[Equest-users] U-Value unexpected impact
Omar Osama
o_osama at live.com
Thu Oct 13 12:37:04 PDT 2011
Thanks so much,I do appreciate your reply ,, I shall re-check internal loads, guess I have excessive lighting loads.
Omar AlRawiProject Engineer,EA Sustainable Building Consultants
www.ea-buildingconsultants.com
From: akrickx at seriousenergy.com
To: chris at greenengineer.com; o_osama at live.com; equest-users at lists.onebuilding.org
Date: Thu, 13 Oct 2011 10:39:02 -0700
Subject: RE: [Equest-users] U-Value unexpected impact
Hi Omar,
Another thing to check is that you are modeling a glass with a low-Solar Heat Gain Coefficient (SHGC). Low SHGC glasses and glass-units are best for situations where there is no need for passive heating (hot climates and internal load-dominated
buildings).
You can still maintain high VT (>0.5) with low SHGC (<0.3), so it doesn't need to sacrifice aesthetics and daylighting options.
Great point on the internal loads Chris.
Cheers,
Alex
Alex Krickx, LEED AP
Building Energy Specialist
Serious Energy, Inc.
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
akrickx at seriousenergy.com
The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then
you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments.
From: equest-users-bounces at lists.onebuilding.org [equest-users-bounces at lists.onebuilding.org] On Behalf Of Christopher Schaffner [chris at greenengineer.com]
Sent: Thursday, October 13, 2011 10:04 AM
To: Omar Osama; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] U-Value unexpected impact
In mild weather, with high internal heat gains, the losses through the glazing reduce the cooling load. In this situation, increasing the performance of the glass will cause increased energy consumption.
This counterintuitive result is often the result of an overestimation of internal heat gains. You should perform a reality check on your internal heat gains, before you determine if this result is correct.
--
Chris Schaffner, PE
LEED Fellow
Founder and Principal
The Green Engineer, LLP
Sustainable Design Consulting
50 Beharrell Street
Concord, MA 01742
T: 978.369.8978
M:978.844.1464
chris at greenengineer.com
www.greenengineer.com
The Green Engineer, LLP is a Certified B Corporation
From: Omar Osama <o_osama at live.com>
Date: Thu, 13 Oct 2011 16:07:13 +0200
To: <equest-users at lists.onebuilding.org>
Subject: [Equest-users] U-Value unexpected impact
All,
I'am modelling a mid-rise, curtain wall, office building in Egypt (hot humid climate 2a). while I do decrease the glazing's U-value, below 0.5, the energy consumption tends to increase. does this
issue have a reality related explanation, is it a problem in my file, or is it a software bug issue?
Thanks for consideration,
Omar AlRawi
Project Engineer , EA Sustainable Building Consultants
www.ea-buildingconsultants.com
_______________________________________________ Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111013/2caa164e/attachment.htm>
More information about the Equest-users
mailing list