Okay,

 

Thanks for all of the feedback - great discussions. Here is a copy of a
typical floor (the middle floor of three). The ground floor has a small
library and student center. I have also included a screen shot of the zoning
pattern for the west side which is for one half of the building as well as a
copy of the zoning for the east side first floor which has the library and
student center. The east side second and third floors are similar to the
west side. The building has several fume hoods.

 



 



 

 



 

Regards,

 

Jeffrey G Ross-Bain, PE, LEED AP, BEMP

404-228-2893 office 

404-408-2577 mobile
www.rbgb.com

  _____  

From: Arpan Bakshi [mailto:arpanbakshi at gmail.com] 
Sent: Wednesday, May 04, 2011 7:09 PM
To: Jeremy Poling
Cc: Paul Diglio; Jeff Ross-Bain; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Thermal Blocks

 

Jeff

 

Your query has generated a lot of discussion. Please attach the following
for your benefit--

 

1. Screenshot of your baseline equest zoning

2. Architectural floor plan

 

 

On Wed, May 4, 2011 at 6:26 PM, Jeremy Poling
<Jeremy.Poling at transwestern.net> wrote:

Maybe this helps the definition debate (apologies for the length, but some
things require more words to described).  Section 2 in ASHRAE 90.1-2007
gives the following definitions:

 

Space: an enclosed space within a building. (It goes on to define the
different types of spaces, conditioned, semi-heated, etc., but those don't
seem to be of concern for this discussion).

 

Zone: a space or group of spaces within a building with heating and cooling
requirements that are sufficiently similar so that desired conditions (e.g.
temperature) can be maintained throughout using a single sensor (e.g.,
thermostat or temperature sensor).

 

Thermal Block: a collection of one or more HVAC zones grouped together for
simulation purposes.  Spaces need not be contiguous to be combined within a
single thermal block.

 

Appendix G goes on to set up rules as to how to determine a thermal block in
Table G3.1(7):

 

Where HVAC zones are defined on HVAC design drawings, each HVAC zone shall
be modeled as a separate thermal block.  Exception: Different HVAC zones may
be combined to create a single thermal block or identical thermal blocks to
which multipliers are applied, provided that all of the following conditions
are met:

a. The space use classification is the same throughout the thermal block.

b. All HCAV zones in the thermal block that are adjacent to glazed exterior
walls face the same orientation or their orientations vary by less than 45
degrees.

c. All of the zones are served by the same HVAC system or by the same kind
of HVAC system.

 

 

The Users Manual has additional explanation on how to put together thermal
blocks.  For the purposes of the LEED reviewers comment, don't forget that
they are not assessing your use of the software you chose for the model,
they are assessing whether you complied with Appendix G correctly.  The
specific comment issued is related to G3.1.1 of ASHRAE 90.1-2007
specifically.  I couldn't tell from the screen capture if this was the case,
but based on the comment I would assume that the reviewer agrees with you
that your baseline system is one of the systems numbered 1-4.  They are
expecting to see a separate system modeled per thermal block.

 

To address eQuest definitions, the DOE-2.2 Volume 2: Definitions classifies
the "SPACE" keyword as an Envelope Component and more specifically,
something the LOADS portion of the software uses to determine the loads to
impose on a system.  the "ZONE" keyword is defined as an HVAC Component used
by the HVAC portion of the software to determine the system and plant
operating responses to loads in the building.  Very specifically, the ZONE
keyword definition states:

 

"Each zone is associated with one and only one SYSTEM command, which
specifies the system to which the zone belongs. This applies to conditioned
zones as well as unconditioned zones and plenum zones. Note that there must
be a one-to-one match-up between the zones specified here and the spaces
specified in the LOADS program. That is, for each SPACE command in LOADS
there will be a corresponding ZONE command to represent a physically
identical portion of the building."

So you can see from the definitions in eQuest and in ASHRAE 90.1-2007 that
the software is really not concerned with how many spaces are in a zone.  It
relies on the modeler and HVAC designer to ensure that they have
appropriately zoned the building.

 

In addition, I wouldn't interpret the reviewers comment as questioning your
zoning at all: they specifically are asking that the model include 1 system
per thermal block.  Unless you are using the exception (and it is an
exception) that allows multiple zones to be combined into the same thermal
block, this means that you will have one eQuest zone per system.  

 

For my personal interpretation: all of the wording in ASHRAE 90.1-2007 in
G3.1.1 and Table G3.1 really points to systems 1-4 being single-zone systems
and systems 5-8 being multi-zone systems.  If you have a building that is
non-residential, 3 floors or less, and less than 25,000 SF in real life, it
would seem more probable that this building has single-zone systems and that
larger buildings have multi-zone systems.  The system-per-floor requirement
seems to match my experience as to how most mid-rise and high-rise office
buildings are designed: one air handling unit per floor serving a primary
duct system that terminal units in the tenant space connect to.

