[Equest-users] Sizing runs in baseline model
Mark Darrall
MDarrall at a2so4.com
Fri May 27 12:40:40 PDT 2011
Thanks, David. I could have been more clear. The sub-meter first came up when we discussed our big exhaust hood / makeup air unit. They wanted to see that energy shown as process energy. Later in the discussion, and this is where my notes got fuzzy - task lighting and receptacle loads got mentioned as process energy - I don't know if they asked that those be put on the sub-meter too or not.
Here's what I'm looking at
[cid:image005.png at 01CC1C84.6C76D650][cid:image010.png at 01CC1C84.6C76D650][cid:image002.png at 01CC1C83.009CA0A0][cid:image003.png at 01CC1C83.009CA0A0][cid:image006.jpg at 01CC1C84.6E457BD0]
[cid:image007.png at 01CC1C83.5C205CA0][cid:image009.jpg at 01CC1C84.6E457BD0]
[cid:image013.png at 01CC1C84.6C76D650][cid:image016.jpg at 01CC1C84.6E457BD0]
Meter EM1-A is my sub-meter. All three dialogs are in the same zone. If I switch "Task Lighting" and "Elec Equipment" to EM1-A, will eQUEST automatically assign the numbers circled above to this meter? I can't see a way to assign loads to a meter within the zone internal loads dialogs...
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
[cid:image001.jpg at 01CC1C82.87A622C0]
DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL 317 388 8850
FAX 317 280 0692
MOB 765 749 0841
www.a2so4.com
Please consider the environment before printing this e-mail.
CONFIDENTIALITY NOTICE: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient, you may not review, copy or distribute this message. If you have received this email in error, please notify the sender immediately and delete the original message. Neither the sender nor the company for which he or she works accepts any liability for any damage caused by any virus transmitted by this email.
From: David Eldridge [mailto:dse at grummanbutkus.com]
Sent: Friday, May 27, 2011 3:22 PM
To: Mark Darrall
Cc: equest-users
Subject: RE: Sizing runs in baseline model
I think it shows up pretty clearly as "miscellaneous equipment" end-use in the eQuest reports, so I'm not sure why they asked you about the submeter, unless there was some inquiry about splitting up components of the process load...I think it is an unneeded step, but you'll have to work that out with the reviewer as to why they asked specifically for it.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Mark Darrall [mailto:MDarrall at a2so4.com<mailto:MDarrall at a2so4.com>]
Sent: Friday, May 27, 2011 2:05 PM
To: David Eldridge
Cc: equest-users
Subject: RE: Sizing runs in baseline model
Hi!
I got the unmet hours fixed in my baseline model. I think it had something to do with the return air path - I had switched them from ducted to plenum (to match design case because I didn't see an App. G requirement for it) but had them as unconditioned.
Back to the sub-metering question. I missed this in my discussion with the review team -would it make sense to put ALL the process power on the sub-meter as a way to directly see it? Seems that way to me. For our project process power includes:
* Receptacles (office equipment and task lights)
* Refrigeration
* Cooking
I don't think there are any difficulties in assigning these to the sub-meter. I see there are places to directly assign them in the meter properties - is there a risk of duplicating / double-counting them if they're also entered at the zone / system inputs?
Thanks, all. Have a great Memorial Day weekend and take a moment to thank a Vet!
MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2061 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 605 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 214 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 618 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 214 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 614 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 1959 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 30394 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 33832 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016.jpg
Type: image/jpeg
Size: 49415 bytes
Desc: image016.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/4b1e8e70/attachment-0003.jpg>
More information about the Equest-users
mailing list