This error seems to come from screen 14 in the Shell Wizards if one or
more zones is not assigned to a zone group.  When you copy an existing
shell, it seems like the zone group assignments are not copied (which,
if you think about it, makes sense).  On the screen shown below, make
sure all of your zones are green in one of the zone groups in your model
and the error should go away.  That is, it solved the error for me the
only time I have seen it so far.

 

 

 

Jeremy R. Poling, PE, LEED AP+BDC



 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Caton
Sent: Friday, May 20, 2011 10:35 AM
To: ashok singh; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Error-shellwiz has no valid ZNgRPwIZ
Children

 

Ashok,

 

I haven't seen these particular errors before, but it appears your
wizard-tier inputs are awry... are you currently in wizard edit mode
(SD/DD) or detailed edit mode?

 

May have been caused by trying to copy the shell in an unconventional
manner (like editing the PRD)...  I've also known conflicting/impossible
geometries to cause eQuest to choke up and corrupt input data in both
detailed and wizard modes, on occasion...  or else maybe the program
just randomly hiccupped at the wrong time?

 

If possible, I'd save a separate copy, try to delete the new offending
shell (preferably inside, but otherwise outside of the program within
the .INP/.PRD), and see if that makes the errors go away.  Then I'd try
copying the shell again - but feel free to share the procedure you're
following to see if others can identify a problem.

 

~Nick 

 

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of ashok
singh
Sent: Friday, May 20, 2011 5:33 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Error-shellwiz has no valid ZNgRPwIZ Children

 

 

Dear all,

 i am modeling a building, which has 8 floor. 5-8 floor are similar.
when itry to copy 5th floor shell for making 6th floor shell, it shows
error "shellwiz has no valid ZNgRPwIZ Children" same as i attached the
screenshot.

 

Plz guide me how should i resolve it.

Thanks

Regards

Ashok Singh Tanwar

M.Tech (Energy engg.)

 

 




-- 
your's-
Ashok SinghTanwar
(THE PERSON  WITH  INFINITE HORIZON)

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110520/f5501d5e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 30683 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110520/f5501d5e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110520/f5501d5e/attachment.jpeg>


More information about the Equest-users mailing list