorry Jason, could you please school me-- what is going on with CanQuest? Why is it that the well documented complience tools can not be used? What should I not say to not upset the modarater? I only said what I think is true from research and use of the tool. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951/ /www.cleantechanalytics.com/ * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer >> wrote: Jeremiah, Did you mean to send this to the mailing list? Jason On 4/26/2012 11:16 AM, CleanTech Analytics wrote: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951 >/ /www.cleantechanalytics.com/ > * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue > >>> wrote: Hi Maria Elena,____ __ __ eQuest doesn't have metric units available yet, though that's one of the major features the Canadian version (called CanQuest) that is under development will add. It has been "soon to be released" for a couple of years now, though, so I would get used to manual unit conversions for the moment.____ __ __ Alex____ __ __ *From:*equest-users-bounces at __lists.onebuilding.org > __lists.onebuilding.org >> [mailto:equest-users-bounces@__lists.onebuilding.org > __lists.onebuilding.org >>] *On Behalf Of *Maria Elena Soldatti *Sent:* April 25, 2012 5:10 PM *To:* equest-users at lists.__onebuilding.org > __onebuilding.org >> *Subject:* [Equest-users] Question about Units____ __ __ ____ Can I usemetric units? when andwhere I can makethe change in units?____ __ __ Thanks. Maria Elena..____ -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios!____ _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > >> _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists IMPORTANT NOTICE: This email message is intended to be received only by persons entitled to receive the confidential information it may contain. Email messages to clients of Performance Systems Development may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From ncaton at smithboucher.com Fri Apr 27 10:27:02 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Fri, 27 Apr 2012 17:27:02 +0000 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: References: Message-ID: Jeff, your input is *extremely* appreciated! Thank you very much for the development the status update and clarifying a number of issues re: support and your team?s business model. Much of this is news to me. As eQuest/DOE updates become available, I trust we?ll get a heads up here on the onebuilding.org lists ? are there any other venues where your team is providing status updates in the interim? Thanks again for taking the time to set the record straight, ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff Hirsch Sent: Thursday, April 26, 2012 9:52 PM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Is eQuest still under development ? The Mark Twain quote is most appropriate. Thank you Chris. Our group rarely participates in these forums, but I felt some response to this somewhat annoying rumor was needed. Some of the discussion also brings to mind another familiar proverb: a bad workman always blames his tools. But also I am reminded that, if all you have is a hammer everything looks like a nail. So I add to the ?controversy? here. eQUEST and DOE-2 are alive and well and our combined development efforts are at an equal or higher funding and effort level than ever before. However, we will continue to provide all our DOE-2 and eQUEST products as freeware to the simulation communities around the world. We support the overall community activities so that the community can offer analysis and support services to derive income based upon use of our products. We tend not to compete with the community by offering those same analyses and support services ourselves with the exception of providing eQUEST and DOE-2 training. Thus we as a group do not normally offer fee based support services except to a small group of our long-term clients who also generally support our development efforts ? we leave those fee based support service opportunities to you, the user community, as an income source. With thousands of eQUEST and DOE-2 installation around the world, we receive too many emails per day to possibly respond. We especially cannot respond to standard support requests as that request should be directed to those offering fee based support services. We try to pay attention and examine requests when program bugs or errors are suspected. But quite often we need to delay any fixes to the next program release. Our focus on DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 has slowed our releases for the past two years. That will change this year, so be patient please. We do not develop eQUEST or DOE-2 using a license fee income based model. Rather we develop our tools to support the analysis needs of our major clients and the general user community. We have no plans to change our model. Like all software, eQUEST and DOE-2 will have quirks, bugs and limitations. No realistic or truthful company offering software could claim otherwise. However, we plan to continue making improvements and have the resources to do so. What is coming? Several things are coming in the next year. DOE-2.3 has been in beta for some time. We will release that new version when we are confident it can be used in production work in place of DOE-2.2. A version of eQUEST that fully supports DOE-2.3 that will be released at the same time. DOE-2.2 is also still under development, but we tend to implement all major new features in DOE-2.3 rather than DOE-2.2. We expect to release an update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version later. The DOE-2.2 refrigeration version development continues, however more priority has been placed on DOE-2.3 recently; however, we will also release an update to that application as well and we consider that version an important product to continue to upgrade well into the future. I am not sure why rumors of the impending death of DOE-2, that started in the late 1990?s, continue to persist since the evidence for the past fifteen years should have proven those rumors wrong. Similarly, the rumors about the death of eQUEST that have appeared more recently can be also similarly be ignored as completely false. The real history shows that our DOE-2 and eQUEST products have proven to have more funding and longevity ?legs? than any other existing similar software. While other development groups struggle to advance one simulation program or one user interface we have shown that our group can do both the engine and interface with major advances to both for decades and as freeware. I see no change coming in our ability to continue the upgrade of both in the current decade. You should, as a community, be more concerned with the long term viability of other groups making big claims that have a long way to go before they can claim to be offering the simulation community the mature, stable, reliable capabilities free as you get from our products. It is much easier for a developer to claim their product can do amazing things than it is for the user community to realize those possible gains while maintaining the ability to deliver services to their clients competitively in a timely manner. We plan to do our best to continue to offer you products that allow you to perform your job or earn a living, and keep your clients satisfied. In return we ask for your continued support, patience and generally good vibes. We also ask that you continue to support one another in this and other forums, as the freeware nature of our products requires the user community to hang together and exchange information and ideas. With that, I return to my observation deck. ps ? For some reason I and others in my group do not get all the emails from this forum ? of the multiple emails Mr. Crossett sent to the forum and myself below I received none but I did, obviously see the one I am now responding to. Not sure of the cause, but I do get hundreds of emails per day and cannot even open many. ________________________________ Jeff Hirsch James J. Hirsch & Associates From: Chris Balbach Sent: Thursday, April 26, 2012 10:05 AM To: CleanTech Analytics ; jglazer at gard.com ; equest-users at lists.onebuilding.org ; jeff.hirsch at doe2.com Subject: RE: [Equest-users] Is eQuest still under development ? All: I think it was Mark Twain who said ?The reports of my death are greatly exaggerated." I note a (presumably working) demonstration of the CanQuest software is on the slate for the ESim conference in Halifax next week. See page 14 of the ESim Program posted here: http://esim.ca/ All the Best, _Chris Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP Vice President of Research and Development Performance Systems Development of NY,LLC 124 Brindley Street, Suite 4,Ithaca, NY 14850 http://www.psdconsulting.com ph: (607)-327-1647 From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 12:50 PM To: jglazer at gard.com; equest-users at lists.onebuilding.org; jeff.hirsch at doe2.com Subject: Re: [Equest-users] Is eQuest still under development ? List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com [http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG] This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer > wrote: I am not upset. I just couldn't tell if you meant to just send that to Maria Elena. My guess is you are going to generate some controversy but that is ok with me. Jason On 4/26/2012 11:28 AM, CleanTech Analytics wrote: Sorry Jason, could you please school me-- what is going on with CanQuest? Why is it that the well documented complience tools can not be used? What should I not say to not upset the modarater? I only said what I think is true from research and use of the tool. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951/ /www.cleantechanalytics.com/ * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer >> wrote: Jeremiah, Did you mean to send this to the mailing list? Jason On 4/26/2012 11:16 AM, CleanTech Analytics wrote: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951 >/ /www.cleantechanalytics.com/ > * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue > >>> wrote: Hi Maria Elena,____ __ __ eQuest doesn?t have metric units available yet, though that?s one of the major features the Canadian version (called CanQuest) that is under development will add. It has been ?soon to be released? for a couple of years now, though, so I would get used to manual unit conversions for the moment.____ __ __ Alex____ __ __ *From:*equest-users-bounces at __lists.onebuilding.org > __lists.onebuilding.org >> [mailto:equest-users-bounces@__lists.onebuilding.org > __lists.onebuilding.org >>] *On Behalf Of *Maria Elena Soldatti *Sent:* April 25, 2012 5:10 PM *To:* equest-users at lists.__onebuilding.org > __onebuilding.org >> *Subject:* [Equest-users] Question about Units____ __ __ ____ Can I usemetric units? when andwhere I can makethe change in units?____ __ __ Thanks. Maria Elena..____ -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios!____ _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > >> _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists IMPORTANT NOTICE: This email message is intended to be received only by persons entitled to receive the confidential information it may contain. Email messages to clients of Performance Systems Development may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: From david.j.reddy1 at gmail.com Fri Apr 27 10:32:42 2012 From: david.j.reddy1 at gmail.com (David Reddy) Date: Fri, 27 Apr 2012 10:32:42 -0700 Subject: [Equest-users] OA schedule In-Reply-To: <4F9AD016.6030001@gmail.com> References: <4F9AD016.6030001@gmail.com> Message-ID: <4F9AD83A.3010908@gmail.com> For LEED or other rating systems referencing ASHRAE PRM, it does seem that the 90.1-2007, appendix g, table 3.1 statement is misleading. However, the mandatory shutoff damper controls in section 6.4.3.4.3, I believe, clarifies that the outdoor air should be 0 if cycling system during unoccupied hours, except if the use of OA reduces energy costs (night purge, economizer). If you specify 0.001 in your MIN-AIR-SCH (enables use of economizer), I would review your system's hourly OA levels to make sure it is behaving as expected, especially for multizone systems. I have found that this can lead to a significant amount of additional heating, as the economizer will be used to achieve the SAT control setpoint, even if this is not appropriate in the middle of the winter... As such, I typically set the unoccupied MIN-AIR-SCH value to 0. - David On 4/27/2012 9:57 AM, Patrick J. O'Leary, Jr. wrote: > depends on the modeling requirements. 90.1? owner requirement? > leed? something else? > > for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically > states the "hvac fans that provide outdoor air for ventilation shall > run continuously whenever spaces are occupied and shall be cycled on > and off to meet heating and cooling loads during unoccupied hours." > 90.1-2004 doesn't specify fans specifically for outdoor air for > ventilation, it just says hvac fans - which is the same as the system > supply fan in a non-doas/economizer capable of completely closing the > outdoor air damper system so the outdoor air can't be shut off. > > so for a 90.1-2007 simulation the minimum oa should not be zero during > unoccupied hours. > > On 4/27/12 9:44 AM, sambhav tiwari wrote: >> Hi All, >> It is necessary to specify the min OA schedule as -999 for >> occupied and 0 for unoccupied hrs at either system or zone level or it >> can be skipped. >> >> >> Thanks >> Sambhav >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From poleary1969 at gmail.com Fri Apr 27 11:07:19 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Fri, 27 Apr 2012 11:07:19 -0700 Subject: [Equest-users] OA schedule In-Reply-To: <4F9AD83A.3010908@gmail.com> References: <4F9AD016.6030001@gmail.com> <4F9AD83A.3010908@gmail.com> Message-ID: <4F9AE057.9090009@gmail.com> good point david, considering a baseline (i.e. minimally compliant building) would have to meet the requirement i think the intent of the appendix g requirement is to simulate a worst-case scenario concerning outside air scheduling and energy consumption. not unlike the simulation requirement for a proposed building that a thermal block not specified with a cooling or heating system must simulated with one that is the same type used in the baseline building simulation (app g, table 3.1, no 10, d). your reference to 6.4.3.4.3 (2007) would explain why a usgbc/gbci reviewer could comment on the oa schedule, even though app g is pretty specific on how the oa should be scheduled for simulation purposes. Sambhav, if you're working on a leed project can you ask the review team (thru the project on leed online) to clarify which oa requirement method should be followed in the simulation - app g or 6.4.3.4.3? On 4/27/12 10:32 AM, David Reddy wrote: > For LEED or other rating systems referencing ASHRAE PRM, it does seem > that the 90.1-2007, appendix g, table 3.1 statement is misleading. > > However, the mandatory shutoff damper controls in section 6.4.3.4.3, I > believe, clarifies that the outdoor air should be 0 if cycling system > during unoccupied hours, except if the use of OA reduces energy costs > (night purge, economizer). > > If you specify 0.001 in your MIN-AIR-SCH (enables use of economizer), > I would review your system's hourly OA levels to make sure it is > behaving as expected, especially for multizone systems. I have found > that this can lead to a significant amount of additional heating, as > the economizer will be used to achieve the SAT control setpoint, even > if this is not appropriate in the middle of the winter... As such, I > typically set the unoccupied MIN-AIR-SCH value to 0. > > - David > > On 4/27/2012 9:57 AM, Patrick J. O'Leary, Jr. wrote: >> depends on the modeling requirements. 90.1? owner requirement? >> leed? something else? >> >> for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically >> states the "hvac fans that provide outdoor air for ventilation shall >> run continuously whenever spaces are occupied and shall be cycled on >> and off to meet heating and cooling loads during unoccupied hours." >> 90.1-2004 doesn't specify fans specifically for outdoor air for >> ventilation, it just says hvac fans - which is the same as the system >> supply fan in a non-doas/economizer capable of completely closing the >> outdoor air damper system so the outdoor air can't be shut off. >> >> so for a 90.1-2007 simulation the minimum oa should not be zero >> during unoccupied hours. >> >> On 4/27/12 9:44 AM, sambhav tiwari wrote: >>> Hi All, >>> It is necessary to specify the min OA schedule as -999 for >>> occupied and 0 for unoccupied hrs at either system or zone level or it >>> can be skipped. >>> >>> >>> Thanks >>> Sambhav >>> _______________________________________________ >>> Equest-users mailing list >>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>> To unsubscribe from this mailing list send a blank message to >>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >>> >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > From bbishop at pathfinder-ea.com Fri Apr 27 11:19:29 2012 From: bbishop at pathfinder-ea.com (Bishop, Bill) Date: Fri, 27 Apr 2012 18:19:29 +0000 Subject: [Equest-users] OA schedule In-Reply-To: <4F9AE057.9090009@gmail.com> References: <4F9AD016.6030001@gmail.com> <4F9AD83A.3010908@gmail.com> <4F9AE057.9090009@gmail.com> Message-ID: <90D829482BDEDB4CB264DE5060592B1904885618@lightning.pathfinderengineers.com> I don't see any conflict between App. G and 6.4.3.4.3. I interpret the "cycling" language as requiring that the fans cycle to meet heating and cooling loads but without providing ventilation. Providing ventilation when cycling conflicts with the G3.1.2.5 requirement that ventilation rates be the same - you won't get the same ventilation during cycling since the proposed and baseline cases will differ in the frequency and duration that they cycle. Regards, Bill -----Original Message----- From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr. Sent: Friday, April 27, 2012 2:07 PM To: David Reddy Cc: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] OA schedule good point david, considering a baseline (i.e. minimally compliant building) would have to meet the requirement i think the intent of the appendix g requirement is to simulate a worst-case scenario concerning outside air scheduling and energy consumption. not unlike the simulation requirement for a proposed building that a thermal block not specified with a cooling or heating system must simulated with one that is the same type used in the baseline building simulation (app g, table 3.1, no 10, d). your reference to 6.4.3.4.3 (2007) would explain why a usgbc/gbci reviewer could comment on the oa schedule, even though app g is pretty specific on how the oa should be scheduled for simulation purposes. Sambhav, if you're working on a leed project can you ask the review team (thru the project on leed online) to clarify which oa requirement method should be followed in the simulation - app g or 6.4.3.4.3? On 4/27/12 10:32 AM, David Reddy wrote: > For LEED or other rating systems referencing ASHRAE PRM, it does seem > that the 90.1-2007, appendix g, table 3.1 statement is misleading. > > However, the mandatory shutoff damper controls in section 6.4.3.4.3, I > believe, clarifies that the outdoor air should be 0 if cycling system > during unoccupied hours, except if the use of OA reduces energy costs > (night purge, economizer). > > If you specify 0.001 in your MIN-AIR-SCH (enables use of economizer), > I would review your system's hourly OA levels to make sure it is > behaving as expected, especially for multizone systems. I have found > that this can lead to a significant amount of additional heating, as > the economizer will be used to achieve the SAT control setpoint, even > if this is not appropriate in the middle of the winter... As such, I > typically set the unoccupied MIN-AIR-SCH value to 0. > > - David > > On 4/27/2012 9:57 AM, Patrick J. O'Leary, Jr. wrote: >> depends on the modeling requirements. 90.1? owner requirement? >> leed? something else? >> >> for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically >> states the "hvac fans that provide outdoor air for ventilation shall >> run continuously whenever spaces are occupied and shall be cycled on >> and off to meet heating and cooling loads during unoccupied hours." >> 90.1-2004 doesn't specify fans specifically for outdoor air for >> ventilation, it just says hvac fans - which is the same as the system >> supply fan in a non-doas/economizer capable of completely closing the >> outdoor air damper system so the outdoor air can't be shut off. >> >> so for a 90.1-2007 simulation the minimum oa should not be zero >> during unoccupied hours. >> >> On 4/27/12 9:44 AM, sambhav tiwari wrote: >>> Hi All, >>> It is necessary to specify the min OA schedule as -999 for >>> occupied and 0 for unoccupied hrs at either system or zone level or it >>> can be skipped. >>> >>> >>> Thanks >>> Sambhav >>> _______________________________________________ >>> Equest-users mailing list >>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>> To unsubscribe from this mailing list send a blank message to >>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >>> >> >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > _______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From david.j.reddy1 at gmail.com Fri Apr 27 11:23:38 2012 From: david.j.reddy1 at gmail.com (David Reddy) Date: Fri, 27 Apr 2012 11:23:38 -0700 Subject: [Equest-users] OA schedule In-Reply-To: <90D829482BDEDB4CB264DE5060592B1904885618@lightning.pathfinderengineers.com> References: <4F9AD016.6030001@gmail.com> <4F9AD83A.3010908@gmail.com> <4F9AE057.9090009@gmail.com> <90D829482BDEDB4CB264DE5060592B1904885618@lightning.pathfinderengineers.com> Message-ID: <4F9AE42A.8040103@gmail.com> Yes, thanks Bill, these are exactly the same points that I was going to follow up with... -DR On 4/27/2012 11:19 AM, Bishop, Bill wrote: > I don't see any conflict between App. G and 6.4.3.4.3. I interpret the "cycling" language as requiring that the fans cycle to meet heating and cooling loads but without providing ventilation. Providing ventilation when cycling conflicts with the G3.1.2.5 requirement that ventilation rates be the same - you won't get the same ventilation during cycling since the proposed and baseline cases will differ in the frequency and duration that they cycle. > > Regards, > Bill > > -----Original Message----- > From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr. > Sent: Friday, April 27, 2012 2:07 PM > To: David Reddy > Cc: equest-users at lists.onebuilding.org > Subject: Re: [Equest-users] OA schedule > > good point david, considering a baseline (i.e. minimally compliant > building) would have to meet the requirement i think the intent of the > appendix g requirement is to simulate a worst-case scenario concerning > outside air scheduling and energy consumption. not unlike the > simulation requirement for a proposed building that a thermal block not > specified with a cooling or heating system must simulated with one that > is the same type used in the baseline building simulation (app g, table > 3.1, no 10, d). > > your reference to 6.4.3.4.3 (2007) would explain why a usgbc/gbci > reviewer could comment on the oa schedule, even though app g is pretty > specific on how the oa should be scheduled for simulation purposes. > > Sambhav, if you're working on a leed project can you ask the review team > (thru the project on leed online) to clarify which oa requirement method > should be followed in the simulation - app g or 6.4.3.4.3? > > On 4/27/12 10:32 AM, David Reddy wrote: >> For LEED or other rating systems referencing ASHRAE PRM, it does seem >> that the 90.1-2007, appendix g, table 3.1 statement is misleading. >> >> However, the mandatory shutoff damper controls in section 6.4.3.4.3, I >> believe, clarifies that the outdoor air should be 0 if cycling system >> during unoccupied hours, except if the use of OA reduces energy costs >> (night purge, economizer). >> >> If you specify 0.001 in your MIN-AIR-SCH (enables use of economizer), >> I would review your system's hourly OA levels to make sure it is >> behaving as expected, especially for multizone systems. I have found >> that this can lead to a significant amount of additional heating, as >> the economizer will be used to achieve the SAT control setpoint, even >> if this is not appropriate in the middle of the winter... As such, I >> typically set the unoccupied MIN-AIR-SCH value to 0. >> >> - David >> >> On 4/27/2012 9:57 AM, Patrick J. O'Leary, Jr. wrote: >>> depends on the modeling requirements. 90.1? owner requirement? >>> leed? something else? >>> >>> for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically >>> states the "hvac fans that provide outdoor air for ventilation shall >>> run continuously whenever spaces are occupied and shall be cycled on >>> and off to meet heating and cooling loads during unoccupied hours." >>> 90.1-2004 doesn't specify fans specifically for outdoor air for >>> ventilation, it just says hvac fans - which is the same as the system >>> supply fan in a non-doas/economizer capable of completely closing the >>> outdoor air damper system so the outdoor air can't be shut off. >>> >>> so for a 90.1-2007 simulation the minimum oa should not be zero >>> during unoccupied hours. >>> >>> On 4/27/12 9:44 AM, sambhav tiwari wrote: >>>> Hi All, >>>> It is necessary to specify the min OA schedule as -999 for >>>> occupied and 0 for unoccupied hrs at either system or zone level or it >>>> can be skipped. >>>> >>>> >>>> Thanks >>>> Sambhav >>>> _______________________________________________ >>>> Equest-users mailing list >>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>>> To unsubscribe from this mailing list send a blank message to >>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >>>> >>> _______________________________________________ >>> Equest-users mailing list >>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >>> To unsubscribe from this mailing list send a blank message to >>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> _______________________________________________ >> Equest-users mailing list >> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org >> To unsubscribe from this mailing list send a blank message to >> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG >> > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG From smartin at shaunmartinconsulting.com Fri Apr 27 11:30:00 2012 From: smartin at shaunmartinconsulting.com (Shaun Martin) Date: Fri, 27 Apr 2012 11:30:00 -0700 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: References: Message-ID: <0EAD8301557542F9BE11978C9A24390B@SM> Hi Jeff, Your comments beg the question: what's new in DOE-2.3? Details please! Shaun Shaun Martin LEED AP Principal Shaun Martin Consulting 2060 Pine Street, Vancouver BC V6J 4P8 604-789-1095 smartin at shaunmartinconsulting.com member CAGBC, ASHRAE _____ From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff Hirsch Sent: Thursday, April 26, 2012 7:52 PM To: equest-users at lists.onebuilding.org Subject: Re: [Equest-users] Is eQuest still under development ? The Mark Twain quote is most appropriate. Thank you Chris. Our group rarely participates in these forums, but I felt some response to this somewhat annoying rumor was needed. Some of the discussion also brings to mind another familiar proverb: a bad workman always blames his tools. But also I am reminded that, if all you have is a hammer everything looks like a nail. So I add to the "controversy" here. eQUEST and DOE-2 are alive and well and our combined development efforts are at an equal or higher funding and effort level than ever before. However, we will continue to provide all our DOE-2 and eQUEST products as freeware to the simulation communities around the world. We support the overall community activities so that the community can offer analysis and support services to derive income based upon use of our products. We tend not to compete with the community by offering those same analyses and support services ourselves with the exception of providing eQUEST and DOE-2 training. Thus we as a group do not normally offer fee based support services except to a small group of our long-term clients who also generally support our development efforts - we leave those fee based support service opportunities to you, the user community, as an income source. With thousands of eQUEST and DOE-2 installation around the world, we receive too many emails per day to possibly respond. We especially cannot respond to standard support requests as that request should be directed to those offering fee based support services. We try to pay attention and examine requests when program bugs or errors are suspected. But quite often we need to delay any fixes to the next program release. Our focus on DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 has slowed our releases for the past two years. That will change this year, so be patient please. We do not develop eQUEST or DOE-2 using a license fee income based model. Rather we develop our tools to support the analysis needs of our major clients and the general user community. We have no plans to change our model. Like all software, eQUEST and DOE-2 will have quirks, bugs and limitations. No realistic or truthful company offering software could claim otherwise. However, we plan to continue making improvements and have the resources to do so. What is coming? Several things are coming in the next year. DOE-2.3 has been in beta for some time. We will release that new version when we are confident it can be used in production work in place of DOE-2.2. A version of eQUEST that fully supports DOE-2.3 that will be released at the same time. DOE-2.2 is also still under development, but we tend to implement all major new features in DOE-2.3 rather than DOE-2.2. We expect to release an update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version later. The DOE-2.2 refrigeration version development continues, however more priority has been placed on DOE-2.3 recently; however, we will also release an update to that application as well and we consider that version an important product to continue to upgrade well into the future. I am not sure why rumors of the impending death of DOE-2, that started in the late 1990's, continue to persist since the evidence for the past fifteen years should have proven those rumors wrong. Similarly, the rumors about the death of eQUEST that have appeared more recently can be also similarly be ignored as completely false. The real history shows that our DOE-2 and eQUEST products have proven to have more funding and longevity "legs' than any other existing similar software. While other development groups struggle to advance one simulation program or one user interface we have shown that our group can do both the engine and interface with major advances to both for decades and as freeware. I see no change coming in our ability to continue the upgrade of both in the current decade. You should, as a community, be more concerned with the long term viability of other groups making big claims that have a long way to go before they can claim to be offering the simulation community the mature, stable, reliable capabilities free as you get from our products. It is much easier for a developer to claim their product can do amazing things than it is for the user community to realize those possible gains while maintaining the ability to deliver services to their clients competitively in a timely manner. We plan to do our best to continue to offer you products that allow you to perform your job or earn a living, and keep your clients satisfied. In return we ask for your continued support, patience and generally good vibes. We also ask that you continue to support one another in this and other forums, as the freeware nature of our products requires the user community to hang together and exchange information and ideas. With that, I return to my observation deck. ps - For some reason I and others in my group do not get all the emails from this forum - of the multiple emails Mr. Crossett sent to the forum and myself below I received none but I did, obviously see the one I am now responding to. Not sure of the cause, but I do get hundreds of emails per day and cannot even open many. _____ Jeff Hirsch James J. Hirsch & Associates From: Chris Balbach Sent: Thursday, April 26, 2012 10:05 AM To: CleanTech Analytics ; jglazer at gard.com ; equest-users at lists.onebuilding.org ; jeff.hirsch at doe2.com Subject: RE: [Equest-users] Is eQuest still under development ? All: I think it was Mark Twain who said "The reports of my death are greatly exaggerated." I note a (presumably working) demonstration of the CanQuest software is on the slate for the ESim conference in Halifax next week. See page 14 of the ESim Program posted here: http://esim.ca/ All the Best, _Chris Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP Vice President of Research and Development Performance Systems Development of NY,LLC 124 Brindley Street, Suite 4,Ithaca, NY 14850 http://www.psdconsulting.com ph: (607)-327-1647 From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of CleanTech Analytics Sent: Thursday, April 26, 2012 12:50 PM To: jglazer at gard.com; equest-users at lists.onebuilding.org; jeff.hirsch at doe2.com Subject: Re: [Equest-users] Is eQuest still under development ? List, I do not mean to cause controversy but I am going to re-post this to see if it gets a response this time. When I had an issue I tracked down the phone number for the Hirsch's of 805-532-1045, and left a voicemail, then was texted back the message "please send email to jeff.hirsch at doe2.com and when I emailed the below I never got a response, and after that as well as after much research showed there is no DOE funding, or sales revenue to fund the eQuest project assumed that the project is "dead"....If I am wrong, someone from the eQuest development team please respond to my questions? Jeff, I am working on a LEED compliance building model in eQUEST, and have to ask you a question. So I created a building that has zero insulation, standard lighting watts/sqft and ran the compliance analysis. The building that is not at code energy costs are in the sixty thousand range, and the 0,90,180,270 average that should be at code is in the ninty thousand range.This %30 savings for the building that has zero insulation over the building that has been auto generated to be complaint with ASHRAE/LEED shows that for some reason the building that is not at code (zero insulation) uses 30% less then the building that is suppose to be at code, and I am sure that the software is wrong. Now I have read the PDF published on the subject, and am very curios if the compliance analysis tool is something that you believe to work correctly? (I would be happy to find out I made some error, but can not find any such errors on my part, and someone told me that the tool does not work so I doubt it is error on my part) Jeremiah D. Crossett CleanTech Analytics 503-688-8951 www.cleantechanalytics.com This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer wrote: I am not upset. I just couldn't tell if you meant to just send that to Maria Elena. My guess is you are going to generate some controversy but that is ok with me. Jason On 4/26/2012 11:28 AM, CleanTech Analytics wrote: Sorry Jason, could you please school me-- what is going on with CanQuest? Why is it that the well documented complience tools can not be used? What should I not say to not upset the modarater? I only said what I think is true from research and use of the tool. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951/ /www.cleantechanalytics.com/ * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer > wrote: Jeremiah, Did you mean to send this to the mailing list? Jason On 4/26/2012 11:16 AM, CleanTech Analytics wrote: The eQuest project is dead, anything that is current is what there is, and there is not more development going into the code. There many are issues, and no support other then this list. To use eQuest you must be comfortable with developing workflows to work around issues you may come across. CanQuest will never be finished, so don't hold your breath, also do not use the compliance tools if you expect to create a compliant building, as they do not work. You could allwees use a spreadsheet to convert, but the text files are very time consuming to convert to spreadsheet. /Jeremiah D. Crossett/ /CleanTech Analytics/ /503-688-8951 / /www.cleantechanalytics.com/ > * This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics * On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue >> wrote: Hi Maria Elena,____ __ __ eQuest doesn't have metric units available yet, though that's one of the major features the Canadian version (called CanQuest) that is under development will add. It has been "soon to be released" for a couple of years now, though, so I would get used to manual unit conversions for the moment.____ __ __ Alex____ __ __ *From:*equest-users-bounces at __lists.onebuilding.org > [mailto:equest-users-bounces at __lists.onebuilding.org >] *On Behalf Of *Maria Elena Soldatti *Sent:* April 25, 2012 5:10 PM *To:* equest-users at lists.__onebuilding.org > *Subject:* [Equest-users] Question about Units____ __ __ ____ Can I usemetric units? when andwhere I can makethe change in units?____ __ __ Thanks. Maria Elena..____ -- La vida te da sorpresas, sorpresas te da la vida. Ay Dios!____ _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > _________________________________________________ Equest-users mailing list http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists -- Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin for onebuilding.org building performance mailing lists IMPORTANT NOTICE: This email message is intended to be received only by persons entitled to receive the confidential information it may contain. Email messages to clients of Performance Systems Development may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. -------------- next part -------------- An HTML attachment was scrubbed... URL: From poleary1969 at gmail.com Fri Apr 27 11:48:16 2012 From: poleary1969 at gmail.com (Patrick J. O'Leary, Jr.) Date: Fri, 27 Apr 2012 11:48:16 -0700 Subject: [Equest-users] OA schedule In-Reply-To: <4F9AE42A.8040103@gmail.com> References: <4F9AD016.6030001@gmail.com> <4F9AD83A.3010908@gmail.com> <4F9AE057.9090009@gmail.com> <90D829482BDEDB4CB264DE5060592B1904885618@lightning.pathfinderengineers.com> <4F9AE42A.8040103@gmail.com> Message-ID: <4F9AE9F0.7090909@gmail.com> the app g, 3.1, no 4 text (2007) states: "HVAC Fan Schedules. Schedules for HVAC fans that provide outdoor air for ventilation shall run continuously whenever spaces are occupied and shall be cycled on and off to meet heating and cooling loads during unoccupied hours." so separating outdoor ventilation from fan cycling does not appear (to me) to be the intent of the app g requirement. why would a fan that provides outdoor air for ventilation be required to operate if it is not providing outdoor air? e.g. doas system or outdoor air supply fan separate from fan in the ahu, or even if the outdoor air ventilation fan is the ahu supply fan (per app g, 3.1, 4). how does the requirement (6.4.3.4.3) apply to an evaporatively cooled system with zero return air? i.e. no return air path. or an evaporative system with no return air path in cooling mode but 80% return in heating mode when mated with a furnace section? app g, 3.1, 4, sounds more logical (to me) without even getting into the debate about how to properly simulate a baseline building system of system type 3 or 4 when the proposed building system is an evaporative cooler with 100% outside air. On 4/27/12 11:23 AM, David Reddy wrote: > Yes, thanks Bill, these are exactly the same points that I was going > to follow up with... > -DR > > On 4/27/2012 11:19 AM, Bishop, Bill wrote: >> I don't see any conflict between App. G and 6.4.3.4.3. I interpret >> the "cycling" language as requiring that the fans cycle to meet >> heating and cooling loads but without providing ventilation. >> Providing ventilation when cycling conflicts with the G3.1.2.5 >> requirement that ventilation rates be the same - you won't get the >> same ventilation during cycling since the proposed and baseline cases >> will differ in the frequency and duration that they cycle. >> >> Regards, >> Bill >> >> -----Original Message----- >> From: equest-users-bounces at lists.onebuilding.org >> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of >> Patrick J. O'Leary, Jr. >> Sent: Friday, April 27, 2012 2:07 PM >> To: David Reddy >> Cc: equest-users at lists.onebuilding.org >> Subject: Re: [Equest-users] OA schedule >> >> good point david, considering a baseline (i.e. minimally compliant >> building) would have to meet the requirement i think the intent of the >> appendix g requirement is to simulate a worst-case scenario concerning >> outside air scheduling and energy consumption. not unlike the >> simulation requirement for a proposed building that a thermal block not >> specified with a cooling or heating system must simulated with one that >> is the same type used in the baseline building simulation (app g, table >> 3.1, no 10, d). >> >> your reference to 6.4.3.4.3 (2007) would explain why a usgbc/gbci >> reviewer could comment on the oa schedule, even though app g is pretty >> specific on how the oa should be scheduled for simulation purposes. >> >> Sambhav, if you're working on a leed project can you ask the review team >> (thru the project on leed online) to clarify which oa requirement method >> should be followed in the simulation - app g or 6.4.3.4.3? >> >> On 4/27/12 10:32 AM, David Reddy wrote: >>> For LEED or other rating systems referencing ASHRAE PRM, it does seem >>> that the 90.1-2007, appendix g, table 3.1 statement is misleading. >>> >>> However, the mandatory shutoff damper controls in section 6.4.3.4.3, I >>> believe, clarifies that the outdoor air should be 0 if cycling system >>> during unoccupied hours, except if the use of OA reduces energy costs >>> (night purge, economizer). >>> >>> If you specify 0.001 in your MIN-AIR-SCH (enables use of economizer), >>> I would review your system's hourly OA levels to make sure it is >>> behaving as expected, especially for multizone systems. I have found >>> that this can lead to a significant amount of additional heating, as >>> the economizer will be used to achieve the SAT control setpoint, even >>> if this is not appropriate in the middle of the winter... As such, I >>> typically set the unoccupied MIN-AIR-SCH value to 0. >>> >>> - David >>> >>> On 4/27/2012 9:57 AM, Patrick J. O'Leary, Jr. wrote: >>>> depends on the modeling requirements. 90.1? owner requirement? >>>> leed? something else? >>>> >>>> for 90.1-2007, appendix g, table 3.1, no. 4 schedules, specifically >>>> states the "hvac fans that provide outdoor air for ventilation shall >>>> run continuously whenever spaces are occupied and shall be cycled on >>>> and off to meet heating and cooling loads during unoccupied hours." >>>> 90.1-2004 doesn't specify fans specifically for outdoor air for >>>> ventilation, it just says hvac fans - which is the same as the system >>>> supply fan in a non-doas/economizer capable of completely closing the >>>> outdoor air damper system so the outdoor air can't be shut off. >>>> >>>> so for a 90.1-2007 simulation the minimum oa should not be zero >>>> during unoccupied hours. >>>> >>>> On 4/27/12 9:44 AM, sambhav tiwari wrote: >>>>> Hi All, >>>>> It is necessary to specify the min OA schedule as -999 >>>>> for >>>>> occupied and 0 for unoccupied hrs at either system or zone level >>>>> or it >>>>> can be skipped. >>>>> > From robbyoylear at gmail.com Fri Apr 27 13:08:33 2012 From: robbyoylear at gmail.com (Robby Oylear) Date: Fri, 27 Apr 2012 13:08:33 -0700 Subject: [Equest-users] Is eQuest still under development ? In-Reply-To: <0EAD8301557542F9BE11978C9A24390B@SM> References: <0EAD8301557542F9BE11978C9A24390B@SM> Message-ID: eQUEST twitter account to follow for updates/random musings would be pretty great.... Just a thought :) -Robby On Fri, Apr 27, 2012 at 11:30 AM, Shaun Martin < smartin at shaunmartinconsulting.com> wrote: > ** > Hi Jeff, > > Your comments beg the question: what's new in DOE-2.3? Details please! > > Shaun > > Shaun Martin LEED AP > Principal > Shaun Martin Consulting > 2060 Pine Street, Vancouver BC V6J 4P8 > 604-789-1095 > smartin at shaunmartinconsulting.com > member CAGBC, ASHRAE > > > ------------------------------ > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jeff Hirsch > *Sent:* Thursday, April 26, 2012 7:52 PM > *To:* equest-users at lists.onebuilding.org > > *Subject:* Re: [Equest-users] Is eQuest still under development ? > > The Mark Twain quote is most appropriate. Thank you Chris. Our group > rarely participates in these forums, but I felt some response to this > somewhat annoying rumor was needed. Some of the discussion also brings to > mind another familiar proverb: a bad workman always blames his tools. But > also I am reminded that, if all you have is a hammer everything looks like > a nail. So I add to the ?controversy? here. > > > > eQUEST and DOE-2 are alive and well and our combined development efforts > are at an equal or higher funding and effort level than ever before. > However, we will continue to provide all our DOE-2 and eQUEST products as > freeware to the simulation communities around the world. We support the > overall community activities so that the community can offer analysis and > support services to derive income based upon use of our products. > > > > We tend not to compete with the community by offering those same analyses > and support services ourselves with the exception of providing eQUEST and > DOE-2 training. Thus we as a group do not normally offer fee based support > services except to a small group of our long-term clients who also > generally support our development efforts ? we leave those fee based > support service opportunities to you, the user community, as an income > source. > > > > With thousands of eQUEST and DOE-2 installation around the world, we > receive too many emails per day to possibly respond. We especially cannot > respond to standard support requests as that request should be directed to > those offering fee based support services. We try to pay attention and > examine requests when program bugs or errors are suspected. But quite often > we need to delay any fixes to the next program release. Our focus on > DOE-2.3 and program develop environment changes for both eQUEST and DOE-2 > has slowed our releases for the past two years. That will change this year, > so be patient please. > > > > We do not develop eQUEST or DOE-2 using a license fee income based model. > Rather we develop our tools to support the analysis needs of our major > clients and the general user community. We have no plans to change our > model. Like all software, eQUEST and DOE-2 will have quirks, bugs and > limitations. No realistic or truthful company offering software could claim > otherwise. However, we plan to continue making improvements and have the > resources to do so. > > > > What is coming? Several things are coming in the next year. DOE-2.3 has > been in beta for some time. We will release that new version when we are > confident it can be used in production work in place of DOE-2.2. A version > of eQUEST that fully supports DOE-2.3 that will be released at the same > time. DOE-2.2 is also still under development, but we tend to implement all > major new features in DOE-2.3 rather than DOE-2.2. We expect to release an > update to both eQUEST and DOE-2.2 soon with DOE-2.3 and its eQUEST version > later. The DOE-2.2 refrigeration version development continues, however > more priority has been placed on DOE-2.3 recently; however, we will also > release an update to that application as well and we consider that version > an important product to continue to upgrade well into the future. > > > > I am not sure why rumors of the impending death of DOE-2, that started in > the late 1990?s, continue to persist since the evidence for the past > fifteen years should have proven those rumors wrong. Similarly, the rumors > about the death of eQUEST that have appeared more recently can be also > similarly be ignored as completely false. The real history shows that our > DOE-2 and eQUEST products have proven to have more funding and longevity > ?legs? than any other existing similar software. While other development > groups struggle to advance one simulation program or one user interface we > have shown that our group can do both the engine and interface with major > advances to both for decades and as freeware. I see no change coming in our > ability to continue the upgrade of both in the current decade. > > > > You should, as a community, be more concerned with the long term viability > of other groups making big claims that have a long way to go before they > can claim to be offering the simulation community the mature, stable, > reliable capabilities free as you get from our products. It is much easier > for a developer to claim their product can do amazing things than it is for > the user community to realize those possible gains while maintaining the > ability to deliver services to their clients competitively in a timely > manner. We plan to do our best to continue to offer you products that allow > you to perform your job or earn a living, and keep your clients satisfied. > In return we ask for your continued support, patience and generally good > vibes. We also ask that you continue to support one another in this and > other forums, as the freeware nature of our products requires the user > community to hang together and exchange information and ideas. > > > > With that, I return to my observation deck. > > ps ? For some reason I and others in my group do not get all the emails > from this forum ? of the multiple emails Mr. Crossett sent to the forum and > myself below I received none but I did, obviously see the one I am now > responding to. Not sure of the cause, but I do get hundreds of emails per > day and cannot even open many. > > ------------------------------ > Jeff Hirsch > James J. Hirsch & Associates > > *From:* Chris Balbach > *Sent:* Thursday, April 26, 2012 10:05 AM > *To:* CleanTech Analytics ; > jglazer at gard.com ; equest-users at lists.onebuilding.org ; > jeff.hirsch at doe2.com > *Subject:* RE: [Equest-users] Is eQuest still under development ? > > > All: > > > > I think it was Mark Twain who said ?The reports of my death are greatly > exaggerated." > > > > I note a (presumably working) demonstration of the CanQuest software is on > the slate for the ESim conference in Halifax next week. See page 14 of the > ESim Program posted here: http://esim.ca/ > > > > All the Best, > > > > _Chris > > > > Chris Balbach, PE, CEM, CMVP, BEAP, BESA, BEMP > > Vice President of Research and Development > > Performance Systems Development of NY,LLC > > 124 Brindley Street, Suite 4,Ithaca, NY 14850 > > http://www.psdconsulting.com > > ph: (607)-327-1647 > > > > > > > > > > > > *From:* equest-users-bounces at lists.onebuilding.org [mailto: > equest-users-bounces at lists.onebuilding.org] *On Behalf Of *CleanTech > Analytics > *Sent:* Thursday, April 26, 2012 12:50 PM > *To:* jglazer at gard.com; equest-users at lists.onebuilding.org; > jeff.hirsch at doe2.com > *Subject:* Re: [Equest-users] Is eQuest still under development ? > > > > List, I do not mean to cause controversy but I am going to re-post this to > see if it gets a response this time. > > > > > > When I had an issue I tracked down the phone number for the Hirsch's of > 805-532-1045, and left a voicemail, then was texted back the message > "please send email to jeff.hirsch at doe2.com and when I emailed the below I > never got a response, and after that as well as after much research showed > there is no DOE funding, or sales revenue to fund the eQuest project > assumed that the project is "dead"....If I am wrong, someone from the > eQuest development team please respond to my questions? > > > > > Jeff, > I am working on a LEED compliance building model in eQUEST, and have to > ask you a question. So I created a building that has zero insulation, > standard lighting watts/sqft and ran the compliance analysis. The building > that is not at code energy costs are in the sixty thousand range, and the > 0,90,180,270 average that should be at code is in the ninty thousand > range.This %30 savings for the building that has zero insulation over the > building that has been auto generated to be complaint with ASHRAE/LEED > shows that for some reason the building that is not at code (zero > insulation) uses 30% less then the building that is suppose to be at code, > and I am sure that the software is wrong. > > Now I have read the PDF published on the subject, and am very curios if the > compliance analysis tool is something that you believe to work correctly? > (I would be happy to find out I made some error, but can not find any such > errors on my part, and someone told me that the tool does not work so I > doubt it is error on my part) > > > *Jeremiah D. Crossett* > > *CleanTech Analytics* > > *503-688-8951* > > *www.cleantechanalytics.com* > > > > *This document may contain valuable information proprietary to CleanTech > Analytics which is private and confidential. It may not be shared, copied, > stored or transmitted in any form without the prior written consent of > CleanTech Analytics*** > > > > > > On Thu, Apr 26, 2012 at 9:30 AM, Jason Glazer wrote: > > I am not upset. I just couldn't tell if you meant to just send that to > Maria Elena. My guess is you are going to generate some controversy but > that is ok with me. > > Jason > > > > On 4/26/2012 11:28 AM, CleanTech Analytics wrote: > > Sorry Jason, could you please school me-- what is going on > with CanQuest? Why is it that the well documented complience > tools can not be used? What should I not say to not upset > the modarater? I only said what I think is true > from research and use of the tool. > > > > > /Jeremiah D. Crossett/ > /CleanTech Analytics/ > /503-688-8951/ > /www.cleantechanalytics.com/ > > > * > > This document may contain valuable information proprietary > to CleanTech Analytics which is private and confidential. It > may not be shared, copied, stored or transmitted in any form > without the prior written consent of CleanTech Analytics > > * > > > On Thu, Apr 26, 2012 at 9:19 AM, Jason Glazer > > > wrote: > > Jeremiah, > > Did you mean to send this to the mailing list? > > Jason > > > On 4/26/2012 11:16 AM, CleanTech Analytics wrote: > > The eQuest project is dead, anything that is current > is what > there is, and there is not more development going > into the > code. There many are issues, and no support other > then this > list. To use eQuest you must be comfortable with > developing > workflows to work around issues you may come across. > CanQuest will never be finished, so don't hold your > breath, > also do not use the compliance tools if you expect > to create > a compliant building, as they do not work. > > You could allwees use a spreadsheet to convert, but > the text > files are very time consuming to convert to spreadsheet. > > > > > > /Jeremiah D. Crossett/ > /CleanTech Analytics/ > > /503-688-8951 / > /www.cleantechanalytics.com/ > > > > > > > > > * > > This document may contain valuable information > proprietary > to CleanTech Analytics which is private and > confidential. It > may not be shared, copied, stored or transmitted in > any form > without the prior written consent of CleanTech Analytics > > * > > > > On Thu, Apr 26, 2012 at 6:49 AM, Alex Blue > > > > > >> wrote: > > Hi Maria Elena,____ > > __ __ > > > eQuest doesn?t have metric units available yet, > though > that?s one of the major features the Canadian > version > (called CanQuest) that is under development will > add. > It has been ?soon to be released? for a couple > of years > now, though, so I would get used to manual unit > conversions for the moment.____ > > __ __ > > Alex____ > > __ __ > > *From:*equest-users-bounces at __lists.onebuilding.org equest-users-bounces at lists.onebuilding.org> > > > > [mailto:equest-users-bounces at __lists.onebuilding.org equest-users-bounces at lists.onebuilding.org> > > > >] *On > Behalf Of *Maria Elena Soldatti > *Sent:* April 25, 2012 5:10 PM > > *To:* equest-users at lists.__onebuilding.org > > > > > > *Subject:* [Equest-users] Question about Units____ > > __ __ > > > ____ > > Can I usemetric units? when andwhere I can makethe > change in units?____ > > __ __ > > Thanks. Maria Elena..____ > > > -- > La vida te da sorpresas, sorpresas te da la vida. Ay > Dios!____ > > _________________________________________________ > Equest-users mailing list > > http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org > > > < > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org> > To unsubscribe from this mailing list send a blank > message to > > EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > > > > > > > > > _________________________________________________ > Equest-users mailing list > > http://lists.onebuilding.org/__listinfo.cgi/equest-users-__onebuilding.org > > > < > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org> > To unsubscribe from this mailing list send a blank > message to > > EQUEST-USERS-UNSUBSCRIBE at __ONEBUILDING.ORG > > > > > > -- > Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair > > Admin for onebuilding.org > building performance mailing lists > > > -- > Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair > Admin for onebuilding.org building performance mailing lists > > > IMPORTANT NOTICE: This email message is intended to be received only by > persons entitled to receive the confidential information it may contain. > Email messages to clients of Performance Systems Development may contain > information that is confidential and legally privileged. Please do not > read, copy, forward, or store this message unless you are an intended > recipient of it. If you have received this message in error, please forward > it to the sender and delete it completely from your computer system. > > _______________________________________________ > Equest-users mailing list > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org > To unsubscribe from this mailing list send a blank message to > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG > > -------------- next part -------------- An HTML attachment was scrubbed... URL: From sharma_vipin138 at yahoo.com Sat Apr 28 21:30:14 2012 From: sharma_vipin138 at yahoo.com (Vipin Sharma) Date: Sat, 28 Apr 2012 21:30:14 -0700 (PDT) Subject: [Equest-users] Temperature and relative humidity in eQUEST Message-ID: <1335673814.21025.YahooMailNeo@web45607.mail.sp1.yahoo.com> How can I know Hourly Temperature and relative humidity in eQUEST Thanks and Regards vipin sharma M.Tech.(Energy) -------------- next part -------------- An HTML attachment was scrubbed... URL: From hutiejun1223 at 126.com Mon Apr 30 07:55:15 2012 From: hutiejun1223 at 126.com (tiejun hu) Date: Mon, 30 Apr 2012 22:55:15 +0800 (CST) Subject: [Equest-users] CAD draws handling Message-ID: <32bda2a0.f213.13703bf939b.Coremail.hutiejun1223$126.com> Hi: guys Does anybody has good expirience in handling CAD draws, Generlly, the draws are complicated, for example all the walls are comprised of double line or more,however during creating simple draws for equest, we just need walls only include one line. but if we use "line" order in cad tools to draws walls one by one, i think this is time-consuming. and i doubt whether exist some plug-in of CAD tools which can automatcally transform all multi-line walls to single-line wall? if any, or any good methords, please guide! thanks in advance! BEST REGARDS Tiejun -------------- next part -------------- An HTML attachment was scrubbed... URL: From ncaton at smithboucher.com Mon Apr 30 14:09:58 2012 From: ncaton at smithboucher.com (Nick Caton) Date: Mon, 30 Apr 2012 21:09:58 +0000 Subject: [Equest-users] Temperature and relative humidity in eQUEST In-Reply-To: <1335673814.21025.YahooMailNeo@web45607.mail.sp1.yahoo.com> References: <1335673814.21025.YahooMailNeo@web45607.mail.sp1.yahoo.com> Message-ID: Hi Vipin, Explore the Hourly Reports feature and you'll find what you're looking for. You will need to peruse the variety of options to find more precisely what you're thinking of. The attached discussion from the archives should help you find where to get started. "Hourly Temperature" can suggest a lot of things - if you're looking for temperature in a room that is a zone variable. If you're looking for a temperature in a specific airstream that is probably a system variable. Best advice here is to take a few minutes to explore what is available under all the various categories to build a degree of familiarity, and be sure to select a zone/system/space/loop/etc... that applies to what you're investigating specifically. Humidity ratios can be tracked for a variety of airstreams: return, mixed air, after coils, after humidification/de-humidification and so on... All these are system variables, though there exist a few zonal/terminal system options as well. Best of luck! ~Nick [cid:489575314 at 22072009-0ABB] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vipin Sharma Sent: Saturday, April 28, 2012 11:30 PM To: equest-users at lists.onebuilding.org Subject: [Equest-users] Temperature and relative humidity in eQUEST How can I know Hourly Temperature and relative humidity in eQUEST Thanks and Regards vipin sharma M.Tech.(Energy) -------------- next part -------------- An HTML attachment was scrubbed... URL: -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 1459 bytes Desc: image001.jpg URL: -------------- next part -------------- An embedded message was scrubbed... From: Neil Bulger Subject: Re: [Equest-users] OA from System Date: Mon, 13 Jun 2011 21:33:11 +0000 Size: 90784 URL: From bruce5 at bellnet.ca Mon Apr 30 15:27:20 2012 From: bruce5 at bellnet.ca (Bruce Easterbrook) Date: Mon, 30 Apr 2012 18:27:20 -0400 Subject: [Equest-users] CAD draws handling In-Reply-To: <32bda2a0.f213.13703bf939b.Coremail.hutiejun1223$126.com> References: <32bda2a0.f213.13703bf939b.Coremail.hutiejun1223$126.com> Message-ID: <4F9F11C8.6060405@bellnet.ca> An HTML attachment was scrubbed... URL: From A.Marston at eb-engineers.com Mon Apr 30 16:10:21 2012 From: A.Marston at eb-engineers.com (Annie Marston) Date: Mon, 30 Apr 2012 23:10:21 +0000 Subject: [Equest-users] IBPSA DC Meeting 16th MAY Message-ID: <0AA5AFEB744B3B45A874C5905D6C3686F62BA779@EB-MAIL01.ebertbaumann.com> Hi, we are having a DC IBPSA meeting on the 16th May, it would be lovely to see as many people there as possible, here are the details: May 16th DC National IBPSA Chapter Topic: Understanding the Energy Service Company Performance Contracting process and the advantages and disadvantages of energy modeling within that process. Presenter: James Kiriazes, Engineering Manager, Honeywell Americas Federal Systems Group. Mr. Kiriazes has over 20 years of experience in the energy industry and has worked in power generation as well as in energy efficiency and conservation. He is responsible for the development of energy saving performance contracts for Honeywell's Federal Systems Group where over $500m in ESPC projects have been developed in the past three years. Mr. Kiriazes manages a team of energy engineers and professionals across the country, all of which operate in a virtual work environment. He holds his Professional Engineer registration in Florida, is a Certified Energy Manager with the Association of Energy Engineers and is a LEED(tm) accredited professional with US Green Building Council. Location: WRL DC Office (1634 Eye St NW Suite 900, Washington, DC 20006, Located Above Farragut West Metro @ 17th St Exit) Please contact me if you have any questions Annie Dr. A. Marston, Ph.D. LEED(r) AP BEMP Head of the Building Performance Group Ebert & Baumann Consulting Engineers, Inc. An Enterprise of the Ebert-Consulting Group 734 15th Street, NW Suite 1000 Washington, D.C. 20005, USA Tel +1.202.608.1334 Fax +1.202.544.1434 a.marston at eb-engineers.com -------------- next part -------------- An HTML attachment was scrubbed... URL: