Because the unit is discharging the relief air and not individual room
exhaust fans, you should leave all exhaust fans out of the picture. Make
sure you set the unit to be minimum of 1.00 ratio of outdoor air as well, to
ensure that the unit is 100% OA.
I would also check your elevation coefficient, this could be the cause of
the increased supply air numbers you are seeing (but for the rather large
increase you are seeing, something else may be causing issues as well). I
typically see values less than 10% for elevation values (at 1.10, would make
your 7,500 cfm unit become 8,250 cfm).
I'm sure others will have good ideas as well.
-Rob
On Tue, May 17, 2011 at 7:59 AM, Brad Robinson <brad.robinson at yahoo.com>wrote:
> Sorry for all of the questions recently on this list, but this is the first
> serious modelling attempt I am trying with eQuest.
>
> I have a constant volume, 100% OA unit serving patient rooms and corridors
> in a long term care facility. I have set the airflow for the unit at 7,500
> cfm. When I look at the SV-A report, the airflow is showing at 9,090 cfm.
> I then tried going into each individual sub-zone and setting the airflows.
> The sub-zones airflows in the SV-A report are higher than what I have
> entered, and the total airflow still remains at 9,090. I am thinking perhaps
> I have picked the wrong system. I assumed I could use a packaged single
> zone for this case. Perhaps I should be using a different system type?
>
> The other part of the question is how do I model the fact that is 100% OA?
> Th only reasonable solution I have found is to have the exhaust air in each
> zone track the supply flow. It is also asking for either static pressure
> and efficiency, or kw/cfm. As the exhaust is at the unit itself via heat
> recovery using a heat pipe, I am not sure what I should be entering here, as
> the fan details would be entered at the unit itself. Thanks in advance for
> any help.
>
> Brad Robinson
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110517/7c5b98c2/attachment.htm>
More information about the Equest-users
mailing list