[Equest-users] Low-E Window Film
Raphael, Dan
draphael at IDS-TROY.COM
Fri May 27 10:32:59 PDT 2011
I tried the window film again in eQuest, but this time I applied the film to the inside instead of the outside in order to trap the heat in the building. It looks like this has done the trick and both the electricity and natural gas consumptions have decreased. Thanks for the help, everybody!
Dan Raphael
Building Performance Analyst
Integrated Design Solutions
Architecture, Engineering, Interiors & Technology
1441 W. Long Lake, Suite 200
Troy, Michigan 48098
tel: 248.823.2171
fax: 248.823.2200
www.ids-troy.com <http://www.ids-troy.com/>
<http://www.energystar.gov/>
From: MattDubrovich at Eaton.com [mailto:MattDubrovich at Eaton.com]
Sent: Friday, May 27, 2011 1:14 PM
To: danielk at arborus.ca; Mike.McAardle at state.vt.us
Cc: equest-users at lists.onebuilding.org; Raphael, Dan
Subject: RE: [Equest-users] Low-E Window Film
Low-e films reflect heat back into the space based on their emissivity so you can expect heating savings even with a lower SHGC.
I’d expect Window5 to include the correct emissivity and for that to be passed through the glass definition to eQuest. Is the film on the correct surface in Window5? If you were entering your glass in eQuest using the simplified method you would have to change the emissivity manually.
Though this is from the manufacture, it’s still an interesting read: http://www.enerlogicfilm.com/pdf/EnerLogic-White-Paper.pdf
Matt Dubrovich
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daniel Knapp
Sent: Friday, May 27, 2011 9:23 AM
To: McArdle, Mike
Cc: equest-users at lists.onebuilding.org; Dan Raphael
Subject: Re: [Equest-users] Low-E Window Film
On 2011-05-27, at 11:05 AM, McArdle, Mike wrote:
Dan, Do You mean decreasing the heat load ( not increasing )
If the solar heat gain is reduced in winter, less heat from the sun will enter the windows and the heating load will be increased.
Thank you, Sincerely,
Michael J. McArdle , P.E.
Buildings Engineer II, Project Manager
State of Vermont,
Buildings and General Services (BGS)
2 Governor Aiken Avenue
Montpelier, Vt. 05633
Office: 802-828-5650; cell: 802-272-4828
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daniel Knapp
Sent: Friday, May 27, 2011 11:01 AM
To: Raphael, Dan
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Low-E Window Film
How does the film affect the U-value and the SHGC for the window? It sounds like the film is reducing the solar heat gain coefficient, and increasing the heating load. You should also keep in mind that outdoor air loads can dominate the heating load in winter and that envelope effects can be minimal depending on the climate and type of building. You may want to look into the loads reports in the SIM file to see what effects the film has on the building cooling and heating loads.
Cheers,
Dan
—
Daniel Knapp, PhD, LEED® AP O+M
danielk at arborus.ca
Arborus Consulting
Energy Strategies for the Built Environment
www.arborus.ca <http://www.arborus.ca/>
76 Chamberlain Avenue
Ottawa, ON, K1S 1V9
Phone: (613) 234-7178 ext. 113
Fax: (613) 234-0740
On 2011-05-27, at 10:42 AM, Raphael, Dan wrote:
Has anybody successfully modeled window film installation using eQuest? Specifically, I am trying to model the Vista EnerLogic low-e film (since it is eligible for tax incentives). I’ve used Optics5/Window5 to construct the glass type using the EnerLogic applied film (NFRC ID# 2545) and imported that into eQuest. When I test this retrofit in a sample building, the savings are not what I expect (~65 yr. payback, assuming $7 installed cost). I would expect to see a payback somewhere around 10-15 years. What bothers me is that in the model, the heating load increases, which would be expected for a typical window film, but this film claims to have savings in all seasons due to the ability to trap heat in the building. If anybody has had any success in modeling these window films and could provide me with step-by-step instructions or any guidance, it’d be greatly appreciated.
Thanks!
Dan Raphael
Building Performance Analyst
Integrated Design Solutions
Architecture, Engineering, Interiors & Technology
1441 W. Long Lake, Suite 200
Troy, Michigan 48098
tel: 248.823.2171
fax: 248.823.2200
www.ids-troy.com <http://www.ids-troy.com/>
<image001.png> <http://www.energystar.gov/>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/e3b98d9c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3562 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110527/e3b98d9c/attachment.png>
More information about the Equest-users
mailing list