[Equest-users] Underheating warning for bunch of zones

Rob Hudson rdh4176 at gmail.com
Tue Nov 29 12:02:43 PST 2011


I would first check your system level inputs.  Have you used a VAV system?
if so, you need to know that these systems don't like to use the heating
coil in the air handler and therefore you need to specify a reheat coil
size and a preheat coil.  Also, if you have baseboards in the model, they
don't like to operate very well when set to activate to outdoor conditions.
 I always set the baseboard control to thermostat.

Hopefully these few tips help out.

Rob

On Tue, Nov 29, 2011 at 2:52 PM, Nikola Kravik <NKravik at willdan.com> wrote:

> hi,****
>
> ** **
>
> I’m simulating CHW Plant with CAV AHU’s and bunch of packaged/split system
> units around supporting areas of the hospital/clinic.****
>
> ** **
>
> I get the warning messages similar to below for almost all my zones  and
> my gas heating hot water is extremely low, no matter what I try do on the
> heating side. I added baseboards but it didn’t make a difference-still have
> bunch of zones underheated looking at the ss-o’s. ****
>
> Do you any other hints you can share where else to look for the HHW low
> consumption?****
>
> ** **
>
> Best,****
>
> Nikola****
>
> ****
>
> ****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111129/d4deaf76/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 92188 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111129/d4deaf76/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 47313 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111129/d4deaf76/attachment.png>


More information about the Equest-users mailing list