Sabmhav,

 

I find that the overhang and left/right fins allowed for each window
take care of most of shading I encounter. You can use building shades
for anything else. Building shades might even make more sense if you
have a single continuous overhang that shades several windows, or if the
shade is non-opaque.

 

   

 

Regards,

Bill

 

 

-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg
Collins
Sent: Tuesday, May 10, 2011 3:21 PM
To: sambhav tiwari; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Exterior Shades

 

There is no standard formula for doing this.  A correction factor for
the SHGC could be calculated, but this factor would change significantly
depending on geographic location (sun angles), and would not give you
accurate results at an hourly level (accurate for annual only).  If
you're trying to avoid modeling all of the shades, you could pick one
typical window for each exposure to model, and apply those results to
all of them, but I'd recommend against that.  

 

This is when modeling geometries in Revit comes in handy ;) 

 

Greg Collins

GLUMAC | (949) 833-8190

 

 

-----Original Message-----

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sambhav
tiwari

Sent: Tuesday, May 10, 2011 4:38 AM

To: equest-users at lists.onebuilding.org

Subject: [Equest-users] Exterior Shades

 

Hi All,

           My Glazing is having exterior shade from all four side it

is like 2 overhangs one at top and other at bottom of glazing and two

side  fins. is this any formula to calculate reduction in shgc value

by all four shades as it is just by one  overhang.

 

 

Thanks

Sambhav

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110510/52f86749/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20821 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110510/52f86749/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 34834 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110510/52f86749/attachment-0001.jpeg>


More information about the Equest-users mailing list