[Equest-users] EEM Reports

Dave Bastow dbastow at mcclure-engineering.com
Wed Nov 9 14:09:40 PST 2011


Of course, you can always take the existing base file and Save As under a
new file name and then make modifications to the new file and run both files
and compare the output results.

Dave

 

From: Scott Criswell [mailto:scott.a.criswell at gmail.com] 
Sent: Wednesday, November 09, 2011 11:26 AM
To: andres.franco at microcad.com.co
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EEM Reports

 

There are two separate design alternative analysis systems available in
eQUEST.  The EEM (Energy Efficiency Measure) run mechanism that is accessed
via the toolbar button you have identified is only able to operate on
building creation wizard inputs.  Since the building model you have loaded
into eQUEST was not created using the eQUEST wizards, the EEM run option is
not available to you for this project.
The other "Parametric Run" feature IS however available for projects such as
this one, where the model is editable in the detailed interface.  Access
this feature using the menu bar via Tools - Parametric Runs.
The parametric run interface doesn't hold your hand quite as much as the EEM
one does, as you have to identify each individual parametric run change, but
there should be plenty of flexibility to setup alternative design runs.
I recommend you review the eQUEST tutorials for more information on the
Parametric Run feature.  This section can be found in the eQUEST Modeling
Procedures Quick Reference Guide in the most recent release(s) but in
earlier releases it was located in the Introductory Tutorial.

Best regards,

- Scott

On 11/9/2011 7:39 AM, Andres Franco Usme MicroCAD S.A.S wrote: 

Hi everyone, I want to make an EEM, but the button is grayed out, how is
possible to activate it?, see image below, I need to know if it’s due to an
input error or any other parameter that I wasn’t  see, any suggestion will
be appreciated, thanks a lot.

 



 

 

Cordialmente,

 

Andrés Franco U.

Arquitecto/ LEED Green Associate

Director División Arquitectura Construcción y Mantenimiento 

MicroCAD S.A.S.
www.microcad.info <http://www.microcad.info/>  // blog.microcad.info
<http://blog.microcad.info/> 
Tel: (57) (4) 293 21 21 ext 108 // 444 81 49 // Fax: 604 16 02
Calle 55 # 46-14 Ed. Perú Oriental Piso 13 // Medellín – Colombia

Description: Descripción: Descripción:
cid:7985792F-A620-443C-96D9-D84A8364C671

Antes de imprimir este mensaje, asegúrese de que es realmente necesario

El medio ambiente es cosa de todos

 






_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG






No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1869 / Virus Database: 2092/4605 - Release Date: 11/08/11

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111109/871c0280/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 29997 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111109/871c0280/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 37885 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111109/871c0280/attachment.png>


More information about the Equest-users mailing list