Thanks Robby, Keith, Jeremy and Brian for your feedback.
I like the idea of referencing C-ACTIVITY-DESC in user input
expressions. What is the size limit of nested If-Then statements if you
want to allow for many space activity types? In particular, would it be
possible to create a user expression that returned the ASHRAE 90.1
baseline lighting value (W/ft2) based on space activity type? I would
want to allow at least 20 or so space types. Could you use a Switch
statement? Is there a way to assign integer values to space activity
types, since Switch needs an integer-compatible expression?
Thanks,
Bill
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Robby
Oylear
Sent: Friday, October 14, 2011 11:13 AM
To: Dane Heimerman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Using global parameters to streamline
modeling
Dane,
What I'm discussing is in the Detailed Edit mode. Part of our efforts
to streamline energy modeling has been to stay out of the wizard as much
as possible. We mainly just use the wizard to setup the building shell,
define slab penetrations, and infiltration rates (i.e. things that are
hard to do in detailed edit mode).
Under the Building Shell tab in, select any space within your project.
C-ACTIVITY-DESC is located here:
We use a three letter acronym to describe the space type. In the
example above this space is a corridor. You can then create conditional
statements for most of the Space and/or Zone parameters based on this
acronym.
For example, a user default expression for equipment W/SF can be written
as such:
if(#L("C-ACTIVITY-DESC")=="COR")
then (0.25) else
no_default
endif
These statements can have varied levels of complexity due to the nature
of referencing the different variables in eQUEST using the #BDL
functions. For instance, in the above example I'm referencing the local
BDL keyword "C-ACTIVITY-DESC" by using the BDL function #L which
references a local BDL keyword.
Hope this helps,
Robby Oylear, LEED(r) AP BD+C
Mechanical Project Engineer
Energy Analyst
D 206-788-4571 | C 206-354-2721
www.rushingco.com <http://www.rushingco.com/>
On Fri, Oct 14, 2011 at 5:58 AM, Dane Heimerman <daneh at mlnai.com> wrote:
Robby,
Could you go over the basics of this C-ACTIVITY-DESC? I stumbled upon
this thread, and it intrigued me, but I can't find what you're talking
about. Where is 'space parameters'? Is this within the schematic of DD
Wizard, or in detailed mode? If you could just get me pointed in the
right direction, I'm usually able to struggle through it and learn on my
own.
Thanks,
Dane Heimerman, EIT
HVAC Engineer
Michael L. Norris & Associates, Inc.
270 Walker Dr, Suite 201B
State College, PA 16801
p:814.867.3823
f:814.867.4823
daneh at mlnai.com
On 10/13/2011 6:05 PM, Robby Oylear wrote:
Bill,
When I look at most of my project files, the Global Parameters
list is pretty standard, however each parameter is usually project
specific, i.e. Number of Residences, Glazing Ht by Orientation, System
Efficiencies.
One thing that can really help speed up modeling is to get fancy
with the user-defined defaults, using basic IF/THEN statements you can
setup default schedules, lighting w/sf, equip w/sf, infiltration etc.
based on a trigger of the space.
Using the C-ACTIVITY-DESC command under the Space Parameters you
can label a space based on use, and have your defaults do the rest of
the work for you.
-Robby
On Thu, Oct 13, 2011 at 1:11 PM, Bishop, Bill <
wbishop at pathfinder-ea.com> wrote:
Does anyone use pre-defined global parameters in an input file
that they import, as a way to streamline the modeling process?
I already have ASHRAE schedules and building constructions in an
input file that I import, but I never use global parameters.
I make most of my universal changes by using User-Defined
Default Values. Am I missing a big opportunity to speed up the modeling
process?
Thanks,
Bill
Error! Filename not specified.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111014/dc3193b6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 36090 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111014/dc3193b6/attachment.png>
More information about the Equest-users
mailing list