 

Jeremy R. Poling, PE, LEED AP+BDC

 

  _____  

From: equest-users-bounces at lists.onebuilding.org on behalf of Paul Diglio

Sent: Wed 5/4/2011 4:46 PM
To: Jeff Ross-Bain; equest-users at lists.onebuilding.org


Subject: Re: [Equest-users] Thermal Blocks

 

Jeff:

I've seen some of the other e-mails from the forum and I do not agree with
the terminology other people are using, i.e. space v. zone v. thermal block.
Some of these replies are exceedingly long and contradictory.

Let's leave 'thermal block' out of the discussion.   Take one floor of an
office building.  The baseline would usually require one HVAC unit for this
floor per 90.1.  I would create zones in the wizard for each large office
space, the restroom, the utility rooms, the corridor and elevator lobby.  I
would use the same procedure that you used below to add these zones to the
HVAC system.  Having the separate zones allows you to adjust the airflow and
temperatures to the individual zones and also to find out where unmet hours
might be occurring.

As an example of my understanding of a thermal block, say the office
building has 8 floors and each elevator lobby is supplied by the same common
HVAC system.  I would zone each lobby as described above and add them to the
elevator lobby HVAC system.  This is a thermal block because it is a
collection of spaces that share the same system and space characteristics.

Paul Diglio

 

 

  _____  

From: Jeff Ross-Bain <jeff at rbgb.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Sent: Wed, May 4, 2011 9:39:19 AM
Subject: RE: [Equest-users] Thermal Blocks

Hi Paul,

So you establish individual zones in the building footprint window (2) and
discriminate between corridors, classrooms. but what about all the little
closets, odd offices here and there, rest rooms, mechanical rooms, meeting
rooms, etc.? It seems that the zoning patterns would then become a
nightmare. In your Zone Group Definitions window (14) you would then assign
the same system to each of those zones? Here is a screen shot of a zoning
pattern. I have used this approach for years:

 



 

 

 

Jeffrey G Ross-Bain, PE, LEED AP, BEMP

404-228-2893 office 

404-408-2577 mobile
www.rbgb.com <http://www.rbgb.com/> 

  _____  

From: Paul Diglio [mailto:paul.diglio at sbcglobal.net] 
Sent: Wednesday, May 04, 2011 9:21 AM
To: Jeff Ross-Bain; equest-users
Subject: Re: [Equest-users] Thermal Blocks

 

Jeff:

ASHRAE 90.1 allow spaces of similar thermal characteristics to be combined
in thermal blocks.  I do not include what you call support spaces because
the load and occupancy is much different than, say a classroom.  I would
define the corridor as a separate zone within the thermal block but served
by the same HVAC system.  This allows you to have a different set-point,
airflow, occupancy and schedules for the corridor.

You do not have to define a separate shell for each block, you can define
the block by custom zones in the wizard.

I divide up a thermal block into as many reasonable zones as possible.  This
allows me to find out which area of the thermal block is causing any unmet
heating or cooling hours.  It also allows me to change the HVAC system
control zone to that zone which is the hardest to satisfy in the summer and
winter.  These zones can be served by a single HVAC system.

For a proposed model that needs to conform to an actual design, defining
multiple zones per thermal block allows you to balance the airflow to zones
that have unmet hours without increasing the overall airflow of the HVAC
system.  I define the zonal airflow in the Zone tab.  I reduce the airflow
to the zones without any unmet hours and increase the airflow to those zones
that have unmet hours.  I do not define the total fan CFM in the Airside
Systems tab.

What were the comments from the LEED reviewer?

Paul Diglio

 

 

  _____  

From: Jeff Ross-Bain <jeff at rbgb.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Wed, May 4, 2011 9:05:15 AM
Subject: [Equest-users] Thermal Blocks

Hi All,

 

Are there any additional discussions out there regarding thermal blocks
besides what is in ASHRAE Standard 90.1 and the User's Guide? I have
received comments back from a LEED reviewer that seems to reflect an
interpretation of that concept which I have not seen before.

 

In a nutshell, does each thermal block require a separate shell with
individual HVAC system? I understand the concept of having individual
thermal blocks or combining these if they are similar space use categories.
I am assuming then that the similar space use categories (say a college
classroom building) can also include support spaces such as corridors,
storage spaces, faculty offices, etc. 

 

So if several thermal blocks are combined into one, can they not be served
by a single, similar type of HVAC system?

 

I hope that I have made myself clear and many thanks for your thoughts and
comments.

 

Regards,

 

Jeffrey G Ross-Bain, PE, LEED AP, BEMP

404-228-2893 office 

404-408-2577 mobile
www.rbgb.com <http://www.rbgb.com/> 


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




-- 

 

 

Arpan Bakshi  LEED AP BD+C

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110505/d019581f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 43818 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110505/d019581f/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 25323 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110505/d019581f/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20663 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110505/d019581f/attachment-0002.jpeg>