[Equest-users] Supporting to review detail project

Nick Caton ncaton at smithboucher.com
Mon Nov 7 15:59:20 PST 2011


Hi Thu,

 

This looks like a good opportunity to share some things for everyone to
consider when encountering unmet hours... I'd encourage others to read
along!

 

CAUTION:  the files you sent include a 0kB INP file... if it isn't too
late, you should save a copy in a new location if you still have your
project open!

 

That said, the files you did send included a SIM report file from which
I can suggest a few things.  

 

Scrolling through the space temperature summary (SS-O), you have some
very different distributions of binned hours between the zones... many
are floating higher (into the 85+ range) for much of the year...  SS-R
suggests the problem is not isolated to any particular zone/system (I
would normally verify this in my own models using the airside summary
tab after a simulation).

 

A few things catch my eye: 

*         You have a fan schedule for at least one system with zeroes
entered through the work day... I can tell you are trying to define
"residential" and "non-residential" scheduling for different spaces
under the same project... but be very careful you aren't mis-applying
any such system & load scheduling in this sense or you'll have a lot of
cooling that will not be served because your fans are simply off.  The
inverse applies for those systems whose fans are noted "off" in the
evening.  A review of your night-setback inputs may worth your time as
well.

*         As an extension of the first bullet:  Looks like you are
trying to define a cooling setback temperature of 104 degrees using your
zone cooling schedule... check whether that really makes sense.  A
~30-degree differential is going to be tough for any non-oversized
system to catch up with if the building should float far beyond the set
point.

*         Another reason your systems might have trouble keeping up:
this is not necessarily "wrong," but fractional schedules for things
like plug loads and occupancy ordinarily lie in-between 0 and 100% for
an energy model.  Case in point:  100% misc equipment loads and
occupancy for all occupied hours is likely exacerbating the unmet
cooling hour situation (consider these items as an internal heat load),
and may simultaneously be a reason  you have zero unmet heating hours to
consider at the moment although the reports are cautioning you
extensively on the topic of heating capacities...  

 

Not an exhaustive review, but may help you identify a few stumbling
blocks.  If you wish to re-engage the list with your files in the
future, I'd advise including your weather file and ensuring your INP
file is not empty.  

 

Best of luck!

 

~Nick

 

 

 

NICK CATON, P.E.

SENIOR ENGINEER

 

Smith & Boucher Engineers

25501 west valley parkway, suite 200

olathe, ks 66061

direct 913.344.0036

fax 913.345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Thu
Nguyen - Indochine Engineering
Sent: Sunday, November 06, 2011 10:44 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Supporting to review detail project

 

Dear all users, 

 

I'm modeling a project like the attached, with included: office for
staff, dormitory for expert, canteen kitchen for expert and worker. 

 

I'm already fix the schedule for each system following as their properly
schedule. But the unmet hour result still high, out of allowance. 

 

Please would you have a favor to review this modeling and instruct for
me, the detail reason make this wrong. 

 

Thanks so much and hope to see your feedback soon.

 

Regards,

Thu Nguyen

 

Indochine Engineering Vietnam Ltd

Unit 5, 8th Floor, A&B Tower, 76 Le Lai Street

District 1, HCMC, Vietnam

 

Mobile:  +84 (0) 985 277 099 

Tel:  +84 (8) 6290 9400 Ext 300

Fax: +84 (8) 6290 9406

 

Web: www.indoeng.com <http://www.indoeng.com/> 

Skype
<mailto:tien at indoeng.com?subject=Feedback%20on%20ICE%20Quality%20System>
: huongthu.nguyen

 

Annex:

Ho Chi Minh                            Ha Noi
Da Nang

5F FAFILM Bldg                     Suite 429, 4F, Regus Press Club
6F Indochina Riverside Tower Bldg

6 Thai Van Lung St                  59 Ly Thai To St
74 Bach Dang St

District 1, HCMC, Vietnam      Hoan Kiem District, Ha Noi, Vietnam
Hai Chau District, Da Nang, Vietnam

Tel:  +84 (8) 6290 9400           Tel:  +84 (4) 3936 7926
Tel:  +84 (511) 222 1200

Fax: +84 (8) 6290 9406            Fax: +84 (4) 3936 8069
Fax: +84 (511) 222 1201

 

Email us for any feedback on Indochine Engineering
<blocked::mailto:carl at indoeng.com?subject=Feedback%20on%20ICE%20Quality%
20System> 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111107/bac53521/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111107/bac53521/attachment.jpeg>


More information about the Equest-users mailing list