[Equest-users] Thermal Blocks

Paul Diglio paul.diglio at sbcglobal.net
Wed May 4 06:20:32 PDT 2011


Jeff:

ASHRAE 90.1 allow spaces of similar thermal characteristics to be combined in 
thermal blocks.  I do not include what you call support spaces because the load 
and occupancy is much different than, say a classroom.  I would define the 
corridor as a separate zone within the thermal block but served by the same HVAC 
system.  This allows you to have a different set-point, airflow, occupancy and 
schedules for the corridor.

You do not have to define a separate shell for each block, you can define the 
block by custom zones in the wizard.

I divide up a thermal block into as many reasonable zones as possible.  This 
allows me to find out which area of the thermal block is causing any unmet 
heating or cooling hours.  It also allows me to change the HVAC system control 
zone to that zone which is the hardest to satisfy in the summer and winter.  
These zones can be served by a single HVAC system.

For a proposed model that needs to conform to an actual design, defining 
multiple zones per thermal block allows you to balance the airflow to zones that 
have unmet hours without increasing the overall airflow of the HVAC system.  I 
define the zonal airflow in the Zone tab.  I reduce the airflow to the zones 
without any unmet hours and increase the airflow to those zones that have unmet 
hours.  I do not define the total fan CFM in the Airside Systems tab.

What were the comments from the LEED reviewer?

Paul Diglio





________________________________
From: Jeff Ross-Bain <jeff at rbgb.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Wed, May 4, 2011 9:05:15 AM
Subject: [Equest-users] Thermal Blocks

 
Hi All,
 
Are there any additional discussions out there regarding thermal blocks besides 
what is in ASHRAE Standard 90.1 and the User’s Guide? I have received comments 
back from a LEED reviewer that seems to reflect an interpretation of that 
concept which I have not seen before.
 
In a nutshell, does each thermal block require a separate shell with individual 
HVAC system? I understand the concept of having individual thermal blocks or 
combining these if they are similar space use categories. I am assuming then 
that the similar space use categories (say a college classroom building) can 
also include support spaces such as corridors, storage spaces, faculty offices, 
etc. 

 
So if several thermal blocks are combined into one, can they not be served by a 
single, similar type of HVAC system?
 
I hope that I have made myself clear and many thanks for your thoughts and 
comments.
 