Hi Brad!

 

RE: source of the problem,  The only other thing to check that comes to
mind is to make sure you're following your footprint perimeter vertices
exactly when you define your zones... if you're just a little off eQuest
may assume the associated surfaces are interior instead of exterior.  It
may help to make extra vertices along the footprint perimeter for the
zones to snap to.

 

You can correct in detailed using the same principle as the reverse
process:  Right click the space in question in the tree during the 3D
view, create new exterior wall, then select a polygon and/or set points
that match the offending interior wall.  Delete the interior wall and
you're done!

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brad
Robinson
Sent: Wednesday, May 04, 2011 3:21 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] (no subject)

 

I have looked through the email archive and found a number of examples
on how to convert an exterior wall into an interior, but I seem to have
the opposite problem -  I need to make an internal wall exterior.  I
have run across this a few times when testing eQuest.  I inexplicably
end up with one exterior wall showing up as interior in my model.  In
The DD wizard, I have tried right clicking on the wall and, but it
already shows up as exterior.  Has anyone else had this problem, or know
how to force it to an exterior wall?  A better question is why does this
happen?



Thanks.


Brad Robinson

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110504/61119960/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110504/61119960/attachment.jpeg>


More information about the Equest-users mailing list