[Equest-users] Wizard BDL Error When Defining Custom Zones
    Patrick J. O'Leary, Jr. 
    poleary1969 at gmail.com
       
    Tue Sep 13 09:07:53 PDT 2011
    
    
  
looking at screen 14, do you have a zone group defined without a zone 
assigned to it?  this would be the same as having an empty zone in 
detailed mode (i.e. no space assigned to a zone).  detailed mode 
requiring the space (your initial customing zoning) assigned to a zone 
(the zone group wizard screen 14) assigned to an hvac unit of some type.
On 9/13/11 8:41 AM, Paul Diglio wrote:
> Patrick:
>
> The HVAC unit is assigned for each zone I enter.   Initially, I had 
> one zone per floor.  When I started to add custom zones I made sure 
> that each zone on screen 14 of the shell create/modify wizard is 
> assigned to the hvac system.
>
> I am unsure of what the error message means so I am having difficulty 
> correcting it.   I even tried to create custom zones on the second 
> floor of this building and I get the same error, but I was able to 
> create custom zones in the basement of this building without any errors.
>
> Sincerely,
>
> Paul Diglio
>