[Equest-users] equest results for system sizing

Deepika deepika.khowal at gmail.com
Mon Sep 19 07:31:29 PDT 2011


Thanks for the inputs. . 
So typically use the kw numbers from Equest and use it in trace ? 
Do you also add a sizing factor ? 



On Sep 19, 2011, at 6:49 AM, PKConsulting <pasha.pkconsulting at gmail.com> wrote:

> Deepika
> Use the sv-a reports for ahu sizing.
> 
> Pashalu
> 
> On Sep 19, 2011, at 6:33 AM, "Will Mak" <wmak at epsteinglobal.com> wrote:
> 
>> Honestly, I don’t like using eQuest for load calcs. I typically use Trane Trace or HAP…
>> 
>>  
>> 
>> Especially since the load summary states in big letters that ventilation is not accounted for in the calcs. You could do them separately but still…
>> 
>>  
>> 
>> Just my 2 cents.
>> 
>>  
>> 
>> William Mak, LEED AP BD+C
>> Mechanical Design Engineer
>> 
>> EPSTEIN
>> 600 West Fulton Street
>> Chicago, Illinois 60661-1259
>> D: (312) 429-8116
>> 
>> 
>>  
>> 
>> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of deepika khowal
>> Sent: Sunday, September 18, 2011 5:33 PM
>> To: equest-users at lists.onebuilding.org
>> Subject: [Equest-users] equest results for system sizing
>> 
>>  
>> 
>> Hi all
>> 
>> I would like to know to get an idea for system sizing based on modeling in equest.
>> 
>> where in equest do everyone look for sizing Numbers?
>> 
>> I have always been looking at design sizing tons from air side HVAC tab. But I realized they are very different from detailed report sizing.
>> 
>> If anyone can direct me through this, it will be helpful.
>> 
>>  
>> 
>> 1.       Using air-side HVAC summary : design sizing tons
>> 
>> <image001.jpg>
>> 
>>  
>> 
>> 2.       Using building peak components, taking the kbtu/hsf number and diving by 12000 to get cooling tons. This number is very low compared to design capacity.
>> 
>> <image002.jpg>
>> 
>>  
>> 
>> 3.       Using PS-C report
>> 
>> <image003.jpg>
>> 
>>  
>> 
>> Is there any other report which mechanical designers use to size system?
>> 
>> Thanks
>> 
>>  Deepika
>> 
>>  
>> 
>>  
>> 
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110919/98186745/attachment.htm>


More information about the Equest-users mailing list