[Equest-users] Increasing OA temp for specific AHUs
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Tue Sep 13 12:31:43 PDT 2011
    
    
  
Dana,
 
I am not aware of a way to increase OA temp in a model and isolate it to a specific AHU(s). You could change the weather file, but then you are drastically altering your envelope and ventilation loads for the entire building. Even if you could, I don't think it is reasonable to increase the OA temp uniformly, since the relief air will likely be the same temperature within a narrow range year round, while the OA temp has a much bigger range. If your building is in a heating-dominated climate, the short-circuiting of the relief air could actually reduce the ventilation heating load and save heating energy.
 
One thing you could try is to reduce the ventilation load in the model, since your situation is essentially returning more air to the system then the original system design. How much to reduce it is guesswork unless you're a wiz with CFD. For example, you could change your OA from 20% to 10% and see what the impact is. You could also adjust the temperature limits on the economizer.
 
Regards,
Bill
 
 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dana Etherington
Sent: Tuesday, September 13, 2011 2:55 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Increasing OA temp for specific AHUs
 
Modelers,
 
We have relief/exhaust louvers located very close to the intake louvers in an existing mechanical space, and are trying to show the client how this kills their energy consumption. This lowers energy saved from the economizer during winter months, and also makes the unit work even harder in the summer. 
 
Is there a way to raise the OA +20 deg over ambient, for the whole year, and for specific AHUs? I think this will be a decent estimate on the increased energy consumption from this scenario. Or maybe someone has modeled this a different way??
 
Any help is greatly appreciated. Thanks!
 
-Dana
 
Mr. Dana Etherington, E.I.T., LEED AP BD+C | CRB | One Kendall Square Ste B2202 | Cambridge, MA 02139
Main: 617-475-3050 | Direct: 617-475-3061 | Mobile: 617-583-3009 | Fax: 617-475-3052 | Ext: 6061
Email: dana.etherington at crbusa.com <mailto:dana.etherington at crbusa.com>  | www.crbusa.com <http://www.crbusa.com/> 
________________________________________________________________________________________
 
This document may contain confidential information and is intended for use by the addressee only. If you are not 
the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you 
received this message in error, please notify the sender immediately and delete this message.
 
ü Please consider the environment before printing this email.
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/d750826a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110913/d750826a/attachment.jpeg>
    
    
More information about the Equest-users
mailing list