[Equest-users] Appendix G Baseline Systems 1 and 2 efficiency

Bishop, Bill wbishop at pathfinder-ea.com
Wed May 18 06:51:45 PDT 2011


Jeremy,

Can a child component (COOLING-EIR) reference the keyword value of
another child component (COOLING-CAPACITY) of the same parent?

In the case I'm describing, there is no keyword value for
COOLING-CAPACITY, since it is calculated by the program, not entered. Is
there any way to reference program output with a user input function?

Thanks,

Bill

 

From: Jeremy Poling [mailto:Jeremy.Poling at transwestern.net] 
Sent: Tuesday, May 17, 2011 11:52 PM
To: Dahlstrom, Aaron; Bishop, Bill; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Appendix G Baseline Systems 1 and 2
efficiency

 

Have you thought about using a "user input function" to define the EIR?
I haven't used one this way yet, but there are a few examples out there
in the help info.  In theory, you could setup a logic statement that
checks the capacity and uses the EIR value appropriate for that size
system.  I'd be willing to discuss the idea with you guys, but there'll
be a certain amount of "if at first you don't succeed..." involved to
figure out the right code to grab the system capacity.

 

I've been playing more with user input functions after seeing some
examples of powerful ways they can remove some of the repetitive
changes.  For example, for single-zone systems, you could theoretically
program eQuest to auto-calculate the OA based on ASHRAE 62.1
requirements and the zone area and population.  You could probably do it
for multi-zone systems also, but that gets into the complexity level of
the ASHRAE 62.1 spreadsheet and it is probably less time to just do the
calcs in the spreadsheet and input the results.

 

Jeremy R. Poling, PE, LEED AP+BDC

 

________________________________

From: equest-users-bounces at lists.onebuilding.org on behalf of Dahlstrom,
Aaron
Sent: Tue 5/17/2011 10:31 PM
To: Bishop, Bill; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Appendix G Baseline Systems 1 and 2
efficiency

Bill:

 

Your procedure sounds very similar to ours.

 

Beyond the simple automation of a spreadsheet, and dual monitors to copy
data from SIM to XLS quickly, we haven't found any quicker ways to skin
this cat.

 

Aaron Dahlstrom , PE, LEED(r) AP

In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102 

d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
215-735-7290

e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/>  | akf web: www.akfgroup.com
<http://www.akfgroup.com/> 

 

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Tuesday, May 17, 2011 3:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G Baseline Systems 1 and 2 efficiency

 

Appendix G Baseline Systems 1 (PTAC) and 2 (PTHP) have cooling
efficiencies (and for PTHP, heating efficiencies) that vary with cooling
capacity per Table 6.8.1D. Since each thermal block is modeled with its
own system, you can end up modeling as many as 100 or more systems per
project. For LEED projects (or other App. G models), I have been
calculating and manually entering values for cooling EIR for every
single system, based on capacities reported in the SV-A reports. I
factor in the unique fan power (per G3.1.2.9) for each system and remove
its contribution from the efficiency, since fan power is included in EER
and needs to be separated per G3.1.2.1. Once you enter efficiency for
each system, just about any change you make in the model changes the
supply flow rate and/or system capacities, which means you need to redo
all the efficiency calculations.

 

Does this method seem correct?

Has anyone figured out a way to automate this process? (And by
"automate", I don't mean give it to the intern.)

 

Thanks,

Bill

 

 

 


This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended
recipient of this e-mail, do not duplicate or redistribute it by any
means. Please delete it and any attachments and notify the sender that
you have received it in error. Unintended recipients are prohibited from
taking action on the basis of information in this e-mail. E-mail
messages may contain computer viruses or other defects, may not be
accurately replicated on other systems, or may be intercepted, deleted
or interfered without the knowledge of the sender or the intended
recipient. If you are not comfortable with the risks associated with
e-mail messages, you may decide not to use e-mail to communicate with In
Posse. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/88690d41/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110518/88690d41/attachment.jpeg>


More information about the Equest-users mailing list