[Equest-users] Delayed wall warning

Nick Caton ncaton at smithboucher.com
Fri Nov 11 12:01:18 PST 2011


Direct solution:  Define the constructions that space's surfaces
reference using layers that have mass.  Entry with only U-value =
weightless.

 

Otherwise:  I think this message is telling you eQuest can't figure out
how heavy the contents of the room (surfaces, furniture, etc...) are,
and is therefore assuming 70lb/ft2.  You could just accept that
assumption if it's reasonable for your project.

 

~Nick

 

 

 

NICK CATON, P.E.

SENIOR ENGINEER

 

Smith & Boucher Engineers

25501 west valley parkway, suite 200

olathe, ks 66061

direct 913.344.0036

fax 913.345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian
Lo
Sent: Friday, November 11, 2011 1:15 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Delayed wall warning

 

I go the message:

 

custom weighting can not be calculated for SPACE EL1 Core Plnm (B.C43)
has 0 delayed walls, 1 delayed floors and 0 delayed ceilings. There
should be at least a delayed wall and floor, a delayed wall and ceiling,
or a delayed ceiling and floor for custom weighting factors to be
calculated. ASHRAE weighting factors with floor weight of 70 lb/ft2 (342
kg/m2).

 

 

How can i fix this problem?

 

Thanks

Brian

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111111/eedc7f4c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111111/eedc7f4c/attachment.jpeg>


More information about the Equest-users mailing list