[Equest-users] Fan Power for GSHP units
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Fri Sep 23 06:57:42 PDT 2011
    
    
  
Gerry,
 
To allow access to the System kW/cfm field, select "Restore Default" in
the "Static in WG" field first. For zone kW/cfm, I don't think zone fan
power is appropriate unless you are trying to model powered induction
unit boxes or some equivalent.
 
Regards,
Bill
 
 
 
 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gerard
Hazel
Sent: Friday, September 23, 2011 7:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan Power for GSHP units
 
Hi all,
I am modeling a GSHP system for a LEED project. In the proposed model I
am using HVAC  System type Water Loop Heat Pump. I am trying to be
consistent with the way I entered the fan power for the baseline - in
kw/cfm - but the box for that is greyed out in the system level
spreadsheet for Fans- Fan Power and in the Zone Level for Zone Fan
kW/flow (kW/cfm).
I entered the cooling efficiency for these units as EER so I assume I
have to break out the fan power.
Can anyone help?
Thanks in advance.
Gerry Hazel
 
Gerard Hazel
Sustainable Systems LLC
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110923/b7169cc3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 9174 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110923/b7169cc3/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110923/b7169cc3/attachment.jpeg>
    
    
More information about the Equest-users
mailing